Honeywell Process Solutions
DR4500A Truline Circular Chart
Recorder With or Without Control
Product Manual
Doc. No.: 44-45-25-30
Release: P
Last Revision Date: April 2017
ii DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Notices and Trademarks
Copyright 2017 by Honeywell
Release P April 2017
WARRANTY/REMEDY
Honeywell warrants goods of its manufacture as being free of defective materials and faulty
workmanship. Contact your local sales office for warranty information. If warranted goods are
returned to Honeywell during the period of coverage, Honeywell will repair or replace without
charge those items it finds defective. The foregoing is Buyer's sole remedy and is in lieu of all other
warranties, expressed or implied, including those of merchantability and fitness for a particular
purpose. Specifications may change without notice. The information we supply is believed to be
accurate and reliable as of this printing. However, we assume no responsibility for its use.
While we provide application assistance personally, through our literature and the Honeywell web
site, it is up to the customer to determine the suitability of the product in the application.
Honeywell Process Solutions
1250 W Sam Houston Pkwy S
Houston, TX 77042
DR4500 Truline is a U.S. registered trademark of Honeywell.
Other brand or product names are trademarks of their respective owners.
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual iii
April 2017
About This Document
Revision Information
Document ID
44-45-25-30
Document Name
DR4500A Truline Circular Chart Recorder With or Without Control Product Manual
Revision #
Publication Date
N
February 2017, (Daughterboard info updated in parts list)
P
April 2017, Range values table (7.2) updated, Aux Output only spare part added
References
The following list identifies all documents that may be sources of reference for material discussed in this
publication.
Document Title
Doc ID
How to Apply Digital Instrumentation in Severe Electrical
Noise Environments
51-52-05-01
Modbus® RTU Serial Communications User Manual
51-52-25-66
Modbus® RTU Serial Communications User Manual
Configuration Interface for DR4500
51-52-25-69
iv DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Support and Contact Information
For Europe, Asia Pacific, North and South America contact details, refer to the back page of this manual or
the appropriate Honeywell Solution Support web site:
Honeywell Corporate: www.honeywellprocess.com
Honeywell Process Solutions: https://www.honeywellprocess.com/*
Honeywell Circular Recorders: https://www.honeywellprocess.com/circular-chart-recorders/
Telephone and Email Contacts
Organization
Phone Number
Honeywell Inc.
1-800-343-0228 Customer Service
1-800-423-9883 Global Technical Support
Honeywell Process Solutions
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual v
April 2017
Symbol Definitions
The following table lists those symbols used in this document to denote certain conditions.
Symbol
Definition
This CAUTION symbol on the equipment refers the user to the Product Manual for
additional information. This symbol appears next to required information in the manual.
WARNING: risk of electrical shock. This symbol warns the user of a potential shock
hazard where HAZARDOUS LIVE voltages greater than 30 Vrms, 42.4 Vpeak, or 60
VDC may be accessible.
ATTENTION, Electrostatic Discharge (ESD) hazards. Observe precautions for
handling electrostatic sensitive devices
Protective Earth (PE) terminal. Provided for connection of the protective earth (green
or green/yellow) supply system conductor.
Functional earth terminal. Used for non-safety purposes such as noise immunity
improvement. NOTE: This connection shall be bonded to protective earth at the
source of supply in accordance with national local electrical code requirements.
Earth Ground. Functional earth connection. NOTE: This connection shall be bonded to
Protective earth at the source of supply in accordance with national and local electrical
code requirements.
Chassis Ground. Identifies a connection to the chassis or frame of the equipment shall
be bonded to Protective Earth at the source of supply in accordance with national and
local electrical code requirements.
vi DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Contents
1. Overview ........................................................................................ 1
1.1 Introduction ........................................................................................................ 1
Function .................................................................................................................................1
CE Conformity (Europe) .........................................................................................................1
Microprocessor controlled recording and printing ...................................................................1
Digital controller .....................................................................................................................2
Construction ...........................................................................................................................2
1.2 Operator Interface ............................................................................................. 3
Operator interface ..................................................................................................................3
Key functions ..........................................................................................................................4
1.3 Set-up Tasks ..................................................................................................... 5
Major set-up tasks ..................................................................................................................5
2. Installation ...................................................................................... 7
2.1 Overview ............................................................................................................ 7
Introduction ............................................................................................................................7
What’s in this section? ...........................................................................................................7
Pre-installation information .....................................................................................................7
CE Conformity special conditions (Europe) ............................................................................7
Operating limits and condensed specifications ......................................................................8
2.2 Model Number Interpretation ........................................................................... 13
Model number ...................................................................................................................... 13
Example of model number decoding .................................................................................... 14
Location of hardware components ....................................................................................... 14
View of hardware components ............................................................................................. 15
2.3 Mounting Considerations and Overall Dimensions ......................................... 16
Physical considerations ........................................................................................................ 16
Overall dimensions ............................................................................................................... 16
2.4 Mounting Methods ........................................................................................... 17
Introduction .......................................................................................................................... 17
How to remove knockouts for conduits ................................................................................ 17
Mounting flush in panel (New panel cutout) ......................................................................... 18
Reference data for existing panel cutouts ............................................................................ 19
Adapter plate dimensions ..................................................................................................... 19
Mounting flush in panel (using universal filler plate kit) ........................................................ 20
Mounting flush in panel (using cutout made for Kent Model 105M) ...................................... 21
Panel mounting recorder with NEMA4X door ....................................................................... 22
Mounting on a 2-inch pipe .................................................................................................... 24
Mounting on surface (of panel or wall) ................................................................................. 25
2.5 Wiring Prerequisites ........................................................................................ 27
Taking electrical noise precautions ...................................................................................... 27
Electrical considerations ...................................................................................................... 27
Recorder grounding ............................................................................................................. 27
Functional earth ................................................................................................................... 27
CE conformity special conditions (Europe) .......................................................................... 27
Permissible wire bundling..................................................................................................... 28
Identify your wiring requirements ......................................................................................... 28
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual vii
April 2017
2.6 Input Wiring Procedures .................................................................................. 29
Wiring the recorder ............................................................................................................... 29
Ferrite filter locations (CE Mark) ........................................................................................... 29
Shield Wiring ........................................................................................................................ 29
AC line power ....................................................................................................................... 30
Thermocouple, RTD, Radiamatic, mV, or 0-5 Vdc inputs ..................................................... 33
4-20 mA inputs and transmitter power ................................................................................. 35
0-10 Volt dc inputs ............................................................................................................... 37
2.7 Output Wiring Procedures ............................................................................... 39
4-20 mA control output wiring............................................................................................... 39
Position proportional or 3-position step control output wiring ............................................... 41
Relay control output wiring ................................................................................................... 43
2.8 Option Wiring Procedures ............................................................................... 45
Alarm output and digital input wiring .................................................................................... 45
Additional alarm wiring information ...................................................................................... 47
Wiring for alarm outputs #3, 4, 5, and 6 ............................................................................... 49
RS485 Modbus communications wiring ............................................................................... 50
4-20 mA auxiliary output wiring ............................................................................................ 52
2.9 Lockout Switch Configuration .......................................................................... 54
Introduction .......................................................................................................................... 54
Restrictions based on lockout switch position ...................................................................... 54
3. Configuration ................................................................................ 55
3.1 Overview .......................................................................................................... 55
Introduction .......................................................................................................................... 55
What’s in this section? ......................................................................................................... 55
Prompts ................................................................................................................................ 56
3.2 Configuration Prompts ..................................................................................... 57
Diagram: prompt hierarchy ................................................................................................... 57
3.3 How To Get Started ......................................................................................... 60
Read the configuration tips................................................................................................... 60
Read configuration procedure .............................................................................................. 60
Set Up groups ...................................................................................................................... 60
Parameter explanations or definitions .................................................................................. 60
Configuration record sheet ................................................................................................... 60
3.4 Configuration Tips ........................................................................................... 61
Introduction .......................................................................................................................... 61
3.5 Configuration Procedure ................................................................................. 62
Introduction .......................................................................................................................... 62
Procedure............................................................................................................................. 62
3.6 Input Set Up Group.......................................................................................... 64
Introduction .......................................................................................................................... 64
Function prompts ................................................................................................................. 64
3.7 Pen Set Up Group ........................................................................................... 66
Introduction .......................................................................................................................... 66
Function prompts ................................................................................................................. 66
3.8 Chart Set Up Group ......................................................................................... 67
Introduction .......................................................................................................................... 67
Function prompts ................................................................................................................. 67
3.9 Time Set Up Group.......................................................................................... 69
Introduction .......................................................................................................................... 69
Function prompts ................................................................................................................. 69
viii DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
3.10 Totalizer Set Up Group .................................................................................... 70
Introduction .......................................................................................................................... 70
Function prompts ................................................................................................................. 70
3.11 Input Algorithm Set Up Group ......................................................................... 72
Introduction .......................................................................................................................... 72
Function prompts ................................................................................................................. 72
3.12 Control Set Up Group ...................................................................................... 73
Introduction .......................................................................................................................... 73
Function prompts ................................................................................................................. 73
3.13 Tuning Parameters Set Up Group ................................................................... 75
Introduction .......................................................................................................................... 75
Function prompts ................................................................................................................. 75
3.14 SP Ramp Set Up Groups ................................................................................ 76
Setpoint Ramp ..................................................................................................................... 76
Setpoint Rate ....................................................................................................................... 76
Setpoint Program ................................................................................................................. 76
Function prompts ................................................................................................................. 76
3.15 Timer Set Up Group ........................................................................................ 77
Introduction .......................................................................................................................... 77
Function prompts ................................................................................................................. 77
3.16 Alarms Set Up Group ...................................................................................... 78
Introduction .......................................................................................................................... 78
Priority of functions that operate relays ................................................................................ 78
Function prompts ................................................................................................................. 79
3.17 Auxiliary Output Set Up Group ........................................................................ 80
Introduction .......................................................................................................................... 80
Function prompts ................................................................................................................. 80
3.18 Modbus Communications Set Up Group ......................................................... 81
Introduction .......................................................................................................................... 81
Function prompts ................................................................................................................. 81
3.19 Options Set Up Group ..................................................................................... 82
Introduction .......................................................................................................................... 82
Function prompts ................................................................................................................. 82
3.20 Event Message Configuration ......................................................................... 83
Introduction .......................................................................................................................... 83
Function prompts ................................................................................................................. 83
3.21 Lockout Set Up Group ..................................................................................... 86
Introduction .......................................................................................................................... 86
Function prompt ................................................................................................................... 86
3.22 Adjust Printing ................................................................................................. 87
Introduction .......................................................................................................................... 87
Function prompt ................................................................................................................... 87
3.23 Configuration Record Sheet ............................................................................ 88
Keep a record ....................................................................................................................... 88
4. Configuration Parameter Definitions ............................................. 93
4.1 Overview .......................................................................................................... 93
Introduction .......................................................................................................................... 93
Parameter groups and prompts............................................................................................ 93
What’s in this section? ......................................................................................................... 93
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual ix
April 2017
4.2 Input Parameters Set Up Group ...................................................................... 94
Introduction .......................................................................................................................... 94
Input group prompts ............................................................................................................. 94
4.3 Pen Parameters Set Up Group ....................................................................... 98
Introduction .......................................................................................................................... 98
Pen 1-2-3-4 group prompts .................................................................................................. 98
4.4 Chart Parameters Set Up Group ................................................................... 100
Introduction ........................................................................................................................ 100
Chart group prompts .......................................................................................................... 100
4.5 Time Parameters Set Up Group .................................................................... 103
Introduction ........................................................................................................................ 103
Time group prompts ........................................................................................................... 103
4.6 Total Parameters Set Up Group .................................................................... 104
Introduction ........................................................................................................................ 104
Totalizer 1 and 2 group prompts ........................................................................................ 104
4.7 Input Algorithm Set Up Group ....................................................................... 106
Introduction ........................................................................................................................ 106
Prompts .............................................................................................................................. 106
4.8 Control Parameters Set Up Group ................................................................ 109
Introduction ........................................................................................................................ 109
Control group prompts ....................................................................................................... 109
4.9 Tuning Parameters Set Up Group ................................................................. 118
Introduction ........................................................................................................................ 118
Tuning group prompts ........................................................................................................ 118
4.10 Setpoint Ramp Set Up Group ........................................................................ 121
Introduction ........................................................................................................................ 121
Single Setpoint Ramp ........................................................................................................ 121
Setpoint Rate ..................................................................................................................... 121
Setpoint Program ............................................................................................................... 121
Setpoint Ramp/ Program group prompts ............................................................................ 121
4.11 Timer Set Up Group ...................................................................................... 123
Introduction ........................................................................................................................ 123
Timer group prompts .......................................................................................................... 123
4.12 Alarms Set Up Group .................................................................................... 124
Introduction ........................................................................................................................ 124
Priority of functions that operate relays .............................................................................. 124
Alarms group prompts ........................................................................................................ 125
4.13 Auxiliary Output Set Up Group ...................................................................... 127
Introduction ........................................................................................................................ 127
Timer group prompts .......................................................................................................... 127
4.14 Modbus Communications Set Up Group ....................................................... 129
Introduction ........................................................................................................................ 129
Communications group prompts ........................................................................................ 129
4.15 Options Set Up Group ................................................................................... 130
Introduction ........................................................................................................................ 130
Options group prompts ....................................................................................................... 130
4.16 Event Message Set Up Group ....................................................................... 132
Introduction ........................................................................................................................ 132
Event Message group prompts .......................................................................................... 132
x DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
4.17 Lockout Parameters Set Up Group ............................................................... 133
Introduction ........................................................................................................................ 133
Set this group last .............................................................................................................. 133
Lockout group prompts ...................................................................................................... 133
4.18 Printing Characteristics Adjustments ............................................................. 134
Introduction ........................................................................................................................ 134
Configuration choices ......................................................................................................... 134
Printing characteristics adjustments ................................................................................... 134
Printing characteristics adjustments procedure .................................................................. 135
5. Operation ................................................................................... 136
5.1 Overview ........................................................................................................ 136
Introduction ........................................................................................................................ 136
What’s in this section? ....................................................................................................... 136
5.2 Start-up .......................................................................................................... 137
Preparation......................................................................................................................... 137
Diagnostic tests .................................................................................................................. 137
Test failures........................................................................................................................ 137
Troubleshooting ................................................................................................................. 137
Check the displays and keys .............................................................................................. 138
Key error ............................................................................................................................ 138
Start-up procedure ............................................................................................................. 138
5.3 Monitoring Your Recorder ............................................................................. 141
Introduction ........................................................................................................................ 141
Operator interface .............................................................................................................. 141
Meaning of indicators ......................................................................................................... 142
Reading the deviation bargraph ......................................................................................... 143
Viewing the operating parameters ...................................................................................... 144
Diagnostic error messages................................................................................................. 145
Alarm and tuning messages ............................................................................................... 146
5.4 Operator Functions ........................................................................................ 147
Actions an operator can initiate .......................................................................................... 147
CHN indicator ..................................................................................................................... 147
5.5 Operating Modes ........................................................................................... 148
Available modes ................................................................................................................. 148
Mode definitions ................................................................................................................. 148
What happens when you change modes ........................................................................... 148
Selecting manual or automatic mode ................................................................................. 148
Position proportional backup mode .................................................................................... 149
5.6 Setpoints ........................................................................................................ 150
Introduction ........................................................................................................................ 150
Selecting the setpoint source ............................................................................................. 150
Changing the local setpoints .............................................................................................. 150
Switching between setpoints .............................................................................................. 150
Setpoint selection indication ............................................................................................... 151
5.7 Single Setpoint Ramp .................................................................................... 152
Configuring the setpoint ramp ............................................................................................ 152
Procedure........................................................................................................................... 152
Running the setpoint ramp ................................................................................................. 153
Procedure........................................................................................................................... 153
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual xi
April 2017
5.8 Using Two Sets of Tuning Constants (PID Values) ...................................... 155
Introduction ........................................................................................................................ 155
Select two sets ................................................................................................................... 155
Set switchover value .......................................................................................................... 155
Set tuning constant values for each set ............................................................................. 156
Switch between two sets via the keyboard (without automatic switchover) ........................ 157
5.9 Using Accutune II .......................................................................................... 158
Introduction ........................................................................................................................ 158
Starting and Stopping Tuning with Accutune II ................................................................... 158
Using Accutune with Duplex (Heat/Cool) Control ............................................................... 159
Procedure........................................................................................................................... 159
5.10 Alarm Setpoints ............................................................................................. 161
Introduction ........................................................................................................................ 161
Procedure for displaying the alarm setpoints ..................................................................... 161
5.11 Three Position Step Control Algorithm .......................................................... 162
Introduction ........................................................................................................................ 162
Estimated motor position .................................................................................................... 162
Displaying the motor position ............................................................................................. 162
Power up output ................................................................................................................. 162
5.12 Digital Input Option (Remote Switching) ....................................................... 163
Introduction ........................................................................................................................ 163
Action on contact closure ................................................................................................... 163
Keyboard operation ............................................................................................................ 163
5.13 Resetting and Displaying Totalizer Value ..................................................... 164
Introduction ........................................................................................................................ 164
Resetting the totalizer locally.............................................................................................. 164
Resetting the totalizer using the Wake Time feature .......................................................... 164
External totalizer reset ....................................................................................................... 165
Displaying the totalizer value.............................................................................................. 165
5.14 Monitoring the External Event Operation ...................................................... 166
Event pen function ............................................................................................................. 166
Event pen operation ........................................................................................................... 166
5.15 Maximizing Pen Life ...................................................................................... 167
Steps for maximizing pen life ............................................................................................. 167
5.16 Routine Maintenance .................................................................................... 168
Introduction ........................................................................................................................ 168
Cleaning the pen tip ........................................................................................................... 168
Replacing a burned-out chart lamp (optional) .................................................................... 168
5.17 Installing/Replacing Chart ............................................................................. 169
Installing/replacing chart procedure ................................................................................... 169
5.18 Chart Operation ............................................................................................. 170
Normal operation ................................................................................................................ 170
Remote chart operation ...................................................................................................... 171
Recovery from a power loss ............................................................................................... 171
6. Setpoint Ramp/Soak Programming and Operation .................... 172
6.1 Overview ........................................................................................................ 172
Introduction ........................................................................................................................ 172
What’s in this section? ....................................................................................................... 173
xii DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
6.2 Setpoint Program Contents ........................................................................... 174
What you will configure ...................................................................................................... 174
Recycle number ................................................................................................................. 174
Guaranteed soak ................................................................................................................ 174
Profile number .................................................................................................................... 174
Program state ..................................................................................................................... 174
Recovery ............................................................................................................................ 174
Program End State ............................................................................................................. 174
Profile Start and Profile End ............................................................................................... 175
Ramp unit ........................................................................................................................... 175
Ramp time or rate segments .............................................................................................. 175
Soak segments .................................................................................................................. 175
Segment Events ................................................................................................................. 175
Digital input (remote) operation .......................................................................................... 176
6.3 Drawing a Ramp/Soak Profile ....................................................................... 177
Ramp/soak profile example ................................................................................................ 177
Profile graphs ..................................................................................................................... 179
Profile 1 .............................................................................................................................. 179
Profile 2 .............................................................................................................................. 179
Profile 3 .............................................................................................................................. 180
Profile 4 .............................................................................................................................. 180
Profile 5 .............................................................................................................................. 181
Profile 6 .............................................................................................................................. 181
6.4 Entering the Setpoint Program Data ............................................................. 182
Introduction ........................................................................................................................ 182
6.5 SP RAMP1 and SP RAMP2 Set Up Group ................................................... 184
Introduction ........................................................................................................................ 184
SP RAMP prompts ............................................................................................................. 184
SP RAMP 1 and SP RAMP 2 worksheet ............................................................................ 184
6.6 Setpoint Program Profiles Set Up Group ...................................................... 186
Introduction ........................................................................................................................ 186
Setpoint program profiles group prompts ........................................................................... 186
Setpoint program profiles worksheet .................................................................................. 187
6.7 Setpoint Program Segments Set Up Group .................................................. 188
Introduction ........................................................................................................................ 188
Setpoint program segments group prompts ....................................................................... 188
Setpoint program segments worksheet .............................................................................. 189
6.8 Setpoint Program Event Set Up Group ......................................................... 191
Introduction ........................................................................................................................ 191
How to trigger a relay with a segment event ...................................................................... 191
Setpoint Program Event group prompts ............................................................................. 191
Example of how a segment event works ............................................................................ 191
To ensure control of relay by segment event ..................................................................... 192
Setpoint program events worksheet ................................................................................... 193
6.9 Run/Monitor the Program .............................................................................. 195
Introduction ........................................................................................................................ 195
Run/Monitor functions ........................................................................................................ 195
7. Input Calibration ......................................................................... 197
7.1 Overview ........................................................................................................ 197
Introduction ........................................................................................................................ 197
What’s in this section? ....................................................................................................... 197
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual xiii
April 2017
7.2 Restoring Factory Calibration ........................................................................ 198
How to restore it ................................................................................................................. 198
Procedure........................................................................................................................... 198
7.3 Minimum and Maximum Range Values......................................................... 200
Select the range values ...................................................................................................... 200
7.4 Preliminary Information ................................................................................. 202
Disconnect the field wiring.................................................................................................. 202
Equipment needed ............................................................................................................. 203
7.5 Calibration Set Up and Wiring for PV Inputs ................................................. 204
Jumper positions ................................................................................................................ 204
Thermocouple input calibration methods ........................................................................... 205
General set up procedure .................................................................................................. 205
Thermocouple inputs using an ice bath .............................................................................. 206
Thermocouple inputs using a compensated calibrator method .......................................... 207
Thermocouple inputs using the ambient temperature method ........................................... 208
RTD (Resistance Thermometer Device) inputs .................................................................. 209
Radiamatic, millivolts, and volts inputs (except 010 Volts) ............................................... 210
010 Volt inputs ................................................................................................................. 211
420 mA inputs .................................................................................................................. 212
7.6 Calibration Procedure .................................................................................... 213
Introduction ........................................................................................................................ 213
Calibration procedure sequence ........................................................................................ 213
7.7 Printing Characteristics Adjustments ............................................................. 216
Printing characteristics adjustments ................................................................................... 216
8. Output Calibration ...................................................................... 218
8.1 Overview ........................................................................................................ 218
Introduction ........................................................................................................................ 218
What’s in this section? ....................................................................................................... 218
8.2 Current Proportional Output/Aux Out 2 and 3 Calibration ............................. 219
Introduction ........................................................................................................................ 219
Equipment needed ............................................................................................................. 219
Calibrator connections ....................................................................................................... 219
Procedure........................................................................................................................... 220
8.3 Position Proportional and Three Position Step Output Calibration .............. 221
Position proportional control ............................................................................................... 221
3 Position Step control ....................................................................................................... 221
Equipment needed ............................................................................................................. 221
Connections ....................................................................................................................... 221
Auto mode vs manual mode............................................................................................... 221
Rules for auto mode vs manual mode ................................................................................ 221
Displayed values ................................................................................................................ 221
Procedure........................................................................................................................... 221
8.4 Auxiliary Output Calibration ........................................................................... 224
Introduction ........................................................................................................................ 224
Equipment needed ............................................................................................................. 224
Calibrator connections ....................................................................................................... 224
Procedure........................................................................................................................... 225
xiv DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
9. Troubleshooting / Service ........................................................... 226
9.1 Overview ........................................................................................................ 226
Introduction ........................................................................................................................ 226
What’s in this section? ....................................................................................................... 226
Types of problems .............................................................................................................. 226
Installation related problems .............................................................................................. 227
Application related problems .............................................................................................. 227
Hardware and software related problems .......................................................................... 227
9.2 Troubleshooting Aids ..................................................................................... 228
Self diagnostics .................................................................................................................. 228
Visual failure symptoms ..................................................................................................... 228
Check Installation ............................................................................................................... 228
Customer support ............................................................................................................... 228
Determining the software version ....................................................................................... 229
Troubleshooting ................................................................................................................. 229
9.3 Self Diagnostics ............................................................................................. 230
Power-up tests ................................................................................................................... 230
Failsafe .............................................................................................................................. 230
Device status ...................................................................................................................... 231
Error message prompts ...................................................................................................... 232
9.4 Visual Failure Symptoms ............................................................................... 236
Introduction ........................................................................................................................ 236
Symptoms .......................................................................................................................... 236
9.5 Troubleshooting Procedures ......................................................................... 237
Introduction ........................................................................................................................ 237
Equipment needed ............................................................................................................. 237
10. Parts List .................................................................................... 243
10.1 Overview ........................................................................................................ 243
Introduction ........................................................................................................................ 243
What’s in this section? ....................................................................................................... 243
10.2 Exploded Views ............................................................................................. 244
Door assembly ................................................................................................................... 244
Chart plate.......................................................................................................................... 245
Basic recorder components without options ....................................................................... 246
Additional recorder components associated with options ................................................... 248
10.3 Miscellaneous Hardware Kit Contents .......................................................... 251
Kit contents ........................................................................................................................ 251
10.4 Internal Cabling Data ..................................................................................... 252
View of internal cabling ...................................................................................................... 252
10.5 Internal Wiring Diagram Options Only ........................................................ 253
View of internal option wiring.............................................................................................. 253
A. Model DR45AR .......................................................................... 254
A.1 Overview ........................................................................................................ 254
Introduction ........................................................................................................................ 254
What's in this section? ........................................................................................................ 254
A.2 Hardware Identification .................................................................................. 255
Introduction ........................................................................................................................ 255
DR45AR with one input ...................................................................................................... 255
DR45AR with two to four inputs ......................................................................................... 256
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual xv
April 2017
A.3 Fo Reset Configuration ................................................................................. 257
Introduction ........................................................................................................................ 257
Accessing Fo reset prompts ............................................................................................... 257
Function prompts ............................................................................................................... 257
A.4 Options Configuration .................................................................................... 258
Introduction ........................................................................................................................ 258
A.5 Operations Additions ..................................................................................... 260
Introduction ........................................................................................................................ 260
Viewing F
O
sterilization display .......................................................................................... 260
Digital input (REM SW) prompt selection ........................................................................... 260
A.6 Configuration Worksheet Additions ............................................................... 261
Configuration additions ...................................................................................................... 261
B. Model DR45AW .......................................................................... 263
B.1 Overview ........................................................................................................ 263
Introduction ........................................................................................................................ 263
Features ............................................................................................................................. 263
B.2 Installation ..................................................................................................... 264
Field wiring ......................................................................................................................... 264
Pulse output wiring ............................................................................................................. 264
B.3 Configuration ................................................................................................. 265
B.4 Operation ....................................................................................................... 273
B.5 References .................................................................................................... 274
C. Security Lockout ......................................................................... 277
C.1 Overview ........................................................................................................ 277
Introduction ........................................................................................................................ 277
D. Foreign Language Safety Instructions ........................................ 279
D.1 DA2I-6056 ..................................................................................................... 279
UDSTYRS SPECIFIKATIONER ......................................................................................... 279
OMGIVELSES SPECIFIKATIONER .................................................................................. 279
UDSTYRS INSTALLATION................................................................................................ 279
D.2 DU2I-6056 ..................................................................................................... 280
APPARATUUR VOORWAARDEN ..................................................................................... 280
OMGEVINGSCONDITIES.................................................................................................. 280
MONTAGE VAN DE APPARATUUR ................................................................................. 280
D.3 FI2I-6056 ....................................................................................................... 281
LAITTEEN VAATIMUKSET ................................................................................................ 281
KÄYTTÖOLOSUHTEET .................................................................................................... 281
LAITTEEN ASENNUS ........................................................................................................ 281
D.4 FR2I-6056 ...................................................................................................... 282
CARACTERISTIQUES DE L'EQUIPEMENT ..................................................................... 282
CONDITIONS AMBIANTES ............................................................................................... 282
INSTALLATION DE L'EQUIPEMENT ................................................................................ 282
D.5 GE2I-6056 ..................................................................................................... 283
AUSRÜSTUNGSDATEN.................................................................................................... 283
UMGEBUNGSBEDINGUNGEN ......................................................................................... 283
ANBRINGUNG DER AUSRÜSTUNGEN ........................................................................... 283
xvi DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
D.6 GR2I-6056 ..................................................................................................... 284
D.7 IT2I-6056 ....................................................................................................... 285
ALIMENTAZIONE APPARECCHIATURA .......................................................................... 285
CONDIZIONI AMBIENTALI ................................................................................................ 285
INSTALLAZIONE DELL’APPARECCHIO .......................................................................... 285
D.8 NO2I-6056 ..................................................................................................... 286
UTSTYRSPESIFIKASJONER ............................................................................................ 286
D.9 PO2I-6056 ..................................................................................................... 287
ESPECIFICAÇÕES DO EQUIPAMENTO .......................................................................... 287
CONDIÇÕES AMBIENTAIS ............................................................................................... 287
INSTALAÇÃO DO EQUIPAMENTO ................................................................................... 287
D.10 SP2I-6056 ...................................................................................................... 288
DATOS ELECTRICOS DEL EQUIPO ................................................................................ 288
CONDICIONES AMBIENTALES ........................................................................................ 288
INSTALACION DEL EQUIPO ............................................................................................ 288
D.11 SW2I-6056 ..................................................................................................... 289
STRÖMFÖRSÖRJNING .................................................................................................... 289
OMGIVNINGSVILLKOR ..................................................................................................... 289
INSTALLATION .................................................................................................................. 289
Index ................................................................................................... 291
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual xvii
April 2017
Tables
Table 1-1 Function of Keys ......................................................................................................................................... 4
Table 2-1 Operating Limits and Condensed Specifications ......................................................................................... 8
Table 2-2 Procedure to Access Components ............................................................................................................. 14
Table 2-3 Mounting Flush in a New Panel Cutout .................................................................................................... 18
Table 2-4 Reference Data for Mounting DR4500A in Existing Panel Cutouts ......................................................... 19
Table 2-5 Mounting Flush in a Panel Using Universal Filler Kit .............................................................................. 20
Table 2-6 Mounting Flush in a Panel Using Kent Model 105M Cutout .................................................................... 21
Table 2-7 Procedure for Mounting Recorder with NEMA4X Door .......................................................................... 22
Table 2-8 Pipe Mounting Procedure .......................................................................................................................... 24
Table 2-9 Mounting Flush on a Surface (of Panel or Wall) ....................................................................................... 25
Table 2-10 Permissible Wiring Bundling .................................................................................................................. 28
Table 2-11 AC Line Power Wiring............................................................................................................................ 31
Table 2-12 Thermocouple, RTD, Radiamatic, mV, or 05 Vdc Input Wiring .......................................................... 33
Table 2-13 4-20 mA Input Wiring ............................................................................................................................. 35
Table 2-14 0-10 Volt dc Input Wiring ....................................................................................................................... 37
Table 2-15 4-20 mA Control Output Wiring ............................................................................................................. 39
Table 2-16 Position Proportional Control Output Wiring ......................................................................................... 41
Table 2-17 Relay Control Output Wiring .................................................................................................................. 43
Table 2-18 Alarm Output or Digital Input Wiring ..................................................................................................... 45
Table 2-19 Alarm 3 and Alarm 4 Output Wiring ...................................................................................................... 47
Table 2-20 Alarm 5 and Alarm 6 Output Wiring ...................................................................................................... 48
Table 2-21 RS485 Modbus Communications Wiring................................................................................................ 50
Table 2-22 4-20 mA Auxiliary Output Wiring .......................................................................................................... 52
Table 3-1 Configuration Tips .................................................................................................................................... 61
Table 3-2 Configuration Procedure ........................................................................................................................... 62
Table 3-3 Input Group Function Prompts .................................................................................................................. 64
Table 3-4 Pen 1, 2, 3, 4 Group Function Prompts ..................................................................................................... 66
Table 3-5 Chart Group Function Prompts ................................................................................................................. 67
Table 3-6 Time Group Function Prompts .................................................................................................................. 69
Table 3-7 Totalizer Group Function Prompts ............................................................................................................ 70
Table 3-8 Input Algorithm Group Function Prompts ................................................................................................ 72
Table 3-9 Control 1 or Control 2 Group Function Prompts ....................................................................................... 73
Table 3-10 Tuning 1 or Tuning 2 Group Function Prompts ...................................................................................... 75
Table 3-11 SP Ramp 1 or 2 Group Function Prompts ............................................................................................... 76
Table 3-12 Timer Group Function Prompts............................................................................................................... 77
Table 3-13 Priority of functions that operate relays .................................................................................................. 78
Table 3-14 Alarms Group Function Prompts............................................................................................................. 79
Table 3-15 Auxiliary Output Group Function Prompts ............................................................................................. 80
Table 3-16 Modbus Communications Group Function Prompts ............................................................................... 81
Table 3-17 Options Group Function Prompts ............................................................................................................ 82
Table 3-18 Event Message Group Function Prompts ................................................................................................ 83
Table 3-19 Lockout Group Function Prompts ........................................................................................................... 86
Table 3-20 Adjust Group Function Prompts .............................................................................................................. 87
Table 4-1 Input Group Definitions ............................................................................................................................ 94
Table 4-2 Pen 1, 2, 3, or 4 Group Definitions............................................................................................................ 98
Table 4-3 Chart Parameters Group Definitions ....................................................................................................... 100
Table 4-4 Time Parameters Group Definitions ........................................................................................................ 103
Table 4-5 Totalizer Group Definitions .................................................................................................................... 104
Table 4-6 Input Algorithm Group Definitions ......................................................................................................... 106
Table 4-7 Control 1 or 2 Group Definitions ............................................................................................................ 109
Table 4-8 Tuning Group Prompt Definitions ........................................................................................................... 118
Table 4-9 Setpoint Ramp 1 or 2 Group Definitions ................................................................................................. 121
Table 4-10 Timer Group Definitions ....................................................................................................................... 123
xviii DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Table 4-11 Priority of functions that operate relays ................................................................................................. 124
Table 4-12 Alarms Group Definitions ..................................................................................................................... 125
Table 4-13 Auxiliary Output Group Definitions ..................................................................................................... 127
Table 4-14 Modbus Communications Group Definitions ........................................................................................ 129
Table 4-15 Option Group Definitions ...................................................................................................................... 130
Table 4-16 Event Message Group Definitions......................................................................................................... 132
Table 4-17 Lockout Group Definitions ................................................................................................................... 133
Table 4-18 Printing Characteristics Adjustment Procedure ..................................................................................... 135
Table 5-1 Power Up Diagnostic Tests ..................................................................................................................... 137
Table 5-2 Procedure for Testing the Displays and Keys ......................................................................................... 138
Table 5-3 Procedure for Starting Up the Recorder .................................................................................................. 139
Table 5-4 Meaning of Indicators ............................................................................................................................. 142
Table 5-5 Lower Display Key Parameter Prompts .................................................................................................. 144
Table 5-6 Error Messages ........................................................................................................................................ 145
Table 5-7 Alarm and tuning messages ..................................................................................................................... 146
Table 5-8 Operating Mode Definitions .................................................................................................................... 148
Table 5-9 Changing Operating Modes ..................................................................................................................... 148
Table 5-10 Procedure for Selecting Automatic or Manual Mode ............................................................................ 149
Table 5-11 Procedure for Selecting the Setpoint Source ......................................................................................... 150
Table 5-12 Procedure for Changing the Local Setpoint .......................................................................................... 150
Table 5-13 Procedure for Switching Between Setpoints ......................................................................................... 151
Table 5-14 Setpoint Selection Indication ................................................................................................................. 151
Table 5-15 Procedure for Configuring a Single Setpoint Ramp .............................................................................. 152
Table 5-16 Procedure for Running a Setpoint Ramp ............................................................................................... 153
Table 5-17 Procedure for Selecting Two Sets of Tuning Constants ........................................................................ 155
Table 5-18 Procedure for Setting Switchover Values .............................................................................................. 156
Table 5-19 Procedure for Setting Tuning Constant Values ..................................................................................... 156
Table 5-20 Procedure for Switching PID Sets from the Keyboard .......................................................................... 157
Table 5-21 Procedure for Starting Accutune II ........................................................................................................ 158
Table 5-22 Procedure for Using Accutune for Duplex Control ............................................................................... 159
Table 5-23 Procedure for Displaying or Changing the Alarm Setpoints ................................................................. 161
Table 5-24 Procedure for Displaying the 3PSTEP Motor Position ......................................................................... 162
Table 5-25 Digital Input Option Action on Contact Closure ................................................................................... 163
Table 5-26 Procedure for Resetting the Totalizer .................................................................................................... 164
Table 5-27 Procedure for Displaying the Totalizer Value ....................................................................................... 165
Table 5-28 Maximizing Pen Life ............................................................................................................................. 167
Table 5-29 Cleaning the Pen Tip ............................................................................................................................. 168
Table 5-30 Replacing a Chart Lamp ........................................................................................................................ 168
Table 5-31 Installing/Replacing the Chart ............................................................................................................... 169
Table 5-32 Remote Chart Modes ............................................................................................................................. 171
Table 6-1 Parameter settings for example 12-step profile ....................................................................................... 178
Table 6-2 Setpoint program data entry procedure ................................................................................................... 182
Table 6-3 SP RAMP prompts and available selections ........................................................................................... 184
Table 6-4 Setpoint Program Profiles Group Definitions ......................................................................................... 186
Table 6-5 Setpoint Program Segments Group Definitions ...................................................................................... 188
Table 6-6 Setpoint Program Event Group Definitions............................................................................................. 191
Table 6-7 Segment Event relay operation requirements .......................................................................................... 192
Table 6-8 Run/Monitor Functions ........................................................................................................................... 195
Table 7-1 Restoring Factory Calibration ................................................................................................................. 198
Table 7-2 Voltage and Resistance Equivalents for 0 % and 100 % Range Values .................................................. 200
Table 7-3 Disconnect the Field Wiring .................................................................................................................... 202
Table 7-4 Equipment Needed .................................................................................................................................. 203
Table 7-5 General Set Up Procedure ....................................................................................................................... 205
Table 7-6 Set Up Wiring Procedure for Thermocouple Inputs Using an Ice Bath .................................................. 206
Table 7-7 Set Up Wiring Procedure for Thermocouple Inputs Using a Compensated Calibrator Method .............. 207
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual xix
April 2017
Table 7-8 Set Up Wiring Procedure for Thermocouple Inputs Using the Ambient Temperature Method .............. 208
Table 7-9 Set Up Wiring Procedure for RTD Inputs ............................................................................................... 209
Table 7-10 Set Up Wiring Procedure for Radiamatic, Millivolts, and Volts Inputs (except 0-10 Volts) ................ 210
Table 7-11 Set Up Wiring Procedure for 010 Volt Inputs ..................................................................................... 211
Table 7-12 Set Up Wiring Procedure for 420 mA Inputs ...................................................................................... 212
Table 7-13 Calibration Procedure Sequence ............................................................................................................ 213
Table 8-1 Set Up Wiring Procedure Current Proportional Output/Aux Out 2 and 3 ............................................... 219
Table 8-2 Current Proportional Output/Aux Output 2 and 3 Calibration Procedure ............................................... 220
Table 8-3 Position Proportional and 3 Position Step Output Calibration Procedure ............................................... 222
Table 8-4 Set Up Wiring Procedure Auxiliary Output ............................................................................................ 224
Table 8-5 Auxiliary Output Calibration Procedure ................................................................................................. 225
Table 9-1 Identifying the software version .............................................................................................................. 229
Table 9-2 Power-up tests ......................................................................................................................................... 230
Table 9-3 Displaying the test results ........................................................................................................................ 231
Table 9-4 Error message prompts ............................................................................................................................ 232
Table 9-5 Visual failure symptoms .......................................................................................................................... 236
Table 9-6 Procedure #1Troubleshooting recorder failure symptoms................................................................... 237
Table 9-7 Procedure #2Troubleshooting pen trace failure symptoms ................................................................. 238
Table 9-8 Procedure #3Troubleshooting chart rotation failure symptoms........................................................... 238
Table 9-9 Procedure #4Troubleshooting chart rotation failure symptoms........................................................... 239
Table 9-10 Procedure #5Troubleshooting pen failure symptoms ........................................................................ 239
Table 9-11 Procedure #6Troubleshooting keyboard and/or display failure symptoms ....................................... 239
Table 9-12 Procedure #7Troubleshooting current proportional output failure symptoms ................................... 240
Table 9-13 Procedure #8Troubleshooting position proportional output failure symptoms ................................. 240
Table 9-14 Procedure #9Troubleshooting relay output failure symptoms ........................................................... 241
Table 9-15 Procedure #10Troubleshooting current/time or time/current failure symptoms ................................ 241
Table 9-16 Procedure #11Troubleshooting the auxiliary output ......................................................................... 242
Table 9-17 Procedure #12Troubleshooting external alarm function failure symptoms ....................................... 242
Table 9-18 Procedure #13Troubleshooting Modbus communications ................................................................ 242
Table 10-1 Door assembly parts .............................................................................................................................. 244
Table 10-2 Chart plate assembly parts ..................................................................................................................... 246
Table 10-3 Basic recorder parts without options ..................................................................................................... 247
Table 10-4 Recorder parts associated with options ................................................................................................. 249
Table 10-5 Miscellaneous hardware kit ................................................................................................................... 251
Table A-1 Fo RESET group function prompts ........................................................................................................ 257
Table A-2 Options group function prompts, continued from Section 3/Table 3-17 ................................................ 258
Table A-3 Option group definitions, continued from Section 4/Table 4-15 ............................................................ 259
Table B-1 Input Group Function Prompts ................................................................................................. 265
Table B-2 Input Group Function Prompts, Continued ............................................................................ 266
Table B-3 Input Group Function Prompts, Continued ............................................................................ 267
Table B-4 Input Group Function Prompts, Continued ............................................................................ 268
Table B-5 Additional Totalizer Group Function Prompts ...................................................................... 269
xx DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Figures
Figure 1-1 Operator Interface ...................................................................................................................................... 3
Figure 1-2 Set-up Tasks ............................................................................................................................................... 5
Figure 2-1 Model Number Interpretation .................................................................................................................. 13
Figure 2-2 DR4500A Recorder Hardware Components Versus “Table” Selections ................................................. 15
Figure 2-3 Overall Dimensions ................................................................................................................................. 16
Figure 2-4 How to Remove Knockouts ..................................................................................................................... 17
Figure 2-5 Mounting Flush in a New Panel Cutout ................................................................................................... 18
Figure 2-6 Mounting in a Panel Using Universal Filler Kit....................................................................................... 20
Figure 2-7 Mounting in a Panel using Kent Model 105M Cutout ............................................................................. 21
Figure 2-8 Panel Mounting Recorder with NEMA4X Door ...................................................................................... 23
Figure 2-9 Pipe Mounting Brackets ........................................................................................................................... 24
Figure 2-10 Mounting Flush on a Surface (of Panel or Wall) ................................................................................... 26
Figure 2-11 Ferrite Filter Locations and Shield Wiring (CE Mark) .......................................................................... 30
Figure 2-12 AC Line Power Wiring .......................................................................................................................... 32
Figure 2-13 Thermocouple, RTD, Radiamatic, mV, or 05 Vdc Input Wiring ......................................................... 34
Figure 2-14 4-20 mA Input Wiring............................................................................................................................ 36
Figure 2-15 0-10 Volt dc Input Wiring ...................................................................................................................... 38
Figure 2-16 4-20 mA Control Output Wiring (or Aux Out #2 and #3 Wiring) ......................................................... 40
Figure 2-17 Position Proportional Control Output or Three Position Step Wiring.................................................... 42
Figure 2-18 Relay Control Output Wiring ................................................................................................................. 44
Figure 2-19 Alarm Output or Digital Input Wiring ................................................................................................... 46
Figure 2-20 Alarm outputs #3, 4, 5, and 6 wiring ...................................................................................................... 49
Figure 2-21 RS485 Modbus Communications Wiring .............................................................................................. 51
Figure 2-22 4-20 mA Auxiliary Output #1 Wiring .................................................................................................... 53
Figure 2-23 S1 Lockout Switch Location .................................................................................................................. 54
Figure 3-1 DR4500A Prompt Hierarchy ................................................................................................................... 57
Figure 5-1 Operator Interface .................................................................................................................................. 141
Figure 5-2 Deviation Bargraph ................................................................................................................................ 143
Figure 6-1 Ramp/Soak Profile Example .................................................................................................................. 177
Figure 7-1 Location of the Input Connections on the Input Boards......................................................................... 202
Figure 7-2 Location of Jumper Positions W1/MA and W3 on the Input Boards ..................................................... 204
Figure 7-3 Calibration Set Up Diagram for Thermocouple Inputs Using an Ice Bath ............................................ 206
Figure 7-4 Calibration Set Up Diagram for Thermocouple Inputs Using a Compensated Calibrator Method ........ 207
Figure 7-5 Calibration Set Up Diagram for Thermocouple Inputs using the Ambient Temperature Method ......... 208
Figure 7-6 Calibration Set Up Diagram for RTD Inputs ......................................................................................... 209
Figure 7-7 Calibration Set Up Diagram for Radiamatic, Millivolts, and Volts Inputs (except 0-10 Volts) ............ 210
Figure 7-8 Calibration Set Up Diagram for 010 Volt Inputs ................................................................................. 211
Figure 7-9 Calibration Set Up Diagram for 420 mA Inputs .................................................................................. 212
Figure 8-1 Test Equipment Connections for Calibrating Current Proportional Output ........................................... 219
Figure 8-2 Test Equipment Connections for Calibrating Auxiliary Output ............................................................. 224
Figure 10-1 Door assembly ..................................................................................................................................... 244
Figure 10-2 Chart plate assembly ............................................................................................................................ 245
Figure 10-3 Basic recorder components without options ........................................................................................ 246
Figure 10-4 Recorder components associated with options ..................................................................................... 248
Figure 10-5 Internal cabling for DR4500A Truline recorder................................................................................... 252
Figure 10-6 Internal diagram for DR4500A Truline recorder options only ......................................................... 253
Figure A-1 DR45AR with one input........................................................................................................................ 255
Figure A-2 DR45AR with two to four inputs .......................................................................................................... 256
Figure B-1 Flow RecorderField Wiring ....................................................................................................... 264
Introduction
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual
April 2017
1
1. Overview
1.1 Introduction
Function
The DR4500A Truline Recorder is a one to four-channel microprocessor-based circular chart recorder. Its
"one-pen" stylus printhead produces up to four analog traces and prints alphanumeric chart data on a blank
heat-sensitive chart. All four traces share the same time line reference which the Truline prints. This
eliminates the error caused by pen alignment offsets in conventional pen designs. Since the Truline prints
the chart and generates the analog traces at the same time, there is no error due to variations in chart size
caused by changes in temperature and humidity.
In addition to printing chart records, the Truline recorder alternately displays process variable values for all
channels in the selected engineering units.
Models with up to four input channels accept inputs from any one of a variety of sensors or transmitters
within the configurable range limits.
The Truline is also available with one or two independent digital controllers and setpoint programmers.
CE Conformity (Europe)
Indicated models of this product are in conformity with the protection requirements of the following
European Council Directives: 73/23/EEC, the Low Voltage Directive, and 89/336/EEC, the EMC
Directive. Conformity of this product with any other “CE Mark” Directive(s) shall not be assumed.
Deviation from the installation conditions specified in this manual, and the special conditions for CE
conformity in Subsection 2.1, may invalidate this product’s conformity with the Low Voltage and EMC
Directives.
ATTENTION
The emission limits of EN 61326 are designed to provide reasonable protection against
harmful interference when this equipment is operated in an industrial environment. Operation
of this equipment in a residential area may cause harmful interference. This equipment
generates, uses, and can radiate radio frequency energy and may cause interference to radio
and television reception when the equipment is used closer than 30 meters (98 feet) to the
antenna(e). In special cases, when highly susceptible apparatus is used in close proximity, the
user may have to employ additional mitigating measures to further reduce the electromagnetic
emissions of this equipment.
Microprocessor controlled recording and printing
Both the chart and printhead are driven by stepper motors controlled by the microprocessor with
configurable chart speed through the keypad.
You can configure various "printed" chart data such as range marking in engineering units, digital values
for process variables, and trace identification. This data plus printed time lines and engineering units of
scale eliminate the need to maintain an inventory of a variety of preprinted charts.
The Truline recorder uses a dot fill technique from a microprocessor algorithm to produce a continuous
analog trace of a process variable.
Overview
Introduction
2 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Digital controller
The DR4500A recorder controller includes an integral microprocessor-based, single or dual loop PID
controller with optional setpoint program. A variety of output types, including a duplex variation for heat
cool applications, lets you select the output that is right for your final control element. Accutune II lets you
automatically tune your loops.
You can configure the control action as On-Off, PID-A, PID-B, PD with manual reset, or Three Position
Step. English language prompts guide you through the entry of all the controller's configurable parameters.
Construction
The DR4500A recorder is housed in a molded case which can be panel or surface mounted. A glass or
acrylic windowed door (A UL and FM approved NEMA4X door is also available )protects the internal
components while allowing easy access to the chart and operator interface. An optional external keypad
that allows operator selections without opening the door is available.
Circuitry is partitioned on printed circuit boards for ease of service.
Power, input, and output wiring connect to terminations inside the case. Knockouts in the sides and bottom
of the case accept conduit connections for convenient wire entry.
Overview
Operator Interface
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 3
April 2017
1.2 Operator Interface
Operator interface
Figure 1-1 shows the operator interface and defines the displays and indicators. The function of the keys is
described in Table 1-1.
±1% of control setpoint
Control relay 1 or 2 is
ON, when lit.
ALM
CHN
RSP
OUT
12 FC
%
MAN
12
Lower Display - eight characters
Normal operation - Displays selectable
operating parameters and values. Indicates
diagnostic error messages, alarm condition
for alarms 3-6, Accutune in progress.
Configuration mode - Displays function
group and parameters.
Remote set point or
2nd set point is active,
when lit. Blinks when
2nd setpoint or remote
setpoint is attained
through remote switch
PV displayed is for channel
1, 2, 3, or 4
Alarm condition exists for
alarm 1 or 2, when lit.
Indicates temperature units of PV Upper Display - six characters
Normal operation - Displays process
variable (PV) for selected channels.
Configuration mode - Displays selection or
parameter value.
Indicates controller mode:
MAN = Manual
A = Automatic
Bargraph - deviation (±10% of span)
Center green bar indicates PV is within
.
Next small bar will light if PV is between
±1% but less than ±2% in deviation.
If PV is equal to or greater than ±10%
deviation, the green bar plus all ten small
green bars will light.
1234
Keypad /
Key functions
FUNC
LOWR
DISP
CHART
MAN
AUTO
SET
UP
RUN
HOLD
Figure 1-1 Operator Interface
Overview
Operator Interface
4 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Key functions
Table 1-1 shows each key on the operator interface and defines its function.
Table 1-1 Function of Keys
Key
Function
SET
UP
Places the controller in the Configuration Set Up group select mode. Sequentially
displays Set Up groups and allows the FUNC key to display individual functions in
each Set Up group.
FUNC
Used in conjunction with the SET UP key to select the individual functions of a
selected Configuration Set Up group.
Used to toggle between SP1 and SP2.
Used during field calibration procedure.
LOWR
DISP
Selects an operating parameter to be shown in the lower display:
OUT = Output Value (estimated motor position for 3 Position Step)
SP = Local Setpoint 1
SPN = Current setpoint for setpoint rate applications
2SP = Local Setpoint 2
RSP = Remote Setpoint
1IN = Input 1 (if Loop 1 is a derived PV)
2IN = Input 2
3IN = Input 3
4IN = Input 4
DEV = Deviation
EU = PV Engineering Units
RH = % RH Value
PIDSETX = Tuning Parameter Set X=1 or 2
RAMP = Minutes remaining in Setpoint Ramp
#RA = Minutes remaining in SP Prog Ramp
#SK = Minutes remaining in SP Prog Soak
RECYC = Number of recycles left in SP Program
= Time remaining in Timer function
= Time elapsed in Timer function
TUNExXXX = Accutune II indicator. x = 1 or 2
ATTENTION
The lower display can be configured to scroll through the operating
parameters.
MAN
AUTO
Alternately selects:
AUTO Lower display automatically displays setpoint value in engineering units.
MAN Lower display automatically indicates output in %.
CHART
Used to stop printing operation and move pen to outer limit for chart change.
Display will revert to date and time.
RUN
HOLD
Alternate action switch initiates or holds the Setpoint Ramp or Setpoint Program.
In configuration mode, restores the original value or selection if you do not want to
enter a change you are making to a parameter.
Increases the setpoint, output, or configuration values displayed.
Decreases the setpoint, output, or configuration values displayed.
Overview
Set-up Tasks
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 5
April 2017
1.3 Set-up Tasks
Major set-up tasks
As shown in Figure 1-2, there are four major tasks that you must complete to "Set Up" the DR4500A
recorder for operation. For easy reference the section numbers for each task are shown.
START
Ready for
Operation
1.
2.
4.
3.
Determine your recorder's
hardware components and
software functions
Mount the recorder flush in
a panel, or on the surface
of a panel or a wall
Connect the power and
input/output wiring.
Follow the simple keystroke
sequences and English
language prompts to
"configure" the functional
characteristics of your
recorder.
See Section 2
See Section 2
See Section 2
See Sections 3 & 4
For Model DR45AR, also see Appendix A
21402
Figure 1-2 Set-up Tasks
Overview
Set-up Tasks
6 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Release M DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 7
May 2013
2. Installation
2.1 Overview
Introduction
Installation of the DR4500A Recorder consists of mounting and wiring the recorder according to the
instructions given in this section.
Read the preinstallation information, check the model number interpretation and become familiar with your
model selections, then proceed with installation.
What’s in this section?
This section contains the following information:
Topic
See Page
2.1 Overview
7
2.2 Model Number Interpretation
13
2.3 Mounting Considerations and Overall Dimensions
16
2.4 Mounting Methods
17
2.5 Wiring Prerequisites
27
2.6 Input Wiring Procedures
29
2.7 Output Wiring Procedures
39
2.8 Option Wiring Procedures
45
2.9 Lockout Switch Configuration
54
Pre-installation information
If the recorder has not been removed from its shipping carton, inspect the carton for damage and remove
the recorder. Inspect the unit for any obvious shipping damage and report any damage due to transit to the
carrier.
Make sure a bag containing mounting hardware is included in the carton with the recorder.
Check that the model number shown on the chart plate agrees with what you have ordered.
CE Conformity special conditions (Europe)
Braid shielded twisted pair cables are required for all Analog I/O, Process Variable, RTD, Thermocouple,
dc millivolt, low level signal, 4-20 mA, and relay output circuits. Supplementary bonding of the recorder
enclosure to a local ground, using a 3/4” braided copper conductor, is required. Ferrite suppression filters
and capacitor filters (see Subsection 2.5 for Wiring Prerequisites) shall be installed on all cables connected
to the recorder/controller.
Refer to document 51-52-05-01, How to Apply Digital Instrumentation in Severe Electrical Noise
Environments, for additional installation guidance.
Installation - Overview
8 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Operating limits and condensed specifications
We recommend that you review and adhere to the operating limits listed in Table 2-1 when you install your
recorder.
Table 2-1 Operating Limits and Condensed Specifications
Condition
Specifications
Ambient Temperature
32 °F to 131 °F (0 °C to 55 °C)
Relative Humidity
5 % to 90 % RH at 40 °C (104 °F)
Vibration
Frequency
Acceleration
0 to 200 Hz
0.2 g
Mechanical Shock
Acceleration
Duration
5 g
30 ms
Power
102 Vac to 132 Vac 50/60 Hz
204 Vac to 264 Vac 50/60 Hz
Power Consumption
20 VA maximum
Digital Indication
Accuracy
1 digit
Minimum Input Span
Range is fully configurable with span limitation of the operating range selected.
Input Impedance
4-20 mA dc: 250 ohms
0-10 Vdc: 200K ohms
All others: 10 Megohms
Source Impedance
RTD: 100 ohms per lead maximum
Sampling Rate
Each input sampled 3 times a second (1 or 2 inputs); 3 times in 2 seconds (3 or 4
inputs).
Input Filter
Software: Single pole low pass section with selectable time constants (off to 120
seconds).
Digital Displays
Vacuum fluorescent, alphanumeric.
A six-digit display dedicated to the process variable.
Alternate information displayed during configuration mode.
An eight-digit display shows key selected operating parameters. Also provides
guidance during configuration.
Indicators
Channel PV display (CHN 1, 2, 3, or 4)
Alarm status (ALM 1, 2)
Controller Output (OUT 1, 2)
Remote Setpoint (RSP)
Temperature unit (F or C) or Engineering Units
Controller’s mode (A or MAN)
Deviation Bargraph
21 segment, color coded deviation bargraph:
Green (large) = On Control
Green (small) = Deviation to ± 10 % of PV
Controller Modes of
Operation
Manual Operation
Automatic with local setpoint
Automatic with remote setpoint
Transmitter Supply
Voltage
22 Vdc to 26 Vdc at input terminals (50 mA dc at 24 Vdc)
Installation - Overview
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 9
April 2017
Condition
Specifications
Controller Output
1
(Optional)
Output can be field calibrated between: 3.1 to 21.0 mA
On-Off or Time Proportional
One SPST electromechanical relay. Control action can be set for direct or reverse;
N.O. or N.C. contact selectable.
On-Off Duplex or Time Proportional Duplex
Two SPST electromechanical relays. Control action can be set for direct or reverse;
N.O. or N.C. contact selectable.
Current Proportional
21 mA dc maximum into a negative or positive grounded or non-grounded load of 0
to 1000 ohms. Output range can be set between 4 and 20 mA, and as direct or
reverse action.
Resolution: 10 bits
Accuracy: 0.5 % full scale
FM Approved Output (optional)
Position Proportional and Three Position Step
Two SPST electromechanical relays operate motor having a 100 ohm to 1000 ohm
slidewire.
Current/Time Duplex and Time/Current Duplex
Variation of time proportional duplex for Heat/Cool applications. Time proportional
output (heat or cool) is a SPST electromechanical relay. Current proportional output
(heat or cool) is a 4-20 mA signal that can be fed into a negative or positive
grounded load of 0 to 1000 ohms and is operational over 50 % of range or the
entire range.
Time Proportional Relay Resolution: 4.4 mSec
Relay Contact Ratings:
Resistive Load: 5 A @ 120 Vac, 2.5 A @ 240 Vac
Inductive Load: 50 VA @ 120 Vac or 240 Vac
Cycle Time: 1 second to 120 seconds
Current Proportional:
Resolution: 10 bits
Accuracy: 0.5 % full scale
Auxiliary Output
(Optional)
Output can be field calibrated between: 3.1 to 21.0 mA
21 mA dc maximum into a negative or positive grounded load of 0 to 1000 ohms. The
range can be set between 0 to 21 mA. It can be configured to represent any one of 12
control parameters.
Resolution: 12 bits over 0 to 21 mA
Accuracy: 0.2 % of full scale
Temperature Stability: 0.03 % F.S./°C
Installation - Overview
10 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Types of Input
Actuations
2
Range
Reference Accuracy
Temp Stability ±
Degrees Error Per 1
Degree ∆T
°F
°C
± °F
± °C
Thermocouples
3
B
105 to 3300
105 to 150
150 to 500
500 to 1000
1000 to 3300
41 to 1816
41 to 66
66 to 260
260 to 538
538 to 1815
42.00
14.00
3.00
1.50
23.00
7.70
1.70
0.80
2.00
2.00
0.50
0.20
E
454 to 1832
454 to 202
202 to 1832
270 to 1000
270 to 130
130 to 1000
18.00
1.00
10.00
0.55
0.70
0.35
E (low)
200 to 1100
129 to 593
0.50
0.30
0.20
J
0 to 1600
18 to 871
0.40
0.22
0.06
J (low)
20 to 770
7 to 410
0.20
0.11
0.04
K
320 to 2500
320 to 0
0 to 2500
196 to 1371
196 to 18
18 to 1371
1.25
0.60
0.70
0.35
0.18
0.09
K (low)
20 to 1000
29 to 538
0.30
0.16
0.05
NNM (Ni Ni Moly)
32 to 2500
32 to 500
500 to 2500
0 to 1371
0 to 260
260 to 1371
0.75
0.50
0.40
0.30
0.09
0.07
NIC (Nicrosil-Nisil)
0 to 2372
18 to 1300
1.0
0.55
0.01
R
0 to 3100
0 to 500
500 to 3100
18 to 1704
18 to 260
260 to 1704
2.00
1.00
1.10
0.55
0.25
0.13
S
0 to 3100
0 to 500
500 to 3100
18 to 1704
18 to 260
260 to 1704
2.00
1.00
1.10
0.55
0.23
0.13
T
300 to 700
184 to 371
0.60
0.35
0.07
T (low)
200 to 600
129 to 316
0.40
0.22
0.07
W5W26
0 to 4200
0 to 600
600 to 3600
3600 to 4200
18 to 2315
18 to 316
316 to 1982
1982 to 2315
1.40
1.30
1.60
0.77
0.70
0.90
0.17
0.17
0.29
W5W26 (low)
0 to 2240
0 to 600
600 to 2240
18 to 1227
18 to 316
316 to 1227
1.10
1.00
0.60
0.55
0.14
0.10
Radiamatic
1400 to 3400
760 to 1871
1.00
0.55
0.10
RTD
Platinum
100 ohms
200 ohms (high)
5
200 ohms (low)
5
500 ohms
300 to 900
32 to 752
32 to 392
300 to 900
184 to 482
0 to 400
0 to 200
184 to 482
0.40
0.30
0.20
0.20
0.22
0.16
0.12
0.11
0.05
0.05
0.05
0.05
Installation - Overview
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 11
April 2017
Types of Input
Actuations
2
Range
Reference Accuracy
Temp Stability ±
Degrees Error Per 1
Degree ∆T
°F
°C
± °F
± °C
Linear
Milliamperes dc
Millivolts dc
Volts dc
4 to 20
0 to 10
10 to 50
1 to 5 (can be
calibrated
0 to 5)
0 to 10
0.10 %
0.05 %
0.05 %
0.05 %
0.10 %
0.004 %/°F
0.004 %/°F
0.004 %/°F
0.004 %/°F
0.004 %/°F
Relative Humidity
Platinum 100 ohm
Wet/Dry Bulb*
Wet/Dry Input
130 to 392
90 to 200
0.30
0.03
0.03
% RH
4
Measured
% RH
Dry Bulb Range
Reference
Accuracy
Temp. Stability
53 °F to 104 °F/
12 °C to 40 °C
°F
°C
0 to <20
20 to 100
103 to 212
35 to 40
>40 to 100
100 to 212
75 to 100
2 to 4
>4 to 38
38 to 100
2 % RH
2 % RH
1 % RH
1 % RH
0.11 % RH/°F
0.11 %RH/°F
0.06 % RH/°F
0.03 % RH/°F
Condition
Specifications
Case
Molded, foamed-Noryl** with gasketed door.
A UL and FM approved NEMA4X door is also available.
Chart
12-inch (304.8 mm) diameter chart. Plain thermal-sensitive paper.
Wiring Connections
Terminals inside the case.
Color
Case: Black
Door (standard): Caribbean Blue, Black, or Gray
Approval Bodies
U.L. Approval depending on model. CSA Approval. Consult Model Selection Guide for
information.
FM approved for Class I, Div. 2, Groups A, B, C, D areas depending on model.
Weight
13.2 lbs (6 kg)
Mounting
Panel, 2-inch pipe, or surface mounted. Some adapter kits available for existing panel
cutouts.
OPTIONS
Alarm Output
Two, four, or six relays available.
Relay Contact Ratings:
First Relays, Resistive Load: 1 A @ 120 Vac, 1/2 A @ 240 Vac
Relays 3 through 6, Resistive Load: 5 A @ 120 Vac, 2.5 A @ 240 Vac
Digital Input
+20 Vdc source for external dry contact or isolated solid state contacts. Selects one
configured input.
Totalizers
One to four totalizers depending on model.
Eight digit “totals” with multiplier on digital display; 14 digit totalization printout on
chart.
RS485 Modbus RTU
Communications
Baud rate: 300, 600, 1200, 2400, 4800, 9600,19,200, 38,400
Protocol: RS485 Modbus RTU Communications
Length of Link: 4000 ft (1,219 m) maximum
Link Characteristics: Two-wire, multidrop
Installation - Overview
12 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Condition
Specifications
Calculations
F
o
calculation available on DR45AR, Math function.
Miscellaneous
FM Approved 4-20 mA Control Output
A UL and FM approved NEMA4X door
Door Lock
External Keypad
Chart Illumination
U.L. Listing, CSA Approval, FM Class I Div. 2
Control with Accutune II Tuning capability
Math
Glass or Acrylic Window
Configuration Lockout Switch
Customer ID Tag (30 characters maximum)
Pulse output counter alarm function on DR45AW model
CE Conformity (Europe)
This product is in conformity with the protection requirements of the following
European Council Directives: 73/23/EEC, the Low Voltage Directive, and 89/336/EEC,
the EMC Directive. Conformity of this product with any other “CE Mark” Directive(s)
shall not be assumed.
Product Classification
Class 1: Permanently connected, Panel/Surface Mounted Industrial Control Equipment
with protective earthing (grounding). (EN 61010-1)
Enclosure Rating
Panel/Surface Mounted Equipment, IP 54. (ref. IEC 529)
Installation Category
(Overvoltage Category)
Category II: Energy-consuming equipment supplied from the fixed installation. Local
level appliances, and Industrial Control Equipment. (EN 61010-1)
Pollution Degree
Pollution Degree 2: Normally non-conductive pollution with occasional conductivity
caused by condensation. (ref. IEC 664-10
EMC Classification
Group 1, Class A, ESM Equipment (EN 55011, emissions),
Industrial Equipment (EN 50082-2, immunity)
Method of EMC
Assessment
Technical File (TF)
Declaration of
Conformity
Document #51197639-000
*IEC Alpha () = 0.00385 //°C
**Registered TrademarkGeneral Electric Co.
1
Not all controller outputs are available on all models of the Truline Recorder.
Consult Model Selection Guide for information.
2
Not all Input Actuations are available on all models of the Truline Recorder.
Consult Model Selection Guide for information.
3
Includes reference junction calibration of ±0.01 degrees using standard “ice bath” method of calibration. Factory
calibration at reference ± 1.2 °F. Note that factory calibration may vary by as much as ± 10 microvolts or ± 0.3 ohms
for RTDs, which means recalibration may be required to achieve stated accuracy.
4
The RH calculation is inoperative when temperature goes below 32 °F (0 °C) or above 212 °F (100 °C). However,
the dry bulb temperature will be monitored to 103 °F (75 °C). Accuracy stated is for Classic Series Recorder only,
and does not include remaining system accuracies.
5
Only available with Model DR45AR.
Installation - Model Number Interpretation
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 13
April 2017
2.2 Model Number Interpretation
Model number
The model number interpretation is shown in Figure 2-1. Write the model number into the spaces provided
and compare it to the model number interpretation. This information will also be useful when you wire
your recorder. The example on the next page will help you to decode the model.
Input Actuation (Note 1)
D R 4 5 A 00
0
1
3
=
=
=
None
T/C, RTD, Radiamatic, mV, 0–5V, 4–20mA
0–10 Vdc
External Output
0 0
1 0
1 1
4 0
4 4
5 0
6 0
6 6
= None
= 1 Control Output
= 2 Control Outputs
= 1 Control w/SP Programming
= 2 Controls w/SP Programming
= Pulse Output
= 1 Control Output with FM Approval
= 2 Control Outputs with FM Approval
Table 1 Table 2 Table 3 Table 4 Table 5Key Number
Hardware Options
0 - - - - -
1 - - - - -
E - - - - -
F - - - - -
5 - - - - -
6 - - - - -
Software Options
0
A
B
E
F
H
K
L
M
= None
= Totalization, Input 1
= Math Only
= Totalization, Inputs 1 & 2
= Fo Sterilization Calculation
= Totalization, Inputs 1, 2, 3, & 4
= Totalization, Input 1 + Math
= Totalization, Input 1 and 2 + Math
= Totalization, Input 1, 2, 3, 4 + Math
Table 6
Key Number
T
R
W
H
P
S
=
=
=
=
=
=
Standard Recorder
Relay expansion Recorder
Flow Recorder
HTST
Pasteurization Recorder - Flow
Safety Thermal Limit Recorder
NOTE 1:
Every DR4500A recorder has all the available inputactuations stored in its nonvolatile memory
and can accept up to 4 inputs which must be specified sequentially in 1–4 entries in Table 1.
Therefore, you can easily change the input actuation in the field by re-wiring input connections,
changing the input jumper position, and reconfiguring the input type, as applicable.
Gray door / Glass window
Gray door / Acrylic window
Gray door / Glass window and keypad
Gray door / Acrylic window and keypad
Blue door / Glass window
Blue door / Acrylic window
External Interface
0 – –
1 – –
3 – –
4 – –
– 0 –
– 1 –
– – 0
– – 1
– – 2
– – 3
– – 4
= None
= Auxiliary 4-20 mA Output
= RS485 Modbus RTU**
= RS485 Modbus RTU** plus Auxiliary Output
= Standard Pen
= Abrasion Resistant Pen
= None
= 2 Alarm Outputs/2 Digital Inputs
= 4 Alarm Outputs/2 Digital Inputs
= 6 Alarm Outputs/2 Digital Inputs
= 1 Alarm/1 Timer/2 Digital Inputs **
**Only available with key number DR45AT, AR, AW
=
=
=
=
=
=
L - - - - -
9 - - - - -
Black door / Glass window
Black door / Acrylic window
=
=
P - - - - -
R - - - - -
S - - - - -
NEMA4X door / Glass window
NEMA4X door / Acrylic window
NEMA4X HTST door
=
=
=
- 0 - - - -
- A - - - -
- K - - - -
- - 0 - - -
- - L - - -
- - M - - -
- - N - - -
- - - 0 - -
- - - K - -
- - - L - -
- - - M - -
- - - N - -
- - - P - -
Standard door latch
Keyed latch
Door lock with key
No illumination
Configuration lockout / Chart plate seal
Configuration Lockout / Chart plate seal / Illumination
Chart illumination
No approvals
CE Mark
CE Mark + UL + CSA certification
CE Mark + FM approval
CE Mark + UL + FM / CSA certification
UL listing + CSA certification
=
=
=
=
=
=
=
=
=
=
=
=
=
- - - R - - FM approved - Class 1, Div. 2, Groups A, B, C, D
=
- - - U - -
- - - - 0 -
- - - - T -
- - - - B -
- - - - C -
- - - - D -
- - - - E -
- - - - - 0
- - - - - 1
UL listing + CSA certification + FM approval
No I.D. Tag
Customer I.D. Tag (30 characters maximum)
Certificate of Conformance (F3391)
Custom Calibration / Test Report (F3399)
Certificate of Conformance + I.D. Tag
Customer Calibration + I.D. Tag
None
Product Configuration
=
=
=
=
=
=
=
=
=
Figure 2-1 Model Number Interpretation
Installation - Model Number Interpretation
14 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Example of model number decoding
Assume that the model number on the label is
DR45AT - 1300 - 44 - 001 - A - 1KN0T0 - 0
Using the table code definitions from Figure 2-1, this recorder has the following features and options:
2-input type with thermocouple, RTD, Radiamatic, mV, 0-5 Vdc or 4-20 mA input for channel 1
0-10 Vdc input for channel 2
Two controllers with setpoint programming capability
Alarm output / digital input capability
High speed pen
Totalization for input 1
Gray door with acrylic window
Door lock
Chart illumination
Customer I.D. tag
No approvals
Location of hardware components
After you decode your recorder’s model number, refer to Figure 2-2 to match “table” selections with the
location of actual recorder hardware components. This will help you to determine applicable input / output
wiring requirements, as well as identify appropriate software functions to be configured later.
To access and view the actual components inside your recorder, follow the procedure in Table 2-2.
Table 2-2 Procedure to Access Components
Step
Action
1
Turn the latch on the recorder door and swing the door open.
2
Loosen the captive screw on the right hand side of the chart plate and swing the chart plate
out.
3
Reverse the steps to close the chart plate and door.
Installation - Model Number Interpretation
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 15
April 2017
View of hardware components
Figure 2-2 shows the location of the actual hardware components for key number DR45AT. If key number
is DR45AR, see Appendix A for internal views.
Figure 2-2 DR4500A Recorder Hardware Components Versus “Table” Selections
Installation - Mounting Considerations and Overall Dimensions
16 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
2.3 Mounting Considerations and Overall Dimensions
Physical considerations
The recorder can be mounted in a panel by making a new cutout or using an existing cutout with a filler
plate (see Table 2-4). Use the mounting kit supplied. Adequate access space must be available at the back
of the panel for installation and servicing activities.
The overall dimensions and panel cutout requirements for mounting the recorder are shown in Figure 2-3.
Overall dimensions
Figure 2-3 shows the overall dimensions for mounting the recorder.
321
12.6
17.5
0.69
Bottom view
355
14
419
16.5
Front view
322
12.7
322
12.7
Panel cutout (all models)
163
6.4
196
7.7
370
14.6
181
7.1
Surface mounting
Back view
Dimens ions:
millimeters
inches
Left side view
14.5
.57
Short wing latch :
5
.19
Double
bit
latch
:
321
12.6
142
5.6
106
4.2
Reference
20.3
0.8
387
15.25
438
17.25
Front view
NEMA4X
Standard DR4500
NEMA4X DR4500
321
12.6
17.5
0.69
Bottom view
321
12.6
142
5.6
106
4.2
Reference
20.3
0.8
Surface mounting
Back view
11.0
.43
Figure 2-3 Overall Dimensions
Installation - Mounting Methods
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 17
April 2017
2.4 Mounting Methods
Introduction
There are several methods available for mounting your recorder.
Flush in Panel (new panel cutout)
Flush in Panel (using an existing panel cutout)
using universal filler plate kit
using cutout made for Kent Model 105M
Flush in Panel for recorders with NEMA4 Door
On a 2-inch Pipe
On Surface (of panel or wall)
Procedures for each method follow. Choose the one that meets your mounting requirements. Use the
associated dimension drawings for reference.
How to remove knockouts for conduits
Before you mount the recorder, remove the appropriate “knockouts” in the bottom and/or sides of the
recorder case for wire entry via 1/2" (12.7 mm) conduits. Refer to Figure 2-4 for knockout locations.
ATTENTION
The knockouts are really plugs that you just have to push out to remove.
21405
Side View
Bottom View
Figure 2-4 How to Remove Knockouts
Installation - Mounting Methods
18 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Mounting flush in panel (New panel cutout)
Refer to Figure 2-5 and follow the procedure in Table 2-3 to make a new cutout in a panel and mount your
recorder in the cutout.
Table 2-3 Mounting Flush in a New Panel Cutout
Step
Action
1
At the appropriate location, make a square cutout in the panel measuring 12.7 ± 0.060 inches
by 12.7 ± 0.060 inches (322.58 ± 1.52 by 322.58 ± 1.52 millimeters). See Figure 2-3.
2
Orient the recorder case properly and slide it into the cutout from the front of the panel.
Support the recorder as shown in steps 3 and 4.
3
Refer to Figure 2-5. From the back of the panel, attach a mounting bracket to each side of the
recorder case using a 1/4-20 x 1/2 inch hex screw and a lockwasher for each bracket
(mounting hardware supplied with recorder). Leave the screws slightly loose so you can adjust
the brackets.
4
While holding the recorder firmly against the panel, slide each bracket against the back of the
panel and tighten the screws.
Hex screw,
1/4-20 x
1/2 inch and
washer
21406
Figure 2-5 Mounting Flush in a New Panel Cutout
Installation - Mounting Methods
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 19
April 2017
Reference data for existing panel cutouts
Refer to Table 2-4 to determine whether the existing panel cutout can be used. Use the procedure for
mounting with the universal filler kit unless otherwise noted.
Table 2-4 Reference Data for Mounting DR4500A in Existing Panel Cutouts
Manufacturer / Instrument
Dimensions of Existing
Panel Cutout (inches)
Need Universal Filler
Plate Kit
30755134-001 Blue Color
30755134-002 Gray Color
Honeywell/Model AR100*, DR4200
12.7 x 12.7
No*
Honeywell/Class 15
15.8 x 17.2
Yes
Honeywell/Class 45
13.12 x 17.12
Yes
Badger Meter/Model Micro Chart
14.25 x 17.88
Yes
Bristol/Models 4330, 500 Classes 1, 2A, 3B, and 5
3.56 x 18.56
Yes
Fisher and Porter/Model 51-1100
13.75 x 17.31
Yes
Foxboro/Model 40
14.38 x 17.06
Yes
Kent/Model 105M**
13.6 x 13.46
No**
Partlow/Model ER*
13.5 x 12.69
No*
Taylor/Model 76J
13.78 x 16.5
Yes
*No adaptation is required, use procedure for “Flush in Panel - New Panel Cutout”
**Use procedure for “Cutout made for Kent Model 105M”
Adapter plate dimensions
The dimensions of the adapter plate (part number 30755134) are 16.5” x 19”.
Installation - Mounting Methods
20 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Mounting flush in panel (using universal filler plate kit)
Refer to Figure 2-6 and follow the procedure in Table 2-5 to mount your recorder in an existing cutout
using the Universal Filler Kit.
Table 2-5 Mounting Flush in a Panel Using Universal Filler Kit
Step
Action
1
Lay the recorder face down on a clean work surface and position the universal filler plate as
shown in Figure 2-6.
2
Measure the height of the existing panel cutout.
3
Refer to Figure 2-6. Position the support brackets, supplied with the kit, so that the distance
from the top of the “window” in the filler plate to the right angle of the support brackets is just
less than the height of the existing panel cutout.
4
Secure brackets with two 10-32 x 1/4 inch screws, provided in the kit, by inserting them
through the holes in the filler plate into the tapped screw holes in the recorder case.
5
Insert the recorder into the cutout from the front of the panel as shown in Figure 2-6.
6
Refer to Figure 2-6. From the back of the panel attach a mounting bracket to each side of the
recorder case using a 1/4-20 x 1/2-inch hex screw and a lockwasher for each bracket
(mounting hardware supplied with recorder). Leave the screws slightly loose so you can adjust
the brackets.
7
While holding the recorder firmly against the panel, slide each bracket against the back of the
panel and tighten the screws.
Universal
filler plate
Height
of
cutout
in
panel
Tapped
screw holes
Support
brackets
Universal
filler plate
21407
Support brackets
(included in kit 30755134-xxx
Mounting brackets (supplied
with recorder)
NOTE: Universal filler plate and attaching
hardware are included in kit 30755134-xxx
Figure 2-6 Mounting in a Panel Using Universal Filler Kit
Installation - Mounting Methods
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 21
April 2017
Mounting flush in panel (using cutout made for Kent Model 105M)
Refer to Figure 2-7 and follow the procedure in Table 2-6 to mount your recorder in an existing cutout
using the cutout made for Kent Model 105M.
Table 2-6 Mounting Flush in a Panel Using Kent Model 105M Cutout
Step
Action
1
Drill two 1/4-inch holes in the back of the panel as shown in Figure 2-7. These holes are for 10-
32 screws to be inserted from back of panel into threaded inserts in the back of the recorder
case.
ATTENTION
If the panel is more than 1/4-inch thick, substitute 10-32 x 1/2-inch long
screws for the 3/8-inch long screws supplied with the recorder.
2
While supporting the recorder, insert it through the panel cutout and orient the case so that the
threaded inserts at the bottom of the case align with the holes drilled in the panel.
3
From the rear of the panel, insert two 10-32 pan head screws of appropriate length into
threaded inserts in the recorder case.
4
From the back of the panel, attach a mounting bracket to each side of the recorder case using
a 1/4-20 x 1/2-inch hex screw and a lockwasher for each bracket (mounting hardware supplied
with recorder). Leave the screws slightly loose so you can adjust the brackets.
5
While holding the recorder firmly against the panel, slide each bracket against the back of the
panel and tighten the screws.
21408
7 "
3-1/2"
2 "
Drill two
1/4-inch holes
Cutout for
Kent model 105M
Figure 2-7 Mounting in a Panel using Kent Model 105M Cutout
Installation - Mounting Methods
22 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Panel mounting recorder with NEMA4X door
Refer to Figure 2-8 and follow the procedure in Table 2-7 to panel-mount your recorder if it has a
NEMA4X door.
Table 2-7 Procedure for Mounting Recorder with NEMA4X Door
Step
Action
1
Place the panel gasket onto the rear flange of the recorder case.
2
Install five #8-32 x 3/4 screws on each of the four mounting brackets so the ends of the screw
threads are flush with the face of the bracket.
NOTE: Screw heads to be flange side of brackets.
3
Insert the case with gasket into the panel opening.
4
Position the bracket so that the tabs on the end of the bracket slide into the holes in the case,
Secure the four brackets with 1/4-20 x 5/8 long bolts and lockwashers; one to the top, bottom
and each side of the case. Tighten the bolts.
5
Start to tighten the #8-32 x 3/4 screws on a bracket. Tighten the end screws first then those
toward the middle until all five screws have a 5 to 8 lb-in of torque applied. Do the same to
both the other three brackets.
When completed all twenty screws should have a 5 to 8 lb-in of torque applied. This assures
that the case and panel gaskets are adequately sealed against the panel.
Installation - Mounting Methods
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 23
April 2017
Pan Head Screw
8-32 x 3/4 inch
Hex Head Bolt
1/4-20 x 5/8 inch
Hex Head Bolt
1/4-20 x 5/8 inch
Bracket (4)
Side View
NOTE: Mounting brackets, attaching hardware, and panel gasket are included in kit 30755065-503;
Slot
Slot
8-32 x 3/4 inch
Pan Head Screw
Hex Head Bolt
1/4-20 x 5/8 inch
Slot
Slot
Figure 2-8 Panel Mounting Recorder with NEMA4X Door
Installation - Mounting Methods
24 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Mounting on a 2-inch pipe
Refer to Figure 2-9 and follow the procedure in Table 2-8 to mount your recorder on a 2-inch pipe.
Table 2-8 Pipe Mounting Procedure
Step
Action
1
Using the eight plastite screws supplied with the pipe mounting bracket kit, attach the two
mounting brackets (flat side against the case) to the back of the recorder. Refer to Figure 2-9
for location.
2
Position the recorder with brackets on the 2-inch pipe.
3
Install the U-bolts around the pipe and through the bracket holes. Secure with lockwashers and
hex nuts provided.
Rear
of
Case
24224
Hex Nut
Washer
Pipe Mounting
Bracket
U-bolt
Plastite
Screw
Figure 2-9 Pipe Mounting Brackets
Installation - Mounting Methods
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 25
April 2017
Mounting on surface (of panel or wall)
Refer to Figure 2-10 and follow the procedure in Table 2-9 to mount your recorder on a surface (panel or
wall).
ATTENTION
You must supply three (3) screws for attaching the mounting hardware (brackets and support
hook) to panel or wall.
Table 2-9 Mounting Flush on a Surface (of Panel or Wall)
Step
Action
1
Using two flat-head 10-32 x 1/4-inch screws supplied with the recorder, fasten the support
hook into the recess at the back of the recorder case as shown in Figure 2-10.
2
Using 1/4-20 x 1/2-inch hex screws and lockwashers, attach a mounting bracket to each side
of the case. Leave the screws slightly loose so as to permit some adjustments of the brackets.
3
On the panel mark the locations for the three holes as shown by the hole pattern in Figure
2-10.
4
Using a drill of appropriate size for user-supplied screws, drill a hole in the front of the panel for
the eye of the support hook.
5
Insert the screws for the support hook into the panel, allowing the screw head to protrude
approximately 5/16-inch.
6
Hang the recorder support hook on the screw. Make sure that the locations for the other two
holes (marked in step three) are correct. If not, make sure that the recorder is aligned vertically
and use the brackets as templates to mark the proper locations.
7
Remove the recorder from the panel and drill the other two holes.
8
Hang the recorder on the screw by the support hook and insert the other two user-supplied
screws through the brackets into the panel. Tighten the two hex screws that attach the
brackets to the case.
Installation - Mounting Methods
26 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
181.36
7.14
163.32
6.430
18.03
0.710
196.22
7.725
369.6
14.550
Hole Pattern
Reference:
millimeters
inches
21409
NOTE:
These screws must be supplied by
user; all other mounting hardware
is supplied with recorder.
Support
hook
Figure 2-10 Mounting Flush on a Surface (of Panel or Wall)
Installation - Wiring Prerequisites
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 27
April 2017
2.5 Wiring Prerequisites
Taking electrical noise precautions
Electrical noise is composed of unabated electrical signals which produce undesirable effects in
measurements and control circuits.
Digital equipment is especially sensitive to the effects of electrical noise. Your recorder has built-in circuits
to reduce the effect of electrical noise from various sources. If there is a need to further reduce these
effects:
Separate External Wiring - separate connecting wires into bundles (see Table 2-10) and route the
individual bundles through separate conduits or metal trays.
Use Suppression Devices - for additional noise protection, you may want to add suppression devices at
the external source; appropriate suppression devices are commercially available.
REFERENCE
For additional noise information, refer to document number 51-52-05-01.
Electrical considerations
The recorder is considered “rack and panel mounted equipment” per EN 61010-1, Safety
Requirements for Electrical Equipment for Measurement, Control, and Laboratory Use, Part
1: General Requirements.
Recorder grounding
PROTECTIVE BONDING (grounding) of this recorder shall be in accordance with National
and local electrical codes.
Functional earth
To minimize electrical noise and transients that may adversely affect the system,
supplementary bonding of the recorder enclosure to a functional earth ground, using a 3/4”
braided copper conductor, is required.
A terminal on the rear of the recorder is provided for this connection.
CE conformity special conditions (Europe)
Braid shielded cable is required for all Input I/O and Output Relay cables. All recorder cable shield wires,
except the RS485 Modbus communications cable shield, must be connected to a low impedance earth
ground at the recorder. This can be done by bussing the shields to an earth ground point, or by connecting
the shields to the conduit entry fittings if they are in electrical contact with the enclosure conductive
coating. In either case, the shields shall not extend into the recorder enclosure. The cable shields shall also
be connected to a low impedance earth ground at the farthest end of the cable, through a 0.0047 uF
capacitor. See each of the individual wiring diagrams.
Installation - Wiring Prerequisites
28 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
For the RS485 Modbus communications cable, Alpha XTRA Guard I cable (Alpha P/N 5121C) is required.
At the recorder end, the communications cable shield must be unconnected and must not extend into the
recorder enclosure. The shield of the communications cable must be connected to earth ground at the
farthest end of the cable. See the option wiring procedure for the RS485 Communications Card.
Inside of the enclosure, the user must install ferrite suppression filters and capacitors on all wires connected
to the recorder. ©Fair-Rite Products Corp. part number 0443164151, or equivalent, shall be installed as
shown in Figure 2-11 to Figure 2-22, one filter for each circuit group.
Cable with an outer jacket diameter larger than 6.7 mm (0.264 in.) may require the outer jacket to be
removed to fit the required one turn in the filter, or the selection of a different cable.
Permissible wire bundling
Table 2-10 shows which wire functions should be bundled together.
Table 2-10 Permissible Wiring Bundling
Bundle No.
Wire Functions
1
Line power wiring
Earth ground wiring
Control relay output wiring
Line voltage alarm wiring
2
Analog signal wire, such as:
Input signal wire (thermocouple, 4 to 20 mA, etc.)
4-20 mA output signal wiring
Slidewire feedback circuit wiring
Digital input signals
Communications
4-20 mA auxiliary output
3
Low voltage alarm relay output wiring
Low voltage wiring to solid state type control circuits
Identify your wiring requirements
To determine the appropriate diagrams for wiring your recorder, refer to the model number interpretation in
this section. The model number of the recorder can be found on the chart plate.
Installation - Input Wiring Procedures
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 29
April 2017
2.6 Input Wiring Procedures
Wiring the recorder
Using the information contained in the model number, select the appropriate wiring diagrams from the
figures listed below and wire the recorder accordingly.
Wiring Requirements
Refer to
Ferrite Filter Locations
Figure 2-11
AC Line Power
Figure 2-12
Thermocouple, RTD, Radiamatic, mV, or 05 Vdc Inputs
Figure 2-13
420 mA Inputs
Figure 2-14
010 Vdc Inputs
Figure 2-15
420 mA Current Outputs or Auxiliary Outputs #2 and #3
Figure 2-16
Position Proportional Control Outputs
Figure 2-17
Relay Control Outputs
Time Proportioning
Figure 2-18
Alarm #1 and #2 Outputs and Digital Inputs
Figure 2-19
Alarm Outputs #3, #4, #5, and #6
Figure 2-20
RS485 Modbus Communications
Figure 2-21
Auxiliary Output #1
Figure 2-22
Ferrite filter locations (CE Mark)
Inside of the enclosure, install ferrite suppression filters on all wires connected to the recorder. ©Fair-Rite
Products Corp. part number 0443164151, or equivalent, shall be installed as shown in Figure 2-11, one
filter for each circuit group. Cable with an outer jacket diameter larger than 6.7 mm (0.264 in.) may require
the outer jacket to be removed to fit the required one turn in the filter, or the selection of a different cable.
Shield Wiring
The shield wires of all cables, except the RS485 communications cable, should be tied to earth ground at
the recorder end and to earth ground through a .0047 µF Capacitor at the other end of the cable. An
example of shield wiring to an external ground bus bar is shown in Figure 2-11.
Installation - Input Wiring Procedures
30 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Trans-
former
Mother PCB
Number
1 & 2
Alarm/
Digital
Inputs
Control Loop 1
and Loop 2
Output Relays
Alarm Relays
Current Output 1 & 2
Slidewire 1 & 2
Auxiliary Output
A.C.
Main
Digital Inputs 1 & 2
Transmitter Power
Inpu ts 1–4
Proces sor
Board
Ferrite Filter
23685
Hex Nut
Washer
Use Cable fitting to support wiring and hold in place.
Place the washer on the inside of the recorder between
the case and the fastening nut to protect the recorder conductive
case coating.
Shield Wiring
Exter nal G ro und B us Ba r
To Earth G r ound
1 Recorder Grounding, rear of case - Use 3/4 inch braided copper conductor.
1
2
3
2
22
2
3
33
3
3
2
Cable Fitting
3
Ferrite Filter location - Cable with an outer jacket diameter larger than 6.7 mm (0.264 in.)
may require the outer jacket to be removed to fit the required one turn in the filter,
or the selection of a different cable.
2
RS485/422 Modbus
Communic ations
3
Figure 2-11 Ferrite Filter Locations and Shield Wiring (CE Mark)
AC line power
Refer to Figure 2-12 and follow the procedure in Table 2-11 to connect the AC line power.
WARNING
Be sure that the line voltage is OFF before connecting the power wires to the recorder
or personal injury could result.
This equipment is suitable for connection to 120/240 Vac, 50/60 Hz, power supply mains. It is the user’s
responsibility to provide a switch and non-time delay (North America), quick-acting, high breaking
capacity, Type F, (Europe) 1/2 A, 250 V fuse(s) or circuit-breaker as part of the installation. The switch or
circuit-breaker shall be located in close proximity to the recorder, within easy reach of the OPERATOR.
The switch or circuit-breaker shall be marked as the disconnecting device for the recorder.
Installation - Input Wiring Procedures
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 31
April 2017
Table 2-11 AC Line Power Wiring
Step
Action
1
Open the recorder door. Loosen the captive screw in the chart plate and swing the plate out.
2
Locate connector J10 on the bottom edge of the main printed circuit board. (Refer to Figure
2-12.)
3
Remove the unwired plug from J10.
4
Run the power wires separately through second conduit from the right.
5
For CE Mark conformity, install the ferrite filter as shown in Figure 2-11.
6
Strip insulation from the end of each wire.
7
Loosen the screws in plug J10 terminals and position the plug as you would to plug it into J10.
8
Insert
the green wire (G) into the first screw clamp from the right,
the white wire (L2) into the second screw clamp from the right, and
the black wire (L1) into the third screw clamp from the right.
Tighten the screws to secure the wires.
CAUTION
To avoid damaging the recorder, be sure that you install the power wires
into the correct screw clamps. Make sure the fuse block is installed properly for the
given supply rating –– 120 Vac or 240 Vac. The fuse is in the 120 Vac location from the
factory.
9
Make sure the fuse block is installed in the proper location. Refer to Figure 2-12 for fuse block
location.
120 Vac Fuse block in location F2
240 Vac Fuse block in location F1
10
Dress the wires as slack as possible. This keeps the noise signal on these wires from
bypassing built-in suppression. Also, do not bundle any low level signal wires with the power
wires. Refer to Table 2-10 for permissible wire bundling.
Refer to document 51-52-05-01 for additional information concerning noise interference
prevention.
11
Insert the wired plug into J10.
W ARNING
Input line voltage will be present on the instrument ground plane if safety
ground is not attached; personal injury and product damage could result.
Installation - Input Wiring Procedures
32 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
#3
#4
#2 #1
L1 L2
120 or 240 Vac
H
N
PLUG J10
21410B
Fair-Rite P/N 0443164151
or equivalent
Required for CE Mark Conformity—
Kit supplied Part No. 51197612-502,
contains two ferrite filters. More than
one kit may be supplied. Install
inside of case. See Figure 2-11.
Required for CE Mark Conformity—
14 AWG Braided Wire to AC supply
ground
Fuse Block on Main PC Board
P/N51309355-tab
F1
240 Vac
F2
120 Vac
Figure 2-12 AC Line Power Wiring
Installation - Input Wiring Procedures
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 33
April 2017
Thermocouple, RTD, Radiamatic, mV, or 0-5 Vdc inputs
You can wire input 1, 2, 3, or 4 for thermocouple, RTD, Radiamatic, mV, or 0-5 Vdc actuations.
The polarity for inputs #1, #2, #3, and #4 is identical.
The prerequisites are:
Model Number - Table 1 = 1XXX, X1XX, XX1X, XXX1
ATTENTION
For thermocouple or RTD inputs, calibrate the recorder to achieve the stated accuracy. Refer
to Section 7 Input Calibration
Refer to Figure 2-13 and follow the procedure in Table 2-12 to wire Thermocouple, RTD, Radiamatic, mV,
or 05 Vdc inputs.
Table 2-12 Thermocouple, RTD, Radiamatic, mV, or 05 Vdc Input Wiring
Step
Action
1
Open the recorder door. Loosen the captive screw in the chart plate and swing the plate out.
2
Locate connector J2 on the printed circuit board for input 1 (refer to Figure 2-13).
3
Remove the unwired plug from J2.
4
Run the input wires through the desired knockout - DO NOT bundle them with the power wires.
5
For CE Mark conformity:
Install the ferrite filter as shown in Figure 2-11.
Install a .01 µF capacitor across the J2 terminals and a .0047 µF capacitor at the
sensor end of the input wiring as shown in Figure 2-13.
6
Locate jumper position MA/W1 and make sure the jumper is in the W1 position. (See Figure
2-13 for the location.)
7
Locate jumper position W3 and make sure the jumper is in the proper position for your input
type. (See Figure 2-13 for the jumper locations.)
8
Strip insulation from the end of each wire.
9
Loosen the screws in plug J2 terminals and position the plug as you would to plug it into J2.
10
Insert the wires into the appropriate screw clamps for the applicable input type. See Figure
2-13 for specific input actuation plug wiring. Tighten the screws to secure the wires.
11
Insert the wired plug into J2.
12
Repeat steps 2 through 11 for input 2, 3, and 4 printed circuit boards as applicable.
Installation - Input Wiring Procedures
34 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Figure 2-13 Thermocouple, RTD, Radiamatic, mV, or 05 Vdc Input Wiring
Installation - Input Wiring Procedures
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 35
April 2017
4-20 mA inputs and transmitter power
You can wire input 1, 2, 3, or 4 for 420 mA actuations.
The polarity for inputs #1, #2, #3, and #4 is identical.
The prerequisites are:
Model Number - Table 1 = 1XXX, X1XX, XX1X, XXX1
ATTENTION
Connector J11 on the main processor printed circuit board can be used to provide 24 Vdc
power to up to two field transmitters (without power) which are supplying the 420 mA input
signals to the recorder (1.2W @ 24 Vdc = 50 mA available).
Refer to Figure 2-14 and follow the procedure in Table 2-13 to wire 4-20 mA inputs.
Table 2-13 4-20 mA Input Wiring
Step
Action
1
Open the recorder door. Loosen the captive screw in the chart plate and swing the plate out.
2
Be sure that the jumper MA/W1 is installed in the position labeled “MA”; this connects an
internal 250-ohm resistor across the 4-20 mA input terminals on J2. (Refer to Figure 2-14 for
location of jumper.)
3
Locate jumper position W3 and make sure the jumper is in the proper position for your input
type (see Figure 2-14 for the location).
4
Locate connector J2 on the printed circuit board for input 1 (refer to Figure 2-14).
5
Remove the unwired plug from J2.
6
Run the input wires through the desired knockout - DO NOT bundle them with the power wires.
7
For CE Mark conformity, install the ferrite filter as shown in Figure 2-11 and the capacitors as
shown in Figure 2-14.
8
Strip insulation from the end of each wire.
9
Loosen the screws in plug J2 terminals and position the plug as you would to plug it into J2.
10
For transmitters with power:
Insert the wires into the appropriate screw clamps and tighten the screws to secure the
wires.
ATTENTION
The DR4500A Recorder inputs are protected from overvoltage by a
protection diode. The wake-up pulse on the ST3000 may not be recognized by the transmitter
due to this clamping action. It may be necessary to add 100 ohms of additional loop resistance
so the transmitter and SFC can communicate.
For transmitters which require power:
Remove the unwired plug from J11 then wire the transmitter power to J11 and the
input to J2. Tighten the screws in the plugs to secure the wires.
11
Insert the wired plug into J2 and J11 as applicable.
12
Repeat steps 2 through 11 for input 2, 3, and 4 printed circuit boards as applicable.
Installation - Input Wiring Procedures
36 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Figure 2-14 4-20 mA Input Wiring
Installation - Input Wiring Procedures
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 37
April 2017
0-10 Volt dc inputs
You can wire input 1, 2, 3, or 4 for 010 Volt dc actuations.
The polarity for inputs #1, #2, #3, and #4 is identical.
The prerequisites are:
Model Number - Table 1 = 3XXX, X3XX, XX3X, XXX3
ATTENTION
Calibrate the recorder to achieve the stated accuracy. Refer to Section 7 Input Calibration.
Refer to Figure 2-15 and follow the procedure in Table 2-14 to wire 0-10 Vdc inputs.
Table 2-14 0-10 Volt dc Input Wiring
Step
Action
1
Open the recorder door. Loosen the captive screw in the chart plate and swing the plate out.
2
Locate connector J2 on the printed circuit board for input 1 (refer to Figure 2-15).
3
Remove the unwired plug from J2 and replace it with the modified 4-screw plug from the bag of
accessories supplied with the recorder.
4
Run the input wires through the desired knockoutDO NOT bundle them with the power
wires.
5
For CE Mark conformity:
Install the ferrite filter as shown in Figure 2-11.
Install the .01 µF capacitor and the .0047 µF capacitor as shown in Figure 2-15.
6
Strip insulation from the end of each wire.
7
Loosen the screws in plug J2 terminals and position the plug as you would to plug it into J2.
8
Using the 30755232-002, 100K-ohm, voltage divider connector kit supplied in the bag of
accessories, insert the wires into the appropriate screw clamps. Tighten the screws to secure
the wires.
9
Install the wired plug into J2. Since J2 has only three receptacles, one of the modified plug
connectors is designed to slide outside J2 when the plug is installed.
10
Locate jumper position W3 and make sure the jumper is in the proper position for your input
type. (See Figure 2-15 for the location.)
11
Locate jumper position MA/W1 and make sure the jumper is in the W1 position. (See Figure
2-15 for the location.)
12
Repeat steps 2 through 11 for input 2, 3, and 4 printed circuit boards as applicable.
Installation - Input Wiring Procedures
38 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Figure 2-15 0-10 Volt dc Input Wiring
Installation - Output Wiring Procedures
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 39
April 2017
2.7 Output Wiring Procedures
4-20 mA control output wiring
You can wire control output 1 or 2 for 4-20 mA output.
The prerequisites are:
Model Number - Table 2 = 10, 40, 44, 60, or 66
Refer to Figure 2-16 and follow the procedure in Table 2-15 to wire 4-20 mA control outputs.
Table 2-15 4-20 mA Control Output Wiring
Step
Action
1
Open the recorder door. Loosen the captive screw in the chart plate and swing the plate out.
2
Locate connector J1 near the top of the control output #1 or #2 printed circuit board (refer to
Figure 2-16 for location).
3
Remove the unwired plug from J1.
4
Run the output wires through the desired knockout.
5
For CE Mark conformity, install the ferrite filter as shown in Figure 2-11 and the .0047 µF
capacitor as shown in Figure 2-16.
6
Strip insulation from the end of each wire.
7
Loosen the screws in plug J1 terminals and position the plug as you would to plug it into J1.
8
Observing the polarity, insert the wires into the appropriate screw clamps as shown (refer to
Figure 2-16). Tighten the screws to secure the wires.
9
Install the wired plug into J1.
10
Locate jumper position W6/W7 on the bottom left portion of the board. Make sure W7 position
is selected for 4-20 mA output.
11
Repeat steps 2 through 10 for control output #2 printed circuit board as applicable.
TIP
The 4-20 mA output can be used as a retransmission output if it is not used as a control
output.
Installation - Output Wiring Procedures
40 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
#3
#4
#2 #1
+
_
Controller load
0-1000 ohms
4-20 mA
output
Plug J1
21414
Control Output #1 PCB
or
Auxiliary Output #2
Control Output #2 PCB
or
Auxiliary Output #3
Ferrite Filter
W6
W7
Control Output #1-2 PCB
Current Output Select Jumper
W7 = Relay or
Current Output
Capacitor Kit 51197755-001
Install capacitors as shown in figure.
Required for CE Mark Conformity
Kit Part No. 51197612-502, contains two
ferrite filters; Part No.51197612-508
contains 8 ferrite filters. Install inside of
case. See Figure 2-11.
Cable Shield
.0047 μF
Capacitor
Fair-Rite P/N 0443164151
or equivalent
Figure 2-16 4-20 mA Control Output Wiring (or Aux Out #2 and #3 Wiring)
Installation - Output Wiring Procedures
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 41
April 2017
Position proportional or 3-position step control output wiring
You can wire control output 1 or 2 for position proportional or 3 position step output.
The prerequisites are:
Model Number Key = DR45AT
Model Number - Table 2 = 10, 40, or 44
Refer to Figure 2-17 and follow the procedure in Table 2-16 to wire position proportional or 3 position step
control outputs.
ATTENTION
Be sure to calibrate the position proportional control output so that the increase and decrease
relays operate properly with respect to the position of the external feedback slidewire. Refer to
Section 8 - Output Calibration in this manual.
Slidewire input is not required for 3 position step control but can be used for motor position indication.
Table 2-16 Position Proportional Control Output Wiring
Step
Action
1
Open the recorder door. Loosen the captive screw in the chart plate and swing the plate out.
2
Locate connector J2 and J5 on the control output #1 printed circuit board (refer to Figure 2-17
for location).
3
Locate jumper positions W2/W3 and W4/W5 below connector J5 on the printed circuit board.
Remove plug-in output #1 printed circuit board for better access to the jumpers. Be sure to tag
and remove all the plug connections to the printed circuit board before removing it. Position the
jumpers as shown in Figure 2-17 for desired relay contact action. Locate jumper position
W6/W7 on the bottom left portion of the board. Make sure position W6 is selected for position
proportioning, then reinstall the printed circuit board.
4
Run the feedback slidewire (not required for 3 position step) and motor drive wires through the
desired knockouts.
5
For CE Mark conformity:
install the ferrite filter as shown in Figure 2-11
install the shield capacitors as shown in Figure 2-17.
6
Strip insulation from the end of each wire.
7
Loosen the screws in plug J2 terminals and position the plug as you would to plug it into J2.
8
Insert the wires from the motor’s feedback slidewire into the appropriate screw clamps as
shown (refer to Figure 2-17). Tighten the screws to secure the wires.
9
Loosen the screws in plug J5 terminals and position the plug as you would to plug it into J5.
10
Insert the wires for the motor into the appropriate screw clamps as shown (refer to Figure
2-17). Tighten the screws to secure the wires.
11
Install the wired plug into J2 and J5, as applicable.
12
Repeat steps 2 through 11 for Control Output #2 printed circuit board as applicable.
Installation - Output Wiring Procedures
42 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
21415
Fair-Rite P/N 0443164151
or equivalent
Ferrite Filter
Control output
#1-2 PCB
Relay No. 1
W2 = N.O. contact
W3 = N.C. contact
Relay No. 2
W4 = N.O. contact
W5 = N.C. contact
W5
W4
W3
W2
W6
W7
1
2
3
Plug J2
OPEN
CLOSED
Motor's feedback
slidewire 100
to 1000
(Not required for
Three Position
Step Control)
#3
#4
#2 #1
Control
output
#2 PCB
Control
output
#1 PCB
Plug J5
N
H
Motor
power
supply
CLOSED (CCW)
OPEN (CW)
Capacitor Kit 51197755-001
Install capacitors as shown in figure.
Required for CE Mark Conformity
Kit Part No. 51197612-502, contains
two ferrite filters; Part No.
51197612-508 contains 8 ferrite filters.
Install inside of case. See Figure 2-11.
.0047 μF
Capacitor
Relay 2
Relay 1
.0047 μF
Capacitor
W6 = Position
Proportional
Output
Cable Shield
Figure 2-17 Position Proportional Control Output or Three Position Step Wiring
Installation - Output Wiring Procedures
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 43
April 2017
Relay control output wiring
You can wire control output 1 or 2 for relay output including Time proportional and 3 position step
applications.
The prerequisites are:
Model Number - Table 2 = 10, 40, 60, 11, 44, 66
Refer to Figure 2-18 and follow the procedure in Table 2-17 to wire relay control outputs.
ATTENTION
Relay #2 is used for time proportional control. Relay 2 can also be used for 3 position step
control (see Figure 2-17).
Table 2-17 Relay Control Output Wiring
Step
Action
1
Open the recorder door. Loosen the captive screw in the chart plate and swing the plate out.
2
Locate connector J5 on the control output #1 printed circuit board (refer to Figure 2-18 for
location).
3
Remove the unwired plug from J5.
4
Locate jumper positions W2/W3 and W4/W5 below connector J5 on the printed circuit board.
Remove plug-in output #1 printed circuit board for better access to the jumpers. Be sure to tag
and remove all the plug connections to the printed circuit board before removing it. Position the
jumpers as shown in Figure 2-18 for desired relay contact action. Locate jumper position
W6/W7 on the bottom left portion of the board. Make sure W7 position is selected for relay
control output, then reinstall the printed circuit board.
5
Run the relay load wires through the desired knockouts.
6
For CE Mark conformity:
- install the ferrite filter as shown in Figure 2-11.
- install the shield capacitor as shown in Figure 2-18.
7
Strip insulation from the end of each wire.
8
Loosen the screws in plug J5 terminals and position the plug as you would to plug it into J5.
9
Insert the relay wires and relay power into the appropriate screw clamps for single or duplex
action as shown (refer to Figure 2-18); tighten the screws to secure the wires.
10
Install the wired plug into J5.
11
Repeat steps 2 through 10 for control output #2 printed circuit board as applicable.
Installation - Output Wiring Procedures
44 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
W5
W4
W3
W2
W6
W7
Relay No. 1
W2 = N.O. contact
W3 = N.C. contact
Relay No. 2
W4 = N.O. contact
W5 = N.C. contact
21416
Position when shipped
N.O. with power applied
and out indicator light off.
Notes:
1.
2.
3.
J5 terminals 2 and 4 are the non-switched connections to an SPST relay.
Selectable for normally open or normally closed as required.
This relay supplies a dry contact closure. User must supply appropriate
power connections for his external device.
This relay has a resistive load rating of 5A @ 120 Vac
Load calculation example:
Supply voltage
(for example: 115 Vac)
Resistance of customer
controlled device
=
must equal a
number less
than 5 amps
#3
#4
#2 #1
N
H
Plug J5 (see Notes)
Relay 2
load
H
N
Relay 1
load
External Load
power supply
*Relay 2 is used for time proportional duplex.
Also used for 3 position step. See Figure 2-17.
Heat
Cooling
*
Control
output
#1 PCB
Control
output
#2 PCB
Fair-Rite P/N 0443164151
or equivalent
Ferrite Filter
Control
output
#1-2 PCB
Cable Shield
.0047 µ F
Capacitor
Capacitor Kit 51197755-001
Install capacitors as shown in figure.
Required for CE Mark Conformity
Kit Part No. 51197612-502, contains two
ferrite filters; Part No.51197612-508
contains 8 ferrite filters. Install inside of
case. See Figure 2-11.
W7 = Relay or
Current Output
Figure 2-18 Relay Control Output Wiring
Installation - Option Wiring Procedures
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 45
April 2017
2.8 Option Wiring Procedures
Alarm output and digital input wiring
You can wire #1 and #2 Alarm Outputs and Digital Inputs.
The prerequisites are:
Model Number - Table 3 = XX1
Refer to Figure 2-19 and follow the procedure in Table 2-18 to wire alarm outputs or digital inputs.
The alarm output is a dry contact closure.
Table 2-18 Alarm Output or Digital Input Wiring
Step
Action
1
Open the recorder door. Loosen the captive screw in the chart plate and swing the plate out.
2
Locate connector J3 and J4 on the alarm output/digital input printed circuit board (refer to
Figure 2-19 for location).
3
Remove the unwired plug from J3.
4
Run the digital input wires through the desired knockout.
5
For CE Mark conformity, install the ferrite filter as shown in Figure 2-11.
6
Strip insulation from the end of each wire.
7
Loosen the screws in plug J3 terminals and position the plug as you would to plug it into J3.
8
Insert the wires for the digital inputs into the appropriate screw clamps as shown (refer to
Figure 2-19). Note that you can wire the contacts in an and/or fashion, so that both contacts
or either contact initiates the configured action. Tighten the screws to secure the wires.
9
Install the wired plug into J3.
10
Remove the unwired plug from J4.
11
Run the alarm output wires through the desired knockout.
12
For CE Mark conformity:
install the ferrite filter as shown in Figure 2-11
install the shield capacitors as shown in Figure 2-19.
13
Strip insulation from the end of each wire.
14
Loosen the screws in plug J4 terminals and position the plug as you would to plug it into J4.
15
Insert the wires for the alarm devices into the appropriate screw clamps as shown (refer to
Figure 2-19). Tighten the screws to secure the wires.
16
Locate the jumper positions W1/W2 and W3/W4 on the printed circuit board. Reposition the
jumpers as shown in Figure 2-19 for the desired relay control action. The recorder is shipped
with the W1 and W3 in N.C. positions.
17
Install the wired plug into J4.
Installation - Option Wiring Procedures
46 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
21417
Fair-Rite P/N 0443164151
or equivalent
Ferrite Filter
Alarm No. 1
W3 = N.C. contact
W4 = N.O. contact
Alarm No. 2
W1 = N.C. contact
W2 = N.O. contact
W4
W3
W2
W1
Alarm outputs
Plug J4
(see Notes)
Position when shipped
N.C. with power off or
Alarm indicator light on.
#3
#4
#2 #1
External Load
Power Supply
Alarm #1
Relay Load
Alarm #2
Relay Load
Plug J3
Digital inputs
PIN 3 - 2nd Control Loop + Digital 2
PIN 2 - 1st Control Loop + Digital 1
PIN 1 - Recorder Supplied
Voltage Source
for Digital Inputs
Supply voltage
(for example: 115 Vac)
Resistance of customer
controlled device
=
must equal a
number less
than 1 amps
Cable Shield
.0047 µF
Capacitor
Capacitor Kit 51197755-001
Install capacitors as shown in figure.
Required for CE Mark Conformity
Kit Part No. 51197612-502, contains two
ferrite filters; Part No.51197612-508
contains 8 ferrite filters. Install inside of
case. See Figure 2-11.
Cable Shield
.0047 µF
Capacitor
Notes:
1. J4 terminals 2 and 4 are the non-
switched connections to an
SPST relay. Selectable for
normally open or normally closed
as required.
2. This relay supplies a dry contact
closure. User must supply
appropriate power connections
for his external device.
3. This relay has a resistive load
rating of 1 A @ 120 Vac
Load calculation example:
Figure 2-19 Alarm Output or Digital Input Wiring
Installation - Option Wiring Procedures
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 47
April 2017
Additional alarm wiring information
The DR4500 has the ability to provide for Alarm outputs 3, 4, 5, and 6.
Follow the procedures listed below to wire No. 3 and No. 4 Alarm Outputs and No. 5 and No. 6 Alarm
Outputs.
Alarms 3 and 4 output wiring
You can wire #3 and #4 Alarm Outputs.
The prerequisites are:
Model Number - Model Table 2 = 1X, 4X, 6X*
*If control output is 4-20 mA, then the relays on the control card are available for use as
alarms on all models except DR45AH/AS/AP models.
Refer to Figure 2-20 and follow the procedure in Table 2-19 to wire Alarm 3 and Alarm 4 outputs.
Table 2-19 Alarm 3 and Alarm 4 Output Wiring
Step
Action
1
Open the recorder door. Loosen the captive screw in the chart plate and swing the plate out.
2
Locate connector J5 on the 4-20 mA control output printed circuit board to wire relays #3 and
#4. Refer to Figure 2-20 for location.
3
Remove the unwired plug from J5.
4
Locate jumper position W2/W3 and W4/W5 below connector J5 on the printed circuit board.
Note that you may want to remove the plug-in output printed circuit board for better access to
jumpers. Be sure to tag and remove all the plug connections to the printed circuit boards
before removing it. Position the jumpers as shown for the desired relay contact action and
reinstall the printed circuit board.
5
Run the alarm output wires through the desired knockout.
6
For CE Mark conformity:
install the ferrite filter as shown in Figure 2-11
install the capacitors as shown in Figure 2-20
7
Strip insulation from the end of each wire.
8
Loosen the screws in plug J5 terminals and position the plug as you would to plug it into J5.
9
Insert the wires for the alarm devices into the appropriate screw clamps as shown. Refer to
Figure 2-20. Tighten the screws to secure the wires.
10
Install the wired plug into J5.
Installation - Option Wiring Procedures
48 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Alarms 5 and 6 output wiring
You can wire #5 and #6 Alarm outputs.
The prerequisites are:
Model Number - Model Table 2 = X1, X4, X6*
*If control output is 4-20 mA, then the relays on the control card are available for use as
alarms on all models except DR45AH/AS/AP models.
Refer to Figure 2-20 and follow the procedure in Table 2-20 to wire Alarm 5 and Alarm 6 outputs.
Table 2-20 Alarm 5 and Alarm 6 Output Wiring
Step
Action
1
Open the recorder door. Loosen the captive screw in the chart plate and swing the plate out.
2
Locate connector J5 on the 4-20 mA control output printed circuit board to wire relays #5 and
#6. Refer to Figure 2-20 for location.
3
Remove the unwired plug from J5.
4
Locate jumper position W2/W3 and W4/W5 below connector J5 on the printed circuit board.
Note that you may want to remove the plug-in output printed circuit board for better access to
jumpers. Be sure to tag and remove all the plug connections to the printed circuit boards
before removing it. Position the jumpers as shown for the desired relay contact action and
reinstall the printed circuit board.
5
Run the Alarm output wires through the desired knockout.
6
For CE Mark conformity:
install the ferrite filter as shown in Figure 2-11
install the capacitors as shown in Figure 2-20
7
Strip insulation from the end of each wire.
8
Loosen the screws in plug J5 terminals and position the plug as you would to plug it into J5.
9
Insert the wires for the alarm devices into the appropriate screw clamps as shown. Refer to
Figure 2-20. Tighten the screws to secure the wires.
10
Install the wired plug into J5.
Installation - Option Wiring Procedures
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 49
April 2017
Wiring for alarm outputs #3, 4, 5, and 6
Plug J5
4 - 20 mA
control output
and no. 3 & 4
alarm outputs
PCB
Alarm No. 4
W4 = N.O. contact
W5 = N.C. contact
W3 W2
W5 W4
Alarm No. 3
W2 = N.O. contact
W3 = N.C. contact
#3
#4
#2 #1
21466
No. 5 & 6
Alarm outputs PCB
W3 W2
W5 W4
Alarm No. 5
W2 = N.O. contact
W3 = N.C. contact
Alarm No. 6
W4 = N.O. contact
W5 = N.C. contact
Alarm #5
Relay Load
Alarm #6
Relay Load
Fair-Rite P/N 0443164151
or equivalent
Ferrite Filter
Ferrite filter
Plug J5
Alarm #3
Relay Load
Alarm #4
Relay Load
External Load
Power Supply
Ferrite filter
External Load
Power Supply
.0047 μF
Cable Shield
Capacitor
.0047 μF
Cable Shield
Capacitor
Capacitor Kit 51197755-001
Install capacitors as shown in figure.
Required for CE Mark Conformity
Kit Part No. 51197612-502, contains two
ferrite filters; Part No.51197612-508
contains 8 ferrite filters. Install inside of
case. See Figure 2-11.
Figure 2-20 Alarm outputs #3, 4, 5, and 6 wiring
Installation - Option Wiring Procedures
50 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
RS485 Modbus communications wiring
RS485 Modbus Communications is an option available on the DR4500A recorder.
The prerequisites are:
Model Key Number - All models except DR45AH/AP/AS
Model Number - Table 3 = 3XX or 4XX
Refer to Figure 2-21 and follow the procedure in Table 2-21 to wire the RS485 Modbus communications
option.
Table 2-21 RS485 Modbus Communications Wiring
Step
Action
1
Open the recorder door. Loosen the captive screw in the chart plate and swing the plate out.
2
Locate connector J3 on the RS485 Modbus communications option printed circuit board (refer
to Figure 2-21 for location).
3
Remove the unwired plug from J3.
4
Run the communications option wires through the desired knockout.
5
For CE Mark conformity
Install the ferrite filter as shown in Figure 2-11.
Refer to Figure 2-21 for shield information.
6
Strip insulation from the end of each wire.
7
Loosen the screws in plug J3 terminals and position the plug as you would to plug it into J3.
8
Insert the wires for the communications option into the appropriate screw clamps as shown
(refer to Figure 2-22). Tighten the screws to secure the wires.
9
Install the wired plug J3 into J3 connector on the communications board.
REFERENCE
Refer to documents 51-52-25-66 and 51-52-25-69 for a complete description of RS485
Modbus Communications Option.
Installation - Option Wiring Procedures
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 51
April 2017
#3
#4
#2 #1
Communications master
Plug J3
SHLD
Tx–/
Rx–
Tx+/
Rx+
To other
communications
instruments
(Maximum 15)
Optional communication
21418G
Fair-Rite P/N 0443164151
or equivalent
Required for CE Mark Conformity— Kit
supplied Part No. 51197612-502,
contains two ferrite filters. More than one
kit may be supplied. Install inside of case.
See Figure 2-11.
Communication wire must be Alpha
XTRA Guard I Cable (Alpha P/N 5121C)
Ferrite Filter
120 Ohm
Resistor
See
Note 1
See
Note 2
Place 120 ohm resistor on
last device, between Tx+/Rx+
and Tx–/Rx–.
Notes:
1. The shield of the RS485 Modbus Communications cable is not
connected at the recorder end and should not extend into the
recorder enclosure. The shield of the communication cable
should be connected to earth ground at the farthest end on the cable.
2. For non-CE Mark applications, use shielded twisted pair cables
(Belden 4271 Twinax or equivalent).
Figure 2-21 RS485 Modbus Communications Wiring
Installation - Option Wiring Procedures
52 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
4-20 mA auxiliary output wiring
You can wire an auxiliary output for 420 mA.
The prerequisites are:
Model Number - Table 3 = 1XX or 4XX
Refer to Figure 2-22 and follow the procedure in Table 2-22 to wire 420 mA auxiliary output.
Table 2-22 4-20 mA Auxiliary Output Wiring
Step
Action
1
Open the recorder door. Loosen the captive screw in the chart plate and swing the plate out.
2
Locate connector J2 near the bottom of the auxiliary output printed circuit board (refer to
Figure 2-22 for location).
3
Remove the unwired plug from J2.
4
Run the output wires through the desired knockout.
5
For CE Mark conformity, install the ferrite filter as shown in Figure 2-11.
6
Strip insulation from the end of each wire.
7
Loosen the screws in plug J2 terminals and position the plug as you would to plug it into J2.
8
Observing the polarity, insert the wires into the appropriate screw clamps as shown (refer to
Figure 2-22). Tighten the screws to secure the wires.
9
Install the wired plug into J2.
ATTENTION
Be sure that the 4-20 mA auxiliary output is aligned. Refer to Subsection 8.4 Auxiliary Output
Calibration.
TIP
The 4-20 mA output on the control output board can also be set up for an Auxiliary
retransmission output if it is not being used for a control output. This requires model selection
option Table II = 10, 40, 44, 60, 66.
TIP
Auxiliary output 2 and Auxiliary output 3 use Control current output 1 and Control current
output 2 if Control “OUT ALG” is not set to “CURRENT”. Refer to Figure 2-16 for Aux Out #2
and #3 wiring.
Installation - Option Wiring Procedures
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 53
April 2017
#3
#4
#2 #1
+
_
4-20 mA
auxiliary
output
Plug J2
22841G
Auxiliary
Output
PCB
Fair-Rite P/N 0443164151
or equivalent
Ferrite Filter
.0047 μF Capacitor
Controller load
0-1000 ohms
Capacitor Kit 51197755-001
Install capacitors as shown in figure.
Required for CE Mark Conformity
Kit Part No. 51197612-502, contains two
ferrite filters; Part No.51197612-508
contains 8 ferrite filters. Install inside of
case. See Figure 2-11.
Figure 2-22 4-20 mA Auxiliary Output #1 Wiring
ATTENTION
Refer to Figure 2-16 for Auxiliary Output 2 and Auxiliary Output 3 wiring.
Installation - Lockout Switch Configuration
54 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
2.9 Lockout Switch Configuration
Introduction
The configuration can be locked using S1 switch located next to the microprocessor U17 on the main
printed circuit board.
Restrictions based on lockout switch position
Figure 2-23 shows the location of the S1 lockout switch on the main printed circuit board.
When the lockout switch is OFF (DownConfigure):
You can view and change all applicable operating parameters as described in Section 4
Configuration Parameter Definitions.
When the lockout switch is ON (UpLocked):
Most parameters for the recorder are locked and the parameters may not be changed except for
Tuning 1 and Tuning 2 parameters and adjustments to time/date/day/year.
U17
S1
U19
J17
R47
C55
C56
Y2
R45
R43
R42
C50
UP (ON) Locked
DOWN (OFF) Configure
Main Printed
Wiring Board
(Right Side)
S1 Lockout Switch
22709
Figure 2-23 S1 Lockout Switch Location
ATTENTION
Lockout can also be configured under set up group “LOCKOUT”. See Subsection 3.21.
This feature also includes the special screw and plate that provide the lead seal capability for
sealing the chart plate. This feature is normally used with DR45AH model recorders.
Release M DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 55
May 2013
3. Configuration
3.1 Overview
Introduction
Configuration is a dedicated operation where you use straightforward keystroke sequences to select and
establish (configure) pertinent control data best suited for your application.
What’s in this section?
The table below lists the topics that are covered in this section.
Topic
See Page
3.1 Overview
55
3.2 Configuration Prompts
57
3.3 How to Get Started
60
3.4 Configuration Tips
61
3.5 Configuration Procedure
62
3.6 Input Set Up Group
64
3.7 Pen Set Up Group
66
3.8 Chart Set Up Group
67
3.9 Time Set Up Group
69
3.10 Totalizer Set Up Group
70
3.11 Input Algorithm Set Up Group
72
3.12 Control Set Up Group
73
3.13 Tuning Parameters Set Up Group
75
3.14 SP Ramp Set Up Group
76
3.15 Timer Set Up Group
77
3.16 Alarms Set Up Group
78
3.17 Auxiliary Output Set Up Group
80
3.18 Modbus Communications Set Up Group
81
3.19 Options Set Up Group
82
3.20 Event Message
83
3.21 Lockout Set Up Group
86
3.22 Adjust Printing
87
3.23 Configuration Record Sheet
88
Configuration - Overview
56 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Prompts
To assist you in the configuration process, there are prompts that appear in the upper and lower displays.
These prompts let you know what group of configuration data (set up prompts) you are working with and
also the specific parameters (function prompts) associated with each group.
Figure 3-1 shows an overview of the prompt hierarchy.
Configuration - Configuration Prompts
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 57
April 2017
3.2 Configuration Prompts
Diagram: prompt hierarchy
Figure 3-1 shows an overview of the DR4500A Set Up prompts and their associated Function prompt - read
from left to right.
Figure 3-1 DR4500A Prompt Hierarchy
Set Up Group
Function Prompts
FO RESET
RESET FO
Only with key number DR45AR, see Appendix A
INPUT 1
ENABLE
DECIMAL
UNITS
ENGUNITS
IN1 TYPE
XMITTER
IN1 HI
IN1 LO
CUTOFF 1
INPTCOMP
FILTER1
BURNOUT
EMISSIV
INPUT 2
INPUT 3
INPUT 4
Same as INPUT 1
PEN 1
ENABLE
PEN 1 IN
CHART1HI
CHART1LO
PEN1ON
PEN1OFF
MAJORDIV
MINORDIV
RNG1TAG
PEN 2
PEN 3
PEN 4
Same as PEN 1
CHART
CHRTSPD
HOUR/REV
TIME DIV
MINORDIV
CONTINUE
CHARTNAM
HEADER
REM CHRT
TIME
MINUTES
HOURS
DAY
MONTH
YEAR
DAY
WAKE MIN
WAKE HR
WAKE DAY
WAKE MON
TOTAL 1
(Value)
RSET TOT
TOTAL 1
TOTAL EU
RATE
SCALER
RSETABLE
INHIBIT
TOTAL 2
Same as TOTAL 1
INP ALG
INP ALG
COEFF
PV HIGH
PV LOW
RATIO A
BIAS A
RATIO B
BIAS B
RATIO C
BIAS C
POLYNOM
C0 VALUE
C2x10-1
C3x10-3
C4x10-5
C5x10-7
Configuration - Configuration Prompts
58 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Set Up Group
Function Prompts
CONTROL 1
ENABLE
PID SETS
SW VALUE
SP SOURC
RATIO
BIAS
SP TRACK
POWER UP
PWR OUT
SP HILIM
SP LOLIM
ACTION
OUT HILIM
OUT LOLIM
DROPOFF
DEADBAND
OUT HYST
FAILSAFE
REM SW
MAN KEY
PBorGAIN
MINorRPM
CONT1ALG
OUT1ALG
4-20 RNG
CONTROL 2
Same as CONTROL 1
TUNING 1
FUZZY
ACCUTUNE
AT ERR
PROP BD
or
GAIN
RATE MIN
RSET MIN
or
RSET RPM
MAN RSET
PROP BD2
or
GAIN 2
RATE2MIN
RSET2MIN
or
RSET2RPM
CYC SEC
CYC2SEC
TUNING 2
Same as TUNING 1
SP RAMP1
ENABLE
SP RAMP
TIME MIN
FINAL SP
SP RATE
EU/HR UP
EU/HR DN
SP PROG
RECYCLES
SOAK DEV
PROFILE
STATE
RECOVERY
PROG END
SP RAMP2
Same as SP RAMP1
PROFILES
PRx STRT
PRx END
RAMPUNIT
SYNC 1+2
SPP SEGS
SEGxRAMP
SEGx SP
SEGxTIME
SPP EVNT
SEGx EV
TIMER
TIMER
PERIOD
START
LDISPLAY
RSET
ON-TIME
INCRMENT
ALARM 1
A1S1 VAL
A1S2 VAL
A1S1TYPE
A1S2TYPE
A1S1 H L
A1S1SCAL
A1S2 H L
A1S2SCAL
AL1 HYST
ALARM 2
ALARM 3
ALARM 4
ALARM 5
ALARM 6
Same as ALARM 1
Configuration - Configuration Prompts
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 59
April 2017
Set Up Group
Function Prompts
AUX OUT
AUX OUT
4 mA VAL
20mA VAL
AUX OUT 2
4 mA VAL
20mA VAL
AUX OUT 3
4mA VAL
20 mA VAL
COMM
ComSTATE
Com ADDR
BAUD
XMT DLAY
DBL BYTE
OPTIONS
REJ FREQ
HF REJ
RELHUMID
ATMPRES
DEVIATION
DEVSETPT
SCROLL
GRANDTOT
If key number is DR45AR, see Appendix A for Fo calculation prompts.
EVNT MSG
EVENT 1
MESSAGE1
POSITION1
EVENT 2
MESSAGE2
POSITION2
EVENT 3
MESSAGE3
POSITION3
EVENT 4
MESSAGE4
POSITION4
EVENT 5
MESSAGE5
POSITION5
EVENT 6
MESSAGE6
POSITION6
LOCKOUT
PASSWORD
LOCKOUT
CHANGE
ADJUST
TRACE LN
GRID LN
PEN TYPE
CALIB
For field calibrationsee Calibration section of manual
STATUS
VERSION
FAILSAFE*
RAM TEST
CONFTEST
CAL TEST
COMMTEST
FACT CRC
BATTERY
*Displayed on test failure only
Configuration - How To Get Started
60 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
3.3 How To Get Started
Read the configuration tips
Read Subsection 3.4 Configuration Tips which will help you to easily and quickly configure your recorder.
Read configuration procedure
Read Subsection 3.5 Configuration Procedure which tells you how to access the Set Up groups, and the
function parameters within each of these groups that are shown in the Prompt Hierarchy in Figure 3-1.
Set Up groups
The Set Up groups and function parameters are listed in the order of their appearance. The list includes the
name of the prompt, the range of setting or selections available, and the factory setting. It allows you to
quickly find a parameter and obtain the available range or selection you require.
Parameter explanations or definitions
If you need a detailed explanation of any prompt listed, refer to Section 4 Configuration Parameter
Definitions. This section lists the set up and function prompts, the selections or range of settings that you
can make for each, plus a detailed explanation or definition of each parameter.
Configuration record sheet
Located in Subsection 3.23 is a Configuration Record Sheet. When you make your configuration selections,
record them on this sheet. Then you will have a record of how the recorder was configured.
Set up the recorder in this order:
Inputs (Display will be correct)
Pens (Trace will agree with display)
Chart
Alarms
Control
Tuning
Other functions as needed
Configuration - Configuration Tips
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 61
April 2017
3.4 Configuration Tips
Introduction
Listed below in Table 3-1 are some tips that will help you enter the configuration data more quickly.
Table 3-1 Configuration Tips
Function
Tip
Displaying groups
Use the SET UP key to display the Set Up groups. The group titles are listed in
this section in the order that they appear in the recorder.
Displaying
functions
Use the FUNC key to display the individual parameters under each group. The
prompts are listed in the order of their appearance in each group.
Scrolling
To get to a Set Up group prompt more quickly, hold the SET UP key in. To get
to a function prompt more quickly, hold the FUNC key in. The display will scroll
through the parameters.
ATTENTION
The prompting scrolls at a rate of 2/3 seconds when the SET
UP or FUNC key is held in. Also, [▲] [▼] keys will move group prompts
forward or backward at a rate twice as fast.
Changing values
quickly
When Changing the value of a parameter, you can adjust a more significant
digit in the upper display by holding in one key [▲] or [▼] , and pressing the
other [▲] or [▼] at the same time.
The adjustment will move one digit to the left.
Press the key again and you will move one more digit to the left.
Restoring to the
original value
When you change the value or selection of a parameter while in Set Up mode
and decide not to enter it, press RUN/HOLD once, the original value or
selection will be recalled.
Exiting Set Up mode
To exit Set Up mode, press the LOWR DISP key. This returns the display to
the same state it was in immediately preceding entry into the Set Up mode.
Timing out from Set
Up mode
If you are in Set Up mode and do not press any keys for one minute, the
recorder will time out and revert to the mode and display that was being used
prior to entry into Set Up mode.
Key error
When a key is pressed and the prompt “KEY ERROR” appears in the lower
display, it will be for one of the following reasons:
parameter not available
not in Set Up mode, press SET UP key first
key malfunction, do keyboard test (operation)
individual key locked out
Configuration - Configuration Procedure
62 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
3.5 Configuration Procedure
Introduction
Each of the Set Up groups and their functions are preconfigured at the factory.
The factory settings are shown in the Set Up group tables that follow this procedure.
If you want to change any of these selections or values, follow the procedure in Table 3-2. This
procedure tells you the keys to press to get to any Set Up group and any associated Function parameter
prompt.
If you need a detailed explanation of any prompt, refer to Section 4 Configuration Parameter
Definitions.
Procedure
Follow the procedure listed in Table 3-2 to access the Set Up groups and Function prompts.
TIP
The prompting scrolls at a rate of 2/3 seconds when the SET UP or FUNC key is held in. Also,
[▲] [▼] keys will move group prompts forward or backward at a rate twice as fast.
Table 3-2 Configuration Procedure
Step
Operation
Press
Result
1
Select Set Up mode
SET
UP
Upper Display: SET UPLets you know you are in the
configuration mode and a Set Up group title is being
displayed in the lower display.
Lower Display: INPUT 1This is the first Set Up group
title.
2
Select any Set Up group
SET
UP
Successive presses of the SET UP key will
sequentially display the other Set Up group titles
shown in the prompt hierarchy in Figure 3-1.
You can also use the [▲] [▼] keys to scan the Set Up
groups in both directions.
Stop at the Set Up group title which describes the
group of parameters you want to configure. Then
proceed to the next step.
3
Select a Function
parameter
FUNC
Upper Display: Shows the current value or selection for
the first function prompt of the particular Set Up group
that you have selected (EXAMPLE: ENABLE/DISABLE).
Lower Display:Depends on what is selected in Set Up
group. Shows the first function prompt within that Set Up
group. Example: “INPUT 1”
4
Select other Function
parameters
FUNC
Successive presses of the FUNC key will sequentially
display the other function prompts of the Set Up group
you have selected.
Stop at the function prompt that you want to change,
then proceed to the next step.
Configuration - Configuration Procedure
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 63
April 2017
Step
Operation
Press
Result
5
Change the value or
selection
or
These keys increment or decrement the value or
selection that appears for the function prompt you have
selected.
See Subsection 3.4 Configuration Tips for instructions
to increase or decrease value quickly.
Change the value or selection to meet your needs.
If the display flashes, you are trying to make an
unacceptable entry.
6
Enter the value or selection
FUNC
or
SET
UP
This key selects another function prompt.
This key selects another Set Up group.
The value or selection you have made will be entered into
memory after another key is pressed.
7
Exit configuration
LOWR
DISP
This exits configuration mode and returns the recorder to
the same state it was in immediately preceding entry into
the Set Up mode. It stores any changes you have made.
Configuration - Input Set Up Group
64 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
3.6 Input Set Up Group
Introduction
This data deals with various parameters required to configure input 1, input 2, input 3, or input 4.
Function prompts
Table 3-3 lists all the function prompts in the “INPUT 1” Set Up group. Repeat the process for each input
you want to set up.
Press the SET UP key until INPUT 2, INPUT 3, or INPUT 4 appears in the display.
Table 3-3 Input Group Function Prompts
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
INPUT 1
Input 1 Actuation
DISABL
ENABLE
ENABLE
DECIMAL
Decimal Point Location
XXXX None
XXX.X One
XX.XX Two
X.XXX Three
XXX.X
UNITS
Temperature Units
DEG F
DEG C
XXXXX (make selection at prompt
"ENGUNITS")
DEG F
ENGUNITS
Engineering Units
0 to 9
A to Z
+
\
(blank)
IN1 TYPE
Input 1 Actuation Type
B TC W TC H
E TC H W TC L
E TC L 100 PT
J TC H 200 HI*
J TC L 200 LO*
K TC H 500 PT
K TC L 100 RH
NNM TC 4-20 mA
NIC TC 0-10 mV
R TC 10-50m
S TC 0-5 V
T TC H 0-10 V
T TC L RADIAM
*DR45AR only
100 PT
or
0-5 V
with Control
Configuration - Input Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 65
April 2017
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
XMITTER
Transmitter Characterization
B TC T TC H
E TC H T TC L
E TC L W TC H
J TC H W TC L
J TC L 100 PT
K TC H 500 PT
K TC L 100 RH
NNM TC H LINEAR*
NIC TC SQROOT*
R TC
S TC
*Set “IN1HI” and “IN1LO”
Linear
IN1 HI
Input 1 High Range Value
(linear inputs only)
999.0 to 9999.
in engineering units
900
IN1 LO
Input 1 Low Range Value
(linear inputs only)
999.0 to 9999.
in engineering units
-300
CUTOFF 1
Low Flow Cutoff Selection
0 to 100 % of input range
0
INPTCOMP
Input Compensation
999.9 to 9999.
0
FILTER 1
Input 1 Filter
0 to 120 seconds
0
BURNOUT
Burnout Protection
NONE
UP
DOWN
UP
EMISSIV
Emissivity
.01 to 1.00
.01
Repeat this procedure for INPUT 2, INPUT 3, and INPUT 4.
Configuration - Pen Set Up Group
66 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
3.7 Pen Set Up Group
Introduction
The functions listed in this group deal with how to configure pen #1, pen #2, pen #3, or pen #4. The
procedure for configuring each pen is the same. The prompts shown in Table 3-4 show PEN 1.
Repeat the process for each pen you want to set up.
Press the SET UP key until PEN 2, PEN 3, or PEN 4 appears in the display.
Function prompts
Table 3-4 lists all the function prompts in the PEN Set Up groups.
Table 3-4 Pen 1, 2, 3, 4 Group Function Prompts
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
PEN 1
(or PEN 2, PEN 3,
PEN 4)
Pen Record
ENABLE
DISABL
ENABLE
PEN1IN
(or PEN2IN,
PEN3IN, PEN4IN)
Pen Input
INPUT1 RH SETPT2
INPUT2 OUTPT1 DGTL1
INPUT3 OUTPT2 DGTL2
INPUT4 SETPT1 PV1
INPUT 1
CHART1HI
(or CHART2HI,
CHART3HI,
CHART4HI)
Chart High Range Value
999.0 to 9999
302.0
CHART1LO
(or CHART2LO,
CHART3LO,
CHART4LO)
Chart Low Range Value
999.0 to 9999
292.0
PEN1ON
(or PEN2ON,
PEN3ON,
PEN4ON)
Pen Chart Position for ON
Event
0 to 100 %
91.0
PEN1OFF
(or PEN2OFF,
PEN3OFF,
PEN4OFF)
Pen Chart Position for OFF
Event
0 to 100 %
93.0
MAJORDIV
Major Chart Divisions
2 to 10
10
MINORDIV
Minor Chart Division
2 to 10
10
RNG1TAG
Range 1 Tag Name
0 to 9
A to Z
+
/
(blank)
RNG 1
Repeat this procedure for PEN 2, PEN 3, and PEN 4.
Configuration - Chart Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 67
April 2017
3.8 Chart Set Up Group
Introduction
The functions listed in this group deal with the parameters that must be set to assure proper chart function.
CAUTION
Before making any configuration changes to the “Chart” Set Up group, place the recorder in
“Chart Hold”. Press the CHART key to stop the chart rotation. Press again after configuration
entry is made.
Function prompts
Table 3-5 lists all the function prompts in the “Chart” Set Up group.
Table 3-5 Chart Group Function Prompts
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
CHRTSPD
Chart Speed Selection
8HR
12HR
24HR
7DAYS
XHR (See prompt "HOUR/REV")
XHR
HOUR/REV
Hours per Revolution
(appears only if "XHR" is
selected above)
6 to 744 (12 hrs for abrasion resistant pen)
NOTE: Below 8 hrs chart speed (24 hrs chart
speed with abrasion resistant pen), printing
may be degraded.
12
TIME DIV
Time Division
8 to 24 time periods
24
MINORDIV
Minor Time Division
Four
Eight
Four
CONTINUE
Continue Chart Rotation
YES
NO
NO
CHARTNAM
Chart Name
0 to 9
A to Z
+
/
(blank)
TRULIN
HEADER
Header for Chart
YES
NO
NO
Configuration - Chart Set Up Group
68 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
REM CHRT
Remote Chart Activation
NONE
EXT SW1
EXT SW2
ALARM 1
ALARM 2
TIME (See “WAKE MIN”, “WAKE HOUR”,
“WAKE DAY”, “WAKE MON” in Time Set Up
group.)
ALARM 3
ALARM 4
ALARM 5
ALARM 6
NONE
Configuration - Time Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 69
April 2017
3.9 Time Set Up Group
Introduction
The functions listed in this group deal with the parameters that let you configure the real time that will
appear on the chart.
Function prompts
Table 3-6 lists all the function prompts in the “Time” Set Up group.
Table 3-6 Time Group Function Prompts
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
MINUTES
Real Time in Minutes Chart
Speed Selection
0 to 59
Set to local
time
HOURS
Real Time in Hours
0 to 23
DAY
Real Time in Days
1 to 31
MONTH
Real Time in Months
1 to 12
YEAR
Real Time in Years
0 to 99
DAY
Day of the Week Chart
Name
MONDAY
TUEDAY
WEDDAY
THRDAY
FRIDAY
SATDAY
SUNDAY
WAKE MIN
Wake Minutes
0 to 59
0
WAKE HR
Wake Hour
0 to 23
0
WAKE DAY
Wake Day
0 to 31
0
WAKE MON
Wake Month
1 to 12
1
Configuration - Totalizer Set Up Group
70 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
3.10 Totalizer Set Up Group
Introduction
The functions listed in this group deal with the calculation and display of the total flow volume as
measured by input 1 (total 1) or input 2 (total 2). The displayed value is 8 digits with a configurable scale
factor.
Function prompts
Table 3-7 lists all the function prompts in the “TOTAL 1” Set Up group. Repeat the process for each input
you want to set up.
Press the SET UP key until TOTAL 2 appears in the display.
Table 3-7 Totalizer Group Function Prompts
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
Actual Current
Totalized Value
View Current Totalized
Value
Current Scale Factor
Example: E1 GPM
E0 GAL
RSET TOT
Reset Totalizer to Zero
(RSETABLE must be set to
“LOCAL”)
NO
YES
NO
TOTAL 1
TOTAL 2
Totalizer 1
Totalizer 2
DISABL, INPUT1, PV1, INPUT2, INPUT 3,
INPUT 4, E TIME
DISABL
TOTAL EU
Total Engineering Units
0 to 9
A to Z
+
/
(blank)
GAL
RATE
Rate of Integration
SECOND
MINUTE
HOUR
DAY
M/DAY (Millions of Units per Day)
SECOND
SCALER
Totalizer Scale Factor
1
10
100
1000
10000
100000
1E6 (1,000,000)
1
RSETABLE
Totalizer Reset
NO
LOCAL
EXTSW1*
EXTSW2*
TIME
*Total will be set to “0” on closure of the
assigned external switch.
NO
INHIBIT
Totalizer Inhibit
NONE
NONE
Configuration - Totalizer Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 71
April 2017
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
S1 OPEN
S1 CLOSE
S2 OPEN
S2 CLOSE
Repeat this procedure for INPUT 2.
Configuration - Input Algorithm Set Up Group
72 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
3.11 Input Algorithm Set Up Group
Introduction
Input Algorithm set up group lets you calculate a process variable (PV1) using Inputs 1, 2, and 3. Input 1 is
represented by ‘A’, Input 2 by ‘B’, Input 3 by ‘C’.
Function prompts
Table 3-8 lists all the function prompts in the Input Algorithm Set Up group.
Table 3-8 Input Algorithm Group Function Prompts
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
INP ALG
Input Algorithm
NONE
A+B+C (Summer)
√A*B/C (Square Root Multiplier/Divider)
√A*B*C (Square Root Multiplier)
A*B/C (Multiplier/Divider)
A*B*C (Multiplier)
(AB)*C (Difference Multiply)
HI SELECT
LO SELECT
NONE
COEFF
Coefficient K
0.000 to 1000.0
1.0
PV HIGH
Calculated PV High Limit
999 to 9999
0.0
PV LOW
Calculated PV Low Limit
999 to 9999
0.0
RATIO A
Ratio for Input 1
20.00 to 20.00
1.0
BIAS A
Bias for Input 1
999 to 9999
0.0
RATIO B
Ratio for Input 2
20.00 to 20.00
1.0
BIAS B
Bias for Input 2
999 to 9999
0.0
RATIO C
Ratio for Input 3
20.00 to 20.00
1.0
BIAS C
Bias for Input 3
999 to 9999
0.0
POLYNOM
Polynomial characterizer
NONE, INPUT 1, INPUT 2, INPUT 3, INPUT
4
NONE
C0 VALUE
Polynomial coefficient CO
99.99 to 99.99
0
C1 VALUE
Polynomial coefficient C1
9.999 to 9.999
0
C2x10-1
Polynomial coefficient C2
9.999 to 9.999
0
C3x10-3
Polynomial coefficient C3
9.999 to 9.999
0
C4x10-5
Polynomial coefficient C4
9.999 to 9.999
0
C5x10-7
Polynomial coefficient C5
9.999 to 9.999
0
Configuration - Control Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 73
April 2017
3.12 Control Set Up Group
Introduction
This data deals with various parameters required to effectively control your process.
Function prompts
Table 3-9 lists all the function prompts in the “CONTROL 1” or “CONTROL 2” Set Up group. You can
enable the Control groups in the Option group.
Table 3-9 Control 1 or Control 2 Group Function Prompts
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
CONTROL1
Control Loop 1
DISABL
ENABLE
ENABLE
PID SETS
Tuning Parameter Sets
1 ONLY
2KEYBD
2PV SW
2SP SW
1 ONLY
SW VALUE
Automatic Switchover Value
999.0 to 9999
0.00
SP SOURC
Setpoint Source
1 LOCAL
REMOTE
2 LOCAL
OUT 2 (available for Control 1 only)
NOTE: If you select “REMOTE,” Input #3 is
automatically assigned as your RSP source
for control #1; Input #4 is assigned for control
#2. However, if the unit has only 2 inputs,
then RSP will be on Input 2.
1 LOCAL
RATIO
Ratio for Remote Setpoint
20.00 to 20.00
1.0
BIAS
Bias for Remote Setpoint
999.0 to 9999 in engineering units
0
SP TRACK
Setpoint TrackingTotalizer
Scale Factor
NONE
RSP
NONE
POWER UP
Power Up Controller Mode
Recall
MANUAL
A LSP
A RSP
AM SP
AM LSP
MANUAL
PWR OUT
Power Up Output
LAST
FAIL SF
NOTE: This prompt will appear only if
“3PSTEP” is selected at function prompt
“CONT ALG”.
LAST
SP HILIM
High Setpoint Limit
999.0 to 9999.
500
SP LOLIM
Low Setpoint Limit
999.0 to 9999.
0
Configuration - Control Set Up Group
74 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
ACTION
Control Output Direction
DIRECT
REVRSE
REVERSE
OUTHILIM
High Output Limit
5.0 to 105.0 % of output
100.0
OUTLOLIM
Low Output Limit
5.0 to 105.0 % of output
0
DROPOFF
Controller Dropoff Value
5.0 to 105.0 % of output
0.0
DEADBAND
Output Relay Deadband
Time Proportional Duplex:
5.0 to 25.0 %
On-Off Duplex:
0.0 to 25.0 %
Position Proportional
0.5 to 5.0 %
2.0
OUT HYST
Output Relay Hysteresis
0.0 to 5.0 % of PV Span
0.5
FAILSAFE
Failsafe Output Value
0 to 100 %
50
For 3 Position Step Control:
100PCT Set motor position to 100 % output
position
0PCT Set motor to 0 % output position
0.0
REM SW or
REM SW2
Remote Switching
(Digital Input)
NONE TO 2SP TUNE
TO MAN TO DIR TIMER
TO LSP RN/HLD
NONE
MAN KEY
Manual Mode Key Selection
ENABLE
DISABL
ENABLE
PB orGAIN
Proportional Band or Gain
Units
PB PCT
GAIN*
*GAIN must be used with OUTPUT ALG
settings of TIME D (TIME DUPLEX) or TI
CUR (TIME CURRENT)
GAIN
MIN orRPM
Reset Units
R P M (repeats per minute)
M I N (minutes per repeat)
MIN
CONT1 ALG or
CONT2 ALG
Control Algorithm
ON-OFF PD+MR
PID-A 3PSTEP*
PID-B
*not applicable for model DR45AR
PID-A
OUT1 ALG or
OUT2 ALG
(appears if not
3PSTEP above)
Output Algorithm
TIME* TIME D*
CURRNT CUR TI*
POSITN* TI CUR*
*not applicable for Model DR45AR
CURRENT
420RNG
Current/Time Duplex Range
(CUR D)
100PCT (FULL)
50 PCT (SPLIT)
50PCT
Configuration - Tuning Parameters Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 75
April 2017
3.13 Tuning Parameters Set Up Group
Introduction
These Tuning Set Up groups contain the Function parameters that will allow your recorder to respond
correctly to changes in process variable or setpoint. You can start with predetermined values but you will
have to watch your process to determine how to modify them.
Function prompts
Table 3-10 lists all the function prompts in the Tuning 1 or Tuning 2 Set Up groups. How the “Algorithm”
and “Control” Set Up groups are configured determines which prompts will appear.
Table 3-10 Tuning 1 or Tuning 2 Group Function Prompts
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
FUZZY
Fuzzy Overshoot
Suppression
DISABL
ENABLE
DISABL
ACCUTUNE
Accutune II for Control Loop
DISABL
ENABLE
DISABL
AT ERR
Accutune Error Codes
No message under normal conditions
Read Only message displayed if tuning has
been manually aborted
––
PROP BD
or
GAIN
Proportional Band
or
Gain
0.1 to 1000 %
0.1 to 1000
1.0
RATE MIN
Rate in minutes
0.00 to 10.00 minutes
0.00
RSET MIN
or
RSET RPM
Reset in minutes/repeat
or
Reset in repeats/minute
0.02 to 50.00
0.02 to 50.00
1.0
1.0
MAN RSET
Manual Reset
100 to 100 % output
0.0
PROP BD2
or
GAIN 2
Proportional Band 2
or
Gain 2
0.1 to 1000 %
0.1 to 1000
5.0
RATE2MIN
Rate 2 in minutes
0.08 to 10.00 minutes
0.00
RSET2MIN
RSET2RPM
Reset 2 in minutes/repeat
Reset 2 in repeats/minute
0.02 to 50.00
0.02 to 50.00
0.2
0.2
CYC SEC
Cycle Time (Heat)
Electromechanical Relays
1 to 120 seconds
20.0
CYC2 SEC
Cycle Time 2 (Cool)
Electromechanical Relays
1 to 120 seconds
20.0
Configuration - SP Ramp Set Up Groups
76 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
3.14 SP Ramp Set Up Groups
The Setpoint Ramp 1 or 2 Set Up groups let you configure 2 setpoint ramps. Each group (SP RAMP1 and
SP RAMP 2) can be configured one of three ways: ramp, rate, or setpoint program.
Setpoint Ramp
Setpoint will ramp between the current local setpoint and a final setpoint over a time interval (SP RAMP).
Setpoint Rate
The Setpoint Ramp Set Up group also contains the function parameters that let you configure a specific
ramp rate up and ramp rate down (SP RATE). These rates are used when the local setpoint is manually
changed.
Setpoint Program
Also included under this group are prompts for configuring a Setpoint program (SP PROG). The prompts
and instructions for Setpoint programming are presented in the Section 6 - Setpoint Ramp/Soak
Programming and Operation.
Function prompts
Table 3-11 lists all the function prompts in the SP RAMP 1 or SP RAMP 2 Set Up group. Configure each
ramp separately. When you enable the ramp type (SP RAMP, SP RATE, SP PROG) the other two types
are hidden from the display.
Table 3-11 SP Ramp 1 or 2 Group Function Prompts
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
SP RAMP*
Single Setpoint Ramp
Selection
DISABL
ENABLE
DISABL
TIME MIN
Single Setpoint Ramp Time
0 to 255 minutes
0
FINAL SP
Single Setpoint Ramp Final
Setpoint
Enter a value within the setpoint limits
100.0
SP RATE*
Setpoint Rate
DISABL
ENABLE
DISABL
EU/HR UP
Rate up value (SP Rate
enabled)
0 to 9999
in units per hour
0
EU/HR DN
Rate down value (SP Rate
enabled)
0 to 9999
in units per hour
0
SP PROG*
Setpoint Programming
(Refer to Section 6)
DISABL
ENABLE
DISABL
*Only one of these can be enabled at a time.
Configuration - Timer Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 77
April 2017
3.15 Timer Set Up Group
Introduction
The Timer gives a countdown or elapsed time, after which Relay 1 energizes. If Timer is enabled, it has
exclusive control over Relay 1; Alarm 1 will not control the relay.
Function prompts
Table 3-12 lists all the function prompts in the TIMER Set Up group.
Table 3-12 Timer Group Function Prompts
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
TIMER
Timer Enable/Disable
ENABLE
DISABL
DISABL
PERIOD
Timeout Period
0:00 to 99:59
0
START
Start Initiation
RHKEY
ALARM2
TIME
RHKEY
LDISPLAY
Timer Display
TREM
ET
TREM
RESET
Timer Reset Control
RHKEY
ALARM1
REPEAT
RHKEY
ON-TIME
Timer Repeat Mode
On-Time
1 SEC
2 SEC
3 SEC
4 SEC
5 SEC
INCRMENT
Timer Count Increment
MINUTE
SECOND
MINUTE
Configuration - Alarms Set Up Group
78 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
3.16 Alarms Set Up Group
Introduction
This data deals with the Alarms function that is available with your recorder.
There are six alarms available. Each alarm has two setpoints.
You can configure each of these two setpoints to alarm on various recorder parameters. There are two
alarm output selections, high or low.
You can also configure the two setpoints to alarm on the same event and to alarm both high and low, if
desired. An adjustable hysteresis of 0.0 % to 100.0 % is configurable for each alarm.
Priority of functions that operate relays
During alarm conditions an alarm will deenergize its associated relay unless a higher priority function has
been configured for that relay. See Table 3-13. If you want the alarm to control the relay, do not configure
a higher priority function.
Table 3-13 Priority of functions that operate relays
Relay
Relay is controlled by (in order of priority)
1
1. Timer function
2. Alarm 1
2
Alarm 2 only
3
1. Controller 1 output algorithms Relay Simplex,
Position Proportional, Relay Duplex,
Current/Relay Duplex
2. Alarm 3
4
1. Controller 1 output algorithms Position
Proportional, Relay Duplex, Current/Relay Duplex
2. Alarm 4
5
1. Controller 2 output algorithms Relay Simplex,
Position Proportional, Relay Duplex,
Current/Relay Duplex
2. Alarm 5
6
1. Controller 2 output algorithms Position
Proportional, Relay Duplex, Current/Relay Duplex
2. Alarm 6
Configuration - Alarms Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 79
April 2017
Function prompts
Table 3-14 lists all the function prompts in the Alarms Set Up group.
Table 3-14 Alarms Group Function Prompts
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
AxS1 VAL
Alarm 1, Setpoint 1 Value
Value in engineering units
90
AxS2 VAL
Alarm 1, Setpoint 2 Value
Value in engineering units
95
AxS1TYPE
Alarm 1, Setpoint 1 Type
NONE
IN 1 (Input 1)
IN 2 (Input 2)
IN 3 (Input 3)
IN 4 (Input 4)
RH (Relative Humidity)
PV (Process Variable Loop 1)
DEV (Loop 1 Deviation)
OUT (Loop 1 Output)
DEV2 (Loop 2 Deviation)
OUT2 (Loop 2 Output)
EVENT (SP Programming-Segment Event)
TOTAL 1 (Totalizer to Alarm On)
TOTAL 2 (Totalizer to Alarm On)
TOTAL 3 (Model DR45AW only)
TOTAL 4 (Model DR45AW only)
IN 1
AxS2TYPE
Alarm 1, Setpoint 2 Type
Same as A1S1TYPE
IN 1
AxS1 H L
Alarm 1, Setpoint 1 State
LO (Low Alarm)
H I (High Alarm)
LO
AxS1SCAL
Alarm 1, Setpoint 1 Scaling
Multiplier for Totalizer
Selection
1 10000
10 100000
100 1E6
1000
1
AxS2 H L
Alarm 1, Setpoint 2 State
LO
H I
HI
AxS2SCAL
Alarm 1, Setpoint 2 Scaling
Multiplier for Totalizer
Selection
1
10
100
1000
10000
100000
1E6
1
ALx HYST
Alarm Hysteresis
0.0 to 100.0 % of Input Span as appropriate
0.1
Repeat this procedure for ALARM 2, ALARM 3, ALARM 4, ALARM 5, ALARM 6.
Configuration - Auxiliary Output Set Up Group
80 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
3.17 Auxiliary Output Set Up Group
Introduction
The auxiliary output will supply a 4-20mA output scaled to one of four operating parameters: Input,
Output, Setpoint, or Deviation. This current is supplied from a separate option card. AUX OUT 2 and
AUX OUT 3 use CONTROL CURRENT OUT 1 and CONTROL CURRENT OUT 2 if CONTROL OUT
ALG is not set to CURRENT.
Function prompts
Table 3-15 lists all the function prompts in the Auxiliary Output Set Up group.
Table 3-15 Auxiliary Output Group Function Prompts
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
AUX OUT 1
Auxiliary Output
Representation
DISABL PV 2
IN 1 DEV 2
IN 2 OUT 2
PV 1 SP 2
DEV 1 IN 3
OUT 1 IN 4
SP 1
DISABL
4 mA VAL
Low Scaling Factor
Low scale value to represent 4 mA
0.0
20mA VAL
High Scaling Factor
High scale value to represent 20 mA
100.0
Repeat this procedure for AUX OUT 2 and AUX OUT 3.
Configuration - Modbus Communications Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 81
April 2017
3.18 Modbus Communications Set Up Group
Introduction
This data deals with the Communications option that is available with your recorder. This option allows the
recorder to be connected to a host computer via the Modbus protocol.
If your recorder does not have this option the prompts will not appear.
ATTENTION
Refer to Documents 51-52-25-66 and 51-52-25-69 for a complete description of the RS485
Modbus Communications Option.
Function prompts
Table 3-16 lists all the function prompts in the Modbus Communications Set Up group.
Table 3-16 Modbus Communications Group Function Prompts
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
ComSTATE
Modbus Communications
DISABL
MODBUS
DISABL
Com ADDR
Communications Station
Address
1 to 99
1
BAUD
Communications Baud Rate
300
600
1200
2400
4800
9600
19200
38400
9600
XMT DLAY
Transmit Delay
(in milliseconds)
NONE
10MSEC
20MSEC
30MSEC
40MSEC
50MSEC
NONE
DBL BYTE
Double Byte Order
FP B
FP BB
FP L
FP LB
FP B
Configuration - Options Set Up Group
82 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
3.19 Options Set Up Group
Introduction
This data deals with various options that are available with your recorder. If your recorder does not have
any of these options the prompts will not appear.
Function prompts
Table 3-17 lists all the function prompts in the Option Set Up group.
Table 3-17 Options Group Function Prompts
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
REJ FREQ
Rejection Frequency
50HZ
60HZ
60HZ
HF REJ
High Frequency Rejection
ENABLE
DISABL
ENABLE
RELHUMID
Relative Humidity
NO
YES
NO
ATMPRES
Atmospheric Pressure
Compensation
590 to 800 mmHg
––
DEVIATION
Deviation Recording Action
NONE
SETPNT
CHAN1
NONE
DEVSETPT
Deviation Setpoint Value
999.0 to 9999
0
SCROLL
Lower Display Scroll
NONE
1 SEC
2 SEC
3 SEC
NONE
GRANDTOT
Grand Totalizer
ENABLE
DISABL
DISABL
Configuration - Event Message Configuration
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 83
April 2017
3.20 Event Message Configuration
Introduction
This Set Up group allows you to specify an event message to be printed on a designated area of the chart
when triggered by a specific selectable actuation.
Function prompts
Table 3-18 lists all the function prompts in the “Event Message” Set Up group.
Table 3-18 Event Message Group Function Prompts
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
EVENT1
Event 1 Trigger
NONE
EXTSW1
EXTSW2
ALARM1
ALARM2
ALARM3
ALARM4
ALARM5
ALARM6
NONE
MESSAGE1
Message for Event 1
(up to six characters)
0 to 9
A to Z
+
/
(blank)*
EVENT1
POSITON1
Chart Position for Message
1 Printing
0 to 100 %
87.3
EVENT 2
Event 2 Trigger
NONE
EXTSW1
EXTSW2
ALARM1
ALARM2
ALARM3
ALARM4
ALARM5
ALARM6
NONE
MESSAGE2
Message for Event 2
(up to six characters)
0 to 9
A to Z
+
/
(blank)*
EVENT2
POSITON2
Chart Position for Message
2 Printing
0 to 100 %
85.5
Configuration - Event Message Configuration
84 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
EVENT 3
Event 3 Trigger
NONE
EXTSW1
EXTSW2
ALARM1
ALARM2
ALARM3
ALARM4
ALARM5
ALARM6
NONE
MESSAGE3
Message for Event 3
(up to six characters)
0 to 9
A to Z
+
/
(blank)*
EVENT3
POSITON3
Chart Position for Message
3 Printing
0 to 100 %
83.6
EVENT 4
Event 4 Trigger
NONE
EXTSW1
EXTSW2
ALARM1
ALARM2
ALARM3
ALARM4
ALARM5
ALARM6
NONE
MESSAGE4
Message for Event 4
(up to six characters)
0 to 9
A to Z
+
/
(blank)*
EVENT4
POSITON4
Chart Position for Message
4 Printing
0 to 100 %
80.0
EVENT 5
Event 5 Trigger
NONE
EXTSW1
EXTSW2
ALARM1
ALARM2
ALARM3
ALARM4
ALARM5
ALARM6
NONE
MESSAGE5
Message for Event 5
(up to six characters)
0 to 9
A to Z
+
/
(blank)*
EVENT5
POSITON5
Chart Position for Message
5 Printing
0 to 100 %
78.2
Configuration - Event Message Configuration
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 85
April 2017
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
EVENT 6
Event 6 Trigger
NONE
EXTSW1
EXTSW2
ALARM1
ALARM2
ALARM3
ALARM4
ALARM5
ALARM6
NONE
MESSAGE6
Message for Event 6
(up to six characters)
0 to 9
A to Z
+
/
(blank)*
EVENT6
POSITON6
Chart Position for Message
6 Printing
0 to 100 %
76.9
*For alphanumeric entries, the display will cycle, from left to right, with highlighting (increased brightness) of each
digit. The value of each digit can be changed only when it is highlighted.
Configuration - Lockout Set Up Group
86 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
3.21 Lockout Set Up Group
Introduction
These are the parameters that you will select to lockout any unauthorized changes to the recorder's
configuration and calibration prompts. You must know the password in order to change the Lockout
configuration.
Function prompt
Table 3-19 lists all the function prompts in the Lockout Set Up group.
Table 3-19 Lockout Group Function Prompts
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
PASSWORD
Lockout Password
Select up to 4 alphanumeric characters
(++++ is factory default password)
For more information on password security,
refer to Appendix B.
XXXX
LOCKOUT
Lockout
NONE
CALIB
+CONF
MAX
CALIB
CHANGE
Change Password
0 to 9
A to Z
XXXX
ATTENTION
Configuration can also be locked using S1 switch on the main printed circuit board. Refer to
Subsection 2.9 Lockout Switch Configuration.
This feature also includes the special screw and plate that provide for the lead seal capability for sealing the
chart plate.
Configuration - Adjust Printing
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 87
April 2017
3.22 Adjust Printing
Introduction
This data deals with the “Adjust Printing” feature of the Truline recorder. This feature is important to the
operation of the hot stylus pen.
Configuration choices are provided for PEN TYPE and the selection must match the stylus design.
PEN TYPE = NORMAL is for the high-speed stylus design. (Model Selection Table III Selection _ 0 _
Standard Pen)
PEN TYPE = JEWEL is used only for abrasion resistant stylus design. (Model Selection Table III
Selection _ 1 _ Abrasion Resistant Pen)
CAUTION
If the “JEWEL” selection is accidentally used with the high-speed design, the life of that stylus
will be shortened.
You can also make slight adjustments to the print contrast.
Function prompt
Table 3-20 lists all the function prompts in the Adjust Set Up group.
Table 3-20 Adjust Group Function Prompts
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
TRACE LN
Trace Line Contrast
DARK
MEDIUM
LIGHT
MEDIUM
GRID LN
Grid Line Contrast
DARK
MEDIUM
LIGHT
MEDIUM
PEN TYPE
Stylus Selection
NORMAL Select if high speed stylus (black
tip) is installed.
JEWEL Select if abrasion resistant stylus
(beige tip) is installed.
NORMAL
Configuration - Configuration Record Sheet
88 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
3.23 Configuration Record Sheet
Keep a record
Enter the value or selection for each prompt on this sheet so you will have a record of how your recorder
was configured.
Group
Prompt
Function
prompt
Value or
Selection
Factory
Setting
Group
Prompt
Function
prompt
Value or
Selection
Factory
Setting
INPUT 1
INPUT 2
INPUT 3
INPUT 4
DECIMAL
UNITS
ENGUNITS
IN1 TYPE
XMITTER
IN1 HI
IN1 LO
CUTOFF 1
BIAS n
FILTER 1
BURNOUT
EMISSIV
DECIMAL
UNITS
ENGUNITS
IN2 TYPE
XMITTER
IN2 HI
IN2 LO
CUTOFF 2
BIAS n
FILTER 2
BURNOUT
EMISSIV
DECIMAL
UNITS
ENGUNITS
IN3 TYPE
XMITTER
IN3 HI
IN3 LO
CUTOFF 3
BIAS n
FILTER 3
BURNOUT
EMISSIV
DECIMAL
UNITS
ENGUNITS
IN4 TYPE
XMITTER
IN4 HI
IN4 LO
CUTOFF 4
BIAS n
FILTER 4
BURNOUT
EMISSIV
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
XXX.X
DEGF
100PT
LINEAR
900
-300
0
n = 1 4
0
UP
.01
XXX.X
DEGF
100PT
LINEAR
900
-300
0
n = 1 4
0
UP
.01
XXX.X
DEGF
100PT
LINEAR
900
-300
0
n = 1 4
0
UP
.01
XXX.X
DEGF
100PT
LINEAR
900
-300
0
n = 1 4
0
DEGF
.01
PEN 1
PEN 2
PEN 3
PEN 4
CHART
TIME
PEN1IN
CHART1HI
CHART1LO
PEN1ON
PEN1OFF
MAJORDIV
MINORDIV
RNG1TAG
PEN2IN
CHART2HI
CHART2LO
PEN2ON
PEN2OFF
MAJORDIV
MINORDIV
RNG2TAG
PEN3IN
CHART3HI
CHART3LO
PEN3ON
PEN3OFF
MAJORDIV
MINORDIV
RNG3TAG
PEN4IN
CHART4HI
CHART4LO
PEN4ON
PEN4OFF
MAJORDIV
MINORDIV
RNG4TAG
CHRTSPD
HOUR/REV
TIME DIV
MINORDIV
CONTINUE
CHARTNAM
HEADER
REM CHRT
MINUTES
HOURS
DAY
MONTH
YEAR
DAY
WAKE MIN
WAKE HR
WAKE DAY
WAKE MON
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
INPUT1
302.0
292.0
91.0
93.0
10
10
RNG1
INPUT2
302.0
292.0
91.0
93.0
10
10
RNG2
INPUT3
302.0
292.0
91.0
93.0
10
10
RNG3
NPUT4
302.0
292.0
91.0
93.0
10
10
RNG4
XHR
12
24
Four
NO
TRULIN
NO
NONE
Set
to
local
time
0
0
0
0
Configuration - Configuration Record Sheet
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 89
April 2017
Group
Prompt
Function
prompt
Value or
Selection
Factory
Setting
Group
Prompt
Function
prompt
Value or
Selection
Factory
Setting
TOTAL 1
TOTAL 2
INP ALG
CONTROL
1
(Value)
RSET TOT
TOTAL 1
TOTAL EU
RATE
SCALER
RSETABLE
INHIBIT
(Value)
RSET TOT
TOTAL 2
TOTAL EU
RATE
SCALER
RSETABLE
INHIBIT
INP ALG
COEFF
PV HIGH
PV LOW
RATIO A
BIAS A
RATIO B
BIAS B
RATIO C
BIAS C
POLYNOM
C0 VALUE
C1 VALUE
C2x10-1
C3x10-3
C4x10-5
C5x10-7
CONTROL1
PID SETS
SW VALUE
SP SOURC
RATIO
BIAS
SP TRACK
POWER UP
PWR OUT
SPHILIM
SPLOLIM
ACTION
OUT HILIM
OUT LOLIM
DROPOFF
DEADBAND
OUT HYST
FAILSAFE
REM SW
MAN KEY
PBorGAIN
MINorRPM
CONT1ALG
OUT1ALG
4-20 RNG
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
E0 GAL
NO
DISABL
GAL
SECOND
1
NO
NONE
E0 GAL
NO
DISABL
GAL
SECOND
1
NO
NONE
NONE
1.0
0.0
0.0
1.0
0.0
1.0
0.0
1.0
0.0
NONE
0
0
0
0
0
0
ENABLE
1ONLY
0.0
1LOCAL
1.0
0
NONE
MANUAL
LAST
500
0
REVRSE
100.0
0
0.0
2.0
0.5
50
NONE
ENABLE
GAIN
MIN
PIDA
CURRENT
50PCT
CONTROL 2
TUNING 1
CONTROL2
PID SETS
SW VALUE
SP SOURC
RATIO
BIAS
SP TRACK
POWER UP
PWR OUT
SP HILIM
SP LOLIM
ACTION
OUTHILIM
OUTLOLIM
DROPOFF
DEADBAND
OUT HYST
FAILSAFE
REM SW2
MAN KEY
PBorGAIN
MINorRPM
CONT2ALG
OUT2ALG
4-20 RNG
FUZZY
ACCUTUNE
AT ERR
PROP BD
or
GAIN
RATE MIN
RSET MIN
or
RSET RPM
MAN RSET
CYCSEC
PROP BD2
or
GAIN 2
RATE2MIN
RSET2MIN
or
RSET2RPM
CYC2SEC
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
Read only
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
ENABLE
1ONLY
0.0
1LOCAL
1.0
0
NONE
MANUAL
LAST
500
0
REVRSE
100.0
0
0.0
2.0
0.5
50
NONE
ENABLE
GAIN
MIN
PIDA
CURRENT
50PCT
DISABL
DISABL
1.0
1.0
0.00
1.0
1.0
0.0
20.0
1.0
1.0
0.00
1.0
1.0
20.0
Configuration - Configuration Record Sheet
90 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Group
Prompt
Function
prompt
Value or
Selection
Factory
Setting
Group
Prompt
Function
prompt
Value or
Selection
Factory
Setting
TUNING 2
SP RAMP1
SP RAMP2
PROFILES
SPP SEGS
SPP EVNT
FUZZY
ACCUTUNE
AT ERR
PROP BD
or
GAIN
RATE MIN
RSET MIN
or
RSET RPM
MAN RSET
CYCSEC
PROP BD2
or
GAIN 2
RATE2MIN
RSET2MIN
or
RSET2RPM
CYC2SEC
SP RAMP
TIME MIN
FINAL SP
SP RATE
EU/HR UP
EU/HR DN
SP PROG
RECYCLES
SOAK DEV
PROFILE
STATE
RECOVERY
PROG END
SP RAMP
TIME MIN
FINAL SP
SP RATE
EU/HR UP
EU/HR DN
SP PROG
RECYCLES
SOAK DEV
PROFILE
STATE
RECOVERY
PROG END
PRx STRT
PRx END
RAMPUNIT
SYNC 1+2
SEGxRAMP
SEGx SP
SEGxTIME
SEGx EV
_______
_______
Read only
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
DISABL
DISABL
1.0
1.0
0.00
1.0
1.0
0.0
20.0
1.0
1.0
0.00
1.0
1.0
20.0
DISABL
0
100.0
DISABL
DISABL
DISABL
0
100.0
DISABL
TIMER
ALARM 1
ALARM 2
ALARM 3
ALARM 4
TIMER
PERIOD
START
LDISPLAY
RESET
ON-TIME
INCRMENT
A1S1 VAL
A1S2 VAL
A1S1TYPE
A1S2TYPE
A1S1 H L
A1S1SCAL
A1S2 H L
A1S2SCAL
AL1 HYST
A2S1 VAL
A2S2 VAL
A2S1TYPE
A2S2TYPE
A2S1 H L
A2S1SCAL
A2S2 H L
A2S2SCAL
AL2 HYST
A3S1 VAL
A3S2 VAL
A3S1TYPE
A3S2TYPE
A3S1 H L
A3S1SCAL
A3S2 H L
A3S2SCAL
AL3 HYST
A4S1 VAL
A4S2 VAL
A4S1TYPE
A4S2TYPE
A4S1 H L
A4S1SCAL
A4S2 H L
A4S2SCAL
AL4 HYST
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
DISABL
0:01
KEY
TREM
KEY
MIN
90
95
INPUT1
INPUT1
LO
1
HI
1
0.1
90
95
INPUT1
INPUT1
LO
1
HI
1
0.1
90
95
INPUT1
INPUT1
LO
1
HI
1
0.1
90
95
INPUT1
INPUT1
LO
1
HI
1
0.1
Configuration - Configuration Record Sheet
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 91
April 2017
Group
Prompt
Function
prompt
Value or
Selection
Factory
Setting
Group
Prompt
Function
prompt
Value or
Selection
Factory
Setting
ALARM 5
ALARM 6
AUX OUT
AUX OUT2
AUX OUT3
COMM
OPTIONS
A5S1 VAL
A5S2 VAL
A5S1TYPE
A5S2TYPE
A5S1 H L
A5S1SCAL
A5S2 H L
A5S2SCAL
AL5 HYST
A6S1 VAL
A6S2 VAL
A6S1TYPE
A6S2TYPE
A6S1 H L
A6S1SCAL
A6S2 H L
A6S2SCAL
AL6 HYST
AUX OUT
4 mA VAL
20mA VAL
AUX OUT2
4 mA VAL
20mA VAL
AUX OUT3
4 mA VAL
20mA VAL
ComSTATE
Com ADDR
BAUD
XMT DLAY
DBL BYTE
REJ FREQ
HF REJ
RELHUMID
ATMPRES
DEVIATION
DEVSETPT
SCROLL
GRANDTOT
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
90
95
INPUT1
INPUT1
LO
1
HI
1
0.1
90
95
INPUT1
INPUT1
LO
1
HI
1
0.1
DISABL
0.0
100.0
DISABL
0.0
100.0
DISABL
0.0
100.0
DISABL
1
9600
NONE
FP B
60
ENABLE
NO
NONE
0
NONE
DISABL
EVNT MSG
LOCKOUT
ADJUST
EVENT 1
MESSAGE1
POSITION1
EVENT 2
MESSAGE2
POSITION2
EVENT 3
MESSAGE3
POSITION3
EVENT 4
MESSAGE4
POSITION4
EVENT 5
MESSAGE5
POSITION5
EVENT 6
MESSAGE6
POSITION6
PASSWORD
LOCKOUT
CHANGE
TRACE LN
GRID LN
PEN TYPE
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
NONE
EVENT1
87.3
NONE
EVENT2
85.5
NONE
EVENT3
83.6
NONE
EVENT4
80.0
NONE
EVENT5
78.2
NONE
EVENT6
76.9
XXXX
CALIB
XXXX
MEDIUM
MEDIUM
NORMAL
Configuration - Configuration Record Sheet
92 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
This page has been intentionally left blank
Release M DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 93
May 2013
4. Configuration Parameter Definitions
4.1 Overview
Introduction
This section provides information for all the user-configurable control parameters listed in the
configuration section. If you aren't familiar with these parameters, this section gives you the parameter
prompt, the selection or range of setting that you can make, and a definition of how each parameter setting
affects recorder performance. It will also refer you to any other prompts that might be affected by your
selection.
Parameter groups and prompts
The control information is found in three configuration groups which are accessed by the SET UP key.
Each of these groups contains prompts, viewed in the lower display, which deal with functions that are
pertinent to that particular group. These are accessed by pressing the FUNC key.
The selections or values are listed in the upper display. Refer to Section 3 - Configuration for step by
step instructions.
What’s in this section?
The table below lists the topics that are covered in this section. They are listed in the order of their
appearance in the recorder.
Topic
See Page
4.1 Overview
93
4.2 Input Parameters Set Up Group
94
4.3 Pen Parameters Set Up Group
98
4.4 Chart Parameters Set Up Group
100
4.5 Time Parameters Set Up Group
103
4.6 Total Parameters Set Up Group
104
4.7 Input Algorithm Set Up Group
106
4.8 Control Parameters Set Up Group
109
4.9 Tuning Parameters Set Up Group
118
4.10 Setpoint Ramp Set Up Group
121
4.11 Timer Set Up Group
123
4.12 Alarms Set Up Group
124
4.13 Auxiliary Output Set Up Group
127
4.14 Modbus Communications Set Up Group
129
4.15 Options Set Up Group
130
4.16 Event Message Set Up Group
132
4.17 Lockout Parameters Set Up Group
133
4.18 Printing Characteristics Adjustments
134
Configuration Parameter Definitions - Input Parameters Set Up Group
94 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
4.2 Input Parameters Set Up Group
Introduction
These are the parameters required for input 1, 2, 3, or 4; temperature units, decimal location, actuation,
transmitter characterization, high and low range values in engineering units, input compensation, filter, and
burnout.
Input group prompts
Table 4-1 lists all the function prompts in the Input 1, 2, 3, or 4 setup group and their definitions.
Table 4-1 Input Group Definitions
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
Input n n=1 - 4
ENABLE/DISABLE parameter
DECIMAL
XXXX
XXX.X
XX.XX
X.XXX
DECIMAL POINT LOCATION -- This selection
determines where the decimal point appears in the
display.
None
One Place
Two Places
Three Places
NOTE: Auto-ranging will occur when one decimal
position has been selected and the value increases
above 999.9 but auto-ranging will not similarly occur
when two decimal positions are selected.
UNITS
DEG F
DEG C
EU
TEMPERATURE UNITS -- This selection will be
indicated on the PV display.
If you select EU, go to prompt “ENGUNITS”
Degrees Fahrenheit
Degrees Celsius
Engineering Units
ENGUNITS
0 to 9
A to Z
+
/
(blank)
ENGINEERING UNITS Make up 5 selections to create
unit identifier.
For example, create unit identifier H
2
O by selecting
an “H” from A to Z, a “2” from 0 to 9, and an “O” from
A to Z.
For alphanumeric entries, the display will cycle, from
left to right, with highlighting (increased brightness) of
each digit. The value of each digit can be changed
only when it is highlighted.
Configuration Parameter Definitions - Input Parameters Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 95
April 2017
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
INn TYPE
(n = 1, 2, 3, or 4)
B TC
E TC H
E TC L
J TC H
J TC L
K TC H
K TC L
NNM
TC
1
NIC TC
1
R TC
1
S TC
T TC H
T TC L
W TC H
1
W TC L
1
100 PT
200 HI
2
200 LO
2
500 PT
100 RH
4-20mA
0-10mV
10-50m
0-5 V
0-10 V
RADIAM
INPUT ACTUATION TYPE -- This selection determines
what actuation you are going to use for input one. Be
sure that the values configured for high and low chart
range, soak setpoint, alarm setpoint, etc. are within the
measuring range for the selected actuation type.
B thermocouple 105 to 3300°F 41 to 1815°C
E thermocouple high 454 to 1832°F 270 to 1000°C
E thermocouple low 200 to 1100°F 129 to 593°C
J thermocouple high 0 to 1600°F 18 to 871°C
J thermocouple low 20 to 770°F 7 to 410°C
K thermocouple high 320 to 2500°F 196 to 1371°C
K thermocouple low 20 to 1000°F 29 to 538°C
NNM NiNiMo
thermocouple 32 to 2500°F 0 to 1371°C
NIC Nicrosil-Nisil
thermocouple 0 to 2372°F 178 to 1300°C
R thermocouple 0 to 3100°F 18 to 1704°C
S thermocouple 0 to 3100°F 18 to 1704°C
T thermocouple high 300 to 700°F 184 to 371°C
T thermocouple low 200 to 500°F 129 to 316°C
W5W26 thermocouple
high 0 to 4200°F 18 to 2316°C
W5W26 thermocouple
low 0 to 2240°F 18 to 1227°C
100 OhmRTD 300 to 1200°F 184 to 649°C
200 OhmRTD 32 to 752 0 to 400
200 OhmRTD 32 to 392 0 to 200
500 OhmRTD 300 to 900°F 184 to 482°C
100 OhmRTD 130 to 392°F 90 to 200°C
4 to 20 Milliamps
3
0 to 10 Millivolts
3
10 to 50 Millivolts
3
0 to 5 Volts
3
0 to 10 Volts
3
Radiamatic 1400 to 3400°F 760 to 1871°C
1
Only available with Model DR45AT
2
Only available with Model DR45AR
3
Go to prompt “XMITTER” to characterize the input.
Configuration Parameter Definitions - Input Parameters Set Up Group
96 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
XMITTER
B TC
E TC H
E TC L
J TC H
J TC L
K TC H
K TC L
NNM H
NIC TC
R TC
S TC
T TC H
T TC L
W TC H
W TC L
100 PT
500 PT
100 RH
LINEAR
SQROOT
TRANSMITTER CHARACTERIZATION This
selection lets you instruct the recorder to characterize a
linear input to represent a nonlinear one.
NOTE: Prompt only appears when a linear actuation
is selected at prompt ‘IN1 TYPE”.
FOR EXAMPLE: If input 1 is a 4 to 20 mA signal, but
the signal represents a type "K" thermocouple; select
"K TC H" and the recorder will characterize the 4 to
20 mA signal so that it is treated as a type "K"
thermocouple input (high range).
B Type Thermocouple
E Type Thermocouple High
E Type Thermocouple Low
J Type Thermocouple High
J Type Thermocouple Low
K Type Thermocouple High
K Type Thermocouple Low
NNM NiNiMo Type Thermocouple High
NIC Nicrosil Nisil Thermocouple
R Type Thermocouple
S Type Thermocouple
T Type Thermocouple High
T Type Thermocouple Low
W5W26 Type Thermocouple High
W5W26 Type Thermocouple Low
100 OhmRTD
500 OhmRTD
100 Ohm RTD
Linear Range
Extracts Square Root
INn HI
(n = 1, 2, 3, or 4)
999.9 to 9999.
or
999 to 9999
in engineering units
INPUT HIGH RANGE VALUE in engineering units is
displayed for all inputs but can only be configured for
linear or square root transmitter characterization.
Otherwise, this is a read-only display of the higher range
value for the selected T/C or RTD input including
transmitter characterization, if applicable.
Scale the #1 input signal to the display value you
want for 100 %.
EXAMPLE:
Actuation (Input) = 4 mA to 20 mA
Process Variable = Flow
Range of Flow = 0 to 250 Gal/Min
High Range display value = 250
Then 20 mA = 250 Gal/Min
The control setpoint will be limited by the range of units
selected here.
Configuration Parameter Definitions - Input Parameters Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 97
April 2017
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
INn LO
(n = 1, 2, 3, or 4)
999.9 to 9999.
or
999 to 9999
in Engineering units
INPUT LOW RANGE VALUE in engineering units is
displayed for all inputs but can only be configured for
linear or square root transmitter characterization.
Otherwise, this is a read-only display of the low range
value for the selected T/C or RTD input including
transmitter characterization, if applicable.
Scale the input signal to the display value you want
for 0 %. See example on previous page. The control
setpoint for Input will be limited by the range of units
selected here.
CUTOFF n
(n = 1, 2, 3, or 4)
0 to 100 % of Input Range
LOW FLOW CUTOFFLets you set a value in percent
of range below which the applicable totalizer does not
increment.
ATTENTION
Prompt appears only if totalizer option
is present in the recorder.
BIAS n n = 1 4
999.9 to 9999.
INPUT COMPENSATION used to compensate the
input for drift of an input value due to deterioration of a
sensor, or some other cause; select the value you want
on the input.
FILTER n
(n = 1, 2, 3, or 4)
0 to 120 seconds
No filter = 0
FILTER FOR INPUT a software digital filter is
provided for the input to smooth the input signal. You
can configure the first order lag time constant from 1 to
120 seconds. If you do not want filtering, enter 0.
BURNOUT
NONE
UP
DOWN
BURNOUT PROTECTION (SENSOR BREAK) provides
most input types with upscale or downscale protection if
the input fails.
Not available for inputs 0-5 V, 0-10 V, or 4-20 mA.
NO BURNOUT Failsafe output applied for failed
input.
UPSCALE BURNOUT will make the indicated PV signal
increase when a sensor fails, and flash the upper
display.
DOWNSCALE BURNOUT will make the indicated PV
signal decrease when a sensor fails, and flash the upper
display.
NOTE: For no Burnout (that is, “None”) to function
properly on a linear input, there must be a dropping
resistor directly across the input terminals (that is, not
remote), then the unit can detect the “zero” voltage that
occurs when the 4-20 mA line is opened.
EMISSIV
.01 to 1.00
EMISSIVITY is a correction factor applied to the
Radiamatic input signal that is the ratio of the actual
energy emitted from the target to the energy which
would be emitted if the target were a perfect radiator.
Available only for “Radiamatic” inputs.
Repeat the procedure for INPUT 2, INPUT 3, and INPUT 4 configuration.
Configuration Parameter Definitions - Pen Parameters Set Up Group
98 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
4.3 Pen Parameters Set Up Group
Introduction
The functions listed in this group deal with how to configure pen #1, pen #2, pen #3, or pen #4. The
procedure for configuring each pen is the same. The prompts shown in Table 4-2 show PEN 1.
Press the SET UP key until PEN 1, PEN 2, PEN 3, or PEN 4 appears in the display.
Pen 1-2-3-4 group prompts
Table 4-2 lists all the function prompts in the Pen 1, 2, 3, 4 set up groups and their definitions.
Table 4-2 Pen 1, 2, 3, or 4 Group Definitions
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
PENn
(n - 1, 2, 3 or 4)
ENABLE
DISABL
PEN RECORD This selection lets you enable or
disable the pen (channel) record
Remember, the lower display prompt could read
PEN2, PEN3, or PEN4.
PENnIN
(n = 1, 2, 3 or 4)
INPUT 1
INPUT 2
INPUT 3
INPUT 4
RH
OUTPT1
OUTPT2
SETPT1
SETPT2
DGTL1
DGTL2
PV1
PEN INPUTWhat do you want the pen to record?
INPUT 1records Input 1
INPUT 2records Input 2
INPUT 3records Input 3
INPUT 4records Input 4
RELATIVE HUMIDITYrecords in % RH. It initiates an
external calculation for measuring relative humidity.
INPUT 1, IN TYP must be configured for 100 PT. INPUT
2, IN TYP must be configured for 100 RH. The RH
prompt only appears when RELHUMID prompt in the
OPTIONS group is configured as YES.
OUTPUT 1records Output 1
OUTPUT 2records Output 2
SETPOINT 1records Setpoint 1
SETPOINT 2records Setpoint 2
DIGITAL 1 INPUTrecords EVENT pen function on
contact closure across digital 1 input.
DIGITAL 2 INPUTrecords EVENT pen function on
contact closure across digital 2 input.
PV1records calculated PV1 when an input algorithm
(INP ALG) has been selected in the Options group.
(Available only in units with software Math Option.)
CHARTnHI
(n = 1, 2, 3 or 4)
999.0 to 999
CHART HIGH RANGE VALUEEnter a value that
corresponds with the chart high range value for
pen 1 (pen 2, pen 3, or pen 4).
CHARTnLO
(n = 1, 2, 3 or 4)
999.0 to 999
CHART RANGE LOW VALUEEnter a value that
corresponds with the chart low range value for
pen 1 (pen 2, pen 3, or pen 4).
Configuration Parameter Definitions - Pen Parameters Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 99
April 2017
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
PENnON
(n = 1, 2, 3 or 4)
0 to 100 %
PEN CHART POSITION FOR ON EVENT This is the
event marker configuration using digital inputs.
Select the chart position where pen 1 (pen 2, pen 3, and
pen 4) is to mark (trace) occurrence of an ON event.
Prompt only appears if DGTL1 or 2 is selected as pen
1 (pen 2, pen 3, or pen 4) input.
PENnOFF
(n = 1, 2, 3 or 4)
0 to 100 %
PEN CHART POSITION FOR OFF EVENT This is
the event marker configuration using digital inputs.
Select the chart position where Pen 1 (pen 2, pen 3, and
pen 4) is to mark (trace) occurrence of an OFF event.
Prompt only appears if DGTL1 or 2 is selected as
pen 1 (pen 2, pen 3, or pen 4) input.
MAJORDIV
2 to 10
MAJOR CHART DIVISIONS This is the number of
Major Divisions in range of chart 1 (2, 3, or 4) scale
(between CHART1HI and CHART1LO). Must divide
evenly into chart range.
ATTENTION
The values of major divisions are now
printed with decimal points when possible. The
restriction is four characters, including the decimal and
() sign.
EXAMPLES:
Pen Range
Print Format
0 to 99
XX.X
0 to 9
X.XX
9 to 9
XX.X
99 to 99
XXX
0 to 999
XXX
MINORDIV
2 to 10
MINOR CHART DIVISIONS This is the number of
Minor Divisions in range of chart 1 (2, 3, or 4) scale
(increments in each Major Division).
RNGnTAG
(n = 1, 2 , 3 or 4)
0 to 9
A to Z
+
/
(blank)
RANGE 1 TAG NAME Enter a tag name for chart 1
(2, 3, or 4) range. It can be up to 5 characters.
For alphanumeric entries, the display will cycle, from
left to right, with highlighting (increased brightness) of
each digit. The value of each digit can only be
changed when it is highlighted.
Repeat this procedure for PEN 2, PEN 3, and PEN 4 configuration.
Configuration Parameter Definitions - Chart Parameters Set Up Group
100 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
4.4 Chart Parameters Set Up Group
Introduction
The functions listed in this group deal with how the chart will be set up. It includes time divisions, speed,
name, rotation, header, remote activation, and wake time parameters that have to be set for the proper chart
function.
CAUTION
Before making any configuration changes to the “Chart” Set Up group, place the recorder in
“Chart Hold”. Press the CHART key to stop the chart rotation. Press again after configuration
entry is made.
Chart group prompts
Table 4-3 lists all the function prompts in the chart parameters setup group and their definitions.
Table 4-3 Chart Parameters Group Definitions
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
CHRTSPD
8HR
12HR
24HR
7DAYS
XHR
CHART SPEED This is the time it will take to drive
the chart one complete revolution.
8 Hour revolution
12 Hour revolution
24 Hour revolution
7 Day revolution
X hour revolution - make Hours per Revolution selection
at prompt “HOUR/REV”.
ATTENTION
If the chart speed selection is 8 hr/8
division, 12 hr/12 division, 24 hr/24 division, 7 day/14
division, or 7 day/21 division, then standard chart has
been selected.
This means that the chart will be printed with the time
lines on the hour. Limited information will be printed on
the chart during the first incomplete segment following
chart initiation and before the first valid hour mark.
NOTE: If X hour chart is selected, standard charts are
disabled.
HOUR/REV
6 to 744 Hours
(12 hrs for abrasion resistant
pen)
HOURS PER REVOLUTION Set the desired chart
speed. Appears only if XHR was selected at prompt
“CHRT SPD”.
ATTENTION
Below 8-hour chart speed (24 hours
with abrasion resistant pen) printing may be degraded.
Configuration Parameter Definitions - Chart Parameters Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 101
April 2017
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
TIME DIV
MAJOR
TIME DIV
MINOR
8 to 24 time periods
Software set for 4 or 8
seg/minor time divisions
TIME DIVISION This is the number of time periods
into which the chart record is to be divided.
TIME PERIOD
21422
ATTENTION
Make sure that the chart selected is
evenly divisible into the time periods. For example: 7
day = 14 or 21 lines.
CONTINUE
YES
NO
CONTINUE CHART ROTATION Do you want to
continue or stop the chart drive after a single 360°
rotation.
Yescontinue chart drive
No—stop chart drive (If “NO” is selected, chart paper
must be replaced for proper printout.)
CHARTNAM
0 TO 9
A TO Z
+
/
(BLANK)
CHART NAME - This is where you determine the chart
name identifier. For example: TRULINE/4.
For alphanumeric entries, the display will cycle, from
left to right, with highlighting (increased brightness) of
each digit.
The value of each digit can be changed only when it
is highlighted.
HEADER
YES
NO
HEADER FOR CHART Is the header to be printed
each time the recorder goes from chart hold to chart run
the CHART key is pressed.
HEADER EXAMPLE
14:57________
08/25/93
<010:020> TRULIN
Chart Ranges
(Lo-Hi)
Date (mo/day/yr)
Pen (channel)
nos.
Chart Speed
Time Division
Chart
Name
Engineering
Units
21423
P1 = 0 TO 350
P2 = 50 TO 450
P3 = 0 TO 1000
P4 = 450 TO 50
PSI
GPM
PSI
GPM
Time (24 HR
clock)
If you select “NO” only the chart name will be printed.
Configuration Parameter Definitions - Chart Parameters Set Up Group
102 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
REM CHRT
NONE
EXT SW1
EXT SW2
ALARM 1
ALARM 2
TIME
ALARM 3
ALARM 4
ALARM 5
ALARM 6
REMOTE CHART ACTIVATION Select the desired
function to activate the chart from a remote location or
an internal signal.
NONE - No selection
EXT SW 1 - External Switch #1 activates chart
(DIgital Input #1)
EXT SW 2 - External Switch #2 activates chart
(Digital Input #2)
ALARM 1 - Alarm 1 activates chart
ALARM 2 - Alarm 2 activates chart
TIME - Wake Time activates chart
ALARM 3 - Alarm 3 activates chart
ALARM 4 - Alarm 4 activates chart
ALARM 5 - Alarm 5 activates chart
ALARM 6 - Alarm 6 activates chart
If you select “TIME”, set wake minutes at prompt
“WAKE MIN” and wake hours at prompt “WAKE HR”
in Time Set Up group.
Configuration Parameter Definitions - Time Parameters Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 103
April 2017
4.5 Time Parameters Set Up Group
Introduction
The functions listed in this group deal with how to configure the real-time in minutes, hours, days, months,
and years. There is also a selection for days of the week.
Time group prompts
Table 4-4 lists all the function prompts in the Time parameters setup group and their definitions.
Table 4-4 Time Parameters Group Definitions
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
MINUTES
0 to 59
REAL-TIME IN MINUTES Set the present time in
minutes.
HOURS
0 to 23
REAL-TIME IN HOURS Set the hour in 24 HR clock
format.
DAY
1 to 31
REAL-TIME IN DAYS Set a number corresponding
to a day.
MONTH
1 to 12
REAL-TIME IN MONTHS Set a number
corresponding to a month.
YEAR
0 to 99
REAL-TIME IN YEARS Set a number
corresponding to a year.
DAY
MONDAY
TUEDAY
WEDDAY
THRDAY
FRIDAY
SATDAY
SUNDAY
DAY OF THE WEEK Select a day of the week.
WAKE MIN
0 to 59
WAKE MINUTES Wake time specifies time, in
minutes, at which Wake Time Event occurs.
WAKE HR
0 to 23
WAKE HOUR Wake time specifies time, in hours, at
which Wake Time Event occurs.
WAKE DAY
0 to 31
WAKE DAY Wake time specifies time, in days, at
which Wake Time Event occurs.
ATTENTION
If day is set to “0”, the wake up day
and month are ignored and only a successful match of
the hours and minutes will cause the event.
WAKE MON
1 to 12
WAKE MONTH Wake time specifies time, in months,
at which Wake Time Event occurs.
Configuration Parameter Definitions - Total Parameters Set Up Group
104 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
4.6 Total Parameters Set Up Group
Introduction
The functions listed in this group deal with the calculation and display of the total flow volume as
measured by Input 1 (Total 1), or Input 2 (Total 2). The displayed value is eight digits with a configurable
scale factor.
Totalizer 1 and 2 group prompts
Table 4-5 lists all the function prompts in the Totalizer 1 and 2 Set Up group and their definitions.
Table 4-5 Totalizer Group Definitions
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
(Actual Current
totalized value)
(Current scale factor)
Example: E1 GPM
VIEW CURRENT TOTALIZED VALUE this selection
lets you view the current totalized value.
In the example shown, E1 represents exponential
value of total (total times 10
1
). GPM represents total
engineering units selected.
See “SCALER” and “TOTAL EU” function prompts in
this group for selections.
RSETTOT
YES
NO
RESET TOTALIZER TO ZERO this selection lets
you reset the totalizer to zero.
Selecting YES will reset the totalizer to zero.
Function prompt “RSETABLE” must be set to “LOCAL”.
TOTAL1
TOTAL2
DISABL, INPUT 1, INPUT 2,
INPUT 3, INPUT 4, PV1,
E TIME
TOTALIZATION FOR INPUT 1 OR 2 this selection
allows you to select the input to Totalizer 1 or 2.
E TIME accumulates elapsed time since last reset in
the units specified under RATE function.
Not DISABL allows selection of the rest of the
prompts associated with totalization.
TOTALEU
0 to 9
A to Z
+
/
(blank)
TOTAL ENGINEERING UNITS this selection allows
you to make up to 3 selections to create a unit identifier
that the total represents.
For alphanumeric entries, the display will cycle, from
left to right, with highlighting (increased brightness) of
each digit. The value of each digit can be changed
only when it is highlighted.
Configuration Parameter Definitions - Total Parameters Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 105
April 2017
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
RATE
SECOND
MINUTE
HOUR
DAY
M/DAY
RATE OF INTEGRATION This selection allows you
to select the desired rate of integration. It must match
input units:
Example:
GPM must use “MINUTE”
PPH must use “HOUR”
SECOND - EU (Engineering Units) per second.
MINUTE - EU per minute
HOUR - EU per hour
DAY - EU per day
M/DAY - Millions of Units per day (multiplier) 10
6
x input
SCALER
1
10
100
1000
10000
100000
1E6
TOTALIZER SCALE FACTOR this selection allows
you to select a scale factor (that is, a Multiplier) for the
totalizer display. It affects only the display.
The desired factor is applied to the calculated value
to extend the maximum flow range that can be
displayed.
Scaler selection does not affect the totalization value
printed on the chart.
EXAMPLE:
1E6 equals 1 times 10
6
. (1,000,000)
RSETABLE
NO
LOCAL
EXT SW1
EXT SW2
TIME
LOCAL TOTALIZER RESET Allows the totalizer
value to be reset via the display/keypad.
EXTERNAL SWITCH 1Allows the totalizer to be set
to zero upon switch #1 closure. (Digital Input #1)
EXTERNAL SWITCH 2Allows the totalizer to be set
to zero upon switch #2 closure. (Digital Input #2)
WAKE TIMEResets the totalizer when the value
configured for the Wake Time Event is reached. (See
WAKE MIN, WAKE HR, WAKE DAY, WAKE MON in the
Time Set Up group.)
INHIBIT
NONE
S1 OPEN
S1 CLOSE
S2 OPEN
S2 CLOSE
The totalizer will be inhibited while the configured action
is true.
External SW1 open inhibits totalizer.
External SW1 closed inhibits totalizer.
External SW2 open inhibits totalizer.
External SW2 closed inhibits totalizer.
Repeat the configuration for TOTAL 2.
Configuration Parameter Definitions - Input Algorithm Set Up Group
106 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
4.7 Input Algorithm Set Up Group
Introduction
The Input Algorithm Set Up Group lets you apply various math algorithms to the inputs.
Prompts
Table 4-6 lists all the function prompts in the Input Algorithm set up group and their functions.
Table 4-6 Input Algorithm Group Definitions
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
INP ALG
INPUT ALGORITHM has the following selections from
which to choose:
ATTENTION
If the input is disabled, the
corresponding term is set to 1 except if the Summer
(A+B+C) is selected in which case the term is set to 0.
The calculated PV1 can be the pen 1-4 source as well
as the input to totalizer 1. The ratio and bias values are
still applied so that the term corresponding to the
unused input can be made into any constant value.
NONE
NONENo algorithm configured
A+B+C (NOTE 1)
SUMMER WITH RATIO AND BIASThe following
formula applies:
PV = K x (Input 1xRatio A+Bias A) + (Input 2xRatio B+Bias B) + (Input 3xRatio C+Bias C)
√A*B/C (NOTE 1)
MULTIPLIER DIVIDER WITH SQUARE ROOTThe
following formula applies:
PV = K x
Error!x (PV
HI
PV
LO
)
√A*B*C (NOTE 1)
MULTIPLIER WITH SQUARE ROOTThe following
formula applies:
PV = K x
Error!x (PV
HI
PV
LO
)
A*B/C (NOTE 1)
MULTIPLIER DIVIDERThe following formula applies:
PV = K x
Error!x (PV
HI
PV
LO
)
A*B*C (NOTE 1)
MULTIPLIERThe following formula applies:
PV = K x (Input 1xRatio A+Bias A)x(Input 2xRatio B+Bias B)x(Input 3xRatio C+Bias C) x (PV
HI
PV
LO
)
Configuration Parameter Definitions - Input Algorithm Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 107
April 2017
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
AB*C (NOTE 1)
SUBTRACTOR MULTIPLIERFor BTU calculations.
The following formula applies:
PV = Kx [(Input 1xRatio A+Bias A)(Input 2xRatio B+Bias B)]x(Input 3xRatio C+Bias C)
LO SEL
LOW SELECTPV is the lower of INPUT 1 or INPUT
2.
HI SEL
HI SELECTPV is the higher of INPUT 1 or INPUT 2.
COEFF
0.00 to 99.00
K CONSTANTAppears only if a selection is made at
“INP ALG” prompt.
PV HIGH
999 to 9999
CALCULATED PV HIGH LIMITOnly applicable for
algorithms “√A*B/C”, “√A*B*C”, “A*B/C”, “A*B*C”.
PV LOW
999 to 9999
CALCULATED PV LOW LIMITOnly applicable for
algorithms “√A*B/C”, “√A*B*C”, “A*B/C”, “A*B*C”.
RATIO A
20 to 20
RATIO FOR INPUT 1—Used with the “A” term in the
match equation selected at prompt “INP ALG”.
BIAS A
999 to 9999
BIAS FOR INPUT 1—Used with the “A” term in the
math equation selected at prompt “INP ALG”.
RATIO B
20 to 20
RATIO FOR INPUT 2—Used with the “B” term in the
math equation selected at prompt “INP ALG”.
BIAS B
999 to 9999
BIAS FOR INPUT 2—Used with the “B” term in the
math equation selected at prompt “INP ALG”.
RATIO C
20 to 20
RATIO FOR INPUT 3—Used with the “C” term in the
math equation selected at prompt “INP ALG”.
BIAS C
999 to 9999
BIAS FOR INPUT 3—Used with the “C” term in the
math equation selected at prompt “INP ALG”.
POLYNOM
NONE, INPUT 1, INPUT 2,
INPUT 3, INPUT 4
POLYNOMIAL EQUATION - A fifth order Polynomial
Equation can be used on any one of the four Analog
Inputs.
The equation is in the form:
Y = C
5
* 10
-7
X
5
+ C
4
* 10
-5
X
4
+ C
3
* 10
-3
X
3
+ C
2
* 10
-1
X
2
+ C
1
X +C
0
Where:
X is the analog input selected in % of span
X% =
X EU
Span EU
100
C
0
is a value between 99.99 to +99.99
C
1
- C
5
are values between 9.999 to +9.999
C0 VALUE
99.99 to 99.99
Polynomial coefficient C0
C1 VALUE
9.999 to 9.999
Polynomial coefficient C1
C2x10-1
9.999 to 9.999
Polynomial coefficient C2
C3x10-3
9.999 to 9.999
Polynomial coefficient C3
Configuration Parameter Definitions - Input Algorithm Set Up Group
108 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
C4x10-5
9.999 to 9.999
Polynomial coefficient C4
C5x10-7
9.999 to 9.999
Polynomial coefficient C5
NOTE 1: A = (Input 1 x Ratio A + Bias A)
B = (Input 2 x Ratio B + Bias B)
C = (Input 3 x Ratio C + Bias C)
The order of the inputs are fixed in the equations.
Configuration Parameter Definitions - Control Parameters Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 109
April 2017
4.8 Control Parameters Set Up Group
Introduction
The functions listed in this group deal with how the DR4500A will control the process including: number
of tuning parameter sets, setpoint source, ratio, bias, tracking, power-up recall, setpoint limits, output
direction and limits, deadband and hysteresis, control algorithm, output algorithm, and the current duplex
range. There are two control groups.
Control group prompts
Table 4-7 lists all the function prompts in the Control 1 or Control 2 set up groups and their definitions.
Table 4-7 Control 1 or 2 Group Definitions
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
CONTROL 1
ENABLE
DISABL
CONTROL 1 allows you to enable or disable control
loop #1.
PID SETS
NUMBER OF TUNING PARAMETER SETS this
selection lets you choose one or two sets of tuning
constants (gain, rate, and reset).
1 ONLY
ONE SET ONLY only one set of tuning parameters is
available. Configure the values for:
Gain (proportional band)
Rate
Reset Time
Cycle Time (if time proportional is used)
2KEYBD
TWO SETS KEYBOARD SELECTABLE two sets of
tuning parameters can be configured and can be
selected at the operator interface.
Press LOWR DISP key until you see "PID SET1" or
“PID SET2” to switch between sets. Configure the
values for:
Gain, Rate , Reset, Cycle Time
Gain #2, Rate #2, Reset #2, Cycle #2 Time
2PV SW
TWO SETS PV AUTOMATIC SWITCHOVER when
the process variable is GREATER than the value set at
prompt "SW VALUE" (Switchover Value), the recorder
will use Gain, Rate, Reset, and Cycle Time. The active
PID SET can be read in the lower display.
When the process variable is LESS than the value
set at prompt "SW VALUE," the recorder will use
Gain #2, Rate #2, Reset #2, and Cycle #2 Time. The
active PID SET can be read in the lower display.
Other prompts affected: SW VALUE
Configuration Parameter Definitions - Control Parameters Set Up Group
110 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
PID SETS
(continued)
2SP SW
TWO SETS SP AUTOMATIC SWITCHOVER when
the setpoint is GREATER than the value set at prompt
"SW VALUE" (Switchover Value), the recorder will use
Gain, Rate, Reset, and Cycle.
When the setpoint is LESS than the value set at
prompt "SW VALUE," the recorder will use Gain #2,
Rate #2, Reset #2, and Cycle #2.
Other prompts affected: SW VALUE
SW VALUE
999.0 to 9999
AUTOMATIC SWITCHOVER VALUE this is the value
of process variable or setpoint at which the recorder will
switch from Tuning Constant Set #2 to Set #1. Only
appears when PID SETS selections “2PV SW” or “2SP
SW” are selected.
SP SOURC
SETPOINT SOURCE this selection determines what
your setpoint source will be; One local or Two local.
Toggled by the “SETPOINT SELECT” key.
1LOCAL
LOCAL SETPOINT the setpoint entered from the
keyboard or from the setpoint program.
REMOTE
REMOTE SETPOINT a signal is brought in through
the second input printed circuit board connector J2 and
used as the control setpoint.
If you select “REMOTE”, Input #3 is automatically
assigned as your RSP source for CONTROL #1;
INPUT #4 is assigned for CONTROL #2. However, if
the unit has only 2 inputs then RSP will be on input 2.
Ratio and Bias can be applied to the remote setpoint.
Mutually exclusive with 2 Local setpoints.
Other prompts affected: RATIO, BIAS.
2LOCAL
TWO LOCAL SETPOINTS this selection lets you
switch between two local setpoints. Mutually exclusive
with Remote setpoint.
OUT2
Only for Loop 1 Setpoint is the output of Control Loop
2.
RATIO
20.00 to 20.00
RATIO used when input 2* operates as a remote
setpoint, prompt "REMOTE."
This ratio value can be applied to the remote setpoint.
It establishes the correct relationship between the
remote setpoint and the input 2 signal applied
according to the formula below (under Bias).
Input 2 must be enabled.
*For recorders with two controllers, use input 3 for
controller #1 and input 4 for controller #2.
Configuration Parameter Definitions - Control Parameters Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 111
April 2017
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
BIAS
9999 to 9999
(engineering units)
BIAS used when input 2 operates as a remote
setpoint (prompt "REMOTE").
Bias, together with ratio, establishes the correct
relationship between the remote setpoint and the
input 2 signal applied according to the formula:
REMOTE SETPOINT = IN2 VALUE (RATIO) + BIAS
NOTE: IN2 VALUE = Actual (engineering units)
All values must be within configured setpoint high and
low limits.
Input 2 must be enabled.
SP TRACK
SETPOINT TRACKING the local setpoint can be
configured to track the remote setpoint as listed below:
NONE
NO TRACKING if local setpoint tracking is not
configured, the LSP will not be altered when transfer
from RSP to LSP is made.
RSP
LSP (LOCAL SETPOINT) TRACKS RSP (REMOTE
SETPOINT) IN AUTO if configured, when the
recorder transfers out of remote setpoint, the last
value of the remote setpoint (RSP) is inserted into the
local setpoint.
POWER UP
POWER UP CONTROLLER MODE RECALL this
selection determines which mode and setpoint the
recorder will use when the it restarts after a power loss.
Select one from below:
MANUAL
MANUAL, LSP at power-up, the recorder will use
manual mode with the output value displayed.
A LSP
AUTOMATIC, LOCAL SETPOINT at power-up,
the recorder will return to the automatic mode and will
use the local setpoint for control.
A RSP
AUTOMATIC, REMOTE SETPOINT at power-up,
the recorder will return to the automatic mode and will
use the remote setpoint for control.
AM SP
LAST MODE, LAST SETPOINT used before power
down.
AM LSP
LAST MODE, LAST LOCAL SETPOINT on power
down.
PWR OUT
POWER UP OUTPUT SELECTION (for 3P Step
Control only) this selection determines what position
the motor will be in when powered up.
LAST
LAST at power up in automatic mode, the motor
position will be the last one prior to power down. When
the unit goes into FAILSAFE, it will stay in automatic
mode; motor will not be driven to the configured
Failsafe position.
Configuration Parameter Definitions - Control Parameters Set Up Group
112 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
PWR OUT
(continued)
FAIL SF
FAIL SF at power up in manual mode, the motor will
be driven to either the 0 % or 100 % output position,
whichever is selected at prompt “FAILSAFE”. When the
unit goes into FAILSAFE, it will go to manual mode;
motor will be driven to the configured Failsafe position.
SP HILIM
999.0 to 9999.
input units
SETPOINT HIGH LIMIT* this selection prevents the
local and remote setpoints from going above the value
selected here. The setting must be equal to or less than
the upper range of input 1 and input 2. Input 2,** when
configured for remote setpoint, will be restricted to this
upper limit.
SP LOLIM
-999.0 to 9999.
inputs units
SETPOINT LOW LIMIT* this selection prevents the
local and remote setpoints from going below the value
selected here. The setting must be equal to or greater
than the lower range of input 1 and input 2. Input 2,**
when configured for remote setpoint, will be restricted to
this lower limit.
ACTION
CONTROL OUTPUT DIRECTION in what direction
do you want the recorder output to go when the process
variable increases.
DIRECT
DIRECT ACTING CONTROL the recorder's output
increases as the process variable increases.
REVRSE
REVERSE ACTING CONTROL the recorder's output
decreases as the process variable increases.
OUTHILIM
5.0 to 105.0 % of output
HIGH OUTPUT LIMIT this is the highest value of
output beyond which you do not want the recorder
automatic output to exceed. Use 0 % to 100 % for time
proportional output type.
OUTLOLIM
5.0 to 105.0 % of output
LOW OUTPUT LIMIT this is the lowest value of
output below which you do not want the recorder
automatic output to exceed. Use 0 % to 100 % for time
proportional output type.
DROPOFF
5 to 105.0 % of output
CONTROLLER DROPOFF VALUE select an output
value that below which the recorder output will dropoff to
the low output limit value set in prompt "OUT LOLIM."
DEADBAND
5.0 to 25.0 %
0 to 25.0 %
0.5 to 5.0 %
DEADBAND is an adjustable gap between the
operating ranges of output 1 and output 2 in which
neither output operates (positive value) or both outputs
operate (negative value). It is the difference between the
nominal trip points of relay 1 and relay 2.
Time Duplex
On-Off Duplex
Position Proportional
*The Local Setpoint will automatically adjust itself to be within the setpoint limit range. For example, if SP
= 1500 and the SP HILIM is changed to 1200, the new Local Setpoint will be 1200.
** Applies for Input 3 and Input 4 for recorders with two controllers.
Configuration Parameter Definitions - Control Parameters Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 113
April 2017
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
OUT HYST
0.0 to 5.0 % of PV span
HYSTERESIS (OUTPUT RELAY ONLY) is an
adjustable overlap of the ON/OFF states of each control
output. This is the difference between the value of the
process variable at which the control outputs energize
and the value at which they de-energize. Only
applicable for ON-OFF control.
FAILSAFE
0 to 100 %
FAILSAFE OUTPUT VALUE the output level used
when you have communications SHED or when NO
BURNOUT is configured and input 1 fails.
100PCT
0PCT
For 3 Position Step Control
100PCT motor position set to 100 % output position
0PCT motor position set to 0 % output position
REM SW
REM SW2
REMOTE SWITCHING (DIGITAL INPUT) contact
closure enables one of the following:
NONE
NO DIGITAL INPUT SELECTION
TO MAN
TO MANUAL contact closure selects Manual mode.
TO LSP
TO LOCAL SETPOINT contact closure selects the
local setpoint.
TO 2SP
TO LOCAL SETPOINT 2 contact closure selects
local setpoint 2.
TO DIR
TO DIRECT ACTION contact closure selects Direct
Control Action.
RN/HLD
RUN/HOLD contact closure suspends setpoint
Ramp/Program. Contact open resumes.
TUNE
AUTOTUNE contact closure initiates Autotune.
TIMER
TIMER starts the timer, if enabled.
The Timer can also be started by the RH KEY or
ALARM2. These parameters are found under the Timer
set up group.
MAN KEY
ENABLE
DISABL
MANUAL MODE KEY SELECTION make selection
to enable or disable the Manual Mode selection through
the MAN/AUTO key.
ENABLE allows you to use the MAN/AUTO key to
select Manual Mode.
DISABLE disables the MAN/AUTO key.
Configuration Parameter Definitions - Control Parameters Set Up Group
114 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
PBorGAIN
Note: GAIN must
be used with
settings of TIME D
(TIME DUPLEX) or
TI CUR (TIME
CURRENT)
PROPORTIONAL BAND UNITS select one of the
following for the Proportional (P) term of the PID
algorithm:
PB PCT
PROPORTIONAL BAND selects units of percent
proportional band for the P term of the PID algorithm,
where:
PB % = 100 % FS
GAIN
GAIN
GAIN selects the unitless term of gain for the P term
of the PID algorithm, where:
GAIN = 100 % FS
PB %
MINorRPM
RESET UNITS selects units of minutes or repeat per
minutes for the I term of the PID algorithm. 20 Repeats
per Minute = 0.05 Minutes per Repeat.
RPM
REPEATS PER MINUTE the number of times per
minute that the proportional action is repeated by reset.
MIN
MINUTES PER REPEAT the time between each
repeat of the proportional action by reset.
CONT1ALG
The CONTROL ALGORITHM lets you select the type of
control that is best for your process.
ATTENTION
If the recorder has two controllers
(both enabled), CONT1ALG applies for controller #1
and CONT2ALG applies for controller #2.
ON-OFF
ON/OFF is the simplest control type. The output can be
either ON (100 %) or OFF (0 %). The Process Variable
(PV) is compared with the setpoint (SP) to determine
the sign of the error (ERROR = PV-SP). The ON/OFF
algorithm operates on the sign of the error signal.
In Direct Acting Control, when the error signal is
positive, the output is 100 %; and when the error
signal is negative, the output is 0 %. If the control
action is reverse, the opposite is true. An adjustable
overlap (Hysteresis Band) is provided between the on
and off states.
Other prompts affected: “OUT HYST”
DUPLEX ON/OFF is an extension of this algorithm
when the output is configured for Duplex. It allows the
operation of a second ON/OFF output. There is a
deadband between the operating ranges of the two
inputs and an adjustable overlap (hysteresis) of the on
and off states of each output. Both Deadband and
Hysteresis are separately adjustable. With no relay
action the controller will read 50 %.
Other prompts affected: “OUT HYST” and
“DEADBAND”
Configuration Parameter Definitions - Control Parameters Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 115
April 2017
CONT1ALG
(continued)
PID A
NOTE: PID A should not be
used for Proportional only action
(that is, no integral (reset)
action.) Instead, use PD+MR
with rate set to 0.
PID A is normally used for three-mode control. This
means that the output can be adjusted somewhere
between 100 % and 0 %. It applies all three control
actions Proportional (P), Integral (I), and Derivative
(D) to the error signal.
Proportional (Gain) regulates the controller’s output
in proportion to the error signal (the difference between
Process Variable and Setpoint).
Integral (Reset) regulates the controller's output to
the size of the error and the time the error has existed.
(The amount of corrective action depends on the value
of proportional Gain.)
Derivative (Rate) regulates the controller's output in
proportion to the rate of change of the error. (The
amount of corrective action depends on the value of
proportional Gain.)
PID B
PID B unlike the PID-A equation, the controller gives
only an integral response to a setpoint change, with no
effect on the output due to the gain or rate action, and it
gives full response to PV changes. Otherwise controller
action is as described for the PID-A equation. See note
on PID-A.
PD+MR
PD WITH MANUAL RESET is used whenever integral
action is not wanted for automatic control. The equation
is computed with no integral contribution. The MANUAL
RESET, which is operator adjustable, is then added to
the present output to form the controller output.
Switching between manual and automatic mode will not
be bumpless.
If you select PD with Manual Reset you can also
configure the following variations:
PD (Two Mode) control,
P (Single Mode) control.
Set Rate (D) and/or Reset Time (I) to 0.
Other prompts affected: "MAN RSET"
Configuration Parameter Definitions - Control Parameters Set Up Group
116 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
CONT1ALG
(continued)
3PSTEP
The THREE POSITION STEP algorithm allows the
control of a valve (or other actuator), with an electric
motor driven by two controller relay outputs; one to
move the motor upscale, the other downscale without a
feedback slidewire linked to the motor shaft. The
deadband and hysteresis are adjustable in the same
manner as the duplex output algorithm.
The Three Position Step Control algorithm provides an
output display (OUT) which is an estimated motor
position since the motor is not using any feedback.
Although this output indication is only an approximation,
it is “corrected” each time the controller drives the motor
to one of its stops (0 % or 100 %). It avoids all the
control problems associated with the feedback slidewire
(wear, dirt, noise). When operating in this algorithm, the
estimated “OUT” display is shown to the nearest percent
(i.e., no decimal).
Refer to the Operation section for motor position
displays.
Other prompts affected: “DEADBAND” and Tuning
prompts “GAIN”, “RATE”, “RESET”.
OUT1ALG
The OUTPUT ALGORITHM lets you select the type of
output you want. Not applicable with Control Algorithm
prompt "3PSTEP."
ATTENTION
If the recorder has two controllers
(both enabled), OUT1ALG applies for controller #1 and
OUT2ALG applies for controller #2.
Selections are model dependent. For example, current
output models cannot be configured for Time
Proportioning Simplex Output.
TIME
RELAY SIMPLEX type of output using one SPDT
relay. Its normally open (NO) or normally closed (NC)
contacts are selected by positioning an internal jumper.
Other prompts affected: "OUT HYST"
Controller #1 uses Relay 3 and overrides control of
relay by Alarm 3. Controller #2 uses Relay 5 and
overrides control of relay by Alarm 5.
CURRNT
CURRENT SIMPLEX type of output using one 4 to
20 mA signal that can be fed into a positive or negative
grounded load of 0 to 1000 ohms. The signal can be
recalibrated for any desired range from 3.25 mA to 21
mA for 0 % to 100 % output.
Configuration Parameter Definitions - Control Parameters Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 117
April 2017
OUT1ALG
(continued)
POSITN
POSITION PROPORTIONAL SIMPLEX type of
output using two SPDT relays and a motor which has a
100 to 1000 ohms feedback slidewire.
(Automatically selected when CONT ALG = 3PSTEP)
Other prompt affected: "DEADBAND"
Controller #1 uses Relays 3 and 4 and overrides
control of relays by Alarms 3 and 4. Controller #2
uses Relays 5 and 6 and overrides control of relays
by Alarms 5 and 6.
TIME D
RELAY DUPLEX type of output using two SPDT
relays. Its normally open (NO) or normally closed (NC)
contacts are selected by positioning an internal jumper
(see Installation section).
Other prompts affected: "DEADBAND"
Controller #1 uses Relays 3 and 4 and overrides
control of relays by Alarms 3 and 4. Controller #2
uses Relays 5 and 6 and overrides control of relays
by Alarms 5 and 6.
CUR TI
CURRENT/RELAY DUPLEX (RELAY = HEAT) is a
variation of duplex with current active for 0 % to 50 %
output (tuning set 2) and relay active for 50 % to 100 %
output (tuning set 1).
Other prompts affected: "4-20 RNG," "DEADBAND"
Controller #1 uses Relay 3 and overrides control of
relay by Alarm 3. Controller #2 uses Relay 5 and
overrides control of relay by Alarm 5.
TI CUR
RELAY/CURRENT DUPLEX (RELAY = COOL) is
similar to "CUR-TI" except that current is active for 50 %
to 100 % and relay is active for 0 % to 50 %.
Other prompts affected: "4-20 RNG,"
"DEADBAND"
Controller #1 uses Relay 4 and overrides control of
relay by Alarm 4. Controller #2 uses Relay 6 and
overrides control of relay by Alarm 6.
4-20 RNG
CURRENT DUPLEX RANGE ALGORITHM used
with Output Algorithm selections "CUR-TI" or "TI-CUR."
50 PCT
CURRENT DUPLEX RANGE (SPLIT) enables the
normal control current output to provide its full range for
50 % output change.
If “CUR-TI” duplex was selected, the current output
provides cool control.
100PCT
CURRENT DUPLEX RANGE (FULL) enables the
normal control current output to provide duplex heat
control over 0-100 % output change and the relay output
to provide cool control.
Repeat this procedure for Control 2 configuration.
Configuration Parameter Definitions - Tuning Parameters Set Up Group
118 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
4.9 Tuning Parameters Set Up Group
Introduction
Tuning consists of establishing the appropriate values for the tuning constants you are using so that your
recorder responds correctly to changes in process variable and setpoint. You can start with predetermined
values but you will have to watch the system to see how to modify them. There are two Tuning groups
available.
Tuning group prompts
Table 4-8 lists all the function prompts in the Tuning 1 and Tuning 2 setup group and their definitions.
Table 4-8 Tuning Group Prompt Definitions
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
FUZZY
DISABL
ENABLE
FUZZY OVERSHOOT SUPPRESSION FEATURE
DISABLE - Disables fuzzy overshoot suppression
ENABLE - The recorder will use fuzzy logic to suppress
or mimimize any overshoot that may occur as a result of
the existing tuning parameters. It does NOT change the
parameters.
ACCUTUNE
DISABL
ENABLE
ACCUTUNE II - On demand tuning algorithm
DISABLE - Disables ACCUTUNE II
ENABLE - TuneOF will be displayed as a status
message. Use the Increment or Decrement key to
toggle status to TuneON. New PID parameters will be
entered automatically when tuning is complete.
AT ERR
NONE
IDFL
ABRT
RUN
ACCUTUNE ERROR CODES (Read Only)
Configuration Parameter Definitions - Tuning Parameters Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 119
April 2017
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
PROP BD
or
GAIN
0.1 to 1000 %
or
0.1 to 1000
PROPORTIONAL BAND is the percent of the range of
the measured variable for which a proportional recorder
will produce a 100 % change in its output.
GAIN is the ratio of output change (%) over the
measured variable change (%) that caused it.
G =
100%
PB%
where PB is the proportional band (in %)
If the PB is 20 %, then the Gain is 5. Likewise, a 3 %
change in the error signal (SP-PV) will result in a
15 % change in the recorder's output due to
proportional action. If the gain is 2, then the PB
is 50 %.
Used with control algorithm PID-A or PID-B.
Defined as "HEAT" Gain on Duplex models for
variations of Heat/Cool applications.
The selection of Proportional Band or Gain is made in
the control parameter group under prompt
"PBorGAIN."
RATE MIN
0.08 to 10.00 minutes
0.08 or less = OFF
RATE action affects the recorder's output whenever the
deviation is changing; and affects it more when the
deviation is changing faster.
Used with control algorithm PID-A or PID-B.
Defined as "HEAT" Rate on Duplex models for
variations of Heat/Cool applications.
RSET MIN
or
RSET RPM
0.02 to 50.00
RSET MIN = RESET IN MINUTES / REPEAT
RSET RPM = RESET IN REPEATS / MINUTE
RESET adjusts the recorder's output in accordance with
both the size of the deviation (SP-PV) and the time it
lasts. The amount of the corrective action depends on
the value of Gain. The Reset adjustment is measured as
how many times proportional action is repeated/minute.
Used with control algorithm PID-A or PID-B.
Defined as "HEAT" Reset on Duplex models for
variations of Heat/Cool applications.
The selection of minutes per repeat or repeats per
minute is made in the control parameters group under
prompt "MINorRPM."
MAN RSET
100 to +100
(in % output)
MANUAL RESET is only applicable if you have control
algorithm PD WITH MANUAL RESET. Because a
proportional recorder will not necessarily line out at
setpoint, there will be a deviation (offset) from setpoint.
This eliminates the offset and lets the PV line out at
setpoint.
PROP BD2
or
GAIN 2
0.1 to 1000 %
or
0.1 to 1000
PROPORTIONAL BAND 2 or GAIN 2, RATE 2, and
RESET 2 parameters are the same as previously
described for “Heat” except that they refer to the cool
Configuration Parameter Definitions - Tuning Parameters Set Up Group
120 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
RATE2MIN
0.08 to 10.00 minutes
0.08 or less = OFF
zone tuning constants on duplex models or the second
set of PID constants, whichever is pertinent.
RSET2MIN
RSET2RPM
0.02 to 50.00
CYC SEC
1 to 120 seconds
CYCLE TIME (HEAT) determines the length of one time
proportional output relay cycle. Defined as "HEAT" cycle
time for Heat/Cool applications.
Electromechanical relays
CYC2 SEC
1 to 120 seconds
CYCLE TIME 2 (COOL) is the same as above except it
applies to Duplex models as the cycle time in the
"COOL" zone of Heat/Cool applications or for 2nd set of
PID constants.
Electromechanical relays
Configuration Parameter Definitions - Setpoint Ramp Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 121
April 2017
4.10 Setpoint Ramp Set Up Group
Introduction
The Setpoint Ramp 1 and 2 Set Up groups contain the Function parameters that enable you to configure 2
setpoints. Each setpoint (SP RAMP 1 and SP RAMP 2) can be configured only one of three ways: ramp,
rate, or setpoint program.
Single Setpoint Ramp
Setpoint will ramp between the current local setpoint and a final setpoint over a time interval of up to 255
minutes. (SP RAMP).
Setpoint Rate
The Setpoint Ramp Set Up group also contains the function parameters that let you configure a specific rate
of change for any local setpoint change (SP RATE). It includes selections for Rate Up and Rate Down.
Setpoint Program
Also included under this group are prompts for configuring a 36-segment Setpoint program (SP PROG).
The prompts and instructions for Setpoint programming are presented in the Section 6 - Setpoint
Ramp/Soak Programming and Operation.
You can start and stop the ramp/program using the RUN/HOLD key.
Setpoint Ramp/ Program group prompts
Table 4-9 lists all the function prompts in the Setpoint Ramp 1 or 2 setup group and their definitions.
When you enable the ramp type (SP RAMP, SP RATE, SP PROG) the other two types are hidden from the
display.
Table 4-9 Setpoint Ramp 1 or 2 Group Definitions
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
SP RAMP
ENABLE
DISABL
SINGLE SETPOINT RAMP Make selection to enable
or disable the setpoint ramp function. Make sure you
configure a ramp time and a final setpoint value. “SP
PROG” and “SP RATE” must be disabled.
ENABLE SETPOINT RAMP Allows you to start the
setpoint ramp (in automatic mode).
DISABLE SETPOINT RAMP Disables the setpoint
ramp.
Configuration Parameter Definitions - Setpoint Ramp Set Up Group
122 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
TIME MIN
0 to 255 minutes
SETPOINT RAMP TIME Enter the number of
minutes desired to reach the final setpoint.
A ramp time of “0” implies an immediate change of
setpoint.
SP
Time
0 255
120
250
Example of SP Ramp Settings:
21421
FINAL SP
Within SP limits
SETPOINT RAMP FINAL SETPOINT Enter the
value desired for the final setpoint. The recorder will
operate at the setpoint set here when ramp is ended.
SP RATE
(option)
ENABLE
DISABL
SETPOINT RATELets you configure a specific rate of
change for any local setpoint change. “SP RAMP” and
“SP PROG” must be disabled.
ENABLE SETPOINT RATEAllows the SP rate
feature.
DISABLE SETPOINT RATEDisables the setpoint
rate.
EU/HR UP
0 to 9999 in Engineering Units
per hour
RATE UPValue for SP Rate selection.
EU/HR DN
0 to 9999 in Engineering Units
per hour
RATE DOWNValue for SP Rate selection.
SP PROG
(option)
ENABLE
DISABL
SETPOINT RAMP/SOAK PROGRAM
Available only with recorders that contain this option.
“SP RAMP” and “SP RATE” must be disabled.
For reasons of convenience, the prompts used when SP
PROG is enabled are included in Section 6 Setpoint
Ramp/Soak Programming and Operation.
Configuration Parameter Definitions - Timer Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 123
April 2017
4.11 Timer Set Up Group
Introduction
The Timer gives a countdown or elapsed time, after which Relay 1 energizes. If Timer is enabled, it has
exclusive control over Relay 1; that is, Alarm 1 will not control the relay.
Timer group prompts
Table 4-10 lists all the function prompts in the Timer setup group and their definitions.
Table 4-10 Timer Group Definitions
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
TIMER
ENABLE
DISABL
Enables or disables the timer option
PERIOD
0:00 to 99:59
Configures the length of the timeout period (from 0 to 99
hours, 59 minutes).
START
RH KEY
ALARM 2
TIME
Timer starts with the keyboard (Run/Hold key).
Timer starts with Alarm 2.
Wake time parameterStarts timer when the value
configured for the Wake Time Event is reached. (See
WAKE MIN, WAKE HR, WAKE DAY, WAKE MON in the
Time Set Up group.)
The Timer can also be started by a discrete input, REM
SW or REM SW2. These prompts are found under the
Control Set Up Group.
LDISPLAY
TREM
ET
Select whether time remaining (TREM) or elapsed time
(ET) is displayed for the timer option. The time is shown
on the lower display in hh:mm format along with a
rotating “clock” character.
Time remaining: If the “clock” rotation is clockwise,
elapsed time is indicated.
Elased time: If the “clock” rotation is counterclockwise,
time left is indicated.
RESET
RH KEY
ALARM 1
REPEAT
Timer resets with the keyboard (Run/Hold key).
Timer resets with Alarm 1.
In Repeat Mode, the timer restarts immediately upon
timeout and activates the relay for 1 to 5 seconds.
ON-TIME
1 SEC
2 SEC
3 SEC
4 SEC
5 SEC
Relay 1 on-time when timer is in repeat mode.
INCRMENT
MINUTE
SECOND
Select the units of the timer.
Configuration Parameter Definitions - Alarms Set Up Group
124 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
4.12 Alarms Set Up Group
Introduction
An alarm is an indication that an event that you have configured (for exampleProcess Variable) has
exceeded one or more alarm limits. There are six alarms available, each with two setpoints. You can
configure each of these two setpoints to alarm on various controller parameters. There are two alarm output
selections, high and low. You can configure each setpoint to alarm either high or low. These are called
single alarms. You can also configure the two setpoints to alarm on the same event and to alarm both high
and low. An adjustable hysteresis of 0.0 % to 100.0 % is configurable for each alarm setpoint.
Priority of functions that operate relays
During alarm conditions an alarm will deenergize its associated relay unless a higher priority function has
been configured for that relay. See Table 3-13. If you want the alarm to control the relay, do not configure
a higher priority function.
Table 4-11 Priority of functions that operate relays
Relay
Relay is controlled by (in order of priority)
1
3. Timer function
4. Alarm 1
2
Alarm 2 only
3
5. Controller 1 output algorithms Relay Simplex,
Position Proportional, Relay Duplex,
Current/Relay Duplex
6. Alarm 3
4
7. Controller 1 output algorithms Position
Proportional, Relay Duplex, Current/Relay
Duplex
8. Alarm 4
5
9. Controller 2 output algorithms Relay Simplex,
Position Proportional, Relay Duplex,
Current/Relay Duplex
10. Alarm 5
6
11. Controller 2 output algorithms Position
Proportional, Relay Duplex, Current/Relay
Duplex
12. Alarm 6
Configuration Parameter Definitions - Alarms Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 125
April 2017
Alarms group prompts
Table 4-12 lists all the function prompts in the Alarms setup group and their definitions. These prompts
repeat for all 6 alarms.
TIP
To configure an alarm for a setpoint program segment event, program either type (AxS1TYPE
or AxS2TYPE) as EVENT. It is not necessary to configure any other alarm prompts.
Table 4-12 Alarms Group Definitions
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
AxS1 VAL
Value in engineering units
ALARM x SETPOINT 1 VALUE this is the value at
which you want the alarm type chosen in prompt
"AxS1TYPE" to actuate. The value depends on what the
setpoint has been configured to represent. NO setpoint
is required for Communications SHED. For SP
Programming the value is the segment number for
which the event applies.
AxS2 VAL
Value in engineering units
ALARM x SETPOINT 2 VALUE this is the value at
which you want the alarm type chosen in prompt
"AxS2TYPE" to actuate.
The details are the same as “AxS1 VAL”.
AxS1TYPE
NONE
IN 1
IN 2
IN 3
IN 4
RH
DEV (loop 1)
OUT (loop 1)
DEV2 (loop 2)
OUT2 (loop 2)
EVENT
TOTAL 1
TOTAL 2
TOTAL 3
TOTAL 4
ALARM x SETPOINT 1 TYPE select what you want
Setpoint 1 of Alarm 1 to represent. It can represent any
of the Inputs, Relative Humidity, Deviation (loop 1 or 2),
Output (loop 1 or 2), and if you have a model with
communications, you can configure the recorder to
alarm on SHED. If you have setpoint programming, you
can alarm when a segment goes ON or OFF (loop 1 or
2).
An alarm can also be set to activate if a totalizer value
has exceeded a configured alarm value.
NO ALARM
INPUT 1
INPUT 2
INPUT 3
INPUT 4
RELATIVE HUMIDITY
LOOP 1 DEVIATION
LOOP 1 OUTPUT
LOOP 2 DEVIATION
LOOP 2 OUTPUT
EVENT ON (SP PROGRAMMING)
TOTALIZER TO ALARM ON
TOTALIZER TO ALARM ON
TOTALIZER TO ALARM ON - MODEL DR45AW ONLY
TOTALIZER TO ALARM ON - MODEL DR45AW ONLY
Configuration Parameter Definitions - Alarms Set Up Group
126 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
AxS2TYPE
Same as AxS1TYPE
ALARM x SETPOINT 2 TYPE select what you want
Setpoint 2 of Alarm x to represent. The selections are
the same as AxS1TYPE.
AxS1 H L
H I
LO
ALARM x SETPOINT 1 STATE select whether you
want the alarm type chosen in prompt "AxS1TYPE" to
alarm high or low or the beginning or end of a segment
in setpoint Ramp/Soak programming.
HI ALARM Relay coil is de-energized when the PV is
above the setpoint.
LO ALARM Relay coil is de-energized when the PV is
below the setpoint.
AxS1SCAL
1
10
100
1000
10000
100000
1E6
MULTIPLIER FOR ALARM TYPE “TOTAL”
SELECTION the alarm is only a high value. Enter a
scaler of from 1 to 1000000.
(Base value x multiplier = alarm setpoint value)
AxS2 H L
H I
LO
ALARM x SETPOINT 2 STATE select whether you
want the alarm type chosen in prompt "AxS2TYPE" to
alarm high or low or the beginning or end of a segment
in setpoint Ramp/Soak programming.
HI ALARM
LO ALARM
AxS2SCAL
1
10
100
1000
10000
100000
1E6
MULTIPLIER FOR ALARM TYPE “TOTAL”
SELECTION the alarm is only a high value. Enter a
scaler of from 1 to 1000000.
(Base value x multiplier = alarm setpoint value)
ALx HYST
0.0 to 100.0 % of span or full
output as appropriate
ALARM HYSTERESIS an adjustable hysteresis is
provided on each alarm such that when the alarm is
OFF it activates at exactly the alarm setpoint; when the
alarm is ON, it will not deactivate until the variable is
0.0 % to 100.0 % (whatever has been set) away from
the alarm setpoint.
Configure the hysteresis of the alarms based on
INPUT signals as a % of input range span.
Configure the hysteresis of the alarm based on
OUTPUT signals as a % of the full scale output
range.
Repeat this procedure for Alarm 2, Alarm 3, Alarm 4, Alarm 5, Alarm 6 configuration.
Configuration Parameter Definitions - Auxiliary Output Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 127
April 2017
4.13 Auxiliary Output Set Up Group
Introduction
This provides a milliampere output representing any of twelve control parameters: Input 1-4, PV 1-2,
Deviation 1-2, Output 1-2, Setpoint 1-2. The display for auxiliary Output viewing will be in engineering
units for all but output. Output will be designated in percent (%).
Timer group prompts
Table 4-13 lists all the function prompts in the Auxiliary Output setup group and their definitions.
Table 4-13 Auxiliary Output Group Definitions
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
AUX OUT
AUXILIARY OUTPUT SELECTION provides an mA
output representing any of twelve control parameters.
The display for Auxiliary Output viewing will be in
engineering units for all but output. Output will be
designated in percent (%).
Other prompts affected by these selections:
“4 mA VAL” and “20mA VAL”.
DISABL
NO AUXILIARY OUTPUT
IN 1
INPUT 1This represents the configured range of input
1. FOR EXAMPLE:
Type “J” Thermocouple (0 to 1600 °F)
0 °F display = 0 % output
1600 °F display = 100 % output
IN 2
INPUT 2 represents the value of the configured range of
input 2.
PV 1
PROCESS VARIABLE 1Represents the value of the
Process Variable for Loop 1. PV = Input 1 + Bias
DEV 1
DEVIATION 1 (PROCESS VARIABLE MINUS
SETPOINT)Represents 100 % to +100 % of the
selected PV span in engineering units for Loop 1.
FOR EXAMPLE:
Type “T” Thermocouple
PV range = 300 °F to +700 °F
PV span = 1000 °F
Deviation range = 1000 °F to +1000 °F
If PV = 500 °F
and SP = 650 °F
then Deviation Display = 150 °F
Auxiliary Output = 42.5 %
NOTE: A deviation of 0 °F yields an auxiliary output of
50 %.
OUT 1
OUTPUT 1Represents the displayed controller output
in percent (%) for Loop 1.
AUX OUT
(continued)
SP 1
SETPOINT 1Represents the value of the setpoint in
units of PV for Loop 1.
Configuration Parameter Definitions - Auxiliary Output Set Up Group
128 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
PV 2
PROCESS VARIABLE 2Represents the value of the
process variable for Loop 2.
DEV 2
DEVIATION 2 (PROCESS VARIABLE MINUS
SETPOINT)Represents 100 % to +100 % of the
selected PV span for Loop 2.
See Example at DEV 1.
OUT 2
OUTPUT 2Represents the displayed controller output
in percent (%) for Loop 2.
SP 2
SETPOINT 2Represents the value of the setpoint in
units of PV for Loop 2.
IN 3
INPUT 3Represents the value of the configured range
of Input 3.
IN 4
INPUT 4Represents the value of the configured range
of Input 4.
4 mA VAL
Low Scale Value
within the range of the selected
variable to represent 4 mA
AUXILIARY OUTPUT LOW SCALING FACTORUse
a value in engineering units for all selections above
except Output.
Use value in percent (%) for Output. (Output can be
between 5 % and +105 %.)
20mA VAL
High Scale Value
within the range of the selected
variable to represent 20 mA
AUXILIARY OUTPUT HIGH SCALING FACTORUse
a value in engineering units for: Input 1, Input 2,
Process Variable, Deviation,* and Setpoint.
Use a value in percent (%) for Output. (Output can be
between 5 % and +105 %.)
*When Deviation is selected, only one operating
parameter will be entered. This value represents the
deviation level that will produce 20 mA output. Zero
deviation will produce a center scale (12 mA) output. A
negative deviation equal in magnitude to the Auxiliary
Output High Value will produce a low end (4 mA) output.
Repeat for AUX OUT 2 and AUX OUT 3.
Configuration Parameter Definitions - Modbus Communications Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 129
April 2017
4.14 Modbus Communications Set Up Group
Introduction
This option allows the DR4500A to be connected to a host computer via the Modbus protocol. Up to 99
addresses and a maximum of 15 units can be configured over this link.
REFERENCE
Refer to Documents 51-52-25-66 and 51-52-25-69 for a complete description of the RS485
Modbus Communications Option.
Communications group prompts
Table 4-14 lists all the function prompts in the Modbus Communications set up group and their functions.
Table 4-14 Modbus Communications Group Definitions
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
ComSTATE
DISABL
MODBUS
DISABLDisables the communications option.
MODBUSAllows Modbus communication prompts.
Com ADDR
1 to 99
COMMUNICATIONS STATION ADDRESS This is a
number that is assigned to the recorder that is to be
used with the communications option.
BAUD
300
600
1200
2400
4800
9600
19200
38400
BAUD RATE is the transmission speed in bits per
second.
300 Baud
600 Baud
1200 Baud
2400 Baud
4800 Baud
9600 Baud
19200 Baud
38400 Baud
XMT DLAY
NONE
10MSEC
20MSEC
30MSEC
40MSEC
50MSEC
TRANSMIT DELAYThis is the approximate time
delay between receipt of Modbus request message and
start of response message (in addition to message
processing time).
DBL BYTE
FP B
FP BB
FP L
FP LB
DOUBLE REGISTER BYTE ORDERThe transmitted
or received order of the 4 bytes comprising an IEEE
floating point value. The default order is EXP, MH, MM,
ML, or 0123 for reference.
0123 (Big Endian)
1032 (Big Endian, Byte Swapped)
3210 (Little Endian)
2301 (Little Endian, Byte Swapped)
Configuration Parameter Definitions - Options Set Up Group
130 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
4.15 Options Set Up Group
Introduction
The Options Set Up Group lets you enable or disable some of the options that are available on the DR4500.
You can select the power frequency, select relative humidity as a measurement and a atmospheric pressure
compensation, select deviation recording action, and set the desired deviation setpoint.
Options group prompts
Table 4-15 lists all the function prompts in the Option set up group and their functions.
Table 4-15 Option Group Definitions
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
REJ FREQ
60HZ
50HZ
REJECTION FREQUENCY be sure that this selection
agrees with the line voltage frequency.
HF REJ
ENABLE
DISABL
HIGH FREQUENCY REJECTION This selection
allows high frequency noise rejection. It is used to quiet
noisy pens or PV.
ATTENTION
For fast processes it will cause
additional lag.
RELHUMID
NO
YES
RELATIVE HUMIDITY allows you to activate or
deactivate the RH calculation algorithm.
You must select 100RH input type for two inputs to
measure RH. It requires two 100-ohm RTD inputs so
INPUT 2 must be enabled for this prompt to appear.
Also, you must select RH for “PEN2IN” which
represents the “wet bulb” temperature when input 2 is
selected.
ATMPRES
590 to 800 mmHg
ATMOSPHERIC PRESSURE COMPENSATION This
prompt only appears if you select “YES” at “RELHUMID”
prompt previously. Select the desired compensation.
DEVIATION
NONE
SETPNT
CHAN1
DEVIATION selects deviation recording action.
NONE No deviation recording
SETPNT Records deviation from setpoint
CHAN1 Pen 1 records the difference between Input
1 and Input 2.
DEVSETPT
999.0 to 9999
DEVIATION SETPOINT VALUE sets the desired
deviation setpoint value for deviation recording.
This prompt only appears if “SETPNT” was selected
at prompt “DEVIATION” previously.
Configuration Parameter Definitions - Options Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 131
April 2017
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
SCROLL
LOWER DISPLAY SCROLLThe lower display will
automatically change to the next item (as if the
LOWR DISP key had been pressed) at the interval
selected.
NONE
NONEDisables the scroll function.
1 SEC
1 SECOne second intervals
2 SEC
2 SECTwo second intervals
3 SEC
3 SECThree second intervals
GRANDTOT
ENABLE
DISABL
GRAND TOTALIZERWhen enabled it prints, on the
chart, the sum of ALL the enabled totalizers as
TOTAL = XXXXXXXXXXX.
This is printed in the space for totalizer 4. If grand total
is disabled, total 4 on the DR45AW model will print
normally.
Configuration Parameter Definitions - Event Message Set Up Group
132 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
4.16 Event Message Set Up Group
Introduction
This Set Up group allows you to specify six event messages to be printed on a designated area of the chart
and triggered by a specific selectable actuation. The message can be six characters long.
Press the FUNC key until the specific event prompt appears in the lower display.
Event Message group prompts
Table 4-16 lists all the function prompts in the Event Message set up group and their definitions.
Table 4-16 Event Message Group Definitions
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
EVENT n
(n = 1, 2, 3, 4, 5, or
6)
60HZ
50HZ
EVENT TRIGGERSelect the triggering source for
each of the six event messages.
NONE
NONENo event message
EXT SW1
EXT SW1Event triggered by external switch 1 closure
EXT SW2
EXT SW2Event triggered by external switch 2 closure
ALARM 1
ALARM 1Event triggered by Alarm 1
ALARM 2
ALARM 2Event triggered by Alarm 2
ALARM 3
ALARM 3Event triggered by Alarm 3
ALARM 4
ALARM 4Event triggered by Alarm 4
ALARM 5
ALARM 5Event triggered by Alarm 5
ALARM 6
ALARM 6Event triggered by Alarm 6
MESSAGEn
(n = 1, 2, 3, 4, 5, or
6)
0 to 9
A to Z
+
/
(blank)*
MESSAGE FOR EVENTSelect a message to be
printed when Event is triggered. You can use up to six
characters.
*For alphanumeric entries, the display will cycle, from
left to right, with highlighting (increased brightness) of
each digit. The value of each digit can be changed only
when it is highlighted.
POSITIONn
(n = 1, 2, 3, 4, 5, or
6)
0 to 100 %
CHART POSITION FOR MESSAGESelect where you
want the message to appear on the chart.
Repeat for all messages required.
Configuration Parameter Definitions - Lockout Parameters Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 133
April 2017
4.17 Lockout Parameters Set Up Group
Introduction
These are the parameters that you will set to lockout any unauthorized changes to the recorder’s
configuration and calibration prompts. You must know the PASSWORD in order to change the Lockout
configuration. Refer to Appendix B for more information on security lockout.
ATTENTION
Configuration can also be locked using S1 switch on the main printed circuit board. Refer to
Subsection 2.9 Lockout Switch Configuration.
This feature also includes the special screw and plate that provide for the lead seal capability for sealing the
chart plate.
Set this group last
Because this group contains functions that have to do with security and lockout, we recommend that you
configure this group last, after all the other configuration data has been loaded.
Lockout group prompts
Table 4-17 lists all the function prompts in the Lockout set up group and their definitions.
Table 4-17 Lockout Group Definitions
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
PASSWORD
Select up to four alphanumeric
characters
PASSWORD -- this selection determines the password
that will be required to gain access to the lockout
prompt.
++++ is the factory default password.
LOCKOUT
NONE
CALIB
+CONF
MAX
LOCKOUT applies to one of the functional groups:
Configuration, Calibration, Tuning, Adaptive Tune. DO
NOT CONFIGURE UNTIL ALL CONFIGURATION IS
COMPLETE.
If the correct password was entered, you can call up
this prompt.
No Lockout all groups read/write.
CALIB All are available for read/write except for the
Calibration group.
+CONF Tuning, SP Ramp and program groups are
read/write. All other groups are read only. Calibration
group is not available.
MAX Calibration group not available. All other groups
are Read-only.
ATTENTION
Do not leave in “NONE” Lockout.
CHANGE
Selections are:
0 to 9
A to Z
CHANGE PASSWORD Changes default password to
one of your own.
Be sure to record the new password in a safe location.
Configuration Parameter Definitions - Printing Characteristics Adjustments
134 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
4.18 Printing Characteristics Adjustments
Introduction
With software version 1005 (and newer), two different hot stylus pen designs are available; check your
model number for:
Table III = _0_ for high speed stylus 30756304-001 (black tip)
Table III = _1_ for abrasion resistant jewel tip stylus 30756304-002
(beige tip)
The abrasion resistant stylus is designed for recording applications that include highly abrasive
environments. The abrasion resistant stylus should only be used with chart speeds from 24 hrs/rev
to 31 days/rev.
Configuration choices
Configuration choices are now provided for PEN TYPE and the selection made must match the stylus
design.
PEN TYPE = NORMAL is for the high speed stylus design.
PEN TYPE = JEWEL is used only for abrasion resistant stylus design.
CAUTION
If the “JEWEL” selection is accidentally used with the high-speed design, the life of that stylus
will be shortened.
Printing characteristics adjustments
Normally there is no need to adjust the printing characteristics as part of an input or output calibration
procedure. However, if the chart printing appears to be faded, you can use the procedure in Table 4-18 to
make slight adjustments in the print contrast.
ATTENTION
To access Set-up group prompt “ADJUST”, the Set Up group prompt “LOCKOUT” must be set
to “NONE”. If the group prompt “LOCKOUT” has been configured for “CALIB” or “MAX
selection, you will not be able to access the Printing Characteristics Group prompt. Refer to
Subsection 4.17 for details.
Configuration Parameter Definitions - Printing Characteristics Adjustments
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 135
April 2017
Printing characteristics adjustments procedure
Table 4-18 is the procedure to adjust the printing characteristics of your recorder.
Table 4-18 Printing Characteristics Adjustment Procedure
Step
Description
Press
Action
1
Enter Set Up Group
ADJUST
SET
UP
Until you see:
Upper Display: ADJUST
Lower Display: {PRINTING)
2
Select Trace Line
Contrast
FUNC
Until you see:
Upper Display: DARK, MEDIUM, or LIGHT
Lower Display: TRACE LN
Press or to select the desired contrast.
3
Select Grid Line Contrast
FUNC
Until you see:
Upper Display: DARK, MEDIUM, or LIGHT
Lower Display: GRID LN
Press or to select the desired contrast..
4
Select Stylus
FUNC
Until you see:
Upper Display: NORMAL or JEWEL
Lower Display: PEN TYPE
Press or to select the pen type.
Select “NORMAL” if high speed stylus (black tip) is
installed.
Select “JEWEL” only if abrasion resistant stylus
(beige tip) is installed.
5
Return to normal
operation
LOWR
DISP
Return to normal operation and observe the change in
printing characteristics.
Change Set Up group “LOCKOUT” to something
other than “NONE”.
Release M DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 136
May 2013
5. Operation
5.1 Overview
Introduction
This section gives you all the information necessary to monitor and operate your recorder and for
performing routine maintenance tasks. In this section assume that the recorder has been properly installed
and configured, and that the inputs are properly calibrated.
Some of the procedures in this section are required only initially, and some are required only randomly, as
conditions dictate. Once the recorder is up and running, required operation actions are infrequent and
straightforward.
Review the Operator Interface, Display and Keypad descriptions shown in Section 1 - Overview.
What’s in this section?
This section contains the following topics:
Topic
See Page
5.1 Overview
136
5.2 Start-up
137
5.3 Monitoring Your Recorder
141
5.4 Operator Functions
147
5.5 Operating Modes
148
5.6 Setpoints
150
5.7 Single Setpoint Ramp
152
5.8 Using Two Sets of Tuning Constants (PID Values)
155
5.9 Using Accutune II
158
5.10 Alarm Setpoints
161
5.11 Three Position Step Control Algorithm
162
5.12 Digital Input Option (Remote Switching)
163
5.13 Resetting and Displaying Totalizer Value
164
5.14 Monitoring the External Event Operation
166
5.15 Maximizing Pen Life
167
5.16 Routine Maintenance
168
5.17 Installing/Replacing Chart
169
5.18 Chart Operation
170
Operation - Start-up
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 137
April 2017
5.2 Start-up
Preparation
Before start-up, there are two tasks to perform:
Install or replace the circular chart as described in 5.16 - Routine Maintenance.
Be sure that the configured settings for the current time and wake time (time at which recording begins)
are correct. Note that the recorder is “awake” during start-up to verify interaction with the process.
During start-up, you should verify the interaction between your process and the DR4500A recorder to be
sure that your process can tolerate some upsets during this procedure.
Diagnostic tests
When power is applied, the recorder will run four diagnostic tests. Table 5-1 lists the four diagnostic tests.
Table 5-1 Power Up Diagnostic Tests
Prompt on Lower Display
Condition
RAM TEST
Check RAM
CONFTEST (configuration checksum)
Check nonvolatile memory
CAL TEST (working calibration)
Check calibration
BATTERY
Check the battery
Test failures
If control is enabled and one or more of these tests fail, the recorder will go to the Failsafe Manual Mode,
and “FAILSAFE” will flash in the lower display.
If control is not configured, the self-test failures will be displayed periodically as other messages are
presently displayed (CNFG ERR, CAL1 ERR, CAL2 ERR, or BATT LOW).
Troubleshooting
Refer to “DEVICE STATUS” in Section 9 - Troubleshooting/Service to identify and correct the problem.
Operation - Start-up
138 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Check the displays and keys
Use the procedure in Table 5-2 to run the display and key test.
Table 5-2 Procedure for Testing the Displays and Keys
Press
Result
SET
UP
and hold in, then press
FUNC
at the same time
The recorder runs a display test. All the displays will light for 8
seconds, then you will see:
Upper Display: keys
Lower Display: try all
Press each key to see if it
works
When the key is pressed, the lower display indicates the name of the
key pressed.
Key Pressed
Lower Display
SET UP
SET UP
LOWR DISP
LWR DISP
MAN/AUTO*
AUTO MAN
RESET*
RESET
CHART
CHART
INCRMENT
DECRMENT
RUN/HOLD
RUN HOLD
*Note that MAN/AUTO or RESET is shown but not both
If no key is pressed for 25 seconds, the test times out and the recorder exits the key test.
If any test fails, go to Subsection 9.3 Self Diagnostics for more information.
Key error
When a key is pressed and the prompt “KEY ERROR” appears in the lower display, it will be for one of
the following reasons:
parameter not available,
not in Set Up mode, press SET UP key first,
key malfunction, perform keyboard test.
Start-up procedure
Use the procedure listed in Table 5-3 to start up the recorder.
Open the recorder door. Apply power and wait for the recorder to run its power-up tests.
Operation - Start-up
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 139
April 2017
ATTENTION
If FAILSAFE starts blinking in the lower display, refer to Section 9 for
troubleshooting data.
For recorders with two controllers (both enabled), be sure the CHN ‘1’ indication is
lit for steps 2-6. If CHN 1 is not lit, sequentially press the LOWR DISP key until “1”
is lit when “OUT” is displayed.
Table 5-3 Procedure for Starting Up the Recorder
Step
Description
Press
Action
1
Pen check
For RECORDER ONLY models, just check that the pen
is operating and skip to step 6.
2
Select manual mode
MAN
AUTO
Until “MAN” indicator is ON.
The recorder is in manual mode and the Output (OUT)
in percent is displayed in the lower display.
3
Adjust the output
or
Adjust the output value and ensure that the final control
element is functioning correctly.
Upper Display: shows the PV value
Lower Display: shows OUT and the output value
in %
Make sure the pen trace on the chart corresponds to
the change in output.
4
Tune the recorder
SET
UP
Make sure the recorder has been configured properly
and all the values and selections have been recorded
on the Configuration Record Sheet.
To tune your recorder automatically, see Subsection
5.9 Using Accutune II.
Refer to Set Up group TUNING 1 or TUNING 2 to
ensure that the proper selections for PROP BD or
GAIN, RATE MIN, and RSET MIN or RSET RPM have
been entered.
5
Enter the local setpoint
LOWR
DISP
Until you see:
Upper Display: shows the PV value
Lower Display: SP and the local setpoint value
or
Adjust the local setpoint to the value at which you want
the process variable maintained.
The local setpoint cannot be changed if the Setpoint
Ramp function is enabled.
“H” or “R” appears in the upper display.
6
Select automatic mode
MAN
AUTO
Until “A” indicator is ON.
The recorder is in Automatic mode.
The recorder will automatically adjust the output to
maintain the process variable at setpoint as tracked by
the pen trace, if the recorder is properly tuned.
Operation - Start-up
140 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Step
Description
Press
Action
7
Start up Controller #2
LOWR
DISP
Until “2” is lit when “OUT” is displayed.
For recorders with two controllers (both enabled),
repeat steps 2-6 for controller #2, but be sure CHN “2”
indicator is lit instead of CHN “1”.
8
Exit Start-up
Close the door and monitor the operation.
Operation - Monitoring Your Recorder
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 141
April 2017
5.3 Monitoring Your Recorder
Introduction
Besides the historical chart record, you can monitor the recorder’s indicators and displays to get an
instantaneous view of various process conditions and of the control loop status.
Diagnostic error messages signal detection of malfunctions in certain internally monitored data. Alarm and
tuning messages indicate alarms in effect and control loops being tuned.
Operator interface
The indicators and displays on the operator interface let you see what is happening to your process and how
the recorder is responding.
Figure 5-1 is a view of the operator interface. A description of the displays and indicators is included.
±1% of control setpoint
Control relay 1 or 2 is
ON, when lit.
ALM
CHN
RSP
OUT
12 FC
%
MAN
12
Lower Display - eight characters
Normal operation - Displays selectable
operating parameters and values. Indicates
diagnostic error messages, alarm condition
for alarms 3-6, Accutune in progress.
Configuration mode - Displays function
group and parameters.
Remote set point or
2nd set point is active,
when lit. Blinks when
2nd setpoint or remote
setpoint is attained
through remote switch
PV displayed is for channel
1, 2, 3, or 4
Alarm condition exists for
alarm 1 or 2, when lit.
Indicates temperature units of PV Upper Display - six characters
Normal operation - Displays process
variable (PV) for selected channels.
Configuration mode - Displays selection or
parameter value.
Indicates controller mode:
MAN = Manual
A = Automatic
Bargraph - deviation (±10% of span)
Center green bar indicates PV is within
.
Next small bar will light if PV is between
±1% but less than ±2% in deviation.
If PV is equal to or greater than ±10%
deviation, the green bar plus all ten small
green bars will light.
1234
Keypad /
Key functions
FUNC
LOWR
DISP
CHART
MAN
AUTO
SET
UP
RUN
HOLD
Figure 5-1 Operator Interface
Operation - Monitoring Your Recorder
142 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Meaning of indicators
During normal operation, the indicators will light for the reasons shown in Table 5-4.
Table 5-4 Meaning of Indicators
Indicator
Definition when lit
ALM 1 2
Alarm condition exists for alarm 1 or 2.*
CHN 1 2 3 4
PV displayed is for channel 1, 2, 3, or 4.
RSP
Remote Setpoint (when available) or 2nd setpoint is active.
OUT 1 2
Control relay 1 or 2 is ON.
A or MAN
Indicates the mode of operation: A = Automatic
MAN = Manual
F or C or blank
Indicates the temperature units of PV: F = Fahrenheit
C = Celsius
R or H or G or blank
(in upper display)
Indicates the state of the setpoint ramp or program if enabled:
R = Run
H = Hold
G = Guar Soak
blank = Disabled
T
Totalizer
KEY ERR
(in lower display)
Indicates parameter not available, not in set up mode, or key
malfunction.
* AL1 indicator can also mean the Interval Timer has timed out. Alarms 3-6 are indicated by a message on
the lower display. See Table 5-7.
Operation - Monitoring Your Recorder
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 143
April 2017
Reading the deviation bargraph
In addition to the indicators, a bargraph containing 21 bars displays Process Variable (PV) deviation from
Setpoint (SP).
ATTENTION
When CHN “1” indicator is lit, the bargraph display applies for Controller #1. It applies for
Controller #2 when CHN “2” indicator is lit. Sequentially press the LOWR DISP key to light the
appropriate CHN indicator (1 or 2) and view the corresponding controller displays.
The green “on-control” bar lights when the PV is within ± 1 % of setpoint.
The 10 small green bars above the “on-control” bar light for each positive deviation up to +10 % and the
10 below light for each negative deviation down to 10 %. If the process deviation is greater than
± 10 %, the “on-control” bar and the specific small green bars light.
Figure 5-2 shows how the deviation bargraph works.
+1 to +10%
small green
deviation bars
21424
-1 to -10%
small green
deviation bars
Green
"on control"
bar
Figure 5-2 Deviation Bargraph
Operation - Monitoring Your Recorder
144 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Viewing the operating parameters
The upper display is a six-character display, four of which show the value of the PV during normal
operation.
The lower display is an eight-character display. During normal operation, you can view various
operating parameters. Press the LOWR DISP key to scroll through the operating parameters listed in
Table 5-5.
The lower display shows only those parameters and their values that apply to your specific model and
the way in which it was configured.
You can configure the lower display to scroll through the items in Table 5-5 at an interval of 1, 2, or 3
seconds. Refer to Subsection 3.19 Options Set Up group, function prompt “SCROLL” to make your
selection.
Pressing the LOWR DISP key will freeze the lower display at the presently viewed item; pressing it
again will advance to the next item and scrolling will resume.
Pressing ▼while pressing LOWR DISP will scroll backwards.
For recorders with two controllers (both enabled) remember that any controller-related values displayed
correspond with the lighted CHN indicator “1” means that the values apply for Controller #1 and “2”
means that the values apply for Controller #2.
Table 5-5 Lower Display Key Parameter Prompts
Prompt
Description
OUT**
Output Value in Percent (%). Note that the output can only be adjusted through the
raise/lower keys when the controller in manual mode. (Estimated motor position for
3 Position Step Control)
SP**
Local Setpoint 1. Also current setpoint of SP Ramp, or SP Ramp/Soak Program.
SPN
Current setpoint for setpoint rate applications.
2SP**
Local Setpoint 2 (where remote setpoint does not apply)
RSP
Remote Setpoint (when configured)
1IN
Value of Channel 1 input (if Loop1 is a derived PV)
2IN
Value of Channel 2 input (when available)
3IN
Value of Channel 3 input (when available)
4IN
Value of Channel 4 input (when available)
DEV
PV deviation from setpoint (±999.9 maximum)
EU
Engineering units that PV represents (when available)
RH
RH value in percent (%) (when available)
PIDSETx**
Tuning Parameter Set x =1 or 2
RAMP
The time (minutes) remaining in the setpoint ramp
#RA
The time (minutes) remaining in the SP Ramp segment
#SK
The time (minutes) remaining in the SP Soak segment
RECYC
The number of recycles remaining to be run in the Setpoint Program
**
Time remaining in Timer function
Operation - Monitoring Your Recorder
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 145
April 2017
Prompt
Description
**
Time elapsed in Timer function
TUNExXXX**
Accutune II indicator. x = Loop number (1 or 2). XXX = ON or OFF.
**You can press or to change the value of this parameter.
Diagnostic error messages
The DR4500A runs background tests to verify data and memory integrity. If there is a malfunction, an error
message will blink in the lower display.
In the case of more than one simultaneous malfunction or alarm, each message will be shown in succession.
A list of error messages is contained in Table 5-6. If any of these error messages occur, refer to Section 9 -
Troubleshooting/Service for information to correct the failure.
Table 5-6 Error Messages
Prompt
Description
EE FAIL
Unable to write to nonvolatile memory
FAILSAFE
Failsafe
INP1FAIL
Two consecutive failures of input 1 integration
INP2FAIL
Two consecutive failures of input 2 integration
INP3FAIL
Two consecutive failures of input 3 integration
INP4FAIL
Two consecutive failures of input 4 integration
INP1 RNG
INP2 RNG
INP3 RNG
INP4 RNG
Input out-of-range
PV LIMIT
PV ± 10 % out-of-range
RV LIMIT
Remote Variable out-of-range
Note: RV = (input 2 x ratio) + bias
CNFG ERR
Configuration data is in error.
CAL1 ERR
Working CAL TEST failure (Control Output #1, Input 1, Input 2)
CAL2 ERR
Working CAL TEST failure (Control Output #2, Input 3, Input 4)
BATT LOW
Battery failure
Operation - Monitoring Your Recorder
146 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Alarm and tuning messages
Alarms #3 through #6 and Accutune II for Control Loops #1 and #2 are indicated in the lower display.
In the case of more than one simultaneous diagnostic or alarm message, each message will be shown in
succession.
Table 5-7 Alarm and tuning messages
Prompt
Description
ALARM 3
Indicates an alarm 3 action.
ALARM 4
Indicates an alarm 4 action.
ALARM 5
Indicates an alarm 5 action.
ALARM 6
Indicates an alarm 6 action.
TUNING 1
Indicates Accutune II in progress for Control Loop 1.
TUNING 2
Indicates Accutune II in progress for Control Loop 2.
ATTENTION
An active alarm will always provide an indication on the display but may not control its
associated relay; that is, a higher priority function such as a control loop or timer may have
control of the relay.
Operation - Operator Functions
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 147
April 2017
5.4 Operator Functions
Actions an operator can initiate
An operator can do the following:
Change the Control Mode (Auto/Man)
Adjust the Output Manually
Change the Setpoint
Switch between Setpoints
Run or Disable a Setpoint Ramp
Run or Disable a Setpoint Program
Switch between Two Sets of PID Values
Run or Disable Control Loop Tuning
Check the Alarm Setpoints
Reset the Totalizer
Run a Key Test
Note that some actions depend upon how the recorder was configured and the features supplied on your
particular recorder model.
Refer to the following pages for functions and procedures.
CHN indicator
Remember, for recorders with two controllers (both enabled) remember that any controller-related values
displayed, including control mode, correspond with the lighted CHN indicator “1” means that the values
apply for Controller #1 and “2” means that the values apply for Controller #2. Sequentially press the
LOWR DISP key to scroll through the displays and light the appropriate CHN indicator for controller-
related values.
Operation - Operating Modes
148 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
5.5 Operating Modes
Available modes
The recorder can operate in any of three basic modes:
Manual
Automatic with Local Setpoint
Automatic with Remote Setpoint
Manual and Automatic with Local setpoint are standard features and Automatic with Remote Setpoint is
optional.
Mode definitions
Table 5-8 Operating Mode Definitions
Operating Mode
Definition
MANUAL
When switched to manual mode, the recorder holds its output at the last value
used during automatic operation and stops adjusting the output for changes in
setpoint or process variable.
Instead, you adjust the output by changing the value shown in the lower display.
See “Selecting Modes”.
AUTOMATIC with
LOCAL SETPOINT
In automatic local mode, the recorder operates from the local setpoint and
automatically adjusts the output to maintain the setpoint at the desired value.
In this mode you can adjust the setpoint. See “Setpoints”.
AUTOMATIC with
REMOTE
SETPOINT
In automatic remote mode, the recorder operates from the setpoint measured at
input 2.
Adjustments are available to ratio this input and add a constant bias before it is
applied to the control equation. See Subsection 3.12 Control Set Up Group.
What happens when you change modes
Table 5-9 explains what happens to the recorder when you switch from one mode to another.
Table 5-9 Changing Operating Modes
Operating Mode
Definition
Manual to
Automatic Local
Setpoint
The local setpoint is usually the value previously stored as the local setpoint.
Manual or Auto
Local to Automatic
Remote SP
The second input value with ratio and bias applied is used to calculate the
control setpoint.
Automatic Remote
SP to Manual or
Auto Local Setpoint
If configured for RSP Tracking, when the recorder transfers out of remote
setpoint, the last value of the control setpoint is inserted into the local setpoint.
If RSP tracking is not configured, the local setpoint will not be altered when the
transfer is made.
Selecting manual or automatic mode
Operation - Operating Modes
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 149
April 2017
An alternate action switch places the recorder in automatic or manual mode of operation.
Switching between manual and automatic will be bumpless, except when the PD+MR algorithm is
selected.
Table 5-10 includes procedures for selecting automatic or manual mode and changing the output while
in manual.
Table 5-10 Procedure for Selecting Automatic or Manual Mode
Step
Operation
Press
Action/Result
1
Selecting automatic
mode
MAN
AUTO
Until “A” indicator is ON.
The recorder regulates its output to maintain the PV at
the desired setpoint.
Upper Display: shows the PV value
Lower Display: shows SP and the setpoint value
The deviation bargraph indicates the PV deviation from
the setpoint.
2
Selecting manual mode
MAN
AUTO
Until “MAN” indicator is ON.
The recorder holds its output at the last value used
during automatic operation and stops adjusting the
output for changes in setpoint or process variable.
Upper Display: shows the PV value
Lower Display: shows OUT and the output value
in %
The deviation bargraph indicates the PV deviation from
the setpoint.
3
Adjust the output in
manual mode
or
Adjust the output value while in manual mode.
Upper Display: shows the PV value
Lower Display: shows OUT and the output value
in %
4
Return to automatic
mode
MAN
AUTO
“A” indicator appears indicating automatic mode.
Position proportional backup mode
This feature provides for Position Proportional models to automatically change to a Three Position Step
algorithm if the slidewire input signal fails. This will maintain control of your process.
“SWFAIL” or “SW2FAIL” will flash in the lower display and the “OUT” display will show an estimated
motor position WITHOUT a decimal point.
Operation - Setpoints
150 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
5.6 Setpoints
Introduction
You can configure the following setpoints for the DR4500A recorder.
A single local setpoint
2 local setpoints
A local setpoint and a remote setpoint
A computer setpoint.
These setpoints can be toggled by the FUNC key.
Selecting the setpoint source
Use the procedure in Table 5-11 to select a single local setpoint source, a remote setpoint source, or two
local setpoints.
Table 5-11 Procedure for Selecting the Setpoint Source
Step
Operation
Press
Action/Result
1
Enter set up mode
SET
UP
Until the displays read:
Upper Display: SET UP
Lower Display: CONTROL
2
Display local setpoint
source selections
FUNC
Until the displays read:
Upper Display: Setpoint source selections
1LOCAL
2LOCAL
REMOTE
Lower Display: SP SOURCE
3
Select the desired source
or
Select the desired setpoint source in the upper display.
4
Return to control
LOWR
DISP
Controller assumes normal control.
Changing the local setpoints
Use the procedure in Table 5-12 to change either local setpoint value.
Table 5-12 Procedure for Changing the Local Setpoint
Step
Operation
Press
Action/Result
1
Select the setpoint
LOWR
DISP
Until you see:
Upper Display: PV value
Lower Display: SP or SP2 and the local setpoint
value
2
Change the value
or
Change the local setpoint to the value at which you
want the process maintained. The deviation bargraph
indicates PV deviation from setpoint.
Switching between setpoints
Operation - Setpoints
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 151
April 2017
You can switch between Local and Remote setpoints or between two Local setpoints when configured. Use
the procedure in Table 5-13 to switch between setpoints.
Table 5-13 Procedure for Switching Between Setpoints
Step
Operation
Press
Action/Result
1
Switch between setpoints
FUNC
or
LOWR
DISP
Alternately select Local setpoint 1 and Remote setpoint
or switch between the 2 Local Setpoints.
or
Press appropriate key until you see the desired setpoint
indicated.
ATTENTION
“KEY ERROR” appears in the lower
display if the remote setpoint or second local setpoint is
not configured as a setpoint source, or if you attempt to
change the setpoint while a setpoint ramp is enabled.
2
Change the Local
setpoint value
or
The REMOTE setpoint cannot be changed at the
keyboard.
Setpoint selection indication
Table 5-14 shows how the indicators react and what the displays show for each type of setpoint.
Table 5-14 Setpoint Selection Indication
Using Local Setpoint
Using Remote Setpoint
Using 2
nd
Local Setpoint
RSP Indicator
OFF
ON (Note 1)
ON (Note 2)
(Note 3)
Upper Display
PV
PV
PV
Lower Display
SP and the Local Setpoint
Source
RSP and Remote Setpoint
Value
2SP and the 2nd Local
Setpoint Value
To Change
Setpoint Value
Press or
Cannot change the value at
the keyboard.
Press or
Note 1RSP blinks when RSP is reached using Digital Input
Note 2RSP solid for 2nd Setpoint
Note 3RSP blinks for 2nd setpoint activated by Digital Switch
Operation - Single Setpoint Ramp
152 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
5.7 Single Setpoint Ramp
Configuring the setpoint ramp
You can configure a single setpoint ramp to occur between the current local setpoint and a final local
setpoint over a time interval of from 1 to 255 minutes. You can RUN or HOLD the ramp at any time.
Procedure
Table 5-15 lists the procedure for configuring the Setpoint Ramp 1 or 2 parameters. The procedure for
Setpoint Program is in Section 6 Setpoint Ramp/Soak Programming and Operation.
Table 5-15 Procedure for Configuring a Single Setpoint Ramp
Step
Operation
Press
Action/Result
1
Select SP RAMP 1 or
SP RAMP 2 Set Up
group
SET
UP
Until you see:
Upper Display: SET UP
Lower Display: SP RAMP X
X = 1 or 2
2
Select the Setpoint Ramp
function
FUNC
Until you see:
Upper Display: DISABL
Lower Display: SP RAMP X
3
Enable Setpoint Ramp
Until you see:
Upper Display: ENABLE
Lower Display: SP RAMP X
NOTE: You cannot change the current local setpoint if
the setpoint ramp function is enabled. Make sure SP
PROG is disabled.
4
Set the Ramp Time
FUNC
Until you see:
Upper Display: The ramp time in minutes
Lower Display: TIME MIN
or
Change the upper display value to the number of
minutes in which you want the final setpoint to be
reached.
Setting Range = 1 to 255 minutes
NOTE: Entering “0” implies an immediate step change
to the final SP.
5
Set the Final Setpoint
value
FUNC
Upper Display: The final setpoint value
Lower Display: FINAL SP
or
Change the upper display value to the desired final
setpoint value.
Setting Range = within the setpoint limits
Operation - Single Setpoint Ramp
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 153
April 2017
Running the setpoint ramp
Running a setpoint ramp includes starting, holding, viewing the ramp time, ending the ramp and disabling
it.
Procedure
Table 5-16 lists the procedure for running the setpoint ramp.
Table 5-16 Procedure for Running a Setpoint Ramp
Step
Operation
Press
Action/Result
1
Put the controller into
automatic mode
MAN
AUTO
Until “A” indicator is ON and you will see:
Upper Display: H and the PV value
Lower Display: SP and the present setpoint value
2
Set Start SP
or
Until the start setpoint value you desire is indicated in
the lower display:
Upper Display: H and the PV value
Lower Display: SP and the start setpoint value
3
Start the ramp
RUN
HOLD
You will see:
Upper Display: R and the PV value
Lower Display: SP and a changing setpoint value
NOTE: The value in the lower display will be increasing
or decreasing toward the final setpoint value.
The PV value in the upper display and the pen trace will
also change.
4
Hold the ramp at the
current value
RUN
HOLD
This holds the ramp at the current setpoint value.
Press again to continue run.
A “KEY ERROR” prompt appears if RUN/HOLD key is
pressed while “SP RAMP” is disabled.
5
View the remaining ramp
time
LOWR
DISP
Until you see:
Upper Display: R or H and the PV value
Lower Display: RAMP XXXM (time remaining)
6
End the ramp
When the final setpoint is reached, the “R” changes to
“H” in the upper display and the recorder operates at
the new setpoint.
ATTENTION
Any time the local setpoint is different
from the final setpoint value and the RUN/HOLD key is
pressed the ramp will start again.
Operation - Single Setpoint Ramp
154 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Step
Operation
Press
Action/Result
7
Disable the setpoint ramp
function
SET
UP
Until you see:
Upper Display: SET UP
Lower Display: SP RAMP X
FUNC
You will see:
Upper Display: ENABLE
Lower Display: SP RAMP X
You will see:
Upper Display: DISABL
Lower Display: SP RAMP X
8
Return to normal
operating mode
LOWR
DISP
Returns to normal operating mode.
Operation - Using Two Sets of Tuning Constants (PID Values)
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 155
April 2017
5.8 Using Two Sets of Tuning Constants (PID Values)
Introduction
You can use two sets of tuning constants for single output types and choose the way they are to be
switched.
The sets can be:
Keyboard selected
Automatically switched when a predetermined Process Variable value is reached.
Automatically switched when a predetermined Setpoint value is reached.
The following procedures show you how to:
Select two sets
Set the switchover value
Set tuning constant value for each set
Switch between two sets via the keyboard (without automatic switchover)
ATTENTION
For recorders with two controllers (both enabled) remember that any controller-related values
displayed correspond with the lighted CHN indicator “1” means that the values apply for
Controller #1 and “2” means that the values apply for Controller #2.
Select two sets
The procedure in Table 5-17 tells you how to select two sets of tuning constants.
Table 5-17 Procedure for Selecting Two Sets of Tuning Constants
Step
Operation
Press
Action/Result
1
Select Control Set Up
group
SET
UP
Until you see:
Upper Display: SET UP
Lower Display: CONTROL
2
Select
PID SETS function
FUNC
You will see:
Upper Display: Available selections are
1 ONLY 1 set of constants
2 KEYBD 2 sets, keyboard selectable
2 PVSW 2 sets, auto switch at PV value
2 SPSW 2 sets, auto switch at SP value
Lower Display: PIDSETS
or
Select the type of PID set.
Set switchover value
If you select 2 PVSW or 2 SPSW, you must set a value at which the sets will switch over.
The procedure in Table 5-18 shows you how to set this value.
Operation - Using Two Sets of Tuning Constants (PID Values)
156 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Table 5-18 Procedure for Setting Switchover Values
Step
Operation
Press
Action/Result
1
Select switchover value
function
FUNC
assuming you
are still in Set Up
group CONTROL
Until you see:
Upper Display: The switchover value
Lower Display: SW VALUE
or
Select the switchover value in the upper display.
Set tuning constant values for each set
There are specific tuning constants that must be set for each set. The procedure in Table 5-19 shows you
how to access these constants and change their values.
Table 5-19 Procedure for Setting Tuning Constant Values
Step
Operation
Press
Action/Result
1
Select Tuning Set Up
group
SET
UP
Until you see:
Upper Display: SET UP
Lower Display: TUNING
2
Select the tuning
constants
FUNC
Successively displays the following constants:
Upper Display: Tuning constant value
Lower Display: PROPBD or GAIN*
RATEMIN*
RSETMIN or RSETRPM*
PROPBD2 or GAIN2**
RATE2MIN**
RSET2MIN or RSET2RPM**
*PIDSET1 will be used when PV or SP, whichever is
selected, is greater than the switchover value.
**PIDSET2 will be used when PV or SP, whichever is
selected, is less than the switchover value.
or
Change the value of any of the above listed prompts in
the lower display.
Operation - Using Two Sets of Tuning Constants (PID Values)
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 157
April 2017
Switch between two sets via the keyboard (without automatic switchover)
This procedure is operational only if 2 PID SETS was configured at “CONTROL” set up group.
The procedure in Table 5-20 shows you how to switch from one set to another.
Table 5-20 Procedure for Switching PID Sets from the Keyboard
Step
Operation
Press
Action/Result
1
Access the PID set
display
LOWR
DISP
Until you see:
Upper Display: The PV value
Lower Display: PIDSETX
X = 1 or 2
or
Change PIDSET1 to PIDSET2 or vice versa.
Operation - Using Accutune II
158 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
5.9 Using Accutune II
Introduction
Accutune II provides foolproof, trouble-free on-demand tuning in the recorder. No knowledge of the
process is required at start-up. The operator simply enters the desired setpoint and initiates the tuning. The
recorder immediately starts controlling to the setpoint while it identifies the process, calculates the tuning
constants and enters them into the tuning set up group, and begins PID control with the correct tuning
parameters. This works with any process, including integrating type processes, and allows retuning at a
fixed setpoint. The tuning sequence will cycle the recorder’s output two full cycles between 0 % and
100 % (or low and high output limits) while allowing only a very small process variable change above and
below the setpoint during each cycle.
Accutune works for all control algorithms except ON/OFF.
The recorder must be in Auto mode.
Accutune works for integrating processes.
Enable/disable Accutune using the tuning set up group ACCUTUNE parameter described in Section 4.
Detailed instructions for using Accutune follow.
Starting and Stopping Tuning with Accutune II
After “ACCUTUNE” has been enabled in the tuning set up group as described in Section 4, use the
procedure in Table 5-21 to start tuning.
To abort tuning in progress, press the MAN/AUTO/RESET key to take the recorder out of Auto mode.
The message “AbRT” (abort) will be displayed as the value of tuning set up group parameter “AT ERR”.
The tuning parameters will retain the values they had at the start of the Accutune operation.
Table 5-21 Procedure for Starting Accutune II
Step
Press
Action/Result
1
DISP
until you see
Until you see
Lower Display: TUNExOFF (x = 1 or 2)
If “TUNExOFF” (tune off) does not appear, then Accutune is not
enabled.
2
or
to toggle to
Lower Display: TUNExON (x = 1 or 2)
Tuning will begin and the lower display will flash “TUNING”.
When tuning has been ompleted the lower display will again show
“TUNExOFF”.
Operation - Using Accutune II
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 159
April 2017
Using Accutune with Duplex (Heat/Cool) Control
“TUNE” can be done for applications using Duplex (Heat/Cool) control.
During tuning, Accutune II assumes SP 1 will cause a Heating demand, and then the calculated tuning
parameters will be automatically entered as the first set of PID constants. Likewise, it assumes tuning at
Local SP 2 will cause a Cooling demand, and the cooling parameters will be entered as the second set of
PID constants.
Procedure
After “ACCUTUNE” has been enabled in the tuning set up group as described in Section 4, use the
procedure in Table 5-22 to start tuning. Note that control group parameter “SP SOURC” must be set to
“2LOCAL” to enable the second setpoint.
To abort tuning in progress, press the MAN/AUTO key to take the recorder out of Auto mode. The
message “AbRT” (abort) will be displayed as the value of tuning set up group parameter “AT ERR”. The
tuning parameters will retain the values they had at the start of the Accutune operation.
Table 5-22 Procedure for Using Accutune for Duplex Control
Step
Press
Action/Result
Heating Tuning
1
DISP
Until you see Setpoint 1.
Lower Display: SP nnn
2
or
Until the value of Setpoint 1 is at the desired value within the Heat
zone.
Make sure the recorder is in Auto mode. (“A” indicator lit.)
If not, use the MAN/AUTO/RESET key to put the unit in Auto.
3
DISP
Until you see
Lower Display: UseSPn
This is the prompt used to select the setpoint. If it is not
“USESP1”, use or to switch to “USESP1”.
4
DISP
Until you see
Lower Display: TUNExOFF (x = 1 or 2)
If “TUNExOFF” (tune off) does not appear, then Accutune is not
enabled.
5
or
to toggle to
Lower Display: TUNExON (x = 1 or 2)
Tuning will begin and the lower display will flash “TUNING”. The
output will cycle between 50 % and 100 % (or high output limit).
When tuning has been completed the lower display will again
show “TUNExOFF”. The Heat tuning parameters are entered for
the first set of PID constants in the tuning set up group.
Operation - Using Accutune II
160 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Step
Press
Action/Result
Cooling Tuning
6
DISP
Until you see Setpoint 2.
Lower Display: SP nnn
7
or
Until the value of Setpoint 2 is at the desired value within the
Cooling zone.
8
DISP
Until you see
Lower Display: Use SP1
9
or
to toggle to
Lower Display: Use SP2
10
DISP
Lower Display: TUNExOFF
11
or
to toggle to
Lower Display: TUNExON
Tuning will begin and the lower display will flash “TUNING”. The
output will cycle between 0 % and 50 % (or low output limit).
When tuning has been completed the lower display will again
show “TUNExOFF”. The Cool tuning parameters are entered for
the second set of PID constants in the tuning set up group.
Operation - Alarm Setpoints
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 161
April 2017
5.10 Alarm Setpoints
Introduction
An alarm consists of a relay contact and an operator interface indication. The alarm relay is de-energized
if Alarm Setpoint 1 or Setpoint 2 is exceeded.
The alarm relay is energized when the monitored value goes into the allowed region by more than the
hysteresis.
There are twelve alarm setpoints, two for each alarm.
The type and state (High or Low) is selected during configuration: see Section 3 - Configuration for
details.
ATTENTION
An active alarm will always provide an indication on the display but may not control the relay;
that is, a higher priority function such as a control loop or timer may have control of the relay.
Procedure for displaying the alarm setpoints
The procedure for displaying and changing the alarm setpoints is listed in Table 5-23.
Table 5-23 Procedure for Displaying or Changing the Alarm Setpoints
Step
Operation
Press
Action/Result
1
Access the Alarm Set Up
group
SET
UP
Until you see:
Upper Display: SET UP
Lower Display: ALARM X
X = 1, 2, 3, 4, 5, 6
2
Access the Alarm
Setpoint Values
FUNC
Successively displays the alarm setpoints and their
values.
Upper Display: The alarm setpoint value
Lower Display: AXS1 VAL Setpoint 1 value of
alarm 1, 2, 3, 4, 5, or 6
AXS2 VAL Setpoint 2 value of
alarm 1, 2, 3, 4, 5, or 6
or
Change any alarm setpoint value you select in the
upper display.
3
Return to normal
operation
LOWR
DISP
Returns to normal operation.
Operation - Three Position Step Control Algorithm
162 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
5.11 Three Position Step Control Algorithm
Introduction
The Three Position Step Control algorithm allows the control of a valve (or other actuator) with an electric
motor driven by two controller output relays; one to move the motor upscale, the other to move it
downscale, without a feedback slidewire linked to the motor shaft.
Estimated motor position
The Three Position Step Control algorithm provides an output display (“OUT”) which is an estimated
motor position since the motor is not using any feedback.
Although this output indication is only accurate to a few percent, it is corrected each time the controller
drives the motor to one of its stops (0 % or 100 %).
It avoids all the control problems associated with the feedback slidewire (wear, dirt, noise).
When operating in this algorithm, the estimated “OUT” display is shown to the nearest percent (i.e., no
decimal).
Displaying the motor position
Table 5-24 lists the procedure for displaying the motor position.
Table 5-24 Procedure for Displaying the 3PSTEP Motor Position
Step
Operation
Press
Action/Result
1
Access the displays
LOWR
DISP
Until you see:
Upper Display: The PV value
Lower Display: OUT
Estimated 3PStep motor position
Power up output
When the controller powers up after a power outage, the position of the motor will correspond to whatever
was configured at set up group prompt “CONTROL”, function prompt “PWR OUT”, selection LAST or
FAILSAFE. Refer to Subsection 4.8, Table 4-7 for definition of each selection.
Operation - Digital Input Option (Remote Switching)
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 163
April 2017
5.12 Digital Input Option (Remote Switching)
Introduction
The digital input option detects the state of external contacts wired to it. On contact closure, the controller
responds according to how each digital input is configured.
Make your selection under set up group “CONTROL1” or “CONTROL2”, function group prompt “REM
SW”: see Subsection 3.12Table 3-9 or Subsection 4.8Table 4-7.
Action on contact closure
Table 5-25 lists the configuration prompt selections, the “Action on Contact Closure”, and the display
indication for each selection available.
Table 5-25 Digital Input Option Action on Contact Closure
REM SW
Selections
Display Indication
Action on Contact Closure
None
None
No Digital Input selection
To MAN
“MAN” blinks
Puts the controller into manual mode; contact open
returns the controller to former mode unless
AUTO/MAN key is pressed while digital input is active.
To LSP
“RSP” blinks
Puts the controller into local setpoint 1 (switches out of
remote). When contact opens, the controller returns to
former operation unless the FUNC key is pressed while
digital input is active.
To 2SP
“RSP” blinks
Puts the controller into local setpoint 2.
To DIR
None
Selects direct controller action (transfer if in reverse).
RN/HOLD
“H” blinks in upper display
Suspends setpoint program or setpoint ramp.
Keyboard takes priority over external switch for
RUN/HOLD function.
Contact open runs the program or ramp.
If initially in the HOLD state, close then open the
contact to remotely start the SP ramp or Program
TUNE
TUNING x
Initiates Accutune
Keyboard operation
If a particular mode or parameter is selected by the contact closure, using the keyboard to select the same
parameter ensures that the selected mode will be maintained after the remote digital switch is reopened.
Operation - Resetting and Displaying Totalizer Value
164 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
5.13 Resetting and Displaying Totalizer Value
Introduction
If the totalizer is enabled and has been configured to allow resetting, you can reset the current totalizer
value as follows.
Refer to Section 3 - Configuration, under set up prompt “TOTAL 1” for Input #1 or “TOTAL 2” for
Input #2 to enable the totalizer function and allow the totalizer to be reset.
Refer to the procedures that follow to:
reset the totalizer locally,
reset the totalizer using the Wake Time feature,
reset the totalizer externally (switch),
display the totalizer value.
Resetting the totalizer locally
Follow the procedure in Table 5-26 to reset the totalizer value.
Table 5-26 Procedure for Resetting the Totalizer
Step
Operation
Press
Action/Result
1
Access the Totalizer Set
Up group
SET
UP
Until you see:
Upper Display: SET UP
Lower Display: TOTAL 1 or TOTAL 2
2
Allow Totalizer Reset
FUNC
once
You will see:
Upper Display: Ex XXX
Lower Display: (a value)
FUNC
again
You will see:
Upper Display: NO
Lower Display: RSET TOT
or
Change NO to YES in the upper display.
ATTENTION
Function prompt “RSETABLE” must
be set to “LOCAL”.
3
Return to normal
operation
LOWR
DISP
Returns to normal operation.
Resetting the totalizer using the Wake Time feature
To reset the totalizer using the Wake Time feature, set the Wake Time ("WAKE MIN", "WAKE HR",
"WAKE DAY", "WAKE MON" in Subsection 3.9 Time Set Up Group) as desired. Then set function
prompt "RSETABLE" (Subsection 3.10 Totalizer Set Up Group) to "TIME". When the configured Wake
Time value is reached, the totalizer will reset to "0".
Operation - Resetting and Displaying Totalizer Value
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 165
April 2017
External totalizer reset
The totalizer can be reset to “0” from external switch #1 or external switch #2. Refer to Subsection 3.10
Totalizer Set Up Group and set function prompt “RSETABLE” to “EXT SW1” or “EXT SW2”.
Displaying the totalizer value
Follow the procedure in Table 5-27 to display the totalizer value.
Table 5-27 Procedure for Displaying the Totalizer Value
Step
Operation
Press
Action/Result
1
Alternating Totalizer
Display
LOWR
DISP
Until you see:
Upper Display: tPV VALUE
Lower Display: (total value)
ATTENTION
When two totalizers are configured,
notice that channels #1 and #2 totalizer values are
alternately displayed.
2
Display Channel #1
totalizer
or
Until CHN “1” indicator lights.
Upper Display: 1TPV VALUE
Lower Display: (total value)
3
Display Channel #2
totalizer
or
Until CHN “2” indicator lights.
Upper Display: 2TPV VALUE
Lower Display: (total value)
4
Return to Alternating
Display
and
simultaneously
You will see:
Upper Display: SCAN
Lower Display: (total value)
After the keys are released, the upper display
alternately shows #1, #2 PV values while lower display
shows #1, #2 totalization values.
5
Return to Normal PV
Display
LOWR
DISP
Returns to normal PV display.
Operation - Monitoring the External Event Operation
166 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
5.14 Monitoring the External Event Operation
Event pen function
If Function prompt “PEN 1IN” under Set-up prompt “PEN 1” has been configured as DGTL1 or DGTL2,
the pen (channel) operates as an “event pen” and tracks the remote contact (switch) closure by way of the
digital 1 or digital 2 input wired to the alarm output/digital input printed circuit board.
Event pen operation
When the switch opens, the trace for the channel tracks at the configured OFF position (0-100 %) on the
chart.
When the switch closes, the trace tracks at the configured ON position (0-100 %) on the chart and tracks at
this position until the switch is opened.
Thus, the “Event Pen” record makes it easy to monitor the on/off operation of an external event.
Operation - Maximizing Pen Life
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 167
April 2017
5.15 Maximizing Pen Life
Steps for maximizing pen life
Table 5-28 lists nine steps that will help to maximize the life of your chart pen.
Table 5-28 Maximizing Pen Life
Step
Action
1
Store the chart paper in a cool, clean dry place where the temperature does not exceed 40 °C
(104 °F) and the humidity is below 65 % RH.
2
Do not expose the pen tip and chart paper to abrasive chemicals or dust that cause excessive
pen wear.
3
If the recorder is used in a dusty atmosphere, provide a positive ‘clean air purge’ to minimize
dust particle accumulation on the chart paper.
4
Periodically clean the pen arm using a cotton swab dipped in alcohol. This is more important
when the recorder is located in a dusty environment and no ‘clean air purge’ is used.
5
Never let the pen tip ride on the chart plate when the paper is not present. Use the pen lifter to
raise the arm when changing the paper.
6
Keep the door closed while recording.
7
Always insert the pen arm tip into the shipping sponge when storing or shipping the recorder.
8
Be sure that the chart paper lays flat against the chart plate. Any ripple in the paper will cause
light pen printing.
9
Be sure the chart hub assembly is pushed onto the motor shaft so that it is flush with the chart
plate.
Operation - Routine Maintenance
168 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
5.16 Routine Maintenance
Introduction
The DR4500A recorder does not require any periodic maintenance as such. But, you will have to clean the
pen tip, and replace the chart and optional chart lamp as required.
WARNING
Do not lubricate the plastic gears on the chart and pen motors.
Cleaning the pen tip
Follow the procedure in Table 5-29 to clean the pen tip.
CAUTION
Cleaning frequency varies with the recording application environment.
Table 5-29 Cleaning the Pen Tip
Step
Action
1
Open the recorder door.
2
Pull the pen lifter up in order to raise the pen from the chart.
3
Carefully clean the pen tip with a cotton swab that has been dipped in alcohol.
4
Push the pen lifter down to lower the pen.
5
Close the door and resume normal operation.
Replacing a burned-out chart lamp (optional)
Follow the procedure in Table 5-30 to replace a burned-out chart lamp.
Table 5-30 Replacing a Chart Lamp
Step
Action
1
Open the recorder door and remove power.
2
Unscrew and remove the hood from the lamp assembly.
3
Push the (bayonet-type) lamp in and turn it counterclockwise to remove it from the socket.
4
Reverse step 3 and install the replacement lamp (General Instrument type 1828 or equivalent)
in the socket.
5
Replace the hood on the lamp assembly.
6
Close the door and apply the power.
Operation - Installing/Replacing Chart
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 169
April 2017
5.17 Installing/Replacing Chart
Installing/replacing chart procedure
Follow the procedure in Table 5-31 to install/replace the chart.
CAUTION
Store replacement charts in a dust-resistant location. Otherwise, accumulated dust on the
chart may cause excessive pen tip abrasion which can shorten expected pen life. In addition,
you may want to air purge the case if the recorder is mounted in an extremely dusty
environment.
Table 5-31 Installing/Replacing the Chart
Step
Action
1
Open the recorder door.
2
Press the CHART key. The pen moves to and stops at the outer limit of pen travel near the
edge of the chart. Also, chart rotation stops CHT HOLD flashes in lower display.
3
Pull the pen lifter up to raise the pen from the chart.
4
Carefully remove the used chart from the hub and retaining clips (do not remove the hub
adapter).
5
Install the new chart so that its edges are under the four retaining clips and its small alignment
hole is over the alignment pin on the hub (that is, press the chart down completely around the
hub adapter).
6
Push the pen lifter down to lower the pen.
7
Press the CHART key. The recorder goes to the “CHART RUN.” CHT HOLD stops flashing in
lower display.
ATTENTION
The recorder has a non-volatile memory. You can reset the processor by
cycling the power, but it will have no affect on any data stored. One portion of this stored data
is how many motor steps remain in the 7200 steps contained in 360 degrees of chart rotation.
The counter that holds this data is reset by going from “CHART HOLD” to “CHART RUN.”
If, in the “CHART” set up group, the recorder is configured for “HEADER” (YES), a new header
is printed, then the pen recording of input values resumes.
If “HEADER” (NO) is configured, recording resumes immediately.
8
Be sure to keep the door closed during operation to minimize dust collection on the chart.
When using REM CHRT (ver: ≥ 10.57) after pressing CHART in this step, CHT HOLD changes
to REM CHRT flashes in lower display to indicate the chart is ready for delayed start. Refer to
Table 3.8
Operation - Chart Operation
170 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
5.18 Chart Operation
Normal operation
The recorder functions differently if “NO CONTINUE” or “YES CONTINUE” is selected in Configuration
Setup Group “CHART,” function prompt “CONTINUE.” Refer to Subsection 3.8 for selection instructions.
NO CONTINUE Operation
A header is printed (only if “HEADER YES” is selected in Configuration Setup Group “CHART,”
function prompt “HEADER.” Refer to Subsection 3.8 for selection instructions.)
Graph starts with a major time line if not a standard chart.
If standard chart, graph starts with a solid line indicating where the chart began. An incomplete segment
will be printed with no time or text information up to the next hour mark. At that point, a new time line
will be printed, on the hour. The initial incomplete segment will be completed, including any partially
printed range values, at the end of the rotation. Additionally, any time or text information being printed
when the chart hits 7200 steps will continue to be completed.
Chart motor takes 7200 steps printing graph, time lines, and PV.
Counter decrements to 0.
Chart stops rotation.
YES CONTINUE Operation
A header is printed (only if “HEADER YES” is selected in Configuration Setup Group “CHART,
function prompt “HEADER.” Refer to Subsection 3.8 for selection instructions.)
Graph starts with a major time line.
Chart motor takes 7200 steps printing graph, time lines, and PV.
Counter decrements to 0.
Graph stops printing.
PV prints forever (or until the next transition from “CHART RUN” to “CHART HOLD.”
Operation - Chart Operation
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 171
April 2017
Remote chart operation
The Remote Chart feature can be configured to activate on any one of six events. Refer to Subsection 3.8
Table 3-5 or Subsection 4.4Table 4-3 under Function prompt “REMCHT” to select an event.
When the Remote Chart feature is activated, there are three chart modes as defined in Table 5-32.
Table 5-32 Remote Chart Modes
Mode
Definition
HOLD
HOLD is the mode when you are changing the paper or when the chart has
completed.
HOLD is indicated by the “CHT HLD” flashing in the lower display.
READY
You enter the READY mode from the Hold mode by pressing the CHART key
once.
When in the READY mode, the lower display will flash “REM CHT”.
READY is the “armed” mode where the remote events are allowed. The chart is
waiting to be activated by whatever event has been configured or by pressing
CHART again. It is not retriggerable.
RUN
RUN is the mode where the chart has received its trigger.
The chart will remain in RUN until the chart is finished (for non-continue charts) or
until you press the CHART key.
When the CHART key is pressed during the RUN mode, the chart will enter the
HOLD mode.
RUN mode can be forced from the READY mode by pressing the CHART key.
All modes are saved in battery backed RAM and will be maintained over power cycles.
Recovery from a power loss
The chart will operate as listed below when power is restored after a power loss.
Recorder shuts down with the remainder of the 7200 motor steps stored.
The processor goes through memory self-test when power is restored.
The recorder prints a new motor time line if not a standard chart.
If standard chart, text information will be lost until the next hour mark.
The chart counter starts to decrement from the motor step value stored at power loss.
Normal chart operation resumes.
A new “HEADER” is not printed.
If power is not interrupted again and normal operation is allowed to continue, the time and date will be
printed behind the new major time line. Thisdocuments the time that power was restored.
ATTENTION
Multiple major time divisions on varying time bases indicate power or operator problems.
Release M DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 172
May 2013
6. Setpoint Ramp/Soak Programming and Operation
6.1 Overview
Introduction
As an option, the recorder can support the programming of a 36-segment setpoint program containing 18
ramp segments and 18 soak segments. In a ramp segment the setpoint value is changed as specified during
configuration. The ramp is configured in terms of ramp time or ramp rate, depending on how you have
configured the RAMPUNIT parameter. During a soak segment the setpoint is held at the specified value.
For each control loop you can build up to 6 profiles using any number of consecutive segments of the
program.
Odd-numbered segments are always ramp segments. Even-numbered segments are always soaks. These
ramp and soak segments can be used in up to six programs. You designate the beginning and end segments
to determine where the program will start or stop.
Every profile must start with a ramp segment and end on a soak segment.
Control Loop must have Setpoint Source set to 1LOCAL.
Control Loop 1 uses SP RAMP1, Control Loop 2 uses SP RAMP2. SP RAMP1 and SP RAMP2 are the
prompts under which the setpoint program is configured.
Recorder must be set to use SP1 (setpoint 1).
Only contiguous segments can be used by a profile.
There can be overlap between programs. For example, Profile 1 could use Segments 1, 2, 3, 4, 5, and 6.
Profile 2 could be configured to begin with Segment 5 and end with Segment 8.
This section contains instructions for setting up a setpoint program, and for executing the program at
runtime.
Note that Section 4 contains instructions for using the setpoint ramp or setpoint rate. The SP RAMP
(setpoint ramp) and SP RATE (setpoint rate) parameters described in Section 4 must be set to
DISABL (disabled) if a setpoint program is to be used.
ATTENTION
If power is lost during execution of a program, upon power-up the recorder will use the last
setpoint value prior to the beginning of the setpoint program. The program is placed in hold at
the beginning. The Manual/Auto mode will be as configured under “POWER UP” in the
“CONTROL” group.
Setpoint Ramp/Soak Programming and Operation - Overview
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 173
April 2017
What’s in this section?
This section contains the following information:
Topic
See Page
6.2 Setpoint Program Contents
174
6.3 Drawing a Ramp/Soak Profile
177
6.4 Entering the Setpoint Program Data
182
6.5 SP RAMP1 and SP RAMP2 Set Up Group
184
6.6 Setpoint Program Profiles Set Up Group
186
6.7 Setpoint Program Segments Set Up Group
188
6.8 Setpoint Program Event Set Up Group
191
6.9 Run/Monitor the Program
195
Setpoint Ramp/Soak Programming and Operation - Setpoint Program Contents
174 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
6.2 Setpoint Program Contents
What you will configure
You will configure all the data that is relevant to each ramp and soak segment for a given setpoint versus
time program (profile). The recorder will prompt you through the sequence of segments and associated
functions. These prompts and functions are described below.
Recycle number
The recycle number allows the program to recycle a specified number of times from beginning to end.
Range = 0 to 99
Guaranteed soak
A SOAK DEV (soak deviation) parameter is provided. If its value is not zero, then soaking will be frozen
for each segment until the difference (plus or minus) between PV and SP is less than or equal to the value
of SOAK DEV.
There are no guaranteed soaks whenever SOAKDEV = 0. In this case, soak segments start timing soak
duration as soon as the soak setpoint is first reached, regardless of where the process variable remains
relative to the soak setpoint during the duration of the segment.
The decimal location corresponds to input 1 decimal selection.
Profile number
The profile number specifies which of up to six profiles will run. Up to 6 profiles can be configured out of
any even number of consecutive segments from the 36 segments configured.
Program state
The program state selection determines the program state after completion.
The selections are:
DISABL = program is disabled
HOLD = program on hold
Recovery
If Recovery is enabled the setpoint program will continue from where it left off after the last power down.
Program End State
This determines the status of the recorder upon completion of the profile. The selections are:
LAST SP = hold at the last setpoint in the program
F SAFE = Manual mode, Failsafe Output
Setpoint Ramp/Soak Programming and Operation - Setpoint Program Contents
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 175
April 2017
Profile Start and Profile End
These selections let you specify the segments that will comprise each of the 6 profiles. The first segment
must be a ramp (odd-numbered segment) and the last segment must be a soak (even-numbered).
Ramp unit
The ramp unit selection determines the engineering units for the ramp segments.
The selections are:
TIME = Hours:Minutes
EU-H = Degrees/Hour OR EU-M = Degrees/Minute
Ramp time or rate segments
A ramp segment is used to change the setpoint to the next soak setpoint value in the program.
Ramps are odd-numbered segments. Segment 1 will be the initial ramp.
Ramps are specifed in terms of either:
TIME* - Hours:Minutes Range = 0-99 hrs:59 min.
or
EU-M* - Degrees/Minute Range = 0 to 999
EU-H* - Degrees/Hour
* The selection of time or rate is made at prompt “RAMP UNIT”
Set this prompt before entering any Ramp information.
ATTENTION
Entering “0” will imply an immediate step change in setpoint to the next soak.
Soak segments
A soak segment is a combination of soak setpoint (value) and a soak duration (time).
Soaks are even-numbered segments.
Segment 2 will be the initial soak value and soak time.
The soak setpoint range value must be within the setpoint high and low range limits in engineering units.
(Specify the setpoint range with SP HI and SP LO in the control group as described in Section 4.)
Soak time is the duration of the soak and is determined in:
TIME - Hours:Minutes Range = 0-99 hrs:59 min.
Segment Events
Each segment can be programmed to trigger an alarm which in turn deenergizes the associated relay. The
selected alarm must be programmed as an event type for this to occur. Selections are:
ALARM 1 ALARM 6.
Segment events will not trigger a relay if that relay is configured with one of these higher priority
functions:
Setpoint Ramp/Soak Programming and Operation - Setpoint Program Contents
176 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Control loop output
Interval Timer
alarm type other than “Event”.
See During alarm conditions an alarm will deenergize its associated relay unless a higher priority function
has been configured for that relay. See Table 3-13. If you want the alarm to control the relay, do not
configure a higher priority function.
Table 3-13.
Digital input (remote) operation
Program can be placed in RUN or HOLD state through a remote dry contact connected to optional digital
input terminals. The Control Loop parameters REM SW and REM SW2 parameters must be configured as
RN/HLD to support this function. The valid states of the contacts are:
RUNcontact closure places program in HOLD state
HOLDcontact open places program in RUN state
Setpoint Ramp/Soak Programming and Operation - Drawing a Ramp/Soak Profile
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 177
April 2017
6.3 Drawing a Ramp/Soak Profile
Ramp/soak profile example
Before you perform the actual configuration, we recommend that you draw your Ramp/Soak profiles in the
space provided on the blank graphs and fill in the associated information on the worksheet. An example of
a Ramp-Soak Profile using the first twelve segments for Profile 1 is shown in Figure 6-1. Start setpoint in
this example is at 200 F. Assume each soak segment is desired to trigger an event. Assume you are
configuring the program to be used by Control Loop1 (SP RAMP1).
500
400
200
300
°
F
Time/Hours
0 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17
SEG 2
SEG 3
SEG 4
SEG 5
SEG 6
SEG 7
SEG 8
SEG 9
SG 10
SG 11
SG 12
SEG 1
F
20765
Setpoint
Figure 6-1 Ramp/Soak Profile Example
Setpoint Ramp/Soak Programming and Operation - Drawing a Ramp/Soak Profile
178 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Table 6-1 Parameter settings for example 12-step profile
Prompt
Function
Segment
Value
Prompt
Function
Segment
Value
SP RAMP1
Settings for
Control Loop 1
ramp
SEG7RAMP
Ramp
7
2hrs:30min.
SP PROG
Enables SP
prompts.
ENABLE
SEG8 SP
Soak SP
8
500
RECYCLES
Number of
Recycles
2
SEG8TIME
Soak Time
8
0hr.:30 min.
SOAK DEV
Deviation
Value
0
SEG9RAMP
Ramp
9
0
PROFILE
Number of
profile to run
1
SEG10 SP
Soak SP
10
400
STATE
Program
State at end
HOLD
SEG10TIME
Soak Time
10
0hr.:30 min.
RECOVERY
Program
resumes after
power
interruption
ENABLE
SEG11RAMP
Ramp
11
3hrs:30min.
PROG END
SP value after
last segment
LAST SP
SEG12 SP
Soak SP
12
200
SPP SEGS
Settings for
segments
SEG12TIME
Soak Time
12
0hr.:30 min.
PR1 STRT
Profile 1 Start
Seg.
1
SEG1 EV
Event
1
NONE
PR1 END
Profile 1 End
Seg.
12
SEG2 EV
Event
2
ALARM1
RAMPUNIT
Ramp Units
TIME
SEG3 EV
Event
3
NONE
SEG1 RAMP
Ramp
1
1 hr.
SEG4 EV
Event
4
ALARM1
SEG2 SP
Soak SP
2
300
SEG5 EV
Event
5
NONE
SEG2TIME
Soak Time
2
1hr.:30 min.
SEG6 EV
Event
6
ALARM1
SEG3RAMP
Ramp
3
1hr.
SEG7 EV
Event
7
NONE
SEG4 SP
Soak SP
4
400
SEG8 EV
Event
8
ALARM1
SEG4TIME
Soak Time
4
1 hr.
SEG9 EV
Event
9
NONE
SEG5RAMP
Ramp
5
1hr.:30 min.
SEG10 EV
Event
10
ALARM1
SEG6 SP
Soak SP
6
250
SEG11 EV
Event
11
NONE
SEG6TIME
Soak Time
6
3hrs.:0min.
SEG12 EV
Event
12
ALARM1
Reminder: There are up to 36 segments available for inclusion in a profile. The above example uses only
the first 12.
Setpoint Ramp/Soak Programming and Operation - Drawing a Ramp/Soak Profile
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 179
April 2017
Profile graphs
Draw your six ramp/soak profiles on the graphs below and fill in the associated information in the
worksheets that follow in the next sections. This will give you a permanent record of your program and will
assist you when entering the ramp and soak values.
Profile 1
20766
Profile 2
20766
Setpoint Ramp/Soak Programming and Operation - Drawing a Ramp/Soak Profile
180 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Profile 3
20766
Profile 4
20766
Setpoint Ramp/Soak Programming and Operation - Drawing a Ramp/Soak Profile
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 181
April 2017
Profile 5
20766
Profile 6
20766
Setpoint Ramp/Soak Programming and Operation - Entering the Setpoint Program Data
182 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
6.4 Entering the Setpoint Program Data
Introduction
The procedure listed in Table 6-2 tells you what keys to press and what prompts you will see when entering
the setpoint program data. Follow the prompts in Subsections 6.5 through 6.8 when selecting the functions
for setpoint programming.
ATTENTION
Make sure SP RAMP and SP RATE are disabled first.
Table 6-2 Setpoint program data entry procedure
Step
Operation
Press
Action/Result
1
Select SP PROG Group
SET
UP
Until you see:
Upper Display: SET UP
Lower Display: SP RAMPn n = 1 or 2
2
Access SP PROG
FUNC
Until you see:
Upper Display: DISABL
Lower Display: SP PROG
If you see
Upper Display: ENABLE
Lower Display: SP RAMP
or
Upper Display: ENABLE
Lower Display: SP RATE
you must disable them. SP PROG and its subordinate
prompts are not visible unless SP RAMP and SP RATE
are disabled. Once they are disabled, press FUNC
until you see SP PROG.
3
Enable SP PROG
or
Until you see:
Upper Display: ENABLE
Lower Display: SP PROG
4
Select the functions
FUNC
Upper Display: shows current value for each prompt
Lower Display: shows individual function prompts within
the setpoint program group
Successive presses of the FUNCTION key
sequentially displays all the functions and their
values or selections.
Using the FUNCTION key, follow the prompts shown
in Sections 6.5 through 6.8.
Setpoint Ramp/Soak Programming and Operation - Entering the Setpoint Program Data
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 183
April 2017
Step
Operation
Press
Action/Result
5
Change the value or
selection of a function
prompt
or
This changes the value or selection in the upper
display. If the display blinks, you are trying to select an
unacceptable value.
6
Enter value or selection
into memory
FUNC
This enters the value or selection and goes to another
prompt.
Repeat steps 4 and 5 for each function you want to
change.
7
Exit configuration
LOWR
DISP
This exits from the configuration mode.
Setpoint Ramp/Soak Programming and Operation - SP RAMP1 and SP RAMP2 Set Up Group
184 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
6.5 SP RAMP1 and SP RAMP2 Set Up Group
Introduction
There is a SP RAMP set up group for each control loop. Use the prompts to select the settings for each
loop’s program.
SP RAMP prompts
Table 6-3 lists all the function prompts for SP RAMP configuration in the order of their appearance. These
prompts are available when SPPROG is enabled in the SPRAMP set up group described in Section 4.
All parameters may be changed while the program is disabled or in HOLD.
Table 6-3 SP RAMP prompts and available selections
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
SPPROG
DISABL
ENABLE
SETPOINT PROGRAMMINGThis must be set to
ENABLE for the setpoint program feature to work, and
for the associated operating parameters to be displayed.
SPRAMP and SP RATE must be disabled. (See Section
4.)
DISABLDisabled
ENABLEEnabled
RECYCLES
0 to 99
RECYCLESEnter the number of times the program
selected for execution will be repeated.
SOAKDEV
-99.9 to 99.9 engineering units
SOAK DEVIATIONEnter the acceptable deviation from
setpoint during a soak cycle. If the PV differs from the
setpoint by more than the value of SOAKDEV, soak time
is frozen.
There are no guaranteed soaks if SOAKDEV = 0.
PROFILE
1 to 6
PROFILE used by Setpoint Program. This can also be
set or changed when viewed in the lower display and the
current profile is in the HOLD state.
STATE
DISABLE
HOLD
Determines the state of the program after it completes
the final program segment cycles. If you select DISABL,
you must enable the program through the function
prompt before you can run the program again. If you
select HOLD, you can run the program again by
pressing the RUN/HOLD key.
RECOVERY
ENABLE
DISABL
This mode, when enabled, will allow the SP Program to
continue from the point at which the power was removed
when there is a power interruption.
PROG END
ENABLE
DISABL
Determines the status of the control output after the
program is run. If you select LASTSP, the recorder
controls to the last setpoint value which becomes the
LSP. For FSAFE selection, the recorder is switched to
manual mode and to the selected failsafe output value.
SP RAMP 1 and SP RAMP 2 worksheet
Setpoint Ramp/Soak Programming and Operation - SP RAMP1 and SP RAMP2 Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 185
April 2017
Use this worksheet to make a record of your SP RAMP1 and SP RAMP2 settings.
Prompt
Description
Range
Your selection
SP RAMP1
Accesses prompts for Control Loop 1’s
profile
N/A
N/A
SP PROG
Enables SP Program prompts.
ENABLE
DISABLE
ENABLE
RECYCLES
Number of Recycles
0-99
SOAK DEV
Deviation Value
0.0-99
PROFILE
Number of profile to run
1-6
STATE
Program State at end
DISABL
HOLD
RECOVERY
Program resumes after power
interruption
ENABLE
DISABLE
PROG END
SP value after last segment
LASTSP
FSAFE
SP RAMP2
Accesses prompts for Control Loop 2’s
profile
N/A
N/A
SP PROG
Enables SP Program prompts.
ENABLE
DISABLE
ENABLE
RECYCLES
Number of Recycles
0-99
SOAK DEV
Deviation Value
0.0-99
PROFILE
Number of profile to run
1-6
STATE
Program State at end
DISABL
HOLD
RECOVERY
Program resumes after power
interruption
ENABLE
DISABLE
PROG END
SP value after last segment
LASTSP
FSAFE
Setpoint Ramp/Soak Programming and Operation - Setpoint Program Profiles Set Up Group
186 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
6.6 Setpoint Program Profiles Set Up Group
Introduction
You can configure up to six profiles; each profile contains a subset of the 36 segments. Each profile starts
with a ramp segment and ends with a soak segment. Each control loop uses one of these profiles. They can
use the same profile, too. The profiles can be synchronized to RUN/HOLD together.
Setpoint program profiles group prompts
Table 6-4 lists all the function prompts in the Setpoint Program Profiles setup group and their definitions.
Table 6-4 Setpoint Program Profiles Group Definitions
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
PRx STRT
RAMP1 RAMP 35
You can configure up to 6 profiles (PR1 PR6). Each
profile contains a subset of the 36 ramp and soak
segments configured later. PRx STRT designates the
number of the first segment of the profile. It will be a
ramp segment (odd number).
PRx END
SOAK2 SOAK36
This designates the number of the last segment of the
profile. It will be a soak segment (even number).
RAMPUNIT
TIME (Hours:Minutes)
EU/MIN (Engineering
Units/Minute)
EU/HR (Engineering Units/Hour)
This determines the engineering units for the ramp
segments.
SYNC 1+2
ENABLE
DISABL
Synchronizes the profiles for Control Loops 1 and 2.
This means that:
a) Both SP programs will RUN or HOLD
simultaneously.
b) A Guaranteed Soak Hold on one profile will cause
the other profile to HOLD for the duration of the
Guaranteed Soak Hold.
Setpoint Ramp/Soak Programming and Operation - Setpoint Program Profiles Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 187
April 2017
Setpoint program profiles worksheet
Use this worksheet to keep a record of your setpoint profile settings.
Prompt
Function
Range
Your selection
PROFILES
Settings for profiles
PR1 STRT
Start Segment for Progam 1
RAMP1 to RAMP35
PR1 END
End Segment for Program 1
SOAK2 to SOAK36
PR2 STRT
Start Segment for Program 2
RAMP1 to RAMP35
PR2 END
End Segment for Program 2
SOAK2 to SOAK36
PR3 STRT
Start Segment for Program 3
RAMP1 to RAMP35
PR3 END
End Segment for Program 3
SOAK2 to SOAK36
PR4 STRT
Start Segment for Program 4
RAMP1 to RAMP35
PR4 END
End Segment for Program 4
SOAK2 to SOAK36
PR5 STRT
Start Segment for Program 5
RAMP1 to RAMP35
PR5 END
End Segment for Progam 5
SOAK2 to SOAK36
PR6 STRT
Start Segment for Program 6
RAMP1 to RAMP35
PR6 END
End Segment for Program 6
SOAK2 to SOAK36
RAMPUNIT
Ramp type
TIME
EU/MIN
EU/HR
SYNC 1+2
Synchronizes profile for Control
Loops 1 and 2.
ENABLE
DISABL
Setpoint Ramp/Soak Programming and Operation - Setpoint Program Segments Set Up Group
188 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
6.7 Setpoint Program Segments Set Up Group
Introduction
You can configure up to 36 ramp and soak segments.
Setpoint program segments group prompts
Table 6-5 lists all the function prompts in the Setpoint Program Segments setup group and their definitions.
Table 6-5 Setpoint Program Segments Group Definitions
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
SEGxRAMP
(x = 1, 3, 5,…35)
0-99 hrs:59 min. (Time)
0 to 999 (Rate)
A ramp segment is the time it takes to change the
setpoint to the next setpoint value in the program.
Ramps are odd number segments. Segment #1 will
be the initial ramp time.
This selection of time or rate is made at prompt
“RAMPUNIT”.
ATTENTION: Entering “0” implies an immediate step
change in setpoint to the next soak.
SEGx SP
(x = 2, 4, 6…36)
Within the setpoint high and low
range limits in engineering units
The soak segment's setpoint value
SEGxTIME
(x = 2, 4, 6…36)
0-99 hrs:59 min.
The soak segment’s duration.
Setpoint Ramp/Soak Programming and Operation - Setpoint Program Segments Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 189
April 2017
Setpoint program segments worksheet
Use this worksheet to keep a record of your setpoint segment settings.
Prompt
Function
Range
Your
Selection
Prompt
Function
Range
Your
Selection
SPP SEGS
Settings for
segments
SG15RAMP
Ramp
00 to 99.59
SEG1RAMP
Start Seg
Prog 1
00 to
99.59
SG16 SP
Soak SP
Within SP
limits
SEG2 SP
End Seg
Prog 1
Within SP
limits
SG16TIME
Soak
Time
00.00 to
99.59
SEG2 TIME
Start Seg
Prog 2
00 to
99.59
SG17RAMP
Ramp
00 to 99.59
SEG3 RAMP
Ramp
00 to
99.59
SG18 SP
Soak SP
Within SP
limits
SEG4 SP
Soak SP
Within SP
limits
SG18TIME
Soak
TIme
00.00 to
99.59
SEG4TIME
Soak Time
00.00 to
99.59
SG19RAMP
Ramp
00 to 99.59
SEG5 RAMP
Ramp
00 to
99.59
SG20 SP
Soak SP
Within SP
limits
SEG6 SP
Soak SP
Within SP
limits
SG20TIME
Soak
TIme
00.00 to
99.59
SEG6TIME
Soak TIme
00.00 to
99.59
SG21RAMP
Ramp
00 to 99.59
SEG7 RAMP
Ramp
00 to
99.59
SG22 SP
Soak SP
Within SP
limits
SEG8 SP
Soak SP
Within SP
limits
SG22TIME
Soak
TIme
00.00 to
99.59
SEG8TIME
Soak TIme
00.00 to
99.59
SG23RAMP
Ramp
00 to 99.59
SEG9RAMP
Ramp
00 to
99.59
SG24 SP
Soak SP
Within SP
limits
SG10 SP
Soak SP
Within SP
limits
SG24TIME
Soak
TIme
00.00 to
99.59
SG10TIME
Soak TIme
00.00 to
99.59
SG25RAMP
Ramp
00 to 99.59
SG11RAMP
Ramp
00 to
99.59
SG26 SP
Soak SP
Within SP
limits
SG12 SP
Soak SP
Within SP
limits
SG26TIME
Soak
Time
00.00 to
99.59
SG12TIME
Soak TIme
00.00 to
99.59
SG27RAMP
Ramp
00.00 to
99.59
SG13RAMP
Ramp
00 to
99.59
SG28 SP
Soak SP
Within SP
limits
SG14 SP
Soak SP
Within SP
limits
SG28TIME
Soak
Time
00.00 to
99.59
SG14TIME
Soak TIme
00.00 to
99.59
SG29RAMP
Ramp
00.00 to
99.59
Setpoint Ramp/Soak Programming and Operation - Setpoint Program Segments Set Up Group
190 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Prompt
Function
Range
Your
Selection
Prompt
Function
Range
Your
Selection
SG30 SP
Soak SP
Within SP
limits
SG34 SP
Soak SP
Within SP
limits
SG30TIME
Soak Time
00.00 to
99.59
SG34TIME
Soak
Time
00.00 to
99.59
SG31RAMP
Ramp
00.00 to
99.59
SG35RAMP
Ramp
00.00 to
99.59
SG32 SP
Soak SP
Within SP
limits
SG36 SP
Soak SP
Within SP
limits
SG32TIME
Soak Time
00.00 to
99.59
SG36TIME
Soak
Time
00.00 to
99.59
SG33RAMP
Ramp
00.00 to
99.59
Setpoint Ramp/Soak Programming and Operation - Setpoint Program Event Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 191
April 2017
6.8 Setpoint Program Event Set Up Group
Introduction
Segment events are used to activate relays by means of alarms. There are six alarms and six corresponding
relays. Alarm 1 controls Relay 1, Alarm 2 controls Relay 2, etc. When the setpoint program reaches the
segment, the segment event triggers the alarm which triggers the relay. The relay stays on for the duration
of the segment. There are no alarm conditions to be satisfied, that is, when the event goes on the alarm
goes on.
How to trigger a relay with a segment event
1. Program the segment event with the alarm corresponding with the desired relay.
2. Program that alarm as type EVENT. It is not necessary to program any alarm parameters other than the
alarm type.
3. Do not program other functions that have higher priority control of the relay. See During alarm
conditions an alarm will deenergize its associated relay unless a higher priority function has been
configured for that relay. See Table 3-13. If you want the alarm to control the relay, do not configure a
higher priority function.
4. Table 3-13.
Setpoint Program Event group prompts
Table 6-6 lists all the function prompts in the Setpoint Program Event setup group and their definitions.
Table 6-6 Setpoint Program Event Group Definitions
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
SEGx EV
(x = 1-36)
NONE
ALARM1, ALARM2, ALARM3,
ALARM4, ALARM5, ALARM6
Configured event will be active during the segment. All
others will be inactive.
Example of how a segment event works
For example, to have Segment 1 energize Relay 1:
Program SEG1 EV as ALARM1.
Program A1S1TYPE or A1S2TYPE as EVENT.
Do not program the Timer function Relay 1; namely, Timer.
For alarm programming information, see Subsection 4.12.
Setpoint Ramp/Soak Programming and Operation - Setpoint Program Event Set Up Group
192 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
To ensure control of relay by segment event
To make sure a segment event operates the associated relay, observe the requirements below.
Table 6-7 Segment Event relay operation requirements
Relay
Relay is controlled by (in order of priority)
Requirements for operation of
relay by segment event
1
13. Timer function
14. Alarm 1
Do not configure Timer.
Configure Alarm 1 type
Event.
2
Alarm 2
Configure Alarm 2 type Event.
3
15. Controller 1 output algorithms Relay Simplex,
Position Proportional, Relay Duplex, Current/Relay
Duplex
16. Alarm 3
Do not configure Controller
#1 with these output
algorithms.
Configure Alarm 3 type
Event.
4
17. Controller 1 output algorithms Position
Proportional, Relay Duplex, Current/Relay Duplex
18. Alarm 4
Do not configure Controller
#1 with these output
algorithms.
Configure Alarm 4 type
Event.
5
19. Controller 2 output algorithms Relay Simplex,
Position Proportional, Relay Duplex, Current/Relay
Duplex
20. Alarm 5
Do not configure Controller
#2 with these output
algorithms.
Configure Alarm 5 type
Event.
6
21. Controller 2 output algorithms Position
Proportional, Relay Duplex, Current/Relay Duplex
22. Alarm 6
Do not configure Controller
#2 with these output
algorithms.
Configure Alarm 6 type
Event.
Setpoint Ramp/Soak Programming and Operation - Setpoint Program Event Set Up Group
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 193
April 2017
Setpoint program events worksheet
Use this worksheet to make a record of the segment event settings.
Prompt
Description
Range
Your selection
SPP EVNT
Access to events
N/A
N/A
SEG1 EV
Event status
NONE
ALARM1
ALARM2
ALARM3
ALARM4
ALARM5
ALARM6
SEG2 EV
Event status
Same
SEG3 EV
Event status
Same
SEG4 EV
Event status
Same
SEG5 EV
Event status
Same
SEG6 EV
Event status
Same
SEG7 EV
Event status
Same
SEG8 EV
Event status
Same
SEG9 EV
Event status
Same
SEG10 EV
Event status
Same
SEG11 EV
Event status
Same
SEG12 EV
Event status
Same
SEG13 EV
Event status
Same
SEG14 EV
Event status
Same
SEG15 EV
Event status
Same
SEG16 EV
Event status
Same
SEG17 EV
Event status
Same
SEG18 EV
Event status
Same
SEG19 EV
Event status
Same
SEG20 EV
Event status
Same
SEG21 EV
Event status
Same
SEG22 EV
Event status
Same
SEG23 EV
Event status
Same
SEG24 EV
Event status
Same
SEG25 EV
Event status
Same
SEG26 EV
Event status
Same
Setpoint Ramp/Soak Programming and Operation - Setpoint Program Event Set Up Group
194 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Prompt
Description
Range
Your selection
SEG27 EV
Event status
Same
SEG28 EV
Event status
Same
SEG29 EV
Event status
Same
SEG30 EV
Event status
Same
SEG31 EV
Event status
Same
SEG32 EV
Event status
Same
SEG33 EV
Event status
Same
SEG34 EV
Event status
Same
SEG35 EV
Event status
Same
SEG36 EV
Event status
Same
Setpoint Ramp/Soak Programming and Operation - Run/Monitor the Program
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 195
April 2017
6.9 Run/Monitor the Program
Introduction
Make sure all the “SP PROG” function prompts under the Set Up group “SP RAMP” have been configured
with the required data.
An “H” appears in the upper display indicating that the program is in the HOLD state. If an “H” doesn’t
appear, go to the SP Program configuration procedure and enable the program instead of disabling.
ATTENTION
For recorders with two controllers (both enabled), remember that any controller-related values
displayed correspond with the lighted CHN indicator. “1” means that the values apply for
Controller #1 and “2” means that the values apply for Controller #2.
Run/Monitor functions
Table 6-8 lists all the functions required to run and monitor the program.
Table 6-8 Run/Monitor Functions
Function
Press
Result
Run State
RUN
HOLD
Initiates the setpoint program.
H” changes to “R” in the upper display indicating that the
program is running.
PV value and pen trace tracks the ramp soak profile.
Hold State
RUN
HOLD
Holds the setpoint program.
An “H” appears in the upper display indicating that the
program is in the HOLD state.
The setpoint holds at the current setpoint. Press again
to continue to run.
External Hold
If Remote Switching (Digital Input Option) is present on
your recorder, contact closure places the recorder in the
HOLD state, if the setpoint program is running.
The “H” in the upper display blinks.
ATTENTION
The keyboard takes priority over
external switch for the RUN/HOLD function.
Contact reopening runs program.
Setpoint Ramp/Soak Programming and Operation - Run/Monitor the Program
196 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Function
Press
Result
Viewing the present
ramp or soak segment
number and time
LOWR
DISP
Until you see:
Upper Display: R and the PV value
Lower Display:
For Ramp segments:
# RA XX.XX
Segment Number (odd only)
Indicates Ramp segment
Ramp Time - Hours:Minutes or
Ramp Rate - Degrees/Minute
For Soak segments:
# SK XX.XX
Segment Number (even only)
Indicates Soak segment
Time remaining in segment in
Hrs:Minutes including current
partially completed minute
Skipping segments
LOWR
DISP
Until you see:
Upper Display: R and the PV value
Lower Display: #RA XX.XX (Ramp Segment)
#SK XX.XX (Soak Segment)
RUN
HOLD
To hold the SP Program
An “H” appears in the upper display indicating that the
program is in the HOLD state.
or
To select new segment
RUN
HOLD
or
LOWR
DISP
To begin running at new segment
To retain the old segment
Viewing the number of
cycles left in the
program
LOWER
DISP
Until you see:
Upper Display: R and the PV value
Lower Display: RECYC XX
Remaining cycles 0 to 99
This number includes the current
partially completed cycle.
End Program
When the final segment is completed, the “R” in the upper
display either changes to “H” if configured for HOLD state,
or disappears if configured for DISABL of setpoint
programming.
The recorder operates at the last setpoint in the
program in automatic or will be in manual mode at the
failsafe output.
Release M DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 197
May 2013
7. Input Calibration
7.1 Overview
SHOCK HAZARD WARNING!
Disregard of these instructions may cause injury or death.
INPUT CALIBRATION MAY REQUIRE ACCESS TO HAZARDOUS LIVE CIRCUITS, AND
SHOULD ONLY BE PERFORMED BY QUALIFIED SERVICE PERSONNEL. MORE THAN
ONE SWITCH MAY BE REQUIRED TO DE-ENERGIZE UNIT BEFORE CALIBRATION.
Introduction
This section describes the field calibration procedures for inputs 1, 2, 3, and 4. All DR4500A recorders are
factory calibrated prior to shipment. It should not, therefore, be necessary to recalibrate the recorder when it
is initially installed. However, you must recalibrate the input if any one of the conditions summarized
below applies:
The thermocouple or RTD input must meet published* accuracy rates. Note that the factory calibration
at reference is ± 1.2 °F plus ± 10 microvolts for thermocouples or ± 0.3 ohms for RTDs.
* Specifications 44-45-03-14
You are using a 0-10 Vdc input. Recalibration is necessary because the resistor network used for this
input has a tolerance of ± 1.0 %.
You have cause to believe that the recorder is out of calibration.
You must perform regularly scheduled or periodic recalibration based on your own needs.
You have performed specific servicing activities such as replacement of an input PCB.
ATTENTION
Replacing a main PCB does not normally require recalibration since a new main PCB is
already factory calibrated, whereas an input PCB is not.
You have changed the input type through configuration which results in the loss of the previous field
calibration, but restores factory calibration. See Subsection 7.2 Restoring Factory Calibration paragraph
that follows.
What’s in this section?
This section contains the following topics:
Topic
See Page
7.1 Overview
197
7.2 Restoring Factory Calibration
198
7.3 Minimum and Maximum Range Values
200
7.4 Preliminary Information
202
7.5 Calibration Set Up and Wiring for PV Inputs
204
7.6 Calibration Procedure
213
7.7 Printing Characteristics Adjustments
216
Input Calibration - Restoring Factory Calibration
198 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
7.2 Restoring Factory Calibration
How to restore it
The factory calibration constants for all the input actuation types that can be used with the DR4500A
recorder are stored in its nonvolatile memory. Thus, you can quickly restore the “Factory Calibration” for a
given input actuation type by simply configuring the actuation type through the IN1 TYPE (or IN2 TYPE,
IN3 TYPE, IN4 TYPE) prompt to another type and then changing it back to the original type. See Table
7-1 for the procedure.
ATTENTION
This procedure applies only for factory-installed inputs. Any input that was field-installed must
be field calibrated.
Procedure
Table 7-1 lists the procedure for restoring factory calibration.
Table 7-1 Restoring Factory Calibration
Step
Operation
Press
Action/Result
1
Enter Input Setup Group
SET
UP
Until you see:
Upper Display: SET UP
Lower Display: INPUT n n = 1, 2, 3, or 4
2
Change input type
FUNC
Until you see:
Upper Display: Note the input type in the upper
display. Make sure that the
selection matches the type of
sensor that is connected to the
input in your application. Write it
down, if necessary.
Lower Display: INn TYPE n = 1, 2, 3, or 4
or
Until you see:
Upper Display: 0-10V
Lower Display: INn TYPE
ATTENTION
If you are already using a 0-10V
input, change to a 0-5V input type.
FUNC
Until the upper display rolls through the input types and
returns to
Upper Display: 0-10V
Lower Display: INn TYPE
Input Calibration - Restoring Factory Calibration
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 199
April 2017
Step
Operation
Press
Action/Result
or
Until you change the input selection in the upper
display back to the proper selection. You will see:
Upper Display: Original input selection that
matches your type of sensor.
Lower Display: INn TYPE
To commit press FUNC before pressing LOWR DISP
3
Return to normal
operating mode
LOWR
DISP
To return to Normal operating mode.
The factory calibration will be restored. If the problem is
not corrected, contact the Honeywell Technical
Assistance Center.
1-800-423-9883 USA and Canada
CAUTION
A restored factory calibration overwrites any previous field calibration done for the input. Be
sure to protect any field calibration from accidental overwrites by configuring the appropriate
“LOCKOUT” selection after calibration. See the Section 3 - Configuration for specific
instructions to set the lockout.
Input Calibration - Minimum and Maximum Range Values
200 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
7.3 Minimum and Maximum Range Values
Select the range values
You should calibrate the recorder for the minimum (0 %) and maximum (100 %) range values of your
particular sensor.
If your recorder has two or more inputs, calibrate each input separately. Select the voltage or resistance
equivalent for 0 % and 100 % range values from Table 7-2, use these values when calibrating your
recorder.
Table 7-2 Voltage and Resistance Equivalents for 0 % and 100 % Range Values
Sensor Type
PV Input Range
PV Input Range
Range Valves*
Thermocouples
DEG F
DEG C
0%
68°F/ 20°C
100%
B TC
105.00
to
3300.00
40.56
to
1815.56
0.000 mV
0.003 mV
13.763 mV
E TC H
-454.00
to
1832.00
-270.00
to
1000.00
-9.835 mV
1.192 mV
76.358 mV
E TC L
-200.00
to
1100.00
-128.89
to
593.33
-6.471 mV
1.192 mV
44.547 mV
J TC H
0.00
to
1600.00
-17.78
to
871.11
-0.885 mV
1.019 mV
50.059 mV
J TC L
20.00
to
770.00
-6.67
to
410.00
-0.334 mV
1.019 mV
22.397 mV
K TC H
-320.00
to
2500.00
-195.56
to
1371.11
-5.822 mV
0.798 mV
54.845 mV
K TC L
-20.00
to
1000.00
-28.89
to
537.78
-1.114 mV
0.798 mV
22.251 mV
NiNiMoly
32.00
to
2500.00
0.00
to
1371.11
-0.001 mV
1.458 mV
71.330 mV
NIC Nicrosil Nisil
0.00
to
2372.00
-17.78
to
1300.00
-0.461 mV
0.525 mV
47.502 mV
R TC
0.00
to
3100.00
-17.78
to
1704.44
-0.089 mV
0.111 mV
20.275 mV
S TC
0.00
to
3100.00
-17.78
to
1704.44
-0.092 mV
0.113 mV
17.993 mV
T TC H
-300.00
to
700.00
-184.44
to
371.11
-5.341 mV
0.789 mV
19.095 mV
T TC L
-200.00
to
600.00
-128.89
to
315.56
-4.149 mV
0.789 mV
15.769 mV
W5W26 H
0.00
to
4200.00
-17.78
to
2315.56
-0.234 mV
0.062 mV
37.066 mV
W5W26 L
0.00
to
2240.00
-17.78
to
1226.67
-0.234 mV
0.062 mV
22.277 mV
RTD***
100 Ω (100 PT)
-300.00
to
900.00
-184.44
to
482.22
25.18 Ω
274.96 Ω
100 Ω (100RH)
-130.00
to
392.00
-90.00
to
200.00
64.30 Ω
175.84 Ω
200 Ω (200 HI)
32.00
to
752.00
0.00
to
400.00
200.00 Ω
498.10 Ω
200 Ω (200 LO)
32.00
to
392.00
0.00
to
200.00
200.00 Ω
353.74 Ω
500 Ω
-300.00
to
900.00
-184.44
to
482.22
125.90 Ω
1374.80 Ω
Input Calibration - Minimum and Maximum Range Values
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 201
April 2017
Sensor Type
PV Input Range
PV Input Range
0%
100%
milliAmps
4 to 20 mA
4 mA
20 mA
milliVolts
0 to 10 mV
0 mV
10 mV
10 to 50 mV
10 mV
50 mV
Volts
0 to 5 V
0 V
5 V
0 to 10 V **
0 V
10 V
Radiamatic
(RH)
1400.00
to
3400.00
760.00
to
1871.11
0.99 mV
57.12 mV
*Range values for thermocouples are based on a cold junction temperature of 32 °F (0 °C). These values must be
adjusted for the actual cold junction temperature when using the ambient temperature method for calibrating
thermocouple inputs.
**Resistor network 30755232-002 must be installed in inputs #1, #2, #3, and #4 when using this range, see set up
diagram for details.
***IEC = .00385—100 Ω
IEC = .003902—200 Ω
Input Calibration - Preliminary Information
202 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
7.4 Preliminary Information
Disconnect the field wiring
Depending on which input (#1, #2, #3, or #4) you are going to calibrate, tag and disconnect any field wiring
connected to the input terminals on the input boards inside the recorder. Reference Figure 7-1 and follow
the procedure in Table 7-3.
Table 7-3 Disconnect the Field Wiring
Step
Action
1
Remove the operating power from the recorder.
2
Open the door on the recorder.
3
Loosen the phillips screw on the right side of the chart plate, and open the chart plate.
4
Depending on the input (1, 2, 3, or 4) you are going to calibrate, remove the wired plug from
the input connector (J2) on the applicable circuit board. See Figure 7-1 for the location of the
circuit boards and input connectors.
5
Tag and disconnect the field wiring installed in the applicable input connector plug.
#3
#4
#2 #1
Mother board
for options
21442
Main board
Alarm output
digital input
board (optional)
J2 on input
#1 board
J2 on input
#2 board
(optional)
J2 on input
#3 board
(optional)
J2 on input
#4 board
(optional)
Figure 7-1 Location of the Input Connections on the Input Boards
Input Calibration - Preliminary Information
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 203
April 2017
Equipment needed
Table 7-4 lists the equipment required to calibrate the specific types of inputs listed in the table. You will
need a medium size bladed screwdriver for general use and a small size bladed screwdriver for use with the
screws on the connector plugs.
Table 7-4 Equipment Needed
Type of Input
Equipment Needed
Thermocouple Inputs
(Ice Bath)
A calibrating device with ± 0.02 % accuracy for use as a
signal source such as a millivolt source.
Thermocouple extension wire that corresponds with the
type of thermocouple that will be used with the recorder
input.
Two insulated copper leads for connecting the
thermocouple extension wire from the ice baths to the
precision calibrator.
Two containers of crushed ice.
Thermocouple Inputs
(Ambient Temperature)
A calibrating device with ± 0.02 % accuracy for use as a
signal source such as a millivolt source.
Two insulated copper leads for connecting the calibrator to
the controller.
Thermocouple Inputs
(Compensated Calibrator)
A calibrating device with temperature compensation and
± 0.02 % accuracy for use as a signal source.
Thermocouple extension wire that corresponds with the
type of thermocouple that will be used with the recorder
input.
RTD (Resistance Thermometer
Device)
A resistance decade box, with ± 0.02 % accuracy, capable
of providing stepped resistance values over a minimum
range of 0 to 1400 ohms with a resolution of 0.01 ohm.
Three insulated copper leads for connecting the decade
box to the controller.
Radiamatic, Milliampere, Millivolt, and
Volts Inputs
A calibrating device with ± 0.02 % accuracy for use as a
signal source.
Two insulated copper leads for connecting the calibrator to
the controller.
Input Calibration - Calibration Set Up and Wiring for PV Inputs
204 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
7.5 Calibration Set Up and Wiring for PV Inputs
Jumper positions
Before starting the calibration activity, check that the jumper plugs on the applicable input circuit board are
installed in the proper jumper position (in W1/MA and W3) for the particular sensor being used (refer to
the wiring connection drawings in this section for each individual setting).
Refer to Figure 7-2 for the location of jumper positions W1/MA and W3 on these circuit boards, and the
status of these jumpers for each type of input sensor.
Main board
Input board
W1
MA
MA
Position MA Position W1
Status of jumper plugs
1. Install W1/MA plug in position W1 for thermocouple, RTD, Radiamatic, mV, 0-5 Vdc, 0-10 Vdc inputs.
2. Install W1/MA plug in position MA f or 4-20 mA inputs.
21443
RTD
W3
Position
T/C
MA
Linear
Position
RTD
3. Install plug in W3 according to y our input ty pe.
T/C
Figure 7-2 Location of Jumper Positions W1/MA and W3 on the Input Boards
Input Calibration - Calibration Set Up and Wiring for PV Inputs
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 205
April 2017
Thermocouple input calibration methods
You can calibrate for a thermocouple input using one of three methods:
using an ice bath,
using a compensated calibrator, or
by measuring the ambient temperature at the input terminals and subtracting the voltage contribution
of the input terminal junction.
General set up procedure
Table 7-5 lists the general set up procedure for all methods of calibration. Do this procedure and then refer
to the set up procedure and diagram for your specific input.
Table 7-5 General Set Up Procedure
Step
Action
1
Set up and connect the calibrator to the input plug for the applicable input circuit board in your
recorder according to the particular input sensor being used. Refer to the following figures for
corresponding set-up diagrams:
Figure 7-3 Thermocouple inputs using an ice bath
Figure 7-4 Thermocouple inputs using a compensated calibrator
Figure 7-5 Thermocouple inputs using the ambient temperature method
Figure 7-6 RTD (Resistance Thermometer Device) inputs
Figure 7-7 Radiamatic, mV and Volts (except 010 Volts) inputs
Figure 7-8 0-10 Volts input
Figure 7-9 420 mA inputs
2
Route leads (for example: copper leads or thermocouple extension wires) through a conduit
hole in the recorder case so that you will be able to close the chart plate.
3
Close the chart plate after you have completed the applicable calibration set up.
Input Calibration - Calibration Set Up and Wiring for PV Inputs
206 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Thermocouple inputs using an ice bath
Refer to Figure 7-3 and wire the recorder according to the procedure given in Table 7-6.
Table 7-6 Set Up Wiring Procedure for Thermocouple Inputs Using an Ice Bath
Step
Action
1
Connect the copper leads to the calibration source (see Figure 7-3).
2
Connect a length of thermocouple extension wire to the end of each copper lead and insert the
junction points into the ice bath.
3
Connect the other end of the thermocouple extension wires to the clamp type terminals in the
plug for the applicable input connector (J2).
4
Reinstall the plug into the input connector (J2) on the applicable circuit board for Input 1, Input
2, Input 3, or Input 4.
#3
#4
#2 #1
21444
Connector plug J2 f or
inputs #1, #2, #3 & #4
MA
W1
Be sure W1/MA
jumper is in position
W1 on the input board.
Containers of
crushed ice
_
+
Copper
wires
Calibration source
+
_
Thermocouple
extension wires T/C
RTD
Be sure W3 jumper
is in position T/C
on the input board.
Figure 7-3 Calibration Set Up Diagram for Thermocouple Inputs Using an Ice Bath
Input Calibration - Calibration Set Up and Wiring for PV Inputs
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 207
April 2017
Thermocouple inputs using a compensated calibrator method
Refer to Figure 7-4 and wire the recorder according to the procedure given in Table 7-7.
Table 7-7 Set Up Wiring Procedure for Thermocouple Inputs Using a Compensated
Calibrator Method
Step
Action
1
Connect the thermocouple extension wire to the Precision Compensated Calibrator (see
Figure 7-4).
2
Connect the other end of the thermocouple extension wires to the clamp type terminals in the
plug for the applicable input connector (J2).
3
Reinstall the plug into the input connector (J2) on the applicable circuit board for Input 1, Input
2, Input 3, or Input 4.
#3
#4
#2 #1
21445
Connector plug J2 f or
inputs #1, #2, #3 & #4
MA
W1
Be sure W1/MA
jumper is in position
W1 on the input board.
+
_
Thermocouple
extension wires
_
+
Compensated
Calibrator
T/C
RTD
Be sure W3 jumper
is in position T/C
on the input board.
Figure 7-4 Calibration Set Up Diagram for Thermocouple Inputs Using a Compensated
Calibrator Method
Input Calibration - Calibration Set Up and Wiring for PV Inputs
208 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Thermocouple inputs using the ambient temperature method
Refer to Figure 7-5 and wire the recorder according to the procedure given in Table 7-8.
Table 7-8 Set Up Wiring Procedure for Thermocouple Inputs Using the Ambient
Temperature Method
Step
Action
1
Connect the copper wire to the Precision Millivolt Source (see Figure 7-5).
2
Connect the other end of the copper wire to the clamp type terminals in the plug for the
applicable input connector (J2).
3
Reinstall the plug into the input connector (J2) on the applicable circuit board for input 1, input
2, input 3, or input 4.
#3
#4
#2 #1
21446
Connector plug J2 f or
inputs #1, #2, #3 and #4
MA
W1
Be sure W1/MA
jumper is in position
W1 on the input board.
Copper
wires
+
_
_
+
Calibration source
Adjust calibration voltages to
compensate f or measured
ambient temperature
Ambient temperature method
T/C
RTD
Be sure W3 jumper
is in position T/C
on the input board.
Figure 7-5 Calibration Set Up Diagram for Thermocouple Inputs using the Ambient
Temperature Method
Input Calibration - Calibration Set Up and Wiring for PV Inputs
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 209
April 2017
RTD (Resistance Thermometer Device) inputs
Refer to Figure 7-6 and wire the recorder according to the procedure given in Table 7-9.
Table 7-9 Set Up Wiring Procedure for RTD Inputs
Step
Action
1
Connect the copper wire to the calibration source (see Figure 7-6).
2
Connect the other end of the copper wire to the clamp type terminals in the plug for the
applicable input connector (J2).
3
Reinstall the plug into the input connector (J2) on the applicable circuit board for input 1, input
2, input 3, or input 4.
#3
#4
#2 #1
21447
Copper
wires
Decade box
Plug J2
MA
W1
Be sure W1/MA
jumper is in position
W1 on the input board.
+
_
T/C
RTD
Be sure W3 jumper
is in position RTD
on the input board.
Figure 7-6 Calibration Set Up Diagram for RTD Inputs
Input Calibration - Calibration Set Up and Wiring for PV Inputs
210 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Radiamatic, millivolts, and volts inputs (except 010 Volts)
Refer to Figure 7-7 and wire the recorder according to the procedure given in Table 7-10.
Table 7-10 Set Up Wiring Procedure for Radiamatic, Millivolts, and Volts Inputs
(except 0-10 Volts)
Step
Action
1
Connect the copper wire to the calibration source (see Figure 7-7).
2
Connect the other end of the copper wire to the clamp type terminals in the plug for the
applicable input connector (J2).
3
Reinstall the plug into the input connector (J2) on the applicable circuit board for input 1, input
2, input 3, or input 4.
Figure 7-7 Calibration Set Up Diagram for Radiamatic, Millivolts, and Volts Inputs
(except 0-10 Volts)
Input Calibration - Calibration Set Up and Wiring for PV Inputs
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 211
April 2017
010 Volt inputs
Refer to Figure 7-8 and wire the recorder according to the procedure given in Table 7-11.
Table 7-11 Set Up Wiring Procedure for 010 Volt Inputs
Step
Action
1
Connect the copper wire to the calibration source (see Figure 7-8).
2
Connect the other end of the copper wire to the clamp type terminals in the plug for the
applicable input connector (J2).
3
Reinstall the plug into the input connector (J2) on the applicable circuit board for input 1, input
2, input 3, or input 4.
Figure 7-8 Calibration Set Up Diagram for 010 Volt Inputs
Input Calibration - Calibration Set Up and Wiring for PV Inputs
212 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
420 mA inputs
Refer to Figure 7-9 and wire the recorder according to the procedure given in Table 7-12.
Table 7-12 Set Up Wiring Procedure for 420 mA Inputs
Step
Action
1
Connect the copper wire to the calibration source (see Figure 7-9).
2
Connect the other end of the copper wire to the clamp type terminals in the plug for the
applicable input connector (J2).
3
Reinstall the plug into the input connector (J2) on the applicable circuit board for input 1, input
2, input 3, or input 4.
#3
#4
#2 #1
21450
MA
W1
Be sure W1/MA jumper is in
position MA on the input board;
this connects 250
resistor
(internal on PCB) across inputs
terminals.
_
+
Copper
wires
Calibration source
+
_
Plug J2
4-20 mA
T/C
RTD
Be sure W3 jumper is in the
Linear position on the Input board.
Figure 7-9 Calibration Set Up Diagram for 420 mA Inputs
Input Calibration - Calibration Procedure
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 213
April 2017
7.6 Calibration Procedure
Introduction
Apply power and allow the recorder to warm up for one hour before you calibrate.
Please read “Set Up Wiring” before beginning the procedure.
Make sure “LOCKOUT” is set to “NONE.” (see Section 3 Configuration).
The calibration procedure for inputs #1, #2, #3, and #4 are identical. The displays indicate the input
number.
CAUTION
For milliampere inputs, be sure the current source is at zero before switching on the calibrator.
Do not switch the calibrator on/off while it is connected to the recorder’s input.
ATTENTION
For linear inputs, avoid step changes in input signal. Vary calibration source signal smoothly
from initial value to final 100 % value.
Calibration procedure sequence
The calibration procedure sequence for all inputs is listed in Table 7-13.
Table 7-13 Calibration Procedure Sequence
Step
Operation
Press
Action/Result
1
Enter Calibration Mode
SET
UP
Until you see:
Upper Display: CALIB
Lower Display: INPUT n n = 1, 2, 3, or 4
FUNC
You will see:
Upper Display: DISABL
Lower Display: CAL INn n = 1, 2, 3, or 4
The calibration sequence is enabled and you will see:
Upper Display: BEGIN
Lower Display: CAL INn
2
Calibrate 0 %
FUNC
You will see:
Upper Display: APPLY
Lower Display: INn ZERO n = 1, 2, 3, or 4
Adjust your calibration device to an output signal
equal to the 0 % range value for your particular input
sensor, see Table 7-2 for Voltage or Resistance
equivalents.
Wait 30 seconds, then go to step 3.
Input Calibration - Calibration Procedure
214 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Step
Operation
Press
Action/Result
Using Ambient
Temperature Method
ATTENTION
If you are using the Ambient
Temperature method to calibrate a thermocouple input,
be sure to measure the temperature at the input
terminals and subtract the equivalent millivolt value (for
your particular thermocouple) from the 0 % value just
prior to doing calibration.
For example, for a Type J Thermocouple and input
temperature of 68 °F:
From 0.885 mV (Type J @ 0° F)
Subtract 1.019 mV (Type J @ 68 °F)
To yield 1.904 mV (calibrator output
for INn ZERO)
3
Calibrate 100 %
FUNC
You will see:
Upper Display: APPLY
Lower Display: INn SPAN n = 1, 2, 3, or 4
Adjust your calibration device to an output signal equal
to the 100 % range value for your particular input
sensor, see Table 7-2 for voltage or resistance
equivalents, wait 30 seconds, and
If …
Then …
you are calibrating a
thermocouple input
Go to
step 4
you are calibrating other than a
thermocouple input
Go to
step 5
Using Ambient
Temperature Method
ATTENTION
If you are using the Ambient
Temperature method to calibrate a thermocouple input,
be sure to measure the temperature at the input
terminals and subtract the equivalent millivolt value (for
your particular thermocouple) from the 100 % value.
For example, for a Type J Thermocouple and input
temperature of 68 °F:
From 50.059 mV (Type J @ 1600 °F)
Subtract 1.019 mV (Type J @ 68 °F)
To yield 49.040 mV (calibrator output
for INn SPAN)
Input Calibration - Calibration Procedure
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 215
April 2017
Step
Operation
Press
Action/Result
4
Check the Cold Junction
Temperature
W ARNING
The
accuracy of the recorder
is directly affected by the
accuracy of this value.
Change this value only if
the zero and span
calibration procedures did
not bring the controller
within the specified
accuracy requirements.
FUNC
The calculations for zero and span are now stored and
you will see:
Upper Display: The cold junction temperature at
the rear terminals
Lower Display: C-J TEMP
The value in the upper display is in the tenths of a
degree. It is the current reading of the temperature
as measured at the thermocouple terminals
(that is, at J2) and recognized by the recorder.
When using the Ice Bath method, this value should
be the terminal ambient temperature.
You can change this value, if it is in error, using
the ▲ or ▼ key.
5
Exit the Calibration Mode
FUNC
The recorder stores the calibration constants and exit
calibration mode.
Input Calibration - Printing Characteristics Adjustments
216 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
7.7 Printing Characteristics Adjustments
Printing characteristics adjustments
Normally there is no need to adjust the printing characteristics as part of an input or output calibration
procedure. However, if the chart printing appears to be faded, you can use the procedure in Section 4 -
Configuration Parameter Definitions, Table 4-18, to make slight adjustments in the print contrast.
ATTENTION
To access Set Up group prompt “ADJUST”, the Set Up group prompt “LOCKOUT” must be set
to “NONE”. If the group prompt “LOCKOUT” has been configured for “CALIB”, “+VIEW”, or
“MAX” selection, you will not be able to access the Printing Characteristics Group prompt.
Refer to Section 3 - Configuration for details.
Input Calibration - Printing Characteristics Adjustments
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 217
April 2017
Release N DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 218
May 2013
8. Output Calibration
8.1 Overview
SHOCK HAZARD WARNING!
Disregard of these instructions may cause injury or death.
OUTPUT CALIBRATION MAY REQUIRE ACCESS TO HAZARDOUS LIVE CIRCUITS, AND
SHOULD ONLY BE PERFORMED BY QUALIFIED SERVICE PERSONNEL. MORE THAN
ONE SWITCH MAY BE REQUIRED TO DE-ENERGIZE UNIT BEFORE CALIBRATION.
Introduction
This section describes the field calibration procedures for the following types of outputs:
Current Output
Position Proportional Output
Auxiliary Output
ATTENTION
Calibration for Control Outputs #1 and #2 is identical except for the particular printed circuit
board involved.
What’s in this section?
This section contains the following topics:
Topic
See Page
8.1 Overview
218
8.2 Current Proportional Output/Aux Out 2 and 3 Calibration
Introduction
Equipment needed
Calibrator connections
● Calibration Procedure
219
219
219
219
220
8.3 Position Proportional and Three Position Step Output Calibration
Position proportional control
Equipment needed
Connections
Auto mode vs manual mode
Displayed values
● Calibration Procedure
221
221
221
221
221
221
221
8.4 Auxiliary Output Calibration
Introduction
Equipment needed
Calibrator connections
● Calibration Procedure
224
224
224
224
225
Output Calibration
Current Proportional Output/Aux Out 2 and 3 Calibration
Release N DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 219
May 2013
8.2 Current Proportional Output/Aux Out 2 and 3 Calibration
Introduction
Calibrate the recorder so that the output provides the proper amount of current over the desired range.
The recorder can provide an output current range of from 3.1 to 21 milliamperes and can be calibrated at
4 mA for 0 % of output and 20 mA for 100 % of output or any other values between 2 and 3.1 mA.
Equipment needed
You will need a standard shop type milliammeter, with whatever accuracy is required, capable of
measuring 0 to 20 milliamps.
Calibrator connections
Refer to Figure 8-1 and wire the recorder according to the procedure given in Table 8-1.
Table 8-1 Set Up Wiring Procedure Current Proportional Output/Aux Out 2 and 3
Step
Action
1
With the power off, door open, and the chart plate swung out; tag and disconnect field wiring
from the plug in connector J1 on the appropriate control output PCB (see Figure 8-1).
2
Observing polarity, connect a milliammeter’s leads to the plug for connector J1.
3
Close the chart plate; apply power and allow the recorder to warm up 15 minutes before you
calibrate.
Figure 8-1 Test Equipment Connections for Calibrating Current Proportional Output
Output Calibration
Current Proportional Output/Aux Out 2 and 3 Calibration
220 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release N
May 2013
Procedure
The procedure for calibrating the Current Proportional Output is listed in Table 8-2. Make sure
“LOCKOUT” in the Set Up group is set to “NONE.” See Section 3 Configuration. Also, “CONTROL
1/2” must be enabled and “OUT ALG” must be set to “CURRNT” in the Control Set Up group.
ATTENTION
Follow this procedure when calibrating Auxiliary Output #2 or #3. Make sure "LOCKOUT" in
the Set Up group is set to "NONE" and "AUX OUT" must NOT be disabled in the Auxiliary
Output group.
Table 8-2 Current Proportional Output/Aux Output 2 and 3 Calibration Procedure
Step
Operation
Press
Action/Result
1
Enter Calibration Mode
SET
UP
Until you see:
Upper Display: CALIB
Lower Display: CURRENT
2
Calibrate 0 %
FUNC
You will see:
Upper Display: (a value) (approximately 380)
Lower Display: ZERO VAL
or
Until the desired 0 % output is read on the
milliammeter. Use the values shown below depending
on the action of your recorder.
4 mA For 4 to 20 mA Direct Action
20 mA For 4 to 20 mA Reverse Action
3
Calibrate 100 %
FUNC
Stores the 0 % value and you will see:
Upper Display: (a value) (approximately 1890)
Lower Display: SPAN VAL
or
Until the desired 100 % output is read on the
milliammeter. Use the values shown below depending
on the action of your recorder.
20 mA For 4 to 20 mA Direct Action
4 mA For 4 to 20 mA Reverse Action
4
Exit the Calibration Mode
FUNC
The recorder stores the span value.
LOWR
DISP
or
SET
UP
To exit the calibration mode.
Output Calibration
Position Proportional and Three Position Step Output Calibration
Release N DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 221
May 2013
8.3 Position Proportional and Three Position Step Output Calibration
Position proportional control
When the DR4500A Recorder has a position proportional control output, calibrate the recorder so that the
increase and decrease relays operate properly with respect to the position of the external feedback
slidewire.
3 Position Step control
This model only requires that the “Motor Time” be entered as shown in the calibration procedure. FULL
CALIBRATION IS NOT REQUIRED.
Equipment needed
None
Connections
Apply power and allow the recorder to warm up 15 minutes before you calibrate.
Leave all field wiring connected to the plugs in connectors J2 and J5 on the appropriate control output
printed circuit board.
Auto mode vs manual mode
There are two ways in which to calibrate Position Proportional control:
AUTO mode or MANUAL mode.
Rules for auto mode vs manual mode
The auto-mode selection must be done at least once before the manual mode will operate properly. Failure
to use the auto-mode procedure will prevent the recorder from going into automatic control mode.
Displayed values
During the auto-mode calibration procedure, the values being displayed are used only to indicate if the
motor is still traveling.
To view the actual calibration value, use the manual mode after the auto-mode is completed. These values
can be changed for purposes of tweaking the calibration.
Procedure
The procedure for calibrating the position proportional output and 3 Position Step control output is listed in
Table 8-3.
Make sure “LOCKOUT” in the Set Up group is set to “NONE.” See Section 3 Configuration. Also,
“CONTROL 1/2” must be enabled in the Control Set Up group.
For “Three Position Step Control Output models”, do steps 1 and 2 only. Make sure “CONT ALG” =
“3P STEP” in the Control Set Up group.
For “Position Proportional Output”, follow the entire calibration procedure. Make sure “CONT ALG”
= “PID A” and “OUT ALG” = “POSITN” in the Control 1 Set Up group.
Output Calibration
Position Proportional and Three Position Step Output Calibration
222 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release N
May 2013
Table 8-3 Position Proportional and 3 Position Step Output Calibration Procedure
Step
Operation
Press
Action/Result
1
Enter Calibration Mode
SET
UP
Until you see:
Upper Display: CALIB
Lower Display: POS PROP
2
Set Motor Traverse Time
NOTE: This is the time it
takes the motor to travel
from 0 % to 100 %.
FUNC
Until you see:
Upper Display: (a value)
Lower Display: MTR TIME
or
Until the proper motor stroke time is reached (see the
motor specs or measure the time).
Range of setting = 5 to 255 Seconds
3
Select Automatic or
Manual Calibration
FUNC
Until you see:
Upper Display: DISABL
Lower Display: POS PROP
You can calibrate the control output manually or let
the recorder calibrate the control output
automatically.
In the “Automatic Calibration Mode” (DO AUTO), the
control relays automatically move the motor in the
proper direction.
If desired, however, the motor may be manually
positioned to 0 % and 100 % positions.
Disconnect the relay wires. “DO MAN”.
In the “Manual Calibration Mode” (DO MAN) the
motor does not move. Instead, the existing 0 % and
100 % values may be changed with the or
keys.
or
Select automatic or manual calibration.
Upper Display: DO AUTO or DO MAN
Lower Display: POS PROP
If you select DO AUTO, go to step 4.
If you select DO MAN, go to step 6.
ATTENTION
When calibration is terminated, this
selection reverts to DISABL.
4
DO AUTO
Set 0 % value
FUNC
The decrement relay is turned on to move the motor to
0 % position.
Upper Display: (counts of feedback slidewire)
(0 to 2047)
Lower Display: ZERO VAL
When the motor stops, the display should stop
counting; go to the next step.
Output Calibration
Position Proportional and Three Position Step Output Calibration
Release N DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 223
May 2013
Step
Operation
Press
Action/Result
5
Set 100 % value
FUNC
The increment relay is turned on to move the motor to
100 % position.
Upper Display: (counts of feedback slidewire)
(0 to 2047)
Lower Display: SPAN VAL
When the motor stops, the display should stop
counting, then go on to step 8.
6
DO MAN
Set 0 % value
FUNC
You will see:
Upper Display: (existing zero calibration value
in counts) (approximately 100)
Lower Display: ZERO VAL
or
Until the desired zero value is reached in the upper
display.
Upper Display: (desired zero value)
Lower Display: ZERO VAL
7
Set 100 % value
FUNC
The recorder stores the 0 % value and you will see:
Upper Display: (existing span calibration value
in counts) (approximately 1500)
Lower Display: SPAN VAL
or
Until the desired span value is reached in the upper
display.
Upper Display: (desired span value)
Lower Display: SPAN VAL
For manual calibration, the motor does not move from
its position prior to the start of position proportional
calibration.
8
Exit the Calibration Mode
FUNC
The recorder stores the 100 % value.
LOWR
DISP
or
SET
UP
To exit the calibration mode.
Output Calibration
Auxiliary Output Calibration
224 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release N
May 2013
8.4 Auxiliary Output Calibration
Introduction
Calibrate the recorder so that the auxiliary output provides the proper amount of current over the desired
range.
The recorder can provide an auxiliary output current range of from 2 to 21 milliamperes and can be
calibrated at 4 mA for 0 % of output and 20 mA for 100 % of output or any other values between 2 and
21 mA.
Equipment needed
You will need a standard shop type milliammeter, with whatever accuracy is required, capable of
measuring 0 to 20 milliamps.
Calibrator connections
Refer to Figure 8-2 and wire the recorder according to the procedure given in Table 8-4.
Table 8-4 Set Up Wiring Procedure Auxiliary Output
Step
Action
1
With the power off, door open, and the chart plate swung out; tag and disconnect field wiring
from the plug in connector J2 on the auxiliary output PCB (see Figure 8-2).
2
Observing polarity, connect a milliammeter’s leads to the plug for connector J2.
3
Close the chart plate; apply power and allow the recorder to warm up 15 minutes before you
calibrate.
Figure 8-2 Test Equipment Connections for Calibrating Auxiliary Output
Output Calibration
Auxiliary Output Calibration
Release N DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 225
May 2013
Procedure
The procedure for calibrating the Auxiliary Output is listed in Table 8-5. Make sure “LOCKOUT” in the
Set Up group is set to “NONE.” See Section 3 Configuration. Also, “AUX OUT” must NOT be disabled
in the Auxiliary Output group.
Table 8-5 Auxiliary Output Calibration Procedure
Step
Operation
Press
Action/Result
1
Enter Calibration Mode
SET
UP
Until you see:
Upper Display: CALIB
Lower Display: AUX OUT
2
Calibrate 0 %
FUNC
You will see:
Upper Display: (a value)
Lower Display: ZERO VAL
or
Until the desired 0 % (4 mA) output is read on the
milliammeter.
3
Calibrate 100 %
FUNC
Stores the 0 % value and you will see:
Upper Display: (a value)
Lower Display: SPAN VAL
or
Until the desired 100 % (20 mA) output is read on the
milliammeter.
4
Exit the Calibration Mode
FUNC
The recorder stores the span value.
LOWR
DISP
or
SET
UP
To exit the calibration mode.
ATTENTION
The calibration for Auxiliary Outputs #2 and #3 follows the procedure for calibrating the current
proportional output (refer to Subsection 8.2).
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 226
April 2017
9. Troubleshooting / Service
9.1 Overview
SHOCK HAZARD WARNING!
Disregard of these instructions may cause injury or death.
TROUBLESHOOTING MAY REQUIRE ACCESS TO HAZARDOUS LIVE CIRCUITS, AND
SHOULD ONLY BE PERFORMED BY QUALIFIED SERVICE PERSONNEL. MORE THAN
ONE SWITCH MAY BE REQUIRED TO DE-ENERGIZE UNIT BEFORE SERVICING.
Introduction
This section explains how to troubleshoot the DR4500A recorder using self-diagnostic test results and error
messages as well as some visual failure symptoms. Using an optimum replacement unit repair philosophy,
trouble is traced to a printed circuit board (PCB)/hardware assembly level rather than to an individual
PCB/hardware assembly component. While troubleshooting is straightforward, we recommend that only
trained service technicians repair the recorder.
What’s in this section?
The following topics are covered in this section.
Topic
See Page
9.1 Overview
226
9.2 Troubleshooting Aids
228
9.3 Self Diagnostics
230
9.4 Visual Failure Symptoms
236
9.5 Troubleshooting Procedures
237
Types of problems
Instrument performance can be adversely affected by installation and application problems as well as
hardware problems. We recommend that you investigate the problems in the following order:
Installation related problems
Application related problems
Hardware and software related problems
and use the information presented in this section to solve them.
If a replacement of any part is required, follow the instructions shipped with the replacment part.
Troubleshooting / Service
Overview
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 227
April 2017
Installation related problems
Read the Installation section in this manual to make sure the DR4500A has been properly installed. The
installation section provides information on protection against electrical noise, connecting external
equipment to the recorder, and shielding and routing external wiring.
ATTENTION
System noise induced into the recorder will result in diagnostic error messages recurring. If the
diagnostic error messages can be cleared, it indicates a “soft” failure and is probably noise
related.
If system noise is suspected, completely isolate the recorder from all field wiring. Use
calibration sources to simulate PV and check all recorder and control functions; that is, Pen
functions, Chart Trace, Gain, Rate, Reset, Output, Alarms, etc.
Application related problems
Review the application of the recorder; then, if necessary, direct your questions to the local sales office.
Hardware and software related problems
Use the troubleshooting error message prompts and recorder failure symptoms to identify typical failures
which may occur in the recorder. Follow the troubleshooting procedures to correct them.
Troubleshooting / Service
Troubleshooting Aids
228 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
9.2 Troubleshooting Aids
Self diagnostics
The DR4500A recorder runs self-diagnostic tests to monitor the recorder’s general health. The tests are
divided into three main groups and will produce an error message when failed.
An error message can occur
at power-up run when power is cycled off and on,
during continuous background tests while in normal operation, and
when the Status Tests are requested by the operator.
Table 9-4 lists all the error message prompts that you could see, the reason for the failure, and how to
correct the problem
Visual failure symptoms
Other failures may occur that deal with the power, pen functions, chart rotation, output, or alarms. Refer to
the visual failure symptom in Table 9-5 to determine what is wrong and the troubleshooting procedures to
use to correct the problem.
Check Installation
If a set of symptoms still persists, refer to Section 2 - Installation and ensure proper installation and proper
use of the recorder in the system.
Customer support
If you cannot solve the problem using the troubleshooting procedures listed in this section; get the model
number and serial number from the label on the chart plate, and software version (see "Determining the
software version") then:
call Customer Support Phone Number
1-800-423-9883 USA and Canada
If it is determined that a hardware problem exists and the recorder is still within the two year warranty, a
replacement recorder will be shipped with instructions for returning the defective unit.
Troubleshooting / Service
Troubleshooting Aids
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 229
April 2017
Determining the software version
Table 9-1 lists the procedure for identifying the software version number.
Table 9-1 Identifying the software version
Step
Operation
Press
Action/Result
1
Select STATUS
Set Up Group
SET
UP
Until you see:
Upper Display: READ
Lower Display: STATUS
2
Read the software
version
FUNC
Until you see:
Upper Display: (Software Version Number)
Lower Display: VERSION
Please give this number to the Customer Support
person. It will indicate which version of DR4500A you
have and help them determine a solution to your
problem.
Troubleshooting
The troubleshooting procedures are divided into two parts:
Self Diagnostics Error Message Prompts, and
Visual Failure Symptoms.
If a “Failed” indication is given for one of the power-up tests and/or an error message prompt blinks in the
lower display, refer to the Self Diagnostic error message prompts.
If erratic operation is observed, refer to the Visual Failure symptoms.
In either case, run the status tests to verify the status of the recorder’s basic self-diagnostic tests.
Troubleshooting / Service
Self Diagnostics
230 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
9.3 Self Diagnostics
Power-up tests
When the recorder is powered-up, four tests are run by the DR4500A software to ensure memory integrity.
As the tests are run, the displays appear as shown in Table 9-2.
Table 9-2 Power-up tests
Lower Display
Upper Display
RAM TEST
PASS or FAIL
CONFTEST (configuration checksum)
PASS or FAIL
CAL TEST (working calibration)
PASS or FAIL
BATTERY*
PASS or FAIL
*Battery test failure does not cause a failsafe.
Failsafe
If control is configured, and any of these tests fail, “FAIL” appears momentarily in the upper display,
then a display test is run, after which the controller goes into manual mode and you will see:
Upper Display: (PV value)
Lower Display: FAILSAFE (blinking)
Refer to “Device Status” (next page) to determine which tests have failed and how to correct them.
If control is not configured, self-test failures will be displayed periodically as other error messages are
presently displayed (CNFG ERR, CAL1 ERR, CAL2 ERR, or BATT LOW).
Troubleshooting / Service
Self Diagnostics
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 231
April 2017
Device status
When required, the results of the power-up tests can be checked to determine the reason the recorder has
gone to “Failsafe”.
The following procedure in Table 9-3 tells you how to display the results of the latest tests run. Table 9-4
lists the tests, the reason for the failure, and how to correct the problem.
Table 9-3 Displaying the test results
Step
Operation
Press
Action/Result
1
Select STATUS
Set Up Group
SET
UP
Until you see:
Upper Display: READ
Lower Display: STATUS
2
Read the status tests
results
FUNC
Until you see:
Upper Display: NO or YES
(YES indicates a failure)
Lower Display: FAILSAFE
Successive presses of the FUNC key will display the
results of the tests (PASS or FAIL) in the following
order:
RAM TEST
CONFTEST
CAL TEST
FACT CRC
BATTERY
Identify the problem from the error message and
correct the failure as shown under “lower display
indication” in Table 9-4.
Troubleshooting / Service
Self Diagnostics
232 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Error message prompts
The messages listed in Table 9-4 may appear during the power-up test or status test, or they may blink in
the lower display as the result of ongoing background tests that verify data and memory integrity.
Simultaneous error messages will be displayed in rotation.
Table 9-4 lists the error message, the test group that prompted the message, the reason for the failure, and
how to correct the problem.
Table 9-4 Error message prompts
Lower
Display
Indication
Test Group
Reason for Failure
How to Correct the Problem
FAILSAFE
(Note 1)
Status or
Background
This error message shows whenever
the recorder goes into a failsafe
mode of operation. This will happen
if control is enabled and:
a power-up test fails,
a specific background test fails.
23. Run through the “Device Status”
check (page 231) to determine the
reason for the failsafe indication.
24. Identify the other failure message in
the display and correct the problem
according to the recommendations
given in this table for that particular
error message.
RAM TEST
(Note 1)
Power-up
RAM failure
25. Cycle power.
26. Check “Device Status” (page 231) to
see if error clears.
27. If error doesn’t clear, replace the
main printed circuit board.
CONFTEST
(Note 1)
Power-up
Configuration data is in error.
28. Check all the configuration prompts
for accuracy.
See Section 3 - Configuration for
selections and limits.
29. Change any configuration item,
check “Device Status” to see if
CONFTEST=PASS, return
configuration item to original value.
See Section 3 - Configuration for
instructions to change a
configuration item.
Troubleshooting / Service
Self Diagnostics
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 233
April 2017
Lower
Display
Indication
Test Group
Reason for Failure
How to Correct the Problem
CNFG ERR
Background
Configuration data is in error.
30. Check all the configuration prompts
for accuracy.
See Section 3 - Configuration for
selections and limits.
31. Change any configuration item, then
return it to the original value.
See Section 3 - Configuration for
instructions to change a
configuration item.
CAL TEST
(Note 1)
Power-up
The working calibration constants in
the recorder are in error.
32. Change to a different input type.
See Section 3 Configuration.
33. Check “Device Status” (page 231) to
see if FACT CRC=PASS.
If PASSreturn to original input
type.
If FAILfield calibrate. Refer to
Section 7 Input Calibration.
CAL1 ERR
Background
Working CAL TEST failure (Control
1, Input 1, Input 2)
34. Change to a different input type.
See Section 3 Configuration.
35. Check “Device Status” (page 231) to
see if FACT CRC=PASS.
If PASSreturn to original input
type.
If FAILfield calibrate Control
Output #1, Input 1, or Input 2.
Refer to Section 7 Input
Calibration and Section 8
Output Calibration.
CAL2 ERR
Background
Working CAL TEST failure (Control
2, Output)
36. Field calibrate Control Output 2.
Refer to Section 8 Output
Calibration.
FACT CRC
Check “Device
Status”
See page 231.
Factory-set input constants have
been changed due to the change in
input type.
37. Check background test error
message being displayed.
38. Recalibrate Input or Output.
Refer to Section 7 Input
Calibration or Section 8 Output
Calibration.
Troubleshooting / Service
Self Diagnostics
234 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Lower
Display
Indication
Test Group
Reason for Failure
How to Correct the Problem
EE FAIL
Background
Unable to write to nonvolatile
memory. Any time you change a
parameter and it is not accepted,
you will see EE FAIL.
39. Check the accuracy of the parameter
and re-enter.
40. Try to change something in
configuration.
41. Call Customer Support
1-800-423-9883 USA and Canada.
IN1FAIL
IN2FAIL
IN3FAIL
IN4FAIL
Background
Two consecutive failures of input 1
integration (for example, cannot
make analog to digital conversion)
42. Be sure the range and actuation are
configured correctly.
43. Check the input source.
44. Recalibrate. Refer to Section 7 -
Input Calibration.
45. Replace the input card.
46. Call Customer Support
1-800-423-9883 USA and Canada.
BATTERY
Power-up or
Status
Battery test failure.
47. Replace battery.
48. Call Customer Support
1-800-423-9883 USA and Canada
BATT LOW
Background
PV LIMIT
Background
Process Variable is out of range.
± 10 % of range
49. Be sure pen input configuration is
correct.
50. Check the displayed PV value to see
if it is outside input limits.
51. Call Customer Support
1-800-423-9883 USA and Canada.
RV LIMIT
Background
The result of the formula shown
below is beyond the range of the
remote variable.
RV = INP2 X RATIO + BIAS
52. Make sure the input signal is correct.
53. Make sure the ratio and bias settings
are correct.
54. Go to CONTROL prompt REMOTE
SOURCE and change REMOTE to
1LOCAL.
SW FAIL
SW2 FAIL
Background
Position proportional slidewire
feedback failure
55. Check motor slidewire connections.
56. Recalibrate the slidewire motor
position.
57. Replace the control card.
Troubleshooting / Service
Self Diagnostics
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 235
April 2017
Lower
Display
Indication
Test Group
Reason for Failure
How to Correct the Problem
IN1RNG
IN2RNG
IN3RNG
IN4RNG
Background
Input out of range. The process input
is outside the range limits.
58. Make sure the range and actuation
are configured properly.
59. Check the input source.
60. Restore the factory calibration:
c) Disconnect the wiring from the
terminals on plug J2 on the input
board (see Figure 2-13). Place a
jumper across these terminals.
The controller should read room
temperature if it is configured for
a thermocouple input.
d) If it does not read room
temperature, see Section 3 -
Configuration and change the
IN1TYP prompt in the INPUT 1
group to another type of
thermocouple.
e) After the change, press FUNC
key, then the LOWR DISP key.
The controller should read the
correct room temperature. If it
does not, the unit has an input
failure.
f) Repeat step b. This time switch
the IN1TYP back to the originally
selected thermocouple.
g) Repeat step c. The controller is
restored with factory calibration.
h) Remove the jumper and
reconnect the thermocouple to
plug J2.
61. Field calibrate. See Section 7 Input
Calibration.
62. Replace the input card.
63. Call Customer Support
1-800-423-9883 USA and Canada.
NOTE 1: Will appear in “STATUS” Set Up GroupSee procedure for displaying the test results on page 231.
Troubleshooting / Service
Visual Failure Symptoms
236 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
9.4 Visual Failure Symptoms
Introduction
In addition to the error message prompts, there are visual failure symptoms that can be identified by noting
the erratic recorder functions.
Symptoms
Compare your symptoms with those shown in Table 9-5 and refer to the troubleshooting procedure
indicated to correct the problem.
Table 9-5 Visual failure symptoms
Symptom
Troubleshooting
Procedure
Recorder will not operate
1
Recorder operation is normal but pen trace is incorrect
2
Chart rotates at wrong speed or will not rotate (pen indication correct)
3
Pen remains at high end of range when input signal is low
4
Pen does not move when input signal changes
5
A key does not respond and/or a display does not light
6
Displayed output does not agree with controller output
Current Proportional Output Type
Position Proportional Output Type
Single or Dual Relay Output Type
Duplex Current/Time or Time/Current Proportional Output Type
Auxiliary Output Type
7
8
9
10
11
External Alarm Function does not operate properly
12
Modbus Communications Failure
13
Troubleshooting / Service
Troubleshooting Procedures
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 237
April 2017
9.5 Troubleshooting Procedures
Introduction
The troubleshooting procedures for the Visual Failure Symptoms are listed in numerical order as they
appear in Table 9-5. Each procedure lists what to do if you have that particular failure and how to do it or
where to find the data needed to accomplish the task. Progressive steps provide aid in finding and fixing the
problem.
Equipment needed
You will need the following equipment in order to troubleshoot the symptoms listed in the tables that
follow:
DC Milliammeter mAdc
Calibration sources T/C, mV, Volt, etc.
Voltmeter
Table 9-6 Procedure #1Troubleshooting recorder failure symptoms
Step
What to do
How to do it or where to find the data
1
Check the fuse on the main printed
circuit board.
Replace if defective.
2
Check the supply voltage.
Measure the line voltage across J10 on the Main
printed circuit board.
3
Check the connections to J10 on the
main printed circuit board.
Refer to Subsection 2.6 - Input Wiring
Procedures (Figure 2-12 AC Line Power Wiring).
4
Check the transformer leadwire
connections to the main printed circuit
board.
Refer to Figure 10-5 in Section 10 - Parts List.
5
Check the system for brown-outs, heavy
load switching, etc.; and conformance to
installation instructions.
Refer to Section 2 - Installation.
6
Replace the transformer.
Disconnect the transformer lead wires from the
main printed circuit board. Replace the
transformer and tighten the screws. Connect the
lead wires to the main printed circuit board.
7
Call Technical Assistance Center.
1-800-423-9883 USA and Canada
Troubleshooting / Service
Troubleshooting Procedures
238 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Table 9-7 Procedure #2Troubleshooting pen trace failure symptoms
WARNING
Do not lubricate the plastic gears on the chart and pen motors.
Step
What to do
How to do it or where to find the data
1
Check the sensor for the proper type and
its ability to function.
Verify the input configuration data and operation
of the sensor.
2
Recalibrate the recorder.
Refer to Section 7 - Input Calibration. For
thermocouple input, be sure to confirm cold-
junction temperature calibration.
3
Replace the servo plate assembly.
Refer to the instructions included with the
replacement part.
4
Call Technical Assistance Center.
1-800-423-9883 USA and Canada
Table 9-8 Procedure #3Troubleshooting chart rotation failure symptoms
WARNING
Do not lubricate the plastic gears on the chart and pen motors.
Step
What to do
How to do it or where to find the data
1
Check the chart installation.
Be sure the drive pin on the hub is in the drive
hole on the chart.
2
Check the configured chart speed value
and change it, if required.
Refer to Section 3 - Configuration.
3
Check the motor cable plug connection
at connector J7 on the main printed
circuit board.
Visually examine the plug and reset it.
4
Replace the chart motor.
Refer to the instructions included with the
replacement part.
5
Call Technical Assistance Center.
1-800-423-9883 USA and Canada
Troubleshooting / Service
Troubleshooting Procedures
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 239
April 2017
Table 9-9 Procedure #4Troubleshooting chart rotation failure symptoms
WARNING
Do not lubricate the plastic gears on the chart and pen motors.
Step
What to do
How to do it or where to find the data
1
Check the sensor and lead wires for
continuity. Check the connections.
Replace the sensor lead wires as needed.
Tighten the connections.
2
Check the pen and input configuration
data.
Refer to Section 3 - Configuration.
3
Replace the servo plate assembly.
Refer to the instructions included with the
replacement part.
4
Call Technical Assistance Center.
1-800-423-9883 USA and Canada
Table 9-10 Procedure #5Troubleshooting pen failure symptoms
WARNING
Do not lubricate the plastic gears on the chart and pen motors.
Step
What to do
How to do it or where to find the data
1
Check the sensor and lead wires for
continuity. Check the connections.
Replace the sensor lead wires as needed. Verify
and tighten the input connections.
2
Check the pen arm for secure
mechanical attachment to the servo
shaft.
Verify that the flat-head screw that attaches the
pen arm to the plastic servo gear on the servo
shaft is tight.
3
Check the servo cable plug connection
(J6) on the main printed circuit board.
Visually examine the plug and reseat it.
4
Replace the servo plate.
Refer to the instructions included with the
replacement part.
5
Call Technical Assistance Center.
1-800-423-9883 USA and Canada
Table 9-11 Procedure #6Troubleshooting keyboard and/or display failure symptoms
Step
What to do
How to do it or where to find the data
1
Run a Key Test to check the operation of
the keys and displays.
Refer to Section 5 - Operation for procedures on
running a key test.
2
Replace the membrane switch
(keyboard) and /or display printed circuit
board as required.
Refer to the instructions included with the
replacement part.
Troubleshooting / Service
Troubleshooting Procedures
240 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Table 9-12 Procedure #7Troubleshooting current proportional output failure symptoms
Step
What to do
How to do it or where to find the data
1
Be sure the recorder is configured for
current output.
Refer to Section 3 - Configuration. Make sure OUT
ALG selection = CURRENT.
2
Check the field wiring.
Refer to Section 2 - Installation.
3
Be sure all the recorder and control
related data is correct.
Refer to Section 3 - Configuration.
Check the tuning, algorithm, and control data.
4
Check the output.
Put the recorder into Manual Mode and raise/lower
the output manually from 0 % to 100 % (4-20 mA).
Use a milliammeter at connection J1 on the control
output printed circuit board.
5
Recalibrate the current proportional
output.
Refer to Section 8 - Output Calibration.
6
Replace the control output printed
circuit board.
Refer to the instructions included with the
replacement part.
Table 9-13 Procedure #8Troubleshooting position proportional output failure
symptoms
Step
What to do
How to do it or where to find the data
1
Be sure the recorder is configured for
position proportional output.
Refer to Section 3 - Configuration. Make sure OUT
ALG selection = POSITN.
2
Check the field wiring.
Refer to Section 2 - Installation.
3
Check the output.
Put the recorder into manual mode and adjust the
output manually to drive the motor from 0 % to
100 %.
4
Check whether the motor drives in both
directions. If it does, go to step 5. If the
motor drives in one direction only, check
the slidewire. If the motor does not drive
in either direction, check the motor.
Refer to Section 8 - Output Calibration for motor
slidewire calibration. Refer to the motor
instructions.
5
Check the output voltage to the
slidewire.
Put the voltmeter across the slidewire terminals at
connector J2 on the control output printed circuit
board and check that the slidewire voltage varies
with the motor position.
6
Be sure that the output relays are
actuating properly. If they are not, check
the field wiring, then go to step 4. If they
are, go to step 7.
Put the recorder into manual mode and adjust the
output manually above and below the present
value. Listen for the click of the relays. One relay
should click when the output is adjusted higher,
and the other should click when the output is
adjusted lower than the present value. Observe
OUT 1 and 2 indicators on the front display.
7
Check the control relay jumper position.
Refer to Section 3 - Configuration.
8
Replace the control output printed
circuit board.
Refer to the instructions included with the
replacement part.
9
Recalibrate the position proportional
output.
Refer to Section 8 - Output Calibration.
Troubleshooting / Service
Troubleshooting Procedures
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 241
April 2017
Table 9-14 Procedure #9Troubleshooting relay output failure symptoms
Step
What to do
How to do it or where to find the data
1
Be sure the recorder is configured for
relay output.
Refer to Section 3 - Configuration. Make sure
OUT ALG selection = TIME.
2
Be sure all the recorder and control
related data is correct.
Refer to Section 3 - Configuration.
Check the Tuning, Algorithm, and Control data.
3
Check that the applicable output relay
actuates properly. If it does, go to step 4.
Put the recorder into manual mode and adjust the
output manually to raise or lower the PV around
the setpoint. Listen for the click of the relay as the
PV moves in either direction. Observe OUT 1 or 2
indicator on the front display.
4
Check the control relay jumper positions.
Refer to Section 3 - Configuration.
5
Check the field wiring.
Refer to Section 2 - Installation.
6
Replace the control output printed circuit
board.
Refer to the instructions included with the
replacement part.
Table 9-15 Procedure #10Troubleshooting current/time or time/current failure
symptoms
Step
What to do
How to do it or where to find the data
1
Be sure the recorder is configured for
current time/time current output.
Refer to Section 3 - Configuration. Make sure
OUT ALG selection = TI CUR or CUR TI.
2
Be sure all the recorder and control
related data is correct.
Refer to Section 3 - Configuration.
Check the tuning, algorithm, and control data.
3
Check that the applicable output relay
actuates properly. If it does, go to step 4.
If it does not check the field wiring; then
go to step 5.
Put the recorder into manual mode and adjust the
output manually to raise or lower the PV around
the setpoint. Listen for the click of the relay as the
PV moves in either direction. Observe OUT 1 or 2
indicator on the front display.
4
Check the control relay jumper positions.
Refer to Section 3 - Configuration.
5
Check the current proportional output.
Put the recorder in manual mode and manually
adjust the output from 0 % to 100 % (4-20 mA).
Use a milliammeter across the terminals in
connector J1 on the control output printed circuit
board to verify the output.
6
Recalibrate the current output.
Refer to Section 8 - Output Calibration.
7
Replace the control output printed circuit
board.
Refer to the instructions included with the
replacement part.
Troubleshooting / Service
Troubleshooting Procedures
242 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Table 9-16 Procedure #11Troubleshooting the auxiliary output
Step
What to do
How to do it or where to find the data
1
Be sure the controller is configured for
Auxiliary Output.
Refer to Subsection 3.17 Auxiliary Output
Group. Make sure AUX OUT is enabled and the
correct parameter is chosen. Check the High and
Low Scale values.
2
Check the field wiring.
Refer to Section 2 Installation.
3
Check the output.
Use a milliammeter at connection J2 on the
Auxiliary Output printed circuit board to determine
the correct output based on your representation
of 4 mA and 20 mA.
4
Recalibrate the Auxiliary Output.
Refer to Subsection 8.4 Auxiliary Output
Calibration.
5
Replace the Auxiliary Output printed
circuit board.
Refer to the instructions included with the
replacement part.
Table 9-17 Procedure #12Troubleshooting external alarm function failure symptoms
Step
What to do
How to do it or where to find the data
1
Be sure all the alarm configuration data
is correct.
Refer to Section 3 - Configuration.
2
Check the applicable alarm relay jumper
position.
Refer to Section 3 - Configuration.
3
Check the field wiring.
Refer to Section 2 - Installation.
4
Check that the applicable alarm relay
actuates properly depending on ALARM
TYPE configuration selection.
Alarms can be triggered either by:
reconfiguring the value of the trip points
(AnSnVAL), or
connecting a signal generator to the input
and setting the generator level beyond the
trip-point values.
Table 9-18 Procedure #13Troubleshooting Modbus communications
Step
What to do
How to do it or where to find the data
1
Check the field wiring and termination
resistor.
Refer to Figure 2-21 in Section 2 Installation in
this manual.
2
Make sure the Modbus Communications
board is properly installed in the
recorder.
Open the recorder door and chart plate, and
inspect the board. Refer to Figure 10-4 for
location of the board.
3
Run a Loopback test.
Refer to Modbus Communications manual
51-52-25-66 for loopback information.
Parts List
Overview
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 243
April 2017
10. Parts List
10.1 Overview
Introduction
This section provides the replacement parts lists for the DR4500A Truline Recorder. Most parts are
supplied on an optimum replacement unit basis; that is, part numbers are given for complete printed circuit
boards rather than for individual PCB components.
The figures that follow are exploded views of the DR4500A recorder. Each part is labeled with a key
number and the key numbers are listed in tables with associated part number.
Also included for your reference are an Internal Cabling drawing (Figure 10-5) and an Internal Wiring
Diagram (Figure 10-6) for options only.
When ordering parts, be sure to specify your recorder’s serial and model numbers (on nameplate) as well as
the part identification.
What’s in this section?
This section contains the following topics:
Topic
See Page
10.1 Overview
243
10.2 Exploded Views
Figure 10-1 Door assembly
Figure 10-2 Chart plate assembly
Figure 10-3 Basic recorder components without options
Figure 10-4 Recorder components associated with options
244
244
245
246
248
10.3 Miscellaneous Hardware Kit Contents
251
10.4 Figure 10-5 Internal Cabling Data
252
10.5 Figure 10-6 Internal Wiring Diagram Options Only
253
Parts List
Exploded Views
244 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
10.2 Exploded Views
Door assembly
Figure 10-1 is an exploded view of the Door Assembly. Table 10-1 is a list of the associated part numbers.
1-1
21452
1-2
1
1-3
1-1
1-2
1-4
1-3A
Figure 10-1 Door assembly
Table 10-1 Door assembly parts
Key
Part Number
Description
Recommended
Spare Parts per
Quantity
per Unit
10
100
1
(Note
3)
30754955-501
30754955-504
30754955-505
30754955-506
30754955-507
30754955-508
30756548-501
30756548-501
51452435-501
51452435-502
51452435-503
51197761-501
51197761-502
51197761-503
51197761-504
51404781-501
51404781-502
51404781-503
Door Assembly
Blue with glass window and latch
Blue with acrylic window and latch
Gray with glass window and latch
Gray with acrylic window and latch
Black with glass window and latch
Black with acrylic window and latch
Stainless Steel Door with Glass window
Stainless Steel Door with Acrylic window
NEMA4X Door with Acrylic window
NEMA4X Door with Glass window
NEMA4X Door with HTST window
SS Heavy duty with acrylic window/heavy duty latch
(before 3/99)
SS HTST door with heavy duty latch (before 3/99)
SS Heavy duty door with lock (before 3/99)
SS Heavy duty HTST door with lock (before 3/99)
SS Heavy Duty door with acrylic window (after 3/99)
SS Heavy Duty door for HTST with acrylic window (after 3/99)
SS Heavy Duty door with glass window (after 3/99)
1
1-1
(K)30755980-001
Hinge Pin (Note 1)
2
1-2
(K)30755980-001
Retaining Ring (Note 1)
2
Parts List
Exploded Views
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 245
April 2017
Key
Part Number
Description
Recommended
Spare Parts per
Quantity
per Unit
10
100
1-3
1-3A
51309609-503
30755980-006
51452208-503
Latch/Lock Assembly Kit (Note 2)
Key kit for keyed latch or lock
NEMA4X Latch Kit
1
3
1
1-4
30755136-502
Truline Door Overlay
1
51404929-501
External Keypad Upgrade Kit (not shown)
1
NOTE 1: For Door 30754955-50X, (K) denotes that these parts are included in the miscellaneous hardware kit 30755980-001. For all other
doors, the parts are included with applicable door assembly.
NOTE 2: For Heavy Duty doors only (before 3/99): for knob type latch, order kit 30756584-001; for latch with lock and key, order kit
30756584-002. For Heavy Duty doors (after 3/99): for knob type latch and/or latch with lock and key, order 51404673-501.
NOTE 3: For instruments with the Door Keypad option, order the correct door assembly and the External Keypad Upgrade kit
Chart plate
Figure 10-2 is an exploded view of the Chart Plate Assembly.
Table 10-2 is a list of the associated part numbers.
8
9
3
4756
1
2
21453
10
Figure 10-2 Chart plate assembly
Parts List
Exploded Views
246 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Table 10-2 Chart plate assembly parts
Key
Part Number
Description
Recommended
Spare Parts per
Quantity
per Unit
10
100
1
30756304-501
30756304-502
Truline Pen Arm Assembly (high speed)
Truline Pen Arm Assembly (abrasion resistant)
1
5
1
2
30754957-501
Membrane Switch Key Pad
1
5
1
3
(K)30756150-001
Chart Hub Kit
1
3
2
4
30756113-501
Chart Motor (includes Chart Hub Kit)
1
3
1
5
30757571-501
Display PCB (includes key no. 6)
1
5
1
6
See above
Ribbon Cable, Display (included with key no. 5)
7
30756114-501
Servo Motor Assembly
8
30754975-503
Servo Plate Assembly (includes key no. 7)
1
2
1
9
(K)30755980-002
Spring, tension
1
10
30754977-503
30754977-504
30754977-513
30754977-514
Chart plate for standard (high speed) pen
Chart plate for abrasion resistant pen
Chart plate for standard (high speed) pen - CE Mark
Chart plate for abrasion resistant pen - CE Mark
1
2
1
Basic recorder components without options
Figure 10-3 is an exploded view of the basic recorder components.
Table 10-3 is a list of the associated part numbers.
1 4 5
4
32
7
4
6
21454
Figure 10-3 Basic recorder components without options
Parts List
Exploded Views
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 247
April 2017
Table 10-3 Basic recorder parts without options
Key
Part Number
Description
Recommended
Spare Parts per
Quantity
per Unit
10
100
1
30754982-502
Main Transformer
1
3
1
2
51309355-502
51309355-503
51309355-504
51309355-505
Main PCB - CE Mark (model DR45AT)
Main PCB - CE Mark (model DR45AR)
Main PCB - CE Mark (model DR45AW)
Main PCB - CE Mark (model DR45AH/AP/AS)
1
5
1
3
(K)30756141-003
Input PCB (input 1, 2, 3, or 4)
1/4
4
See Note 2
3-position connector**
2
5
See Note 2
2-position connector**
1
6
30755980-005
Fuse (Wilkman 19374-041-K 500 ohm or equal)**
1
7
30754924-502
51452182-502
Case
Case NEMA 4
1
PARTS NOT SHOWN
See Note 2
Card guides for Input PCBs**
2
51197612-502
Ferrite Filter - Package of 2 (CE Mark)
1
51197755-001
Capacitor Kit (.01mfd) - 12 per kit (CE Mark)
30755232-502
0-10 Vdc Input Divider (input PCBs)
*
30756461-002
250 ohm Resistor Assembly
*
30755317-001
Box of 100 12” Truline Chart Paper
(K)30755065-501
(K)30755065-502
(K)30755065-503
Mounting Kit (standard)
Mounting Kit (Heavy Duty)
Mounting Kit (NEMA4X)
1
(K)30755134-002
Gray Universal Filler Plate Kit
*
(K)30755011-001
Filler Panel Kit (for replacing Servoline recorder)
*
(K)30757301-001
Configuration Lockout Hardware
1
51197657-502
Panel Mounting Gasket Kit
1
NOTE 2: These parts are included with applicable PCB kits, as required.
* As required
** These parts are also included in the miscellaneous hardware kit 30755980-006
Parts List
Exploded Views
248 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Additional recorder components associated with options
Figure 10-4 is an exploded view of the recorder components associated with options.
Table 10-4 is a list of the associated part numbers.
7-1 7 1 11 10 5 4 8 9
2
3 13
21455
12 9
Figure 10-4 Recorder components associated with options
Daughter board
Parts List
Exploded Views
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 249
April 2017
Table 10-4 Recorder parts associated with options
Key
Part Number
Description
Recommended
Spare Parts per
Quantity
per Unit
10
100
1
30754922-501
30754922-502
Second Control Output PCB
Second Current Output PCB - Current Out Only (Note
4)
1
2
30754922-501
30754922-502
First Control Output PCB
First Control Output - PCB - Current Out Only
1
5
1
30755306-501
30755306-601
Control Output Relay 1 relay
Control Output Relay 5 relays
1
5
2
3
(See
Note 5)
51404561-501
51404561-502
51404561-503
51404561-504
51404561-505
Aux Output (only)
Main board (with Daughterboard Rev.B and w/o
Daughterboard)
RS485 Comms only
RS485 Comms + 4/ 20 mA Aux Output
Main board (with Daughterboard Rev.A)
RS485 Comms only
RS485 Comms + 4/ 20 mA Aux Output
1
5
1
4
(K)30756140-001
Alarm output/digital input PCB kit
1
5
30755119-501
Ribbon cable (34 conductor), See Note 3
1
3
1
7
30755127-502
Light accessory kit
1
7-1
(K)30749598-501
Kit of 5 Bulbs (General Instruments 1828 or equivalent)
1
8
(K)30756140-001
Spacers
4
9, 10, 11
(K)30756141-003
Input PCBs (1, 2, 3, or 4)
1
5
1/4
12
30754919-501
Mother board
1
3
0/1
13
30755980-004
Battery (Duracell DL2450 or equivalent)
1
1
1
NOTE 3: Part included with alarm output/digital input PCB kit 30756140-001.
NOTE 4: 30754922-502 Control Output board is used for Table II Options 60 or 66.
NOTE 5: Processor Board change occurred approximately September 2009. See Diagram below for daughter board.
Parts List
Exploded Views
250 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Main board with
Daughter board
Daughter board
Parts List
Miscellaneous Hardware Kit Contents
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 251
April 2017
10.3 Miscellaneous Hardware Kit Contents
Kit contents
Table 10-5 lists the kit contents of miscellaneous hardware kit part number 30755980-TAB.
Table 10-5 Miscellaneous hardware kit
Part Description
Quantity
Tab
001
Tab
002
Tab
003
Tab
004
Tab
005
Tab
006
Pen lifter/retainer
1
Screw 10-32, 3/4” lg.
5
O-ring
5
Spring, tension
2
Hinge pin
2
Retaining ring
2
Pen arm #1 (classic)
1
Pen arm #2 (classic)
1
Latch without lock
1
Latch pin
1
Latch gasket
1
Card guide
2
4-position connector
2
3-position connector
2
3-position connectorCE Mark
2
2-position connector
2
Fuse 0.5 A, 250 V
20
Batteries 3.0 V Lithium Button Cell
5
Key for latch or lock
1
Key for Door/Keyed latch
1
Noise Suppression Kit 120VAC
51404594-501
Noise Suppression Kit 220VAC
51404594-502
Parts List
Internal Cabling Data
252 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
10.4 Internal Cabling Data
View of internal cabling
Figure 10-5 is a view of the internal cabling for the DR4500A Truline Recorder.
Figure 10-5 Internal cabling for DR4500A Truline recorder
Parts List
Internal Wiring Diagram Options Only
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 253
April 2017
10.5 Internal Wiring Diagram Options Only
View of internal option wiring
Figure 10-6 is a view of the internal wiring diagram - options only for the DR4500A Truline Recorder.
Chart Plate
Display
board
Pen 2
Motor
Chart motor
9 position keyboard cable
J3
2-wire pair
Light
option
Pen 1 Motor
Mother board
J8 1
J13
J2
1
J14
Processor
card
J2
Alarm/digital
inputs
J1
1
34 cond.
ribbon cable
Main transformer
2 wire
gray pair
2 wire
orange pair
J12
Second
input
1
J1
1
J3
Control Output 2
Input Card 4
Input Card 3
Control Output 1
Communication Card
OR
Auxiliary Output Card
4 cond.
cable
Ground
Test
1
T1
(See Table 1 for
connections)
Conn.
Designation on
Destinaton Bd.
J1
J1
J4
J4
J4
J2GRN. WHT.
BLK. RED
2
2
2
2
2
4
No.
of
Cond.
Destination
(Board)
BLU.
BRN.
ORG.
VIO.
WHT.
Female Conn.
GRN, WHT,
BLK, RED.
Input Card #3
Processor Card
Input Card #4
Control Output #1
Control Output #2
Auxiliary Output
Main transformerGRN. WHT.
BLK. RED
T1
Leads
TABLE 1
Dual Connector
Male
Conn
.
Female
Conn
.
22767
No
Connection
Communication Card
(RS485/422)
J4
Auxiliary Output/
Communication
(RS485/422)
Figure 10-6 Internal diagram for DR4500A Truline recorder options only
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 254
April 2017
A. Model DR45AR
A.1 Overview
Introduction
If the key number for your recorder is DR45AR, it is a relay expansion model Truline recorder that can
have up to six alarm relay outputs and include Fo calculation function. While its basic functions are
identical to the standard (DR45AT) Truline recorder, it does have some unique hardware, wiring and
configuration features. This section provides the data pertinent to these unique features as a supplement to
the standard Truline in this product manual.
What's in this section?
The table below lists the topics that are covered in this section.
Topic
See Page
A.1 Overview
254
A.2 Hardware Identification
255
A.3 Fo Reset Configuration
257
A.4 Options Configuration
258
A.5 Operations Additions
260
A.6 Configuration Worksheet Additions
261
Model DR45AR
Hardware Identification
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 255
April 2017
A.2 Hardware Identification
Introduction
Figure A-1 (DR45AR with one input) and Figure A-2 (DR45AR with two to four inputs) identify the
hardware components of the DR45AR model versus "Table" selections.
DR45AR with one input
Figure A-1 identifies the hardware components of the DR45AR with one input.
Number 5 & 6
Alarm outputs PCB
*Table III - 0X3
#1
4-20mA control output
#1 PCB
*Table II = 40
and Number 3 & 4
Alarm outputs PCB
*Table III - 0X2, 0X3
Mother PCB
(for control and
selected options)
Number 1 & 2 Alarm output/
digital input PCB
*Table III - 0X1, 0X2 or 0X3
Main PCB
(common)
#1 Input PCB
*Table I - 1000, 3000
VIEW A - - Key Number: DR45AR
With one input
21464
* Refer to Model Selection Guide
Figure A-1 DR45AR with one input
Model DR45AR
Hardware Identification
256 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
DR45AR with two to four inputs
Figure A-2 identifies the hardware components of the DR45AR with two to four inputs.
4-20mA control
output #1 PCB
*Table II = 40
and Number 3 & 4
Alarm outputs PCB
*Table III - 0X2, 0X3
Mother PCB
(for inputs #3 &#4,
control and
selected options)
Number 1 & 2 Alarm output/
digital input PCB
*Table III - 0X1, 0X2 or 0X3
4-20 mA Control
Output #2 and
Number 5 & 6
Alarm outputs PCB
*Table III - 0X3
#3
#4
#2 #1
Main PCB
(common)
Input PCB's
*Table I - XXXX
x = 0,1, or 3
VIEW B - - Key Number: DR45AR
With two to four inputs
21465
* Refer to Model Selection Guide
Figure A-2 DR45AR with two to four inputs
Model DR45AR
Fo Reset Configuration
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 257
April 2017
A.3 Fo Reset Configuration
Introduction
This SET UP group is specific to Model DR45AR. It allows you to reset the Fo sterilization calculation.
Accessing Fo reset prompts
Press the SET UP key until you see:
Upper Display: SET UP
Lower Display: FO RESET
Press the FUNC key to call up the Fo Reset function prompt that will allow you to reset the Fo sterilization
calculation. The function prompt for the Fo Reset group is listed in Table A-1.
Function prompts
Table A-1 lists the function prompt in the “Fo RESET” Set Up group for model DR45AR.
Table A-1 Fo RESET group function prompts
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
RESET Fo
Reset Fo Sterilization
Calculation
(REM SW or REM SW2
under "OPTIONS" group
must be configured for
"FO RST".)
NO
YES
Model DR45AR
Options Configuration
258 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
A.4 Options Configuration
Introduction
For Model DR45AR there are several additions to be added to Table 3-17 Options Group Function Prompts
(from Section 3). They cover additional options that are only available with this model number.
Table A-3 on the next page shows the additions made for Model DR45AR in the options group definitions.
Table A-2 Options group function prompts, continued from Section 3/Table 3-17
Function Prompt
Lower Display
Function Name
Selections or Range of Setting
Upper Display
Factory
Setting
STERILIZ
Fo Sterilization Time
YES
NO
IN TEMP
Input for Product
Temperature
INPUT 1
INPUT 2
INPUT 3
INPUT 4
STDTEMP
Standard Reference
Temperature
0.1 to 9999
Z VALUE
Thermal Resistance
0.1 to 9999
REM SW
Remote Switching
NONE
TO MAN (from AUTO)
TO LSP (from REMOTE)
TO 2SP (from LSP)
TO DIR (from REV)
TO HOLD (from RUN)
TUNE
FO RST
REM SW2
Remote Switching digital
input 2
NONE
FO RST
Model DR45AR
Options Configuration
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 259
April 2017
Table A-3 Option group definitions, continued from Section 4/Table 4-15
Lower Display
Prompt
Upper Display
Range of Setting or Selection
Parameter Definition
STERILIZ
YES (activates Fo sterilization
calculation)
NO
Fo STERILIZATION TIME This function computes
equivalent sterilization time by accumulating lethality
rates for a product over each 1/3 or 2/3 second scan
interval of the recorder using this equation:
Ts = Ts(t-1) + dt X 10
( tTb)
z
Where:
Ts = sterilization time in minutes
Ts(t-1) = previous sterilization time
dt = time interval (1/3 or 2/3 second)
NOTE: 1/3 second if less than 3
configured inputs; 2/3 second if greater
than 2 configured inputs.
Tb = standard reference temperature
(configurable)
t = product (input) temperature (°F or °C)
z = thermal resistance (configurable)
Only applicable if Model Table II is 40, Model Table III is
0X3, and Model Table IV is F.
INTEMP
INPUT 1
INPUT 2
INPUT 3
INPUT 4
INPUT FOR PRODUCT TEMPERATURE selects
which input will supply product temperature for
sterilization calculation.
STDTEMP
0.1 to 9999
STANDARD REFERENCE TEMPERATURE selects
a reference temperature constant for sterilization
calculation usually 250 °F or 121 °C.
Z VALUE
0.1 to 9999
THERMAL RESISTANCE selects a thermal
resistance constant for sterilization calculation
usually 18 °F or 10 °C.
REM SW
NONE
TO MAN (from AUTO)
TO LSP (from REMOTE)
TO 2SP (from LSP)
TO DIR (from REV)
TO HOLD (from RUN)
TUNE
FO RST
REMOTE SWITCHING allows you to select an action
to be initiated by remote contact closure through digital
input .
NONE No Selection
TO MAN switch to manual mode from automatic
TO LSP switch to local setpoint from remote
TO 2SP switch to 2nd setpoint from local setpoint
TO DIR switch to direct output action from reverse
TO HOLD put ramp/soak program in hold
TUNE start Accutune
FO RST reset sterilization calculation.
REM SW2
NONE
FO RST
REMOTE SWITCHING DIGITAL 2 INPUT allows you
to select remote contact closure through digital 2 input
to reset sterilization calculation or not.
Model DR45AR
Operations Additions
260 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
A.5 Operations Additions
Introduction
In addition to the standard operating functions in this manual the addition listed below appears if you have
model DR45AR.
Viewing F
O
sterilization display
Add the following prompt to Table 5-5 Lower Display Key Parameter Prompts.
Prompt
Description
F
O
F
O
sterilization time in the lower display with the appropriate input in the upper
display
Digital input (REM SW) prompt selection
Add the following selections to Table 5-25 Digital Input Option Action on Contact Closure.
REM SW
Selections
Display Indication
Action on Contact Closure
F
O
RST
None
Resets F
O
sterilization calculation if F
O
RESET
prompt is enabled.
Model DR45AR
Configuration Worksheet Additions
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 261
April 2017
A.6 Configuration Worksheet Additions
Configuration additions
In addition to the Configuration worksheet items that are listed in Section 3 - Configuration, the following
parameters also appear in Model DR45AR.
Group
Prompt
Function
prompt
Value or
Selection
Factory
Setting
FO RESET
OPTIONS
RESET FO
REJ FREQ
HF REJ
RELHUMID
ATMPRES
DEVIATION
DEVSETPT
SCROLL
GRANDTOT
STERILIZ
IN TEMP
STDTEMP
Z VALUE
REM SW
REM SW2
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
_______
60
ENABLE
NO
NONE
0
NONE
DISABL
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 263
April 2017
B. Model DR45AW
B.1 Overview
Introduction
The Model DR45AW is a Truline Recorder that has been designed toperform as an Open Channel Flow
Recorder. This addendum describes thespecial features and includes installation and operating requirements
that are specific to the Model DR45AW.
Features
The following is a list of features specific to the Model DR45AW. Controlfunctions are NOT available in
this unit.
The Open Channel Flow Recorder feature is “Record Only” with anoptional pulse output function.The
pulse output counter alarm function provides a configurable timeduration relay output when a selected
incremental change in volume hasoccurred. The pulse output relay can be reset from the keyboard.
Two additional totalizers can be provided, making a total of up to fourtotalizers possible. A manual
adjustable totalizer function can beselected to make corrections to the accumulated value as a result
ofpower outages.
The Truline Flow Recorder is configurable to five different primaryopen channel flow elements:
V NOTCH WEIR
RECTANGULAR WEIR
CIPOLLETTI WEIR
PARSHALL FLUME
PALMER-BOWLUS FLUME
Metric Flow Rate selections are available.
The product provides a configurable low flow cutoff function for eachinput being used for totalization.
This feature allows the user to select apercent of flow range values that inhibits the totalizers
accumulatorwhenever the input signal is less than that selected value. This featureeliminates the
problems incurred because of shifting zero signals andnoise during low flow levels.
Model DR45AW
Installation
264 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
B.2 Installation
Field wiring
Mount and wire the recorder as described in the Product Manual.
ATTENTION Power wiring, input wiring, alarm output and digital inputwiring remain the same as
specified in Section 2 of the Product Manual.
Pulse output wiring
The Pulse Output Function provides a non-control pulse output counteralarm function with a configurable
time duration relay output when aselected incremental change in volume has occurred. An
applicationexample would be a weigh feeder that will add a predetermined amount ofchemical upstream,
based on every one million gallons of flow through aweir.Refer to Figure 1 for the field wiring of the Pulse
Output Option.
Figure B-1 Flow RecorderField Wiring
INPUT 3
INPUT 4
Plug J5
22675
PULSE O UTPUT
CARD
PULSE
OUTPUT #1
NOT E: Power wiring, input wiring, alarm output and digital input wiring
remain the same as specified in Section 2 of the Product Manual.
PULSE
OUTPUT #2
Model DR45AW - Configuration
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 265
April 2017
B.3 Configuration
General
The DR45AW is basically configured as outlined in Sections 3 and 4 of the Product
Manual. However, some configuration and operation actions have been modified as
outlined in this section.
Configuration for
Open Channel Flow
Operation
Table 1 lists all the function prompts in the “INPUT 1” Set Up group. Repeat the process
for each input you want to set up.
Press the SET UP key to enter the configuration mode, and continue pressing until
“INPUT 1” (INPUT 2, INPUT 3, or INPUT 4) prompt appears in the lower display.
Press the FUNC key to display the prompts in Table 1.
Press s or t key to make selections.
Table B-1 Input Group Function Prompts
Function
Prompt
Lower Display
Function
Name
Selections or
Range of Setting
Upper Display
Remarks
DECIMAL
Decimal Point
Location
XXXX None
XXX.X One
XX.XX Two
Factory setting is XXX.X.
UNITS
Temperature Units
DEG F
DEG C
EU (make selection at
prompt "ENGUNITS")
Factory setting is DEG F.
ATTENTION
Neither UNITS nor
ENGUNITS prompt will be displayed once the
FLOW or HEIGHT prompt is selected in the
Flow Transmitter selection. The engineering
units will then be configured through the
prompt “Flow Rate” selection.
ENGUNITS
Engineering Units
0 to 9
A to Z
+
\
(blank)
See previous note for UNITS.
IN1 TYPE
Input 1 Actuation
Type
B TC W TC H
E TC H W TC L
E TC L 100 PT
J TC H 500 PT
J TC L 100 RH
K TC H 4-20mA
K TC L 0-10mV
NNM TC 10-50m
NIC TC 0-5 V
R TC 0-10V
S TC RADIAM
T TC H
T TC L
Select a linear input type (e.g., 4-20mA, 0-
10mV, 10-50mA, 0-5V, or 0-10V).
Factory setting is 100 PT.
Table 1 is continued on the next page.
Model DR45AW
Configuration
266 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Configuration, Continued
Configuration for Open Channel
Flow Operation, Continued
Table B-2 Input Group Function Prompts, Continued
Function
Prompt
Lower Display
Function
Name
Selections or
Range of Setting
Upper Display
Remarks
XMITTER
Transmitter
Characterization
B TC T TC H
E TC H T TC L
E TC L W TC H
J TC H W TC L
J TC L 100 PT
K TC H 500 PT
K TC L 100 RH
NNM TC H LINEAR
NIC TC SQROOT
R TC
S TC
Select the Linear or Square Root
transmitter.
Factory setting is Linear.
FLOXMIT1
Flow Transmitter
Selection
NONE
HEIGHT
FLOW
NONEIf the input is not being used for
open channel flow measurement.
HEIGHTIf the input is measuring level.
FLOWSelected for an input signal that
represents flow.
ATTENTION
Select FLOW if the
signal represents transmitter flow,
otherwise select HEIGHT.
FLORATE 1
Flow Rate Selection
CFS cubic feet per second
GPS gallons per second
GPM gallons per minute
GPH gallons per hour
MGD million gallons per day
AFD acre feet per day
Metric Selections:
CMS M
3
per second
CMM M
3
per minute
CMH M
3
per hour
LPS Liters per second
MLD 10
6
Liters per day
HMD Hectare-meters per
day
Metric selections when Flow
Units are set to Flow not Height
LB/MIN Pounds per minute
LB/HR Pounds per hour
KG/MIN Kilogram per minute
KG/HR Kilogram per hour
ATTENTION
When a Metric Flow Unit is selected,
Height and Width parameters are read
as centimeters.
Table 1 is continued on the next page.
Model DR45AW - Configuration
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 267
April 2017
Configuration, Continued
Configuration for Open Channel Flow
Operation, Continued
Table B-3 Input Group Function Prompts, Continued
Function
Prompt
Lower Display
Function
Name
Selections or
Range of Setting
Upper Display
Remarks
WEIR 1
Weir Selection
NONE
V NOTCH
RECTNG
CIPOLT
ATTENTION
This prompt appears
only if you select NONE as the Flume
selection.
If you Then go to
select… Function
Prompt…
NONE FLUME 1
V NOTCH ANGLE 1
RECTNG or WIDTH
CIPOLT
FLUME 1
Flume Type
NONE
PARSHALL
PALMER
PARSHALL 1
Parshall Flume Size
Selection
NONE
1-INCH
2-INCH
3-INCH
6-INCH
9-INCH
X-INCH
“#-INCH” denotes the width of the flume
in inches.
For example: “2-INCH” represents a
two-inch wide flume.
ATTENTION
This prompt appears
only if you select NONE as the Weir
selection.
Then go to
Function
If you select… Prompt…
X-INCH WIDTH
anything other MAX HT 1
than X-INCH
PALMER 1
Palmer-Bowlus Flume
Type
4-INCH 24-INCH
6-INCH 27-INCH
8-INCH 30-INCH
10-INCH 36-INCH
12-INCH 42-INCH
15-INCH 48-INCH
18-INCH 60-INCH
21-INCH 72-INCH
ANGLE 1
V-Notch Wire Angle
Selection
30 DEG 90 DEG
60 DEG 120 DEG
Table 1 is continued on the next page.
Model DR45AW
Configuration
268 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Configuration, Continued
Configuration for Open Channel Flow
Operation, Continued
Table B-4 Input Group Function Prompts, Continued
Function
Prompt
Lower Display
Function
Name
Selections or
Range of Setting
Upper Display
Remarks
WIDTH
Width in Inches
Selection
(Centimeters for Metric
Flow Rate selection)
0 to 9999
The width setting is in inches (cm).
ATTENTION
If you selected
X-INCH for the Parshall Flume Size
selection, you cannot select a width less
than 12 inches. (The equation is
different when the width is less than 12
inches.)
MAX HT 1
Maximum Height in
Inches Selection
(Centimeters for Metric
Flow Rate selection)
0 to 9999
The maximum height (in inches or cm)
represents your maximum input signal.
MIN HT 1
Minimum Height in
Inches Selection
(Centimeters for Metric
Flow Rate selection)
0 to 9999
The minimum height (in inches or cm)
represents your minimum signal
(suppressed ranges are possible).
CUT OFF 1
Low Flow Cutoff
Selection
0 to 100% of Input range
The Low Flow Cutoff is selected as a
percentage of maximum flow. This is the
minimum flow that the recorder input will
detect. This is used mostly with flow
transmitters to avoid false minimum
signals.
INPTCOMP
Input Compensation
999.9 to 9999.
Factory setting is 0.
FILTER 1
Input 1 Filter
0 to 120 seconds
Factory setting is 0.
BURNOUT
Burnout Protection
NONE
UP
DOWN
Factory setting is UP.
ATTENTION
Repeat this procedure for INPUT 2, INPUT 3, and INPUT 4.
The function prompts will be the same except that a “2”, “3”, or “4” will appear instead
of a “1”.
Continued on next page
Model DR45AW - Configuration
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 269
April 2017
Configuration, Continued
Totalizer (1 to 4)
configuration
Selected inputs must be enabled to select totalization prompts.
Table 2 lists the additional function prompts available in the “TOTAL 1” Set Up group.
Repeat the process for each input you want to set up.
Press the SET UP key to enter the configuration mode, and continue pressing until
“TOTAL 1” (TOTAL 2, TOTAL 3, or TOTAL 4) prompt appears in the lower display.
Press the FUNC key to display the prompts in Table 2.
Press s or t key to make selections.
ATTENTION
All prompts described in the Product Manual are the same except for
“RATE.” This prompt does not appear for Model DR45AW since the totalizer flow rate
is always the same as the flow rate configured at the input.
Table B-5 Additional Totalizer Group Function Prompts
Function
Prompt
Lower Display
Function
Name
Selections or
Range of Setting
Upper Display
Remarks
ADJUST
Totalizer Adjustment
Selection
YES
NO
Selection of the adjustment to totalizers
in case of power outage.
The following prompts appear only if YES was selected above.
ADJ RATE
Flow Rate for Totalizer
Adjustment
0 to 9999
Select the average flow before the
outage. The ADJ RATE uses the unit
selected as the flow rate. (See input
configuration.)
ADJ TIME
Time for Totalizer
Adjustment
0 to 9999
Enter the time duration of the power
outage. The unit of time is minutes
EXECUTE
Execute Totalizer
Adjustment
YES
NO
No adjustment is made to the totalizer
until YES is selected.
Table 2 is continued on the next page.
Model DR45AW
Configuration
270 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Configuration, Continued
Totalizer (1 to 4)
configuration, Continued
B-2 Additional Totalizer Group Function Prompts, Continued
Function
Prompt
Lower Display
Function
Name
Selections or
Range of Setting
Upper Display
Remarks
The following prompts appear only if “FLORATE1” appears under the “Input 1” set up group.
CNVRT TO
Conversion Selection
NONE
CU FT
GALLON
ACREFT
CU MTR
LITER
HECTMT
Select desired totalizer units. Applicable
conversion factors will be applied based
on the input FLORATE1 selected. This
selection is only available when the input
FLOXMIT1 has been set to FLOW or
HEIGHT.
MULTIPLY
Multiplier Selection
X.001
X.01
X.1
X1
X10
X100
X1K
X10K
X100K
X.001 to X.1 produce a display with the
indicated number of decimal places. If a
multiplier >1 has been selected, the
multiplier will be printed after the
engineering units selected (e.g., GAL x
1K).
TOTAL EU
Totalizer Engineering
Units Selection
(three alpha characters)
Will be printed on chart next to totalizer
value.
A Grand Total feature is available under the OPTIONS Set Up group. If this function is
enabled the recorder will print the sum of all the active totalizers at each major time line.
This is printed in the space where the totalizer #4 is normally printed. (See the Truline
Product Manual Options Set Up.)
Continued on next page
Model DR45AW - Configuration
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 271
April 2017
Configuration, Continued
Pulse Counter
configuration
Table 3 lists the function prompts available in the “PULS OUT” Set Up group.
There is a second pulse output available using control relay 2 on the control 1 card.
Press the SET UP key to enter the configuration mode, and continue pressing until
“PULS OUT” prompt appears in the lower display.
Press the FUNC key to display the prompts in Table 3.
Press s or t key to make selections.
B-3 Pulse Counter Group Function Prompts
Function
Prompt
Lower Display
Function
Name
Selections or
Range of Setting
Upper Display
Remarks
PULS CNT
Pulse Counter Selection
YES
NO
Enable (YES) or disable (NO) the pulse
output option.
TOTALIZER
Totalizer Selection
TOTAL 1
TOTAL 2
TOTAL 3
TOTAL 4
Select one of the four totalizers as the
input to the pulse output counter.
PULSE SP
Pulse Setpoint Value
Selection
0 to 9999
The Pulse Setpoint Value is the
incremental volume selected to close the
pulse output relay for a preselected time
duration. This number will be multiplied
by the scaler selected at the “SP
SCALE” function prompt.
SP SCALE
Setpoint Scale Selection
1
10
100
1000
10000
100000
1E6
The Setpoint Scale is used to scale the
above pulse setpoint.
PULSE WID
Pulse Width Selection
1/2 SEC
1 SEC
5 SEC
Pulse Width is the duration in time of the
contact closure.
ATTENTION
If the measured flow
rate demands contact closure within the
pulse width time, the relay will remain
ON.
PULS RST
Pulse Counter Reset
YES
NO
Used to manually reset the pulse
counter to zero value.
Table 3 is continued on the next page.
Model DR45AW
Configuration
272 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Configuration, Continued
Pulse Counter configuration,
Continued
B-3 Pulse Counter Group Function Prompts, Continued
Function
Prompt
Lower Display
Function
Name
Selections or
Range of Setting
Upper Display
Remarks
PULS2CNT
Pulse Counter Selection
for Control Relay 2
YES
NO
Enable (YES) or disable (NO) the pulse
output option for control relay 2.
TOTLIZR2
Totalizer Selection for
Control Relay 2
TOTAL1
TOTAL2
TOTAL3
TOTAL4
Select one of the four totalizers as the
input to the pulse output counter for
control relay 2.
PULSE2SP
Pulse Setpoint Value
Selection for Control
Relay 2
0 to 9999
The Pulse Setpoint Value is the
incremental volume selected to close the
pulse output relay 2 for a pre-selected
time duration. This number will be
multiplied by the scaler selected at the
“SP2SCALE” function prompt.
SP2SCALE
Setpoint Scale Selection
for Control Relay 2
1
10
100
1000
10000
100000
1E6
The Setpoint Scale is used to scale the
pulse setpoint for control relay 2.
PULSE2WID
Pulse Width Selection
for Control Relay 2
1/2 SEC
1 SEC
5 SEC
Pulse Width is the duration in time of the
contact closure for control relay 2.
ATTENTION
If the measured flow
rate demands contact closure within the
pulse width time, the relay will remain
ON.
PULS2RST
Pulse Counter Reset for
Control Relay 2
YES
NO
Used to manually reset the pulse
counter for control relay 2 to zero value.
Model DR45AW - Operation
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 273
April 2017
B.4 Operation
Displaying totalizers
Follow the procedure in Table 4 to display the totalizer value.
Table B-4 Procedure for Displaying the Totalizer Value
Step
Operation
Press
Action
1
Alternating
Totalizer Display
LOWR
DISP
Until you see:
Lower Display
1 T (PV value)
Upper Display
(Total Value)
ATTENTION
When two or more
totalizers are enabled, the upper and lower
displays repeatedly cycle the PV and
totalization values for the enabled channels.
The red channel annunciator in the upper
display indicates which channel’s values are
being displayed.
2
Select and
Constantly
Display a
Totalization
Value
or
Until the desired channel indicator lights (in
this example, channel #3).
Lower Display
3 T (PV value)
Upper Display
(Total Value)
3
Return to
Alternating
Display
and
simul-
taneously
You will see:
Lower Display
SCAN
Upper Display
(Total Value)
After the keys are released, the upper
display alternately shows PV values while
lower display shows totalization values for all
enabled totalizers.
4
Return to Normal
PV Display
LOWR
DISP
Returns to normal PV display.
Model DR45AW
References
274 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
B.5 References
Summary
This information is provided for customers to review what formula the Truline Recorder
uses to calculate flow.
The selection of Weirs is V NOTCH, RECTANGULAR, or CIPOLLETTI. The Flume is
a Parshall Flume.
Flow equations
For the following equations, both height and width are measured in feet.
ATTENTION
When you configure the input on the Truline Recorder, the height and
width values entered are in inches (except if a Metric Flow Rate was selected, then the
values are in centimeters). This provides better accuracy.
V NOTCH WEIR
30 DEG Q = 0.676 H
2.5
cubic feet per second
60 DEG Q = 1.42 H
2.440
cubic feet per second
90 DEG Q = 2.49 H
2.475
cubic feet per second
120 DEG Q = 4.33 H
2.5
cubic feet per second
RECTANGULAR WEIR
Q = 3.33 (W 0.2H) H
1.5
cubic feet per second
ATTENTION
Width must be greater than three times the height.
CIPOLLETTI WEIR
Q = 3.37 W (H)
1.5
cubic feet per second
PARSHALL FLUME
Throat Width Flow (ft
3
/sec)
1 inch Q = 0.338 H
1.55
cubic feet per second
2 inches Q = 0.676 H
1.55
cubic feet per second
3 inches Q = 0.993 H
1.547
cubic feet per second
6 inches Q = 2.060 H
1.58
cubic feet per second
9 inches Q = 3.068 H
1.53
cubic feet per second
X inches Q = 4 W H(
1.522
W
0.026
) cubic feet per second
(X is greater than 12 inches)
EXAMPLE:
Customer has a 3-inch Parshall Flume and measures height as two feet. Flow is
calculated as
Q = 0.993 (2)
1.547
= 2.9 cubic feet per second
Continued on next page
Model DR45AW - References
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 275
April 2017
Reference, Continued
Flow equations,
Continued
PALMER-BOWLUS FLUME*
Type Flow (ft
3
/sec)
4 inches Q = 1.73 (H + .00588)
1.9573
6 inches Q = 2.071 (H + .005421)
1.9025
8 inches Q = 2.537 (H + .01456)
1.9724
10 inches Q = 2.843 (H + .01616)
1.9530
12 inches Q = 3.142 (H + .017)
1.9362
15 inches Q = 3.574 (H + .0168)
1.9062
18 inches Q = 3.988 (H + .01875)
1.8977
21 inches Q = 4.223 (H + .039)
1.9619
24 inches Q = 4.574 (H + .0408)
1.9497
27 inches Q = 4.97 (H + .038)
1.9269
30 inches Q = 5.022 (H + .0625)
1.9663
36 inches Q = 5.462 (H + .08)
1.991
42 inches Q = 6.12 (H + .078)
1.9628
48 inches Q = 6.626 (H + .085)
1.9586
60 inches Q = 7.183 (H + .126)
1.9833
72 inches Q = 7.839 (H + .155)
1.9871
*Equations provided by Plasti-Fab Inc.
Where:
W = Width (in feet)
Q = Flow (in cubic feet per second)
H = Height (in feet)
Model DR45AW
References
276 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 277
April 2017
C. Security Lockout
C.1 Overview
Introduction
Your recorder has a security bypass code which allows you to enter secured areas if you have forgotten or
lost the operator security code.
To use the universal password, go to the Lockout Set Up group. At PASSWORD enter 1502. This
overrides the existing password.
Be sure to re-enter a new password to lockout any unauthorized changes to the recorder’s configuration and
calibration prompts.
ATTENTION
Remove this page for security.
Note: this applies to firmware revisions: 10.52 or later, for earlier revisions, refer to doc# 44-45-33-39A
(Password Configuration Key)
Security Lockout
Overview
278 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 279
April 2017
D. Foreign Language Safety Instructions
SIKKERHESKRAV
D.1 DA2I-6056
!
For at undgå elektrisk stød med mulighed for personskade, skal alle
sikkerhedsbestemmelser i denne manual følges nøje.
Dette symbol advarer brugeren om en potentiel berøringsfare, såfremt der kan være
adgang til den livsfarlige netspænding.
Beskyttende jordterminal. Terminalen er forberedt for og skal forbindes til beskyttelses-
jordledning i henhold til stærkstrømsberkendtgørelsen (DK).
Hvis udstyret ikke bruges som specificeret i manualen, kan den beskyttelse udstyret yder blive nedsat eller
forsvinde.
Eerstat kun komponenter som udtrykkeligt er specificeret som udskiftelige i manualen.
Alle ledningsforbindelser skal følge stærkstrømsberkendtgørelsen (DK) og udføres af autoriseret erfarent
personel.
Den beskyttende jordterminal skal forbindes først af alle forbindelser (og fjernes som den sidste).
Det anbefales jvf. stærkstrømsberkendtgørelsen, at der installeres en afbryder til frosyningsspændingen nær
udstyret.
UDSTYRS SPECIFIKATIONER
Strømforsyning
102 til 132 Vac - 204 til 264 Vac
Frekvens
50 60 Hz
Nominel effekt
20 watts max.
OMGIVELSES SPECIFIKATIONER
Placer ikke udstyret i nærheden af brandbare væsker eller dampe.
Temperatur
Rumtemperatur : 0 til 55°C
Fugtighed
5 til 90% RH - 40°C
Vibration
0 til 200 Hz
acceleration 0.2 g
UDSTYRS INSTALLATION
Skriveren skal monteres i en tavle for at forhindre adgang til bagterminaler.
Foreign Language Safety Instructions
DU2I-6056
280 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
VEILIGHEIDSVEREISTEN
D.2 DU2I-6056
!
Ter vermindering van het gevaar van elektrische schokken die lichamelijk letsel kunnen
veroorzaken, dient u alle veiligheidsaanwijzingen in dit dokument te volgen.
Dit symbool waarschuwt de gebruiker voor een potentieel schokgevaar wanneer
toegang bestaat tot onderdelen die onder gevaarlijke spanning staan.
Beschermende aarde-aansluiting. Bestemd voor aansluiting van de aardingsdraad van de
voeding.
Indien de apparatuur wordt gebruikt anders dan door de fabrikant gespecificeerd, kan de bescherming, die de
apparatuur biedt ongedaan worden gemaakt.
Alleen die onderdelen mogen worden vervangen die door de fabrikant als uitwisselbaar zijn aangemerkt.
Alle bedrading moet in overeenstemming zijn met de lokale elektriciteiseisen en moet aangelegd worden door
geauthoriseerd, ervaren personeel.
De aardingsdraad moet worden aangesloten vóórdat alle andere bedrading wordt aangesloten (en als laatste
worden verbroken).
Het verdient aanbeveling een netschakelaar aan te brengen vlakbij het instrument.
APPARATUUR VOORWAARDEN
Voedingsspanning
102 tot 132 Vac - 204 to 264 Vac
Frequentie
50 60 Hz
Vermogen of
stroomvermogen
20 watts max.
OMGEVINGSCONDITIES
Gebruik het instrument niet in de aanwezigheid van ontvlambare vloeistoffen of dampen. Het gebruik van
elk elektrisch instrument in een dergelijke omgeving vormt een gevaar voor uw veiligheid.
Temperatuur
In bedrijf : 0 tot 55°C
Vochtigheid
5 tot 90% RH - 40°C
Trilling
0 tot 200 Hz
versnelling 0.2 g
MONTAGE VAN DE APPARATUUR
De recorder moet worden gemonteerd in een paneel om de toegankelijkheid tot de achterste aansluitpunten
te beperken.
Foreign Language Safety Instructions - FI2I-6056
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 281
April 2017
TURVALLISUUSMÄÄRÄYKSET
D.3 FI2I-6056
!
Noudata tämän ohjeen kaikkia turvaohjeita välttääksesi sähkötapaturman vaaraa.
Tämä merkki varoittaa käyttäjää sähköiskun vaarasta paikassa, missä voi koskettaa
vaarallisia jännitteitä.
Suojamaaliitin. Kytke maadoitsjohdin tähän liittimeen.
Jos laitetta käytetään olosuhteissa, joihin sitä ei ole suunniteltu, käyttöturvallisuus voi heikentyä.
Älä vaihda mitään komponettia tai osaa, jota valmistaja ei ole määritellyt käyttäjän vaihdettavaksi.
Asennus ja johdotus on tehtävä paikallisten varmuusmääräysten mukaisesti valtuutetun sähköasentajan
toimesta.
Ensimmäiseksi on kytkettävä suojamaa-liitin (ja viimeiseksi irroittettava).
Laitteen läheisyyteen suositellaan asennettavaksi verkkokytkin.
LAITTEEN VAATIMUKSET
Syöttöjännite
102 - 132 Vac / 204 - 264 Vac
Taajuus
50 60 Hz
Teho
20 watts
KÄYTTÖOLOSUHTEET
Älä käytä laitetta paikassa jossa on syttyviä nesteitä tai kaasuja, koska laitteen käyttö aiheuttaa
räjähdysvaaran.
Lämpötila
ympäröivä : 0 ... 55°C
Kosteus
5 ... 90% RH - 40°C
Tärinä
0 ... 200 Hz
Kiihtyvyys 0.2 g
LAITTEEN ASENNUS
Piirturi on asennettava paneeliin siten, että peräliitimille jää riittävästi tilaa.
Foreign Language Safety Instructions
FR2I-6056
282 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
CONSIGNES DE SECURITE
D.4 FR2I-6056
!
Pour réduire tout risque de décharge électrique qui pourrait provoquer une lésion
corporelle, respectez toutes les consignes de sécurité de cette documentation.
Ce symbole avertit l'utilisateur d'un risque électrique potentiel lorsqu'il peut avoir accès
à des éléments sous tension.
Borne de mise à la terre. Destinée au raccordement du conducteur de mise à la terre de
l'alimentation.
Si l'équipement est utilisé dans un but non spécifié par le constructeur, la protection fournie avec cet équipement
peut être affectée.
Aucun composant (ou pièce) ne doit être remplacé s'il n'est pas explicitement spécifié comme tel par le
constructeur.
Tous les câblages doivent être conformes aux normes locales et doivent être réalisés par un personnel autorisé et
expérimenté.
La borne de masse doit être raccordée avant tout autre câblage (et débranchée en dernier).
Il est obligatoire de connecter cet appareil sur une ligne possédant un moyen de coupure près de l'appareil.
CARACTERISTIQUES DE L'EQUIPEMENT
Tension
d'alimentation
102 à 132 Vac ou 204 à 264 Vca
Fréquence
50 60 Hz
Puissance ou
courant
20 watts max.
CONDITIONS AMBIANTES
Ne jamais utiliser cet équipement en présence de liquides ou vapeurs inflammables.
L'utilisation de tout instrument électrique dans un tel environnement pourrait présenter un risque pour la
sécurité.
Température
Ambiante : 0 à 55°C
Humidité
5 à 90 % HR à 40°C
Vibration
Fréquence : 0 à 200 Hz
Accélération 0.2 g
INSTALLATION DE L'EQUIPEMENT
Cet appareil doit être monté dans un panneau pour limiter l'accès aux bornes arrières par l'opérateur.
Foreign Language Safety Instructions - GE2I-6056
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 283
April 2017
SICHERHEITSHINWEISE
D.5 GE2I-6056
Befolgen Sie alle Sicherheitshinweise in diesen Unterlagen, um das Risiko eines
Stromschlags zu verringern, der zu Körperverletzung führen kann.
Dieses Symbol warnt den Benutzer vor eventueller Berührungsgefahr, wo
lebensgefährliche Spannungen zugänglich sein können.
Schützende Erdung. Für den Anschluß der schützenden Erdung der
Versorgungssystemleitung.
Bei Benutzung der Ausrüstungen auf nicht vom Hersteller angegebene Art und Weise kann der von der
Ausrüstung gewährleistete Schutz beeinträchtigt werden.
Ersetzen Sie keine Komponente (oder Teil), die/das nicht ausdrücklich vom Lieferanten als ersetzbar angegeben
ist.
Die gesamte Verkabelung muß den örtlichen Normen entsprechen und von zugelassenem, erfahrenem Personal
durchgeführt werden.
Die Erde muß vor allen anderen Kabeln angeschlossen (und zuletzt abgeklemmt) werden.
In der Nähe der Ausrüstung muß ein Schalter in der Hauptstromversorgung vorhanden sein.
AUSRÜSTUNGSDATEN
Netzspannung
102 bis 132 Vac oder 204 bis 264 Vac
Frequenz
50 60 Hz
Nennleistung
20 watts max.
UMGEBUNGSBEDINGUNGEN
Betreiben Sie das Gerät nicht in Gegenwart entflammbarer Flüssigkeiten oder Dämpfe. Der Betrieb
elektrischer Geräte in solchen Umgebungen stellt ein Sicherheitsrisiko dar.
Temperatur
Umgebung : 0 bis 55°C
Feuchtigkeit
5 bis 90% RH - 40°C
Vibration
0 bis 200 Hz
Beschleunigung 0.2 g
ANBRINGUNG DER AUSRÜSTUNGEN
Der Regler muß in ein Pult eingebaut sein, damit der Bediener nicht zu oft auf die hinteren Anschlüsse
zugreifen muß.
Foreign Language Safety Instructions
GR2I-6056
284 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
D.6 GR2I-6056
Foreign Language Safety Instructions - IT2I-6056
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 285
April 2017
NORME DI SICUREZZA
D.7 IT2I-6056
!
Per ridurre i rischi di scariche elettriche che potrebbero causare alle persone, seguire
tutte le precauzioni circa la sicurezza indicate in questa documentazione.
Questo simbolo avverte del pericolo di scossa elettrica nelle aree in cui sono accessibili
conduttori sotto tensione.
Terminale di protezione verso terra. Previsto per il collegamento del conduttore di
protezione verso terra del sistema di alimentazione.
Se lo strumento viene utilizzato in modo diverso dalla specifica del costruttore, la protezione fornita dallo
strumento puó essere diversa.
Non sostituire alcun componente (o parte) non specificato esplicitamente come ricambio dal vostro fornitore.
Tutti i cablaggi devono essere in accordo con i regolamenti locali e devono essere eseguiti da personale esperto
ed autorizzato.
Il terminale di massa deve essere collegato prima di ogni altro filo (e scollegato per ultimo).
E necessario che sia presente un interruttore nell’alimentazione principale accanto all’apparecchio.
ALIMENTAZIONE APPARECCHIATURA
Tensione di
alimentazione
Da 102 a 132 Vac ó da 204 a 264 Vac
Frequenza
50 60 Hz
Potenza o corrente
20 watts max.
CONDIZIONI AMBIENTALI
Non far funzionare l’apparecchio in presenza di liquidi o gas infiammabili, in quanto questo potrebbe
essere estremamente pericoloso.
Temperatura
Ambiente : da 0 a 55°C
Umidità relativa
Da 5 a 90% UR a 40°C
Vibrazioni
Da 0 a 200 Hz
accelerazione 0.2 g
INSTALLAZIONE DELL’APPARECCHIO
Il apparecchio deve essere montato su un pannello per limitare l’accesso ai terminali posteriori.
Foreign Language Safety Instructions
NO2I-6056
286 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
SIKKERHETSKRAV
D.8 NO2I-6056
!
Følg alle retningslinjene i dette dokumentet, slik at du reduserer risikoen for
elektrisk støt og mulige personskader.
Dette symbolet advarer brukeren om tilgjengelige terminaler med farlige
spenninger og en potensiell fare for elektrisk støt.
Jordingsterminal. kabelen for jording av systemet skal tilknyttes til denne
terminalen.
Dersom utstyret benyttes på en måte annerledes enn spesifisert av produsent, kan utstyrets beskyttelsesgrad
forringes.
Ingen komponenter eller deler skal skiftes ut dersom de ikke er uttrykkelig spesifisert som utskiftbare av din
forhandler.
Det er påkrevet med en hovedstrømsbryter i nærheten av utstyret.
All kabling må utføres i henhold til gjeldende forskrifter og installeres av autoriser og erfaren installatør.
Jord må tilknyttes før all annen kabling (og frakobles sist).
UTSTYRSPESIFIKASJONER
Strømtilførsel
102 til 132 Vac - 204 til 264 Vac
Nettfrekvens
50 60 Hz
Kraftforbruk
20 watts max.
OMGIVELSER
Instrumentet må ikke opereres i nærheten av lettantennelige væsker eller gasser. Bruk av elektriske
instrumenter i slike omgivelser utgjør en sikkerhetsrisiko.
Temperatur
omgivelse : 0 til 55°C
Fuktighet
5 til 90% HR - 40°C
Vibrasjon
0 til 200 Hz
akselerasjon 0.2 g
UTSTYRSINSTALLASJON
Pass på å montere panelene på regulatoren, slik at berøring av terminalene
på baksiden forhindres.
Foreign Language Safety Instructions - PO2I-6056
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 287
April 2017
INSTRUÇÕES DE SEGURANÇA
D.9 PO2I-6056
!
Para reduzir o risco de choque eléctrico que pode causar danos corporais, seguir todas
as normas de segurança contidas nesta documentação.
Este símbolo avisa o utilizador sobre um eventual perigo de choque quando são
acessíveis voltagens sob tensão perigosas.
Terminal de protecção de terra. Fornecido para ligação do condutor do sistema da
protecção de terra.
Se este equipamento for usado de modo não especificado pelo fabricante, a protecção fornecida pelo
equipamento pode não ser adequada.
Não se deve substituir qualquer componente (ou peça) que não seja explicitamente especificado como
substituível pelo nosso revendedor.
Toda a cablagem deve estar de acordo com os códigos eléctricos locais e deve ser realizada por pessoal
experiente devidamente autorizado.
O terminal de terra deve ser ligado antes de ser feita qualquer outra cabelagem (e desligado em último lugar).
Recomenda-se um comutador na fonte de alimentação principal próximo do equipamento.
ESPECIFICAÇÕES DO EQUIPAMENTO
Voltagem
102 a 132 Vac - 204 a 264 Vac
Frequência
50 60 Hz
Potência ou
consumo de
corrente
20 Watts max.
CONDIÇÕES AMBIENTAIS
Não operar o instrumento na presença de líquidos ou vapores inflamáveis. A operação de qualquer
instrumento eléctrico em tal ambiente constitui um perigo para a segurança.
Temperatura
Ambiente : 0 a 55°C
Humidade
5 a 90% RH a 40°C
Vibração
0 a 200 Hz
aceleração 0.2 g
INSTALAÇÃO DO EQUIPAMENTO
O Registrador deve ser montado num painel para limitar o acesso do operador aos terminais traseiros.
Foreign Language Safety Instructions
SP2I-6056
288 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
NORMAS DE SEGURIDAD
D.10 SP2I-6056
!
Para reducir el riesgo de choque eléctrico el cual podría causar lesiones personales,
seguir todas las indicaciones de este documento.
Este símbolo previene al usuario de un riesgo potencial de descarga cuando se puede
acceder a corrientes de tensión peligrosas.
Terminal de tierra de protección. Proporcionado para la conexión de la tierra de
protección del conductor del sistema de alimentación.
Si el equipo es utilizado de forma no especificada por el fabricante, la protección suministrada con el mismo
podría resultar dañada.
No reemplazar ningún componente (o parte) no explicitamente especificado por el suministrador.
Todo el cableado debe realizarse de acuerdo con las normas eléctricas locales y debe ser realizado por personal
experimentado.
El terminal de tierra debe ser conectado antes que cualquier otro cable y desconectado el último.
Se recomienda la instalación de un interruptor de la alimentación principal, cerca del equipo.
DATOS ELECTRICOS DEL EQUIPO
Tensión de
alimentación
102 a 132 Vac - 204 a 264 Vac
Frecuencia
50 60 Hz
Potencia o
corriente
20 watts max.
CONDICIONES AMBIENTALES
No operar con el instrumento en presencia de liquidos o gases inflamables. La operación de cualquier
equipo eléctrico en tal ambiente constituye un riesgo contra la seguridad.
Temperatura
Ambiente : 0 a 55°C
Humedad
5 a 90% RH a 40°C
Vibración
0 a 200 Hz
acceleración 0.2 g
INSTALACION DEL EQUIPO
Este equipo debe ser montado en un panel para limitar al operador el acceso a los terminales traseros.
Foreign Language Safety Instructions - SW2I-6056
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 289
April 2017
SÄKERHETSFÖRESKRIFTER
D.11 SW2I-6056
!
För att reducera riskerna av elektriska chocker som kan orsaka personskador, följ alla
säkerhetsföreskrifter i denna dokumentation.
Denna symbol varnar användaren för risk för elchock vid tillfällig åtkomst av
spänningsförande del.
Anslutning av skyddsjord. Avsedd för anslutning av elsysternets skyddsjordsledare.
Om utrustningen används på ett sådant sätt, att det inte innefattas av tillverkarens specifikation, kan de inbyggda
säkerhetsfunktionerna äventyras.
Ersätt aldrig någon komponent (eller del) som inte är specificerad som ersättningsbar av tillverkaren.
All ledningsdragning måste utföras i enlighet med lokala bestämmelser och skall utföras av behörig personal
med erfarenhet av sådant arbete.
Skyddsjordsanslutningen skall anslutas före alla andra anslutningar (och losskopplas sist).
En strömbrytare för näströmmen rekommenderas.
STRÖMFÖRSÖRJNING
Spänning
102 a 132 Vac - 204 a 264 Vac
Frekvens
50 60 Hz
Effekt eller
märkström
20 watts max.
OMGIVNINGSVILLKOR
Använd ej instrumentet i närhet av brännbara vätskor eller gaser. Användandet av instrumentet i sådant
miljö är en direkt säkerhetsrisk.
Temperatur
Omgivande : 0 till 55°C
Fuktighet
5 till 90% RH - 40°C
Vibration
0 till 200 Hz
acceleration 0.2 g
INSTALLATION
Instrumentet skall monteras i en panel eller i en låda för att undvika att personalen kommer i beröring med
bakre inkopplingsplintar.
Foreign Language Safety Instructions
SW2I-6056
290 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Release N DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 291
May 2013
Index
0
0-10 Volt dc inputs, 37
010 Volt inputs, 212
4
4-20 mA auxiliary output wiring, 52
4-20 mA control output wiring, 39
4-20 mA input wiring, 35
420 mA inputs, 213
A
AC line power, 30
Accutune II, 159
Alarm hysteresis, 79, 127
Alarm messages, 147
Alarm outputs, 45
Alarm setpoints, 162
Alarms group definitions, 126
Atmospheric pressure compensation, 82, 131
Automatic calibration mode, 223
Automatic local mode, 149
Automatic mode
Return to, 150, 184
Selecting, 149
Automatic remote mode, 149
Automatic switchover, 109
Automatic switchover value, 73, 110
Auxiliary Output, 79, 80, 84
Auxiliary output 2 and 3 calibration, 220
B
Basic recorder components without options, 248
Battery test failure, 235
Baud rate, 81
Bias, 111
Bias for remote setpoint, 73
Burnout, 65
Burnout protection, 97
C
Calibration procedure, 214
Calibration set up, 206
0-10 Volt inputs, 212
4-20 mA inputs, 213
Millivolts and Volts inputs (except 0-10 Volts), 211
RTD inputs, 210
Thermocouple inputs using a compensated calibrator
method, 208
Thermocouple inputs using an ice bath, 207
Thermocouple inputs using the ambient temperature
method, 209
CE Conformity (Europe), 1
CE Conformity special conditions, 7
CE conformity special conditions (Europe), 27
Chart high range value, 98
Chart lamp, 169
Replacing, 169
Chart low range value, 98
Chart name, 67, 69, 101
Chart plate assembly parts, 247
Chart speed selection, 67, 69
CHN indicator, 148
Circuit-breaker, 30
Cleaning, 169
Communications station address, 81, 130
Condensed specifications, 8
Configuration procedure, 62
Configuration prompts, 57
Configuration tips, 61
Control algorithm, 74, 114
Control output direction, 74, 112
Controller dropoff value, 74, 112
Current proportional output calibration, 220, 225
Current simplex, 116
Current/relay duplex, 117
Current/time duplex range, 74
Customer support, 229
Cycle time (heat), 121
Cycle time 2 (cool), 121
D
Deadband, 74, 112
Decimal point location, 64, 94
Deviation, 131
Deviation bargraph, 144
Deviation recording action, 82
Deviation setpoint value, 82, 131
Device status, 232
Diagnostic error messages, 146
Diagnostic tests, 138
Digital inputs, 45
Dimensions, 16
Direct acting control, 112
Display test, 139
Displaying totalizer value, 166
Displays, 3
Index
292 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
E
Electrical noise, 27
Emissivity, 65
Engineering units, 94
Error message
BATT LOW. See
BATTERY, 235
CAL TEST, 234
CAL1 ERR, 234
CAL2 ERR, 234
CONFTEST, 233
EE FAIL, 235
FACT CRC, 234
FAILSAFE, 233
INxFAIL, 235
PV LIMIT, 235
RAM TEST, 233
RV LIMIT, 235
SW FAIL, 235
Error message prompts, 233
Error messages, 146
Event message configuration, 83
Event pen function, 167
Event pen operation, 167
F
Factory calibration, 200
Failsafe, 231
Failsafe output value, 74
Failure symptoms, 229
Ferrite filter locations (CE Mark), 29
Field wiring, 203
Filter, 65, 97
Fo reset, 258
Fo sterilization calculation, 258
Fo sterilization time, 259
G
Gain, 120
Gain 2, 121
Gain units, 74
Grid line contrast, 136, 140
H
Hardware kit contents, 252
Header for chart, 67, 101
High output limit, 74, 112
High range value, 65, 96
High setpoint limit, 73
Hours per revolution, 100
Hysteresis, 74, 113, 127
I
Ice bath, 204
Indicators, 3
Input 1 actuation type, 64
Input actuation type, 95
Input compensation, 65, 97
Input out of range, 236
Input terminals, 203
Inputs
05 Vdc, 33
Radiamatic, mV, 33
RTD, 33
Thermocouple, 33
Installation
Operating limits, 8
Preinstallation information, 7
Installing chart, 170
Internal cabling, 253
J
Jumper positions, 205
K
Key test, 139
Knockout locations, 17
L
Local setpoint, 151
Local setpoint, 110
Lockout, 86, 87, 134
Lockout password, 86, 87
Low flow cutoff selection, 65
Low output limit, 74, 112
Low range value, 65, 97
Low setpoint limit, 73
M
Maintenance, 169
Manual calibration mode, 223
Manual mode, 149
Adjusting output, 150, 151, 183, 184
Selecting, 150
Manual reset, 120
Minutes per repeat, 114
Monitoring your recorder, 142
Motor traverse time, 223
Mounting
Overall dimensions, 16
Mounting methods, 17
2-inch pipe, 24
Flush in panel, 18, 20
Flush in panel, 21
NEMA4X door, 22
Surface, 25
Index
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 293
April 2017
O
ON/OFF algorithm, 114
Operating limits, 8
Operating modes, 149
Operating parameters, 145
Operator functions, 148
Operator interface, 3, 142
Output algorithm, 74, 116
Output wiring for alarms 3 and 4, 47
Output wiring for alarms 5 and 6, 48
P
Parts lists, 245
Password, 134
PD with manual reset, 115
Pen Set Up group, 66
Pen tip, 169
Cleaning, 169
Physical considerations, 16
PID A, 115
PID B, 115
PID sets, 158
Pipe mounting, 24
Polynomial Equation, 107
Position proportional control output wiring, 41
Position proportional output calibration, 222
Position proportional simplex, 117
Power loss, 172
Power supply mains, 30
Power up controller mode recall, 73, 111
Power up diagnostic tests, 138
Power-up tests, 231
Printing characteristics adjustments, 135, 217
Prompt hierarchy, 57
Proportional band, 120
Proportional band 2, 121
Proportional band units, 113
R
Radiamatic, millivolts, and volts inputs (except 010
Volts), 211
Ramp/soak program, 123
Rate 2, 121
Rate action, 120
Rate of integration, 70, 105
Ratio, 110
Ratio for remote setpoint, 73
Recorder components associated with options, 250
Recovery from a power loss, 172
RECYCL parameter, 185
Rejection frequency, 79, 82, 84, 131
Relative humidity, 82, 131
Relay control output wiring, 43
Relay duplex, 117
Relay/current duplex, 117
Remote chart activation, 68, 102
Remote setpoint, 110
Remote switching, 164
Repeats per minute, 114
Replacing chart, 170
Reset, 120
Reset 2, 121
Reset units, 74, 114
Resetting totalizer value, 165
Resistance equivalent, 202
Restoring factory calibration, 200
Reverse acting control, 112
RS485 Modbus communications wiring, 50
RSP, 152
RTD inputs, 210
S
Safety Requirements for Electrical Equipment, 27
Self diagnostics, 229
Setpoint high limit, 112
Setpoint low limit, 112
Setpoint program
profiles set-up, 187
Setpoint Program
Data entry, 183
event setup, 192
overview, 173
ramp setup, 185
run/monitor functions, 196
segment setup, 189
Setpoint ramp, 122
Configuring, 153
Running, 154
Setpoint ramp final setpoint, 123
Setpoint ramp time, 123
Setpoint selection indication, 152
Setpoint source, 73, 110, 151
Setpoint tracking, 73, 111
Set-up tasks, 5
Shield wiring, 29
Single setpoint ramp, 122, 153
SOKDEV parameter, 185
SPPROG parameter, 185
Start up, 139
Stylus, 136, 140
Suppression filters, 29
Switchover value, 157
T
Temperature units, 64, 94
Thermal resistance, 259
Thermocouple inputs using a compensated calibrator
method, 208
Thermocouple inputs using an ice bath, 207
Thermocouple inputs using the ambient temperature
method, 209
Three position step control output wiring, 41
Time division, 101
Time parameters group definitions, 103
Totalizer, 70
Totalizer group definitions, 104
Totalizer reset, 70, 73
Index
294 DR4500A Truline Circular Chart Recorder With or Without Control Product Manual Release P
April 2017
Totalizer scale factor, 70, 73
Totalizer value, 165
Displaying, 166
Resetting, 165
Trace line contrast, 136, 140
Transmitter characterization, 65, 96
Troubleshooting procedures, 238
Ttransmitter power, 35
Tuning constants, 156
Tuning group prompt definitions, 119
Tuning messages, 147
Tuning parameter sets, 73, 109
Two local setpoints, 110
Two sets of tuning constants, 156
V
Visual failure symptoms, 229, 237
Voltage equivalent, 202
W
Wake time days, 103
Wake time hours, 103
Wake time minutes, 103
Wake time months, 103
Wire bundling, 28
Wiring
0-10 Vdc inputs, 37
0-5 Vdc inputs, 33
4-20 mA auxiliary output, 52
4-20 mA control output, 39
4-20 mA inputs. See
AC line power. See
Electrical noise precautions, 27
mV inputs, 33
Position proportional control output, 41
Radiamatic inputs, 33
Relay control output, 43
RS485 Modbus communications, 50
RTD inputs, 33
Shields, 29
Thermocouple inputs, 33
Three position step control output, 41
Transmitter power. See
Wire bundling, 28
Wiring the recorder, 29
Wiring for PV inputs, 206
0-10 Volt inputs, 212
4-20 mA inputs, 213
Millivolts and Volts inputs (except 0-10 Volts), 211
RTD inputs, 210
Thermocouple inputs using a compensated calibrator
method, 208
Thermocouple inputs using an ice bath, 207
Thermocouple inputs using the ambient temperature
method, 209
Error! Cannot open file referenced on page 5
Index
Release P DR4500A Truline Circular Chart Recorder With or Without Control Product Manual 295
April 2017
For more information
To learn more about SmartLine Transmitters,
visit www.honeywellprocess.com
Or contact your Honeywell Account Manager
Process Solutions
Honeywell
1250 W Sam Houston Pkwy S
Houston, USA, TX 77042
Honeywell Control Systems Ltd
Honeywell House, Skimped Hill Lane
Bracknell, England, RG12 1EB
44-45-25-30 Rev.P
April 2017
2017 Honeywell International Inc.
Shanghai City Centre, 100 Jungi Road
Shanghai, China 20061
www.honeywellprocess.com
Sales and Service
For application assistance, current specifications, pricing, or name of the nearest Authorized Distributor, contact one
of the offices below.
ASIA PACIFIC
Honeywell Process Solutions,
Phone: + 800 12026455 or
+44 (0) 1202645583
(TAC) hfs-tac-
support@honeywell.com
Australia
Honeywell Limited
Phone: +(61) 7-3846 1255
FAX: +(61) 7-3840 6481
Toll Free 1300-36-39-36
Toll Free Fax:
1300-36-04-70
China PRC - Shanghai
Honeywell China Inc.
Phone: (86-21) 5257-4568
Fax: (86-21) 6237-2826
Singapore
Honeywell Pte Ltd.
Phone: +(65) 6580 3278
Fax: +(65) 6445-3033
South Korea
Honeywell Korea Co Ltd
Phone: +(822) 799 6114
Fax: +(822) 792 9015
EMEA
Honeywell Process Solutions,
Phone: + 800 12026455 or
+44 (0) 1202645583
Email: (Sales)
FP-Sales-Apps@Honeywell.com
or
(TAC)
hfs-tac-support@honeywell.com
AMERICAS
Honeywell Process Solutions,
Phone: (TAC) (800) 423-9883
or (215) 641-3610
(Sales) 1-800-343-0228
Email: (Sales)
FP-Sales-Apps@Honeywell.com
or
(TAC)
hfs-tac-support@honeywell.com
Specifications are subject to change without notice.